PRODUCT DATA
60-2485-8® U.S. Registered TrademarkCopyright © 2001 Honeywell � All Rights Reserved
T874 Multistage Thermostatsand Q674 Subbases
APPLICATIONThese thermostats and subbases provide low voltage control of multistage heating and cooling systems, including heat pump systems.
FEATURES� T874 Thermostat has silent, dust-free mercury
switches operated by coiled bimetal elements.� Heat anticipator(s) are adjustable or fixed cooling
anticipator(s) are fixed.� Individual heat and cool levers and scales (most
models) for temperature setting located on top of thermostat case.
� Cover thermometer on most T874 Multistage Thermostat models.
� Locking cover and locking lever screws available for T874 Multistage Thermostats.
� Versaguard� Thermostat Guard or custom key lock thermostat guards available for T874 Multistage Thermostats.
� T874 Thermostat requires a Q674 Subbase.� Q674 Subbase provides system and fan switching,
wiring terminals and mounting base for T874 Multistage Thermostat.
� Adapter plate available for mounting Q674 on wall or horizontal outlet box.
� Light-emitting diodes (LEDs) located on subbase for easy reference.
� Up to three stages each of heating and cooling control possible.
� Models with setpoint restrictions and locking cover with no thermometer available for Department of Defense (DoD) and other special applications.
� Outdoor reset used on some models to improve thermal performance.
Contents Application . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 1 Features . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 1 Specifications . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 2 Ordering Information . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 2 Installation . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 7 Settings . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 11 Checkout . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 13 Calibration . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 14 Understanding Circuits . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 14 Operation . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 21 Cross Reference . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 29 Wiring Diagrams . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 96
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 2
ORDERING INFORMATIONWhen purchasing replacement and modernization products from your TRADELINE® wholesaler or distributor, refer to the TRADELINE® Catalog or price sheets for complete ordering number.
If you have additional questions, need further information, or would like to comment on our products or services, please write or phone:
1. Your local Home and Building Control Sales Office (check white pages of your phone directory).2. Home and Building Control Customer Relations
Honeywell, 1885 Douglas Drive NorthMinneapolis, Minnesota 55422-4386 (800) 328-5111
In Canada�Honeywell Limited/Honeywell Limitée, 35 Dynamic Drive, Scarborough, Ontario M1V 4Z9.International Sales and Service Offices in all principal cities of the world. Manufacturing in Australia, Canada, Finland, France, Germany, Japan, Mexico, Netherlands, Spain, Taiwan, United Kingdom, U.S.A.
SPECIFICATIONSIMPORTANT
The specifications given in this publication do not include normal manufacturing tolerances. Therefore, this unit may not exactly match the listed specifica-tions. This product is tested and calibrated under closely controlled conditions, and some minor differ-ences in performance can be expected if those con-ditions are changed.
Super Tradeline®/Tradeline® ModelsSUPER TRADELINE controls offer features not available on TRADELINE or standard models, and are designed to replace a wide range of Honeywell and competitive controls.
TRADELINE models are selected and packaged to provide ease of stocking, ease of handling, and maximum replacement value. Specifications of SUPER TRADELINE and TRADELINE controls are the same as those of standard models except as noted below.
Super Tradeline ModelsT874 THERMOSTATT874D Thermostat. Provides two stages of heating and two
stages of cooling. Use with Q674A-F Subbases.Y594D (T874D/Q674E/TG504A) Thermostat/Subbase/key
lock cover package. Provides two stages of heating and two stages of cooling. Includes a key lock cover for setpoint protection.
Y594G (T874G/Q674F) Thermostat/Subbase package for heat pump. Provides two stages of heating and one stage of cooling. Automatic changeover in heat or cool mode. Available in beige or Premier White® color.
Y594R (T874R/Q674L) Thermostat/Subbase package for heat pump. Provides two stages of heating and one stage of cooling. Manual changeover in heat or cool mode. Avail-able in beige or Premier White® color.
SUPER TRADELINE FEATURES:� SUPER TRADELINE package with cross reference label
and special instruction sheet.� SUPER TRADELINE model supplied with locking lever and
locking cover accessories.� Includes adjustable temperature locking stops.� T874D replaces T874A-F TRADELINE or standard models.
Tradeline ModelsT874 THERMOSTAT� T874 TRADELINE models provide staged heat and/or cool
operation. See Table 1.
Table 1. Heating and Cooling Stages.
� T874A-F are standard models.
TRADELINE FEATURES:� TRADELINE package with cross reference label and
special instruction sheet.� T874A,C model available with factory stops for DoD
applications.� T874A,C model available with adjustable temperature
locking stops.
Q674 SUBBASEQ674 switching subbases provide system and fan switching. See Table 2.
Table 2. System and Fan Switching.
TRADELINE FEATURE:� TRADELINE package with cross reference label and
special instruction sheet.� Q674A-E,G are standard (non-heat pump) models.
Q674F,J,L are heat pump models.
Models A B C D E FHeating Stages 1 1 2 2 � 2Cooling Stages 1 2 1 2 2 �
Q674 System FanA Heat-Auto-Cool Auto-OnB Heat-Off-Cool Auto-OnC Off-Auto Auto-OnD None NoneE Off-Heat-Auto-Cool Auto-OnF Em. Ht.-Off-Heat-Auto-Cool Auto-OnG Off-Auto NoneJ Em. Ht.-Auto-Off Auto-OnL Em. Ht.-Heat-Off-Cool Auto-On
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
3 60-2485�8
Standard ModelsT874 THERMOSTATS
Models: See Table 3.
Electrical Rating: 24 to 30 Vac.
Switching: Coiled bimetal elements operate mercury switches.
Temperature Adjustment: Heating and cooling setting levers, with separate scales located on top of thermostat base. Common lever for heating and cooling on T874R; one cooling lever on T874E,V; and one heating lever on T874F,Q.
Dimensions: See Fig. 1.
Temperature: Scale Range: 42° to 88°F (6° to 31°C) stan-dard; optional ranges available.
Thermometer Range: 42° to 88°F (6 to 31°C)
Changeover Differential: 4°F (2°C) minimum between heat-ing and cooling (5°F [3°C] on T874W). Levers can be set apart for greater separation.
Interstage Differential:Standard Models: Mechanical differential is 1°F (0.6°C)
between heating or cooling stages; operating differential is approximately 1.9°F (1°C) between stages in heating or cooling.
Special Models: See Table 3.
Finish: Beige or Premier White® finish.
Mounting Means: T874 Multistage Thermostat mounts on Q674 Subbase. Subbase mounts horizontally on wall or outlet box. Mounts on vertical outlet box with optional 193121A Adapter Plate Assembly.
Fig. 1. T874 Thermostat and Q674 Subbase dimensions in in. (mm).
Optional Specifications (T874 Only):Temperature scale ranges are 40° to 75°F (4° to 24°C) heat-
ing and 75° to 90°F (24° to 32°C) cooling with stop; 44° to 68°F (7° to 20°C) heating, 80° to 86°F (27° to 30°C) cool-ing; 6° to 29°C (43° to 85°F) Celsius scale; 3° to 22°C (38° to 72°F) and 26° to 32°C (78° to 90°F) cooling with stop.
Nonadjustable factory-added stop limits heating setpoint to 72°F (22°C) maximum and cooling setpoint to 78°F (26°C) minimum.
OEM customer personalization.Locking cover and locking lever (see Thermostat Accesso-
ries).Thermostat cover without thermometer.Adjustable locking temperature stops.Voltage heat anticipation for first or second stage heat or both.
See Table 3.Fast cycling on heating stage(s) for electric heat applications.C815A Outdoor Thermistor for improved performance on
specified models.
Thermostat Accessories:Locking Cover and Locking Lever Assembly: Part no.
194559R with thermometer; 194559S without thermome-ter. See Fig. 2. Includes cover, screws, and Allen wrench for locking cover. The screws must be used to assure proper operation.
Adjustable Lever Stop: Part no. 4074ECK; includes lever stop and screws.
Universal Versaguard� Thermostat Guard: Includes wall-plate, ring base, guard cover, tumbler lock, two keys and optional Honeywell logo insert. Double-wall construction provides extra measure of tamper-resistance. Tamper-resistant lock; key cannot be removed without being in locked position. Vents in guard base allow airflow for opti-mum thermostat performance. See form 68-0104 for more information.
� TG511A1000: Clear cover.� TG511B1008: Opaque cover.� TG511D1004: Painted steel (off-white) cover. See
Fig. 2.
M5849
FANAUTO ON OFF EM. HT. HEAT AUTO COOL
(38)
(87)
SUBBASETHERMOSTAT MOUNTED
ON SUBBASE
SIDE
50 60 70 80
50 60 70 80 50 60 70 80HEAT COOL
FANAUTO ON OFF EM. HT. HEAT AUTO COOL
(89)
FRONT
2-3/16 (56)
1-7/8 (48)
3-1/2
5-1/8 (130)
1-1/2
3-9/32 (83)
3-7/16
3/8 (10)
5-5/8 (143)
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 4
Key Lock Cover: Part no. TG504A replaces existing T874 cover. Mounts on T874 base and covers thermostat settling levers and subbase switches. Includes LED window and two keys. Should not be used with 193121A Adapter Plate.
� TG504A1025: Blank face, internal thermometer.� TG504A1033: External thermometer. See Fig. 2.
Fig. 2. T874 Thermostat accessories.
Table 3. T874 Thermostat Specifications.
Models and Options Replaces ApplicationsSystem Stages
AnticipationHeating (Adj) Cooling (Fixed)
Heat Cool Other Stage 1 Stage 2 Stage 1 Stage 2T874A�Standard and TRADELINE®.� 72°F/78°F (22°C/26°C)setpoint
stops with locking cover.� Adjustable anticipator set 0.4A.� Adjustable locking temperature
stops (TRADELINE®).� 72°F/78°F (22°C/26°C) setpoint
stops with locking cover, no thermometer (for DoDa).
T872A Standard 1 1 � 0.1-1.2A � 0-1.5A �
T874B�Standard and TRADELINE. T872B Standard 1 2 � 0.1-1.2A � 0-1.2A 0-1.0AT874C�Standard and TRADELINE.� 72°F/78°F (22°C/26°C)set stops
with locking cover, no thermometer (for DoDa).
� 12°F (7°C) differential between H1 and H2 stages (T874C1125).
T872C Standard 2 1 � 0.1-1.2A 0.1-1.2A 0-1.5A �
� Fast cycling. 0.12-0.6A
0.12-0.6A
T874D�Standard and SUPER TRADELINE®.� Adjustable locking temperature
stops (SUPER TRADELINE).
T872D Standard 2 2 � 0.1-1.2A 0.1-1.2A 0-1.2A 0-1.0A
T874E�Standard and TRADELINE. T872E 2-Stage Cool � 2 � � � 0-1.2A 0-1.0AT874F�Standard and TRADELINE.� Locking cover.
T872F 2-Stage Heat 2 � � 0.1-1.2A 0.1-1.2A � �
a Department of Defense.b Changeover stage operates with heating.c Fixed voltage type anticipation.d Changeover stage operates with heating; a secondary changeover is provided in cooling switch.e Provides night setback used with standard T874 and timer-operated remote switching.f Manual changeover stage�use Q674B,L subbase.g Changeover stage operates with cooling.Q674 Subbases
194559R Locking Coverwith Thermometer
Allen Wrench
TG511D1004 IncludesPainted Steel Cover,
Opaque Base and Wallplate
TG504A1033 Key LockCover with External
Thermometer
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
5 60-2485�8
Models: See Table 4.
Electrical Ratings:Switch Contacts: 2.5A at 30 Vac (7.5A inrush).LED Lights (Optional): 30 Vac.
Switches: Two slide switches (one switch on Q674G and K; no switches on Q674D) operated by levers. Switch position is shown on scaleplate.
Mounting: Designed to mount horizontally on an outlet box or the wall. Adapter plate assembly available for mounting on a vertical outlet box (see Subbase Accessory).
Finish: Dark brown or gray.
Dimensions in in. (mm): 3-1/2 (89)height; 5-5/8 (143) width; 5/16 (8) depth. See Fig. 1.
Table 4. Q674 Subbase Specifications.
� Fast cycling. Electric Heat 0.12-0.6A
0.12-0.6A
T874G�Heat pump, cool changeover, with fast cycling.
T872G Heat Pump or Standard
2 1 1b 0-1.0Ac 0.1-1.2A 0-1.0A �
� Fixed anticipator for H2. 0.1-1.5A� Fast cycling. 0.12-
0.6AT874H�Use with Q674C. T872H Heat Pump or
Standard1 1 1b 0-1.0Ac � 0-1.0A �
T874J�Heat pump. None Heat Pump 2 1 2d 0-1.0Ae 0-1.5Ac 0-1.0Ac �
T874K�Heat pump. None Heat Pump 2 1 1b 0.1-1.2A 0-1.5Ac 0-1.5A �
T874L�Heat pump. None Heat Pump 2 1 � 0.1-1.2A 0.1-1.2A 0-1.5A �T874N�Heat pump, heat changeover.
T872N Heat Pump 2 1 1b 0.1-1.2A 0.1-1.2A 0-1.0A �
T874P�Heat pump. None Heat Pump 2 1 � 0.1-1.2A 0.1-1.2A 0-1.5A �T874Q�Night setback heating. T872Q Standard 1e � � 0.1-1.2A � � �
T874R�Heat pump. T872R Heat Pumpf 2 1 � 0-1.5Ac 0.1-1.2A 0-1.5A �
T874S�Two-speed compressor heat pump.
None Heat Pump 2 2 1g 0-1.2Ac 0-1.2Ac 0-1.2A 0-1.0A
T874V�Standard. None Standard � 1 � � � 0-1.5A �T874W�Heat pump and standard.� Night setback heating.
T872W Heat Pump or Standard
3 2 � 0-1.2Ab 0-1.2Ac,d 0-1.2A 0-1.0A
a Department of Defense.b Changeover stage operates with heating.c Fixed voltage type anticipation.d Changeover stage operates with heating; a secondary changeover is provided in cooling switch.e Provides night setback used with standard T874 and timer-operated remote switching.f Manual changeover stage�use Q674B,L subbase.g Changeover stage operates with cooling.Q674 Subbases
Models and Options Replaces ApplicationSwitch Positions
Use WithSystem FanQ674A�Standard and TRADELINE®.� Indicator LEDs.
Q672A Standard HEAT-AUTO-COOL AUTO-ON T874A-D
Q674B�Standard and TRADELINE. Q672B Standard HEAT-OFF-COOL AUTO-ON T874A-D� Provision for fan relay operation from Heat Pump T874G,H,L,R
external fan switch (isolate G terminal). OVERRIDE-HEAT- AUTO-ON T874P� Indicator LEDs. OFF-COOLQ674C�Standard and TRADELINE. Q672C Standard OFF-AUTO AUTO-ON T874A-H,W� Indicator LEDs. Heat Pump OVERRIDE-AUTO- AUTO-ON T874K,L,N
OFF T874PQ674D�Standard and TRADELINE.� For use when subbase switching is not
required.
Q672D Standard None None T874A-F
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 6
Optional Specifications (Q674 Only): Models available with up to four LEDs; for example, LEDs can
show EM. HT, AUX. HT, SERVICE, CHECK, FILTER, and LOCKOUT. See Fig. 3.
System switching marked HEAT-OFF/RESET-COOL for sys-tems requiring impedance relay reset. Available on Q674B only.
G terminal isolated on heating to provide fan relay operation from external low voltage fan switch (Q674B only).
Auto fan operation on both heat and cool.
L terminal is used for system monitoring devices.Common R terminal for heating/cooling.Changeover in cool or heat mode for heat pumps.Auto fan in EM.HT. for heat pumps.
Subbase Accessory: 193121A Adapter Plate Assembly for mounting on vertical outlet box. Assembly includes adapter ring and cover plate. Use to cover wall marks from replaced thermostat.
Fig. 3. Heating, cooling levers and system LED indicators.
Q674E�Standard and TRADELINE. Q672E Standard OFF-HEAT-AUTO-COOL
AUTO-ON T874A-D
Q674F�Two LED models.� EM.HT. light.
Q672F Heat Pump OFF-EM.HT.-HEAT-AUTO-COOL
AUTO-ON T874C,D,G,N,S
� Provision for AUTO fan operation in EM.HT.
OFF-COOL-AUTO-HEAT-EM.HT.
AUTO-ON
Q674G�O and B terminals. Q672G Standard OFF-AUTO None T874A-FQ674J�Provision for AUTO fan operation Q672J Heat Pump EM.HT.-AUTO-OFF AUTO-ON T874A,D,G,Jin EM.HT. EM.HT.-ON-OFF AUTO-ON� Provision for outdoor thermistor. SUPL.HT.-ON-OFF AUTO-ONQ674K�Standard. Q672K Standard OFF-HEAT-AUTO-
COOLNone T874F
OFF-WOOD-WOOD/OIL-OIL
None
Q674L�Provision for AUTO fan operation in EM.HT.
Q672L Heat Pump EM.HT.-HEAT-OFF-COOL
AUTO-ON T874R,W
� Indicator LEDs. SUPL.HT.-HEAT-OFF-COOL
AUTO-ON
Q674N�Standard. Q672N Evaporative Cooler
EVAP-COOL-OFF-HEAT
AUTO-ON T874C
Q674P�Standard. Q672P Heat Pump SUPL.HT.-HEAT-COOL
AUTO-ON T874G
Q674Q�Standard. None Fan Coil HEAT-OFF-COOL LO-MED-HI-ON
T874A
Q674R�Standard.� International symbols.
None Fan Coil OFF-COOL LO-HI-CONT.
T874V
Q674S�Indicator LED. None Standard HEAT-COOL None T874C
T874 Thermostat withOne Setpoint Lever
Q674 Subbasewith Four LEDs
T874 Thermostat with Separate
Heating and Cooling Levers
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
7 60-2485�8
MERCURY NOTICEThis control contains mercury in a sealed tube. Do not place control in the trash at the end of its useful life.
If this control is replacing a control that contains mercury in a sealed tube, do not place your old control in the trash.
Contact your local waste management authority for instructions regarding recycling and the proper disposal of this control, or of an old control containing mercury in a sealed tube. If you have questions, call the Honeywell Customer Response Center at 1-800-468-1502.
INSTALLATION
When Installing this Product�1. Read these instructions carefully. Failure to follow them
could damage the product or cause a hazardous condi-tion.
2. Check the ratings given on the product to make sure the product is suitable for your application.
3. Installer must be a trained, experienced service techni-cian.
4. After installation is complete, check out product opera-tion as provided in these instructions.
CAUTIONHazardous Voltage.Can damage heating/cooling system.
1. Disconnect power supply before beginning instal-lation to prevent electrical shock or equipment damage.
2. Do not short across coil terminals on relay. This can burn out thermostat heat anticipator.
3. To prevent interference with the thermostat link-age, keep wire length to a minimum and run wires as close as possible to the subbase.
4. Do not overtighten thermostat captive mounting screws because damage to subbase threads can result.
IMPORTANTAn incorrectly leveled thermostat will cause the tem-perature control to deviate from setpoint. It is not a calibration problem.
LocationInstall the thermostat about 5 ft (1.5m) above the floor in an area with good air circulation at average temperature.
Do not mount the thermostat where it can be affected by:� drafts or dead spots behind doors, in corners or under
cabinets.� hot or cold air from ducts.� radiant heat from the sun, fireplace, or appliances.
� concealed pipes and chimneys.� unheated (uncooled) areas such as an outside wall behind
the thermostat.
Mount SubbaseThe subbase can be mounted on a vertical outlet box, horizontal outlet box or directly on the wall.
1. If the subbase is mounted on a vertical outlet box, order Honeywell part no. 193121A Adapter Assembly. See Fig. 4. The assembly includes an adapter ring, two screws and a cover plate to cover marks on the wall. Install the ring and cover plate on the vertical outlet box.
NOTE: For a wall installation, hold subbase in position and mark holes for anchors. See Fig. 5. Wall anchors must be obtained from local hardware store. Be care-ful that the wires do not fall back into the wall open-ing. Set aside subbase. Drill four 3/16 in. (4.8 mm) holes and gently tap anchors into the holes until flush with the wall.
2. Pull wires through the cover plate (if used) and subbase cable opening. See Fig. 6.
3. Secure the cover plate (if used) and subbase with the screws provided. Do not fully tighten the subbase screws.
Level the subbase using a spirit level, see Fig. 7, and firmly tighten subbase mounting screws. The subbase mounting holes provide for minor out-of-level adjustments.
Fig. 4. Installing Q674 Subbase on outlet box.
M6009
VERTICAL OUTLETBOX
ADAPTERRING
COVER PLATE
MOUNTINGSCREWS (2)
1
SUBBASE
SUBBASEMOUNTING SCREWS (2)
HORIZONTALOUTLETBOX
1
22
1 NOT INCLUDED WITH UNIT.
2 ACCESSORY PART AVAILABLE (193121A).
THERMOSTAT
CAPTIVEMOUNTING SCREWS (2)
50 60 7
0 80
50 60 7
0 80
HEAT
COOL THERMOSTAT COVER
50 60 7
0 80
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 8
Fig. 5. Installing Q674 Subbase on wall.
Fig. 6. Subbase components and leveling procedure.
Wire SubbaseDisconnect power supply before beginning installation to prevent electrical shock or equipment damage.
All wiring must comply with local electrical codes and ordinances.
IMPORTANTUse 18 gauge, solid-conductor wire whenever possi-ble. If using 18 gauge stranded wire, no more than 10 wires can be used. Do not use larger than 18 gauge wire.
Follow equipment manufacturer wiring instructions when available. To wire subbase, proceed as follows:
1. Connect the system wires to the subbase as shown in the applicable diagram. A letter code is located near each terminal for identification. Typical terminal desig-nation and wiring connections are listed in Table 5. The terminal barrier permits straight or wraparound wiring connection. See Fig. 7. The subbase can require one or more jumpers that may or may not be factory-supplied. See Fig. 8 and the wiring diagrams for specific terminals to be jumpered.
Fig. 7. Barrier configuration.
CAUTIONEquipment Damage Hazard.Never install more than one wire per terminal unless using factory-supplied jumper with spade terminal.
2. Firmly tighten each terminal screw. 3. Fit wires as close as possible to the subbase. Push
excess wire back into the hole.4. Plug hole with nonflammable insulation to prevent drafts
from affecting the thermostat.
WIRES THROUGHWALL OPENING
WALL
WALLANCHORS(2)
SUBBASEMOUNTINGSCREWS (2)M926
MOUNTINGHOLES
SPIRIT LEVEL
M927
WIRINGTERMINAL
THERMOSTATCABLE OPENING
TO SPRING FINGER CONTACTS ON THE THERMOSTAT (UP TO 12)
MOUNTINGHOLES (4)
POST FORMOUNTING THERMOSTAT (2)
FOR STRAIGHTINSERTION–STRIP 5/16 IN. (8 MM)
FOR WRAPAROUND–STRIP 7/16 IN. (11 MM)
SUBBASE TERMINAL SCREW M928
BARRIER
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
9 60-2485�8
Fig. 8. Jumper adjacent terminals for special system hookup using stripped wire 3/4 in. (19 mm). For nonadjacent terminals and using jumper wire supplied with subbase.
Table 5. Terminal Designationsa
Standard Terminal Designation
Alternate Designations or Customer Specials Typical Connection
B Heating damper motor; changeover valveE K Emergency heat relayG F Fan relay coilL System monitorO R Cooling damper motor; changeover valveR V Power connection to transformer (internally connected for heating
and cooling)RC Power connection to cooling transformerRH Power connection to heating transformerW1 H1, R3 Stage 1 heating controlW2 H2, Y, R4 Stage 2 heating controlW3 Stage 3 heating controlb
Y1 C1, M Stage 1 cooling controlY2 C2 Stage 2 cooling controlY3 Stage 3 cooling controlX X1,X2,C Clogged filter switch or common connectionT A Outdoor thermistor
L, C, H HSII control panelP DefrostO Momentary circuit, changeover
A, A1, A2, Z, C, L LEDsa Other terminal designations can be used that are not listed on this table. Refer to the hookup drawing and internal schematic
for exact connections.b W3 controls the auxiliary heat like W2, and allows adding additional stages of auxiliary heat with outdoor thermostats while
maintaining the proper second stage anticipation.
M5899
1
1
1 TWO ADJACENT TERMINALS SHOWN JUMPERED ARE FOR EXAMPLE ONLY. COMPARE WIRING DIAGRAM AND SUBBASE TO IDENTIFY TERMINALS TO BE JUMPERED.
JUMPER WIRE(SUPPLIED WITH SOME MODELS)
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 10
Outdoor DisconnectThe National Electrical Code requires the installation of a disconnect switch within sight of the outdoor unit of an air conditioner or heat pump. The switch is for the safety of any technician working on the unit. The technician can assure that the unit remains unpowered.
Install and Adjust Stop BracketsThe stop brackets should be installed only if there is a need to restrict the adjustable range of the heating and cooling temperature setpoint levers. If adjustable lever stops are desired, order 4074ECK Envelope Assembly, which contains two adjustable lever stop brackets, one brass insert, one
mounting screw and two locking screws with insulated heads. When installed, the stop brackets limit the movement of the T874 HEAT and COOL levers.
TO INSTALL:1. Remove the thermostat cover by pulling the bottom
edge of the cover upward until it snaps free of the mounting slots.
2. Turn to the back of the T874 Thermostat. Locate the hole for the brass insert in the plastic base below the LED window.
3. Push the brass insert into the hole with finger.4. Turn to the front of the T874 Thermostat.5. Place the two stop brackets in position with the tabs in
the slot between the HEAT and COOL levers. See Fig. 9.
Fig. 9. Range limiting and lever locking methods.
6. Insert the mounting screw into the two slots in the stop brackets and attach to the brass insert. Tighten the screw to pull the brass insert into the back of the ther-
mostat.7. Loosen the mounting screw enough to free the stop
brackets for adjustment.
T External temperature readout, T relayR1, R2 LO and HI speed fan relays
RS Cooling contactorY M Compressor contactor
Table 5. Terminal Designationsa
Standard Terminal Designation
Alternate Designations or Customer Specials Typical Connection
a Other terminal designations can be used that are not listed on this table. Refer to the hookup drawing and internal schematic for exact connections.
b W3 controls the auxiliary heat like W2, and allows adding additional stages of auxiliary heat with outdoor thermostats while maintaining the proper second stage anticipation.
HEATLEVER
HOLES FOR INSULATEDLOCKING LEVER SCREWS
COOLLEVER
HOLE WITHBRASS INSERT
BRACKETTABS
ADJUSTABLELEVER STOPBRACKETS BRACKET
SLOTS
MOUNTING SCREW
ADJUSTABLE STOPS
ADJUSTABLE LOCKING LEVERS
NONADJUSTABLE STOPSWITH LOCKING LEVER SCREWS75°F (24°C) MAX. HEAT75°F (24°C) MIN. COOL
NONADJUSTABLE D.O.D. STOPS72°F (22°C) MAX. HEAT78°F (26°C) MIN. COOL
M7626
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
11 60-2485�8
8. Move the HEAT and COOL levers to the maximum tem-perature desired.
9. Slide the stop brackets until one rests against the HEAT lever and the other against the COOL lever.
10. Firmly tighten the mounting screw.11. If the HEAT and COOL levers are to be locked in place
at a specific temperature, use the two insulated head screws supplied instead of the two adjustable lever stop brackets.
CAUTIONEquipment Damage Hazard.Do not use standard screws that provide metal-to-metal contact with the stop brackets. Short circuit and potential equipment damage can result.
Mount Thermostat1. Remove the thermostat cover by pulling the bottom
edge of the cover away from the base until it snaps free of the cover clip.
NOTE: The cover is hinged at the top and must be removed by pulling up at the bottom.
2. Carefully remove and discard the polystyrene packing insert that protects the mercury switches during ship-ment.
3. If LED indication (EM.HT., CHECK, etc.) is to be used with the Q674 Subbase, install the preprinted insert under the thermostat setpoint scale. To install, push both thermostat setpoint levers to the far ends of the thermostat. Use index finger to gently pull out the plastic setpoint scale about 1/4 in. (6 mm). Position the desired preprinted insert in the space above the LED lights. Reposition setpoint levers.
4. Turn over the thermostat base and note the spring fin-gers that engage the subbase contacts. Make sure the spring fingers are not bent flat, preventing proper elec-trical contact with the subbase.
5. Set the heat anticipator indicator(s) to the respective current setting of each stage. See Set The Heat Antici-pator section.
6. If the thermostat provides optional locking cover assem-bly, start the Allen locking screws in the cover with the wrench provided. See Fig. 10.
7. Note the two tabs along the top inside edge of the ther-mostat base. The tabs fit into corresponding slots on top of the subbase. Mount the thermostat on the subbase.
8. Align the two captive mounting screws in the thermostat base with the posts on the subbase. Tighten both screws. Do not overtighten screws or damage to sub-base posts can result.
Fig. 10. Installation of locking cover assembly.
SETTINGS
CAUTIONEquipment Damage Hazard.On systems using a gas valve, never apply a jumper across the valve coil terminals, even temporarily. This can burn out thermostat heat anticipator(s).
Set the Heat Anticipator Move the indicator to match the primary control current draw. When using a T874 Thermostat with two stages of heating, set each heat anticipator to match its respective primary control current draw. If you cannot find the current rating on the primary control, or if further adjustment is necessary, see NOTE and use the following procedure to determine the current draw of each stage.
The current draw of each heating stage must be measured with the thermostat removed and power on to the heating system.
1. Connect an ac ammeter of appropriate range between the heating terminals of the subbase:a. Stage 1�between W1 and RH or R;b. Stage 2�between W2 and RH or Rc. Stage 3�between W3 and RH or R.
2. Move the system switch to HEAT or AUTO.3. After one minute, read the ammeter and record the
reading:a. Stage 1�__________A;b. Stage 2�__________A;c. Stage 3�__________A.
NOTE: If equipment cycles too fast, set the indicator to a higher current rating, but not more than one-half divi-sion at a time, and recheck the cycle rate. Most con-ventional two-stage heating equipment is designed to operate at three cycles per hour per stage, and one-stage heating equipment at six cycles per hour, at 50 percent load conditions. When using the T874 Thermostat in heat pump systems, set the heat antic-ipator at 140 percent of the actual primary control current draw to reduce the cycling rate. See Fig. 11.
ALLENRETAININGSCREWS (2)
M956
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 12
Most heat pump systems should cycle 2-1/2 to 3 times per hour.
4. Hang the upper edge of the thermostat cover on top of the thermostat base and swing the cover downward until it engages with the cover clip.
Fig. 11. Adjustable heat anticipator scales.
Temperature SettingMove the heating and cooling levers to the desired comfort positions. See Fig. 12. On some models with two stages of heating or cooling, the same lever controls both stages. The minimum differential between heating and cooling setpoints is 4°F (2°C) (5°F [3°C]) on T874W.
If model has optional screws to lock temperature control levers, loosen these screws before making temperature adjustment; tighten the screws when levers are set at desired position.
Fig. 12. Internal view of T874W (three stages of heating, two stages of cooling).
Subbase SettingThe subbase switching positions control the system operation as described below.SYSTEM SWITCH (see subbase for positions):
OFF�both the heating and cooling systems are off. If the fan switch is at the AUTO position, the cooling fan is also off.
HEAT�heating system is automatically controlled by the thermostat. Cooling system is off.
AUTO�thermostat automatically changes between heat-ing and cooling system operation, depending on the indoor temperature.
COOL�cooling system is automatically controlled by the thermostat. Heating system is off.
EM.HT.�emergency heat relay is automatically controlled by the thermostat. Cooling system is off. Compressor is de-energized.
SUPL.HT.�supplemental heat relay is energized. Cooling system is off. Compressor is de-energized.
WOOD�heating system is operating with only the wood-burning stage.
OIL�heating system is operating with only the oil-burning stage.
WOOD/OIL�wood and oil stages operate sequentially; first the WOOD stage operates, then the OIL stage operates if the WOOD stage cannot handle the load.
EVAP�controls cooling system by water evaporation; see equipment instructions for further information.
OVERRIDE�night setback is disabled.ON�heating system is controlled by the thermostat. EM.
HT. or SUPL. HT. relay is not energized.FAN SWITCH positions control fan operation as follows:
ON or CONT.�fan operates continuously.AUTO�fan operates as controlled by the thermostat in
heat pump systems or conventional cooling mode; fan operates as controlled by the plenum switch in conven-tional heating mode.
LO�fan operates constantly at low speed.MED�fan operates constantly at medium speed.HI�fan operates constantly at high speed.
To move the subbase switches to the desired control positions, use thumb and index finger to slide the lever. The lever must stop over desired function indicator position for proper circuit operation.
Spring return momentary position switching feature is available on selected subbase models. On these models, the fan switch is positioned to the right of the system switch. By moving the fan switch to the far right and releasing it, the ON position circuit makes. The lever springs back on release. This position is not marked on the subbase.
Setting the Adjustable DifferentialThe adjustable interstage differential feature, on a selected T874D model only, can be identified by the scale and tension screw near the heating and cooling mercury switches. See Fig. 13. On this model, the number of degrees between the making of the first and second stage mercury bulbs is adjustable. This feature is especially useful if the first stage controls the comfort temperature, and the second stage controls the energy savings temperature. Timers, such as the S6005, for insertion between the first and second stage control points must be ordered separately.
Each mark on the scale represents 1°F (0.6°C) The differential is factory set at 2°F (1°C) the differential can be set as high as 12°F (7°C) To set the adjustable interstage differential, loosen the tension screw. See Fig. 13. Slide the adjustable scale to align with the number of degrees desired between stages. Use the lower edge of the tension screw bracket as a guide for alignment. In heating, slide the lever wider apart for a larger differential, or closer together for a
1.2 .4.6.3
.2
.15
.12
.10
.8
1.2
.4.6
.3.2
.15
.12
.8.5
MOVE INDICATOR TOMATCH CURRENT RATINGOF PRIMARY CONTROL
STAGE ONEANTICIPATORHEATING CONTROL
STAGE TWOANTICIPATORHEATING CONTROL
M5069
STAGE 1HEATING
STAGE 3HEATING
STAGE 2HEATING
HEATINGLEVER
COOLINGLEVER STAGE 1
COOLING
STAGE 2COOLING
CAPTIVEMOUNTINGSCREWS (2) M7625
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
13 60-2485�8
smaller differential. In cooling, slide the lever closer together for a larger differential, or wider apart for a smaller differential. While supporting the scale with hand, tighten the tension screw.
IMPORTANTSupport the scale with hand while tightening tension screw. See Fig. 13. Failure to do so can result in twisting and damaging bimetal coil.
Fig. 13. Set adjustable interstage differential.
CAUTIONEquipment Damage Hazard.When the thermostat is used to control a two-stage heating or cooling system, the second stage mercury bulb must never make before the first stage bulb, or severe equipment damage could result. To prevent this problem, provide at least 2°F (1°C) differential between stage-one and stage-two make points. Example: in heating, if stage-one makes at 70°F (21°C) stage-two should make at 68°F (20°C) or lower.
Verify the Adjustment
HeatingStart with the heating setpoint lever all the way to the left. Slowly move the lever to the right, just until the first stage bulb makes (mercury rolls to the right side of the bulb). Note the setting on the temperature scale. Slowly move the lever to the right until the second stage bulb makes. Note the setting on the temperature scale. The difference between the two temperatures is the interstage differential, which should match the number set on the scale with the tension screw.
CoolingStart with the cooling setpoint lever all the way to the right. Slowly move the lever to the left, just until the first stage bulb makes (mercury rolls to the left side of the bulb). Note the setting on the temperature scale. Slowly move the lever to the left until the second stage bulb makes. Note the setting on the temperature scale. The difference between the two temperatures is the interstage differential, which should match the number set on the scale with the tension screw.
CHECKOUT
HeatingMove the system switch on the Q674 Subbase to HEAT or AUTO. Move the heat lever on the T874 about 10°F (6°C) above room temperature. See Fig. 12. Heating system should start and the fan should run after a short delay. Move the heat lever about 10°F (6°C) below room temperature. The heating equipment should shut off, and the fan should run for a short time, then shut off.
In heat pump applications, sometimes time delays are involved before the compressor and auxiliary heat are activated. This is due to a minimum-off timer, which prevents the compressor from restarting for five minutes from when the thermostat last turned off the compressor, or from when the system first received power.
Cooling
CAUTIONEquipment Damage Hazard.Do not operate cooling if outdoor temperature is below 50°F (10°C). Refer to manufacturer recommendations.
TENSIONSCREW
ALIGN LOWEREDGE WITHSCALE
NOTCH10°F
SCALE
1
SLIDE LEVERWIDER APARTFOR LARGERDIFFERENTIAL
HEATING
TENSIONSCREW
ALIGN LOWEREDGE WITHSCALE
NOTCH4°F
SCALE
1
SLIDE LEVERCLOSER TOGETHERFOR LARGERDIFFERENTIAL
COOLING
1 EACH MARK ON THE SCALE REPRESENTS 1°F (0.6°C).M937
1.2 .8 .6.3
.2
1.5
.4
50 60 70 80HEATTENSION
SCREW
HEATING SET-POINT LEVER
FIRST STAGESWITCH
SECOND STAGE(ADJUSTABLE)SWITCH
SCALE
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 14
Move the system switch on the Q674 Subbase to COOL or AUTO. Move the cool setting lever on the T874 Multistage Thermostat about 10°F (6°C) below room temperature. See Fig. 12. The cooling equipment and fan should start. If the system has two stages of cooling, both stages should start. Move the cool lever about 10°F (6°C) above room temperature. The cooling equipment and fan should stop.
FanMove the system switch to COOL, OFF, or AUTO. If necessary, position both temperature setting levers so that the heating and cooling equipment are off. Move the fan switch to ON or CONT. The fan should run continuously. When the fan switch is in AUTO, LO, MED, or HI position, fan operation is controlled by the heating or cooling system.
Outdoor Reset Thermistor (Where Applicable)If the system is supplied with a thermistor, it must be used; if not used, thermostat performance deviates radically from proper operation.
The proper thermistor operation must be verified to ensure the correct operation of the thermostat. Check thermistor operations as follows:
1. Disconnect the T wire on the subbase.2. Use an ohmmeter to measure resistance between the
T wire and the A subbase terminal.3. Take outdoor temperature at thermistor location and find
the correct thermistor resistance on the Fig. 14 chart.4. If the resistance measured in step 2 and the calculated
resistance in step 3 vary by more than 15 percent, the thermistor requires replacement. Contact Honeywell or installing dealer for replacement packaged outdoor ther-mistor, part no. C815A1005.
Fig. 14. Thermistor resistance chart.
CALIBRATION
ThermostatT874 Thermostats are accurately calibrated at the factory. They do not have provision for field calibration.
ThermometerThe thermometer in your thermostat has been accurately calibrated at the factory. The thermometer should only need adjustment if it has been dropped or shifted due to mishandling.
If the setpoint lever and the thermometer reading do not agree, use the following procedure:
1. Remove the thermostat cover by pulling up from the bottom edge of the cover away from the base until it snaps free of the cover clip.
2. Set the thermostat cover on a table near an accurate thermometer.
3. Allow ten minutes for cover thermometer to sense area temperature; compare the readings. Be careful not to touch thermometer or breathe on it.
4. If the readings are the same, replace cover and put the system into operation.
5. If the readings are different, insert a small screwdriver in the thermometer slot and turn it until the thermometers have the same reading. See Fig. 15.
6. Replace thermostat cover and put the system into oper-ation.
Fig. 15. Thermometer calibration.
UNDERSTANDING CIRCUITSTo understand wiring diagrams, it is important to know what all the symbols mean and how to trace the path of the circuits from the transformer. See Fig. 16 through 25.
Circuit descriptions and terminology are defined as follows:For standard heating-cooling circuits:
Auto changeover�refers to the presence of an AUTO position in the system switching (EX: Q674E with OFF-HEAT-AUTO-COOL switching). The thermostat auto-matically changes between heat and cool modes as indoor temperature changes.
Manual changeover�requires a system switch movement to change mode (EX: Q674B with HEAT-OFF-COOL switching). T874D Multistage Thermostats with 2 heat or 2 cool switches are shown on most standard circuits. Most standard or TRADELINE® subbases (Q674A-E,G) can be used with T874A-F standard or TRADELINE
TH
ER
MIS
TO
R R
ES
IST
AN
CE
(oh
ms)
C815A THERMISTOR RESISTANCER = 400 ohms ± 10% AT 77°F (25°C)
4600440042004000380036003400320030002800260024002200200018001600140012001000
800600400200
0-20 0 20 40 60 80 100 120 140
TEMPERATURE OF THERMISTOR (°F) M1590A
M5070
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
15 60-2485�8
thermostats. The schematics can be field-modified as required (EX: if T874C is being used, eliminate second stage of heat).
For heat pump circuits:Cool changeover valve�operates on cooling. The revers-
ing valve or relay is activated either by moving the sys-tem switch to COOL (manual changeover) or by a mercury switch that makes on a temperature rise (auto changeover).
Heat changeover valve�operates on heating. The revers-ing valve or relay is activated either by moving the sys-tem switch to HEAT (manual changeover) or by a mercury switch that makes on a temperature fall (auto changeover).
System monitor relay�optional equipment on some heat pumps includes an R4222P1065 or equivalent. This system monitor relay detects a malfunction in the com-pressor and indicates the malfunction by activating the EMERGENCY HEAT LED on the Q674 Switching Sub-base. The system monitor relay is usually wired into the L terminal on the Q674.
Each mercury switch is identified by function:H1�Stage 1 Heating.H2�Stage 2 Heating.H3�Stage 3 Heating.C1�Stage 1 Cooling.C2�Stage 2 Cooling.C3�Stage 3 Cooling.C/O�Changeover (heat pumps).
Each anticipator is identified and each switch affected is named (EX: H1 anticipator, C1 anticipator).
All T874 Multistage Thermostats use mercury switches. Each schematic indicates switch operation by being drawn in the open position with an arrow indicating operation with a temperature RISE or FALL.
One circuit has been selected that is typical of various models used with heat pumps. This circuit has been traced to illustrate the functions performed by these control systems.
Tracing Method:1. Always begin at the system transformer or R terminal.
You may want to draw the switch contacts in each switch position to aid in tracing. Colored pencils are helpful when only one copy of the circuit is available. See Fig. 16 for a description of the hookup symbols and Fig. 17 through 25 for typical hookups.
2. Completely trace only one circuit at a time (for example: heat or cool).
3. Connections are indicated by small dots at the point of intersection. If there is no dot, there is no connection.
4. The left portion of the circuit (the thermostat) contains the mercury switches. The heat switches make on a temperature fall, and the cool switches make on a tem-
perature rise. Fixed anticipation is represented by a zig-zag line and adjustable anticipation is a zigzag with an arrow. The resistance of the fixed anticipator is so large it limits current so that a system relay cannot be pulled in from a circuit path going through the fixed anticipator. The relay can be pulled in through an adjustable antici-pator because its resistance is generally 0 to 5 ohms.
5. The center portion (the subbase) contains the switches. The fan switch is above the system switch. The small circles on the switch represent the maximum possible contacts available on the Q674 Subbase. The larger cir-cles represent the switch positions available on this par-ticular Q674, with the solid circle representing where it is actually switched on the diagram.
NOTE: Solid circles are not interconnected electrically.
At the right, the relays and contactors are shown, attached to the proper terminals. The terminals are represented by large circles with terminal designations in capital letters. See Table 3 for the meaning of each lettered terminal.
Sometimes power for a fixed anticipator is brought through an off system relay like the changeover relay shown in Fig. 20. This current is kept low by the high resistance of the fixed anticipator so that relay does not pull in.
Fig. 16. Key to hookup symbols.
M5848
KEY TO HOOKUP SYMBOLS
TRANSFORMER (24 VAC SECONDARY)
RELAY/CONTACTOR CONTACTS
LED
RELAY OR CONTACTOR COIL
MERCURY SWITCH
FIXED ANTICIPATORHIGH RESISTANCE(TYPICALLY 5 KILOHMS)
ADJUSTABLE ANTICIPATORLOW RESISTANCE(TYPICALLY 0 TO 5 OHMS)
TERMINAL
ODTOUTDOOR THERMOSTAT
EHREMERGENCY HEAT RELAY
RTDTIME DELAY RELAY
RDDEFROST RELAY
CHPPRESSURE SWITCH
LACOLOW AMBIENT CUTOFF
B
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 16
Fig. 17. Internal schematic and typical hookup of a T874R Thermostat and Q674L Subbase in a heat pump application. The thermostat provides two-stage heating and one-stage cooling manual changeover operates on cooling.
M5072A
(HOT) L1 L2
1
LACO CHPY
B
E
O
G
L
X
W2
W3
RODT 1
RTD 1 EHR 1 RTD 2
ODT 2
EHR 2 RTD 3
RDSYSTEM MONITOR
FAN RELAY
COMPRESSORCONTACTOR
COOL CHANGEOVERVALVE
EM. HT. RELAY
RTD 1AUX. HT.LED (GREEN)
EM. HT.LED (RED)
FAN SWITCH
ON
AUTO
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
H2
FALL
H1
FALL
C1
2
3
4
5
6
H1/C1ANTICIPATOR
H2ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
AUXILIARY HEAT LED AVAILABLE ON SOME MODELS.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
2
2
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
17 60-2485�8
Fig. 18. Tracing the changeover relay circuit.
Fig. 19. Tracing the heat 1 and anticipation circuit.
M5840
L1 (HOT)
L2
1
LACO CHPY
B
E
O
G
L
X
W2
W3
R
ODT 1
RTD 1 EHR 1 RTD 2
ODT 2
EHR 2 RTD 3
RDSYSTEM MONITOR
FAN RELAY
COMPRESSORCONTACTOR
CHANGEOVERVALVE
EM. HT. RELAY
RTD 1AUX. HT.LED (GREEN)
EM. HT.LED (RED)
FAN SWITCH
ON
AUTO
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
H2
FALL
H1
FALL
C1
2
3
4
5
6
H1/C1ANTICIPATOR
H2ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
M5841
L1 (HOT)
L2
1
LACO CHP
Y
B
E
O
G
L
X
W2
W3
RODT 1
RTD 1 EHR 1 RTD 2
ODT 2
EHR 2 RTD 3
RDSYSTEM MONITOR
FAN RELAY
COMPRESSORCONTACTOR
CHANGEOVERVALVE
EM. HT. RELAY
RTD 1AUX. HT.LED (GREEN)
EM. HT.LED (RED)
FAN SWITCH
ON
AUTO
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
H2
FALL
H1
FALL
C1
2
3
4
5
6
H1/ C1ANTICIPATOR
H2ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 18
Fig. 20. Tracing the heat 1 anticipation circuit.
Fig. 21. Tracing the heat 2, anticipation and AUX. HT. LED circuit.
M5842
L1 (HOT)
L2
1
LACO CHPY
B
E
O
G
L
X
W2
W3
RODT 1
RTD 1 EHR 1 RTD 2
ODT 2
EHR 2 RTD 3
RDSYSTEM MONITOR
FAN RELAY
COMPRESSORCONTACTOR
CHANGEOVERVALVE
EM. HT. RELAY
RTD 1AUX. HT.LED (GREEN)
EM. HT.LED (RED)
FAN SWITCH
ON
AUTO
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
H2
FALL
H1
FALL
C1
2
3
4
5
6
H1/ C1ANTICIPATOR
H2ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
M5843
L1 (HOT)
L21
LACO CHPY
B
E
O
G
L
X
W2
W3
RODT 1
RTD 1 EHR 1 RTD 2
ODT 2
EHR 2 RTD 3
RDSYSTEM MONITOR
FAN RELAY
COMPRESSORCONTACTOR
CHANGEOVERVALVE
EM. HT. RELAY
RTD 1AUX. HT.LED (GREEN)
EM. HT.LED (RED)
FAN SWITCH
ON
AUTO
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
H2
FALL
H1
FALL
C1
2
3
4
5
6
H1/C1ANTICIPATOR
H2ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
19 60-2485�8
Fig. 22. Tracing the emergency heat and EM. HT. LED circuit.
Fig. 23. Tracing the cooling circuit.
M5844
L1 (HOT)
L2
1
LACO CHP
Y
B
E
O
G
L
X
W2
W3
RODT 1
RTD 1 EHR 1 RTD 2
ODT 2
EHR 2 RTD 3
RDSYSTEM MONITOR
FAN RELAY
COMPRESSORCONTACTOR
CHANGEOVERVALVE
EM. HT. RELAY
RTD 1AUX. HT.LED (GREEN)
EM. HT.LED (RED)
FAN SWITCH
ON
AUTO
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
H2
FALL
H1
FALL
C1
2
3
4
5
6
H1/C1ANTICIPATOR
H2ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
M5845
L1 (HOT)
L2
1
LACO CHPY
B
E
O
G
L
X
W2
W3
RODT 1
RTD 1 EHR 1 RTD 2
ODT 2
EHR 2 RTD 3
RDSYSTEM MONITOR
FAN RELAY
COMPRESSORCONTACTOR
CHANGEOVERVALVE
EM. HT. RELAY
AUX. HT.LED (GREEN)
EM. HT.LED (RED)
FAN SWITCH
ON
AUTO
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
H2
FALL
H1
FALL
C1
2
3
4
5
6
H1/C1ANTICIPATOR
H2ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
RTD 1
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 20
Fig. 24. Tracing the auto fan circuit.
Fig. 25. Tracing the fan on circuit.
M5846
L1 (HOT)
L2
1
LACO CHPY
B
E
O
G
L
X
W2
W3
RODT 1
RTD 1 EHR 1 RTD 2
ODT 2
EHR 2 RTD 3
RDSYSTEM MONITOR
FAN RELAY
COMPRESSORCONTACTOR
CHANGEOVERVALVE
EM. HT. RELAY
RTD 1AUX. HT.LED (GREEN)
EM. HT.LED (RED)
FAN SWITCH
ON
AUTO
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
H2
FALL
H1
FALL
C1
2
3
4
5
6
H1/C1ANTICIPATOR
H2ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
M5847
L1 (HOT)
L2
1
LACO CHPY
B
E
O
G
L
X
W2
W3
RODT 1
RTD 1 EHR 1 RTD 2
ODT 2
EHR 2 RTD 3
RDSYSTEM MONITOR
FAN RELAY
COMPRESSORCONTACTOR
CHANGEOVERVALVE
EM. HT. RELAY
RTD 1AUX. HT.LED (GREEN)
EM. HT.LED (RED)
FAN SWITCH
ON
AUTO
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
H2
FALL
H1
FALL
C1
2
3
4
5
6
H1/C1ANTICIPATOR
H2ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
21 60-2485�8
OPERATION
Heat Anticipation/Cool AnticipationWhen controlling a heating unit with a thermostat, the temperature does not remain exactly at the thermostat setpoint, but varies within a certain temperature range. Heat anticipation is added to the thermostat to reduce this range.
The anticipator is a small resistive heater in the thermostat that heats when the system is on (heat mode) or off (cool mode). The heat produced by the anticipator raises the internal bimetal temperature slightly faster than the surrounding room temperature. The thermostat anticipates the need to shut off the heating system sooner than it would if affected by room temperature only.
There are two types of heat anticipation, adjustable and fixed.
Adjustable anticipation is also called current anticipation. See Fig. 26. The heater is in series with the mercury switch and heating primary. The pointer is adjusted to match the current draw of the primary control, and the correct amount of heat is added for proper cycle rates.
Fig. 26. Adjustable anticipation heater in series with load.
Fixed anticipation is also called voltage anticipation. See Fig. 27. The heater is in parallel with the primary control and is not affected by the current draw of the primary. It establishes the proper cycle rate for any application.
Fig. 27. Fixed anticipation heater in parallel with load.
Heat anticipators add heat during the call for heat. Cooling anticipators are activated while the air conditioner is off. See Fig. 28. This heater makes the thermostat think it is warmer than it really is, and brings it on sooner than the bimetal alone would.
Fig. 28. Internal cooling anticipation schematic.
Interstage DifferentialThe mercury switch of each stage of heat makes at a slightly different temperature; that is, the mercury makes the contacts of the first stage bulb at one temperature, and the second stage bulb at another temperature. The difference between these two temperatures is the interstage differential.
Interstage differential is the difference between the two make points when the bulbs are controlled by the heating of the bimetal and the action of the heat anticipator. The interstage differential is 1.9°F (1°C) between the stages of heating or the stages of cooling for most models.
Mechanical differential is the difference between the make and break points of each switch. The mechanical differential for the T874 is 1°F (0.6°C) between the stages of heating or between the stages of cooling for most models.
DroopThe addition of anticipator heat to the bimetal causes a control factor called droop.
As the weather grows colder, the heating appliance must operate longer and more frequently. More heat must be added to the bimetal. The bimetal now thinks it is warmer than it really is, and actual room temperature is controlled at a lower temperature than the setpoint indicates. At 100 percent heat load, this droop can be significant.
The C815A Outdoor Reset Thermistor is used in heat pump systems to minimize droop. Without some method of countering this situation, the occupant could notice the temperature offset.
Outdoor ResetSome T874/Q674 models are intended for use with the C815A Outdoor Thermistor. The outdoor thermistor provides significantly improved thermostat performance when compared to conventional multistage thermostats. The C815A is usually located in the heat pump condensing unit outdoors.
FALL
L1 (HOT)
L2
M5823
STAGE 1 HEAT RELAY
H1 ANTICIPATOR
H1
FALL
L1 (HOT)
L2
M5824
STAGE 1 HEAT RELAY
H1 ANTICIPATORH1
RISE
L1 (HOT)
L2
M5825
STAGE 1 COOL RELAY
C1 ANTICIPATOR
C1
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 22
CAUTIONEquipment Damage Hazard.Due to calibration techniques used for T874 Thermostats with outdoor reset, the C815A Thermistor must be wired into the system at all times. Failure to do so will result in serious degradation of performance.
Service and Replacement of C815A Outdoor ThermistorTo check and verify thermistor operation, perform the following steps:
1. Disconnect wire from T terminal on subbase.2. Measure resistance with ohmmeter across the T sub-
base wire and X subbase terminal.3. Take outdoor temperature measurement at thermistor
location and find correct thermistor resistance on the chart in Fig. 29.
4. Compare resistance on the chart with measured resis-tance. Replace C815A if resistance varies more than 15 percent. Contact installing dealer for packaged replace-ment outdoor thermistor.
Fig. 29. Thermistor resistance chart.
FeaturesTwo of the features of the T874/Q674 include LED indicators and restricted setpoint.
LED IndicatorsThe light-emitting diodes (LED) indicators on the subbase light on command when something specific happens in the system. See Fig. 30.
Up to four different LEDs are available. The thermostat has a clear lens window for viewing each LED. On TRADELINE models, a small insert is used so the LED function desired can be selected. This must be done during installation.
A blank insert is factory-installed in some T874 models. To remove it, push both temperature setting levers to the far ends of the thermostat. Use index fingernail to gently pull out the scaleplate a fraction of an inch. Turn thermostat upside-down, and the blank insert falls out.
A strip of four inserts is included with TRADELINE T874. Drop a strip into the recessed area behind the scaleplate so selected LEDs show. Make sure insert is completely seated in recessed area. Let scaleplate pop back; then set levers to desired position.� FILTER LED lights when the filter is clogged and needs
replacement.� CHECK LED lights when something needs to be checked
or done to maintain efficient operation of system. See heating system instructions for CHECK LED meaning.
� EM. HT. LED lights when the emergency heat is operating.� SUPL. HT. LED lights when the supplemental heat is
operating.� LOCKOUT LED lights when the system is shut down and
needs maintenance.� AUXILIARY HEAT LED lights when the auxiliary heat is
operating.� SERVICE or MALFUNCTION LED can have several
meanings. Consult heating system instructions.
LEDs cannot be replaced or added in the field.
Fig. 30. T874/Q674 LED location.
Restricted Setpoint (DoD)The Department of Defense (DoD) models are equipped with a restricted setpoint feature for fuel efficiency.
Fixed stops are factory-set so setpoint levers cannot be set above 72°F (22°C) on heating, or below 78°F (26°C) on cooling.
ApplicationsThe T874/Q674 can be applied to standard residential systems for automatic or manual changeover, to commercial rooftop applications, or to heat pump applications.
Changeover on Standard Residential SystemsIn a standard residential heating-cooling circuit, changeover between heating and cooling can be done either automatically or manually.
Automatic changeover is done by an AUTO position on the subbase system switch. See Fig. 31. When the switch is in the AUTO position, the thermostat automatically changes between heat and cool modes, depending on the indoor temperature.
TH
ER
MIS
TO
R R
ES
IST
AN
CE
(oh
ms)
C815A THERMISTOR RESISTANCER = 400 ohms ± 10% AT 77°F (25°C)
4600440042004000380036003400320030002800260024002200200018001600140012001000
800600400200
0-20 0 20 40 60 80 100 120 140
TEMPERATURE OF THERMISTOR (°F) M1590A
80 50 60 70 80 COOLEM.HEAT FILTER SERV.
AUXHEAT
M5830
LEDS
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
23 60-2485�8
Fig. 31. System switching for automatic changeover.
Automatic changeover is frequently used in areas where there are large temperature differences in 24 hours. Some uses for the automatic changeover feature are in the southern states (cool in the morning and hot in the afternoon) and in commercial applications.
Manual changeover requires a system switch movement to change the mode. See Fig. 32. Most manual changeover switches consist of HEAT-OFF-COOL choices. For heating, switch to HEAT. For cooling, switch to COOL. It is not automatic.
Manual changeover is often used in areas where the temperature is relatively stable between day and night.
Fig. 32. System switching for manual changeover.
Commercial Rooftop ApplicationThe T874 can be used as part of a commercial rooftop application to run mechanical cooling.
An economizer is often used as part of a rooftop application to save on air conditioning. See Fig. 33.
Fig. 33. Typical commercial rooftop economizer application.
Enthalpy is the temperature and humidity of the air. A more accurate analysis of the suitability for free cooling can be made by monitoring the enthalpy.
When enthalpy is low enough, the thermostat and a sensor tell the economizer damper to open to let in cool air from the outside. When enthalpy is high, the thermostat and sensor tell the damper to close. No more outside air comes in, so the air conditioner is used instead.
Heat Pump ApplicationA heat pump system operates much like an air conditioner. However, the heat pump is capable of moving heat in two directions; from inside the home to outdoors for cooling, or from outdoors to inside for heating.
The heat pump can be controlled by separate relay/contactor components, which are energized or de-energized by the T874.
Changeover between heating and cooling for heat pump circuits can be accomplished either manually or automatically.
Manual changeover control requires a system switch movement to change the mode. The reversing valve is activated by moving the system switch to COOL for cooling or to HEAT for heating operation.
Automatic changeover is accomplished by one of the mercury bulb switches in the thermostat. On a system with automatic changeover on cooling, the changeover valve is energized by a mercury switch that makes on a temperature rise. On heating, the changeover valve is energized by a mercury switch that makes on a temperature fall.
A description of the methods used to control heat pumps follows.
Space Temperature Sensing Low Voltage ControlsControl systems for heat pumps usually utilize low voltage control circuits. The variety of control functions required and the relative complexity require a versatile and economical method of control. There are several interlocks and indication functions that would be more difficult and expensive to wire in line voltage circuits. Low voltage controls have the precision and flexibility needed.
The thermostat used is a low voltage device that has good temperature sensitivity and several manual and automatic switching capabilities.
Two-Stage ThermostatIn most installations, the heat pump itself requires auxiliary heat, usually in the form of electric strip heaters, to carry the building heating load at design conditions. Since the heat pump is usually more efficient, the control strategy is to run the heat pump whenever possible and the auxiliary heat only when necessary�during very cold weather or if the heat pump fails. Usually the auxiliary heat is used only below the balance point (temperature at which the heat pump cannot handle heating load by itself).
A two-stage thermostat makes this possible. The two stages make sequentially as the temperature drops. There is a degree or two between stages so that the second stage (the
OFF EM. HT. HEAT AUTO COOL
M5828
OFF EM. HT. HEAT COOL
M5829
M5827A
H205 OR H705ENTHALPYCONTROL
RETURN AIR
DISCHARGE AIR SENSORDOWNSTREAM FROM THEEVAPORATOR COIL
OUTDOORAIR
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 24
one controlling the auxiliary heat) makes only when the heat pump alone cannot handle the load. That is how the strategy of using the most economical heat first is implemented.
Cycling RateNormally, thermostat anticipation is set to cycle a fossil fuel furnace about five or six times an hour (at 50 percent load). This provides a reasonable balance between comfort, stability and economy.
A heat pump, being a mechanical refrigeration system, should be cycled at a rate of 2-1/2 to 3 times an hour. With a T874, this is accomplished by setting the anticipator at the total current draw of the controlled device (the contactor and possibly the changeover relay or valve). Most likely, the compressor operates from the first stage of the thermostat.
The second stage normally controls the auxiliary heaters. This heat anticipator can be set for the current draw of the electric heat primary, and produces good control.
Voltage AnticipationAlthough not a specific requirement for heat pumps, several models of the T874 have voltage heat anticipation instead of current anticipation.
With voltage anticipation, the amount of heat added to the thermostat is constant no matter which load is connected to it. The anticipator realizes a constant voltage and produces a constant amount of heat during the ON cycle. This allows the cycling rate to be designed into the thermostat. The heat pump manufacturer is assured of correct performance independent of later thermostat adjustments.
Outdoor ResetOutdoor reset, which a C815A Outdoor Thermistor makes possible, is sometimes applied in heat pump systems to help minimize the effect of the differential between stages. It takes 2°F (1.1°C) change in temperature to bring on the second stage and full heating. Added to a certain amount of droop under high loads, there can be a large offset between the setpoint and room temperature.
Without some method to counteract this situation, the temperature offset from the setpoint could be as much as 6°F (3.3°C) under high load conditions. It is not likely that the occupants accept this variation without making frequent thermostat setting changes.
Outdoor reset has the effect of raising the setpoint at cold outdoor temperatures. Then, even with a few degrees droop, the space temperature stays near the desired setting.
This is done by calibrating the thermostat high by 5°F (3°C)�the amount of expected offset. This offset compensates for differential and droop at high load factors so the thermostat switches at the setpoint. At warm temperatures, heat is added to the thermostat to compensate for this offset; at cold temperatures, the extra heat is automatically removed. The effect is the same as raising the setpoint as the outdoor temperature goes down.
This is particularly important on the 3-stage T874. The additional stage means that more droop is introduced when the system is in operation. That is the reason the TRADELINE T874W is sold in a package with the outdoor sensor and the correct subbase.
Outdoor Reset�How it WorksThe heater in the thermostat is connected in series with a thermistor sensor that measures outdoor temperature. See Fig. 34. In warm weather, the thermistor has very low resistance, permitting a large current flow in the heater, which generates a relatively large amount of heat in the thermostat.
In cold weather, the outdoor sensor has high resistance, which results in low current flow and little or no heat being added to the thermostat. This raises the control point, overcoming the effects of droop and interstage differential.
Fig. 34. Location of thermistor.
ChangeoverChangeover between heating and cooing can be accomplished either automatically or manually, depending on the application. Changeover can occur in heating or cooling.
The changeover valve is energized as long as the subbase function switch is in the appropriate position when manual changeover is used. If a system manually changes over on cooling, the valve energizes whenever the subbase switch is in the cooling mode.
One of the mercury bulb switches is used for control when the thermostat has automatic changeover. When the automatic changeover is in cooling, the changeover valve is energized when the first stage cooling switch makes. The second stage switch turns on the compressor.
It is more common with new equipment to find that changeover occurs with cooling; that is, the changeover valve is energized to produce cooling.
Whether automatic or manual changeover is used and whether the reversing valve is energized with cooling or with heating, a heat pump system can be controlled by the appropriate T874 Multistage Thermostat.
L1 (HOT)
L2
RESETHEATER
C815AOUTDOORTHERMISTORSENSOR
M5826
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
25 60-2485�8
Low Temperature LockoutsSome manufacturers of heat pumps have previously controlled their units so the compressor was locked out below a specified outdoor temperature. This was done because of the stress placed on the compressor by the very cold temperatures, and the fact that efficiency drops off at low temperatures.
Other manufacturers say that although efficiency is low at cold temperatures, the problem of starting the cold compressor is the most critical point. It is more important to keep the compressor running than to shut it off and try to restart it when the temperature warms up to +10°F (-12°C). Also the crankcase heater, which can run only when the compressor is off, compensates for the lower compressor efficiency. So, it is equitable to let the heat pump run even with a coefficient of performance (COP) slightly less than one, rather than to turn it off and have to run the crankcase heater.
NOTE: To determine the COP of a heat pump, use the fol-lowing formula:
COP = Btu Out/Btu we pay for or Btuh CapacityUnit Wattage x 3.413 Btu/Watt
Another factor favoring this control strategy is that newer heat pump designs maintain a level of efficiency even at outdoor temperatures well below zero. Some brands do not reach 1.0 COP until -25°F (-32°C).
Virtually all manufacturers now let the heat pump run continuously rather than lock it out at cold temperatures.
Heat Pumps with Dual CompressorsStaging residential sized heat pumps is a requirement that developed from the need to make heat pumps as efficient as possible. One of the methods used to improve overall seasonal efficiency is to reduce the amount of time the machine is operating in a transitional mode. Transitional mode is starting and stopping in addition to recovering from defrost. Under light loads, when the heat pump is cycling on and off, this can be a significant amount of time and can result in a significant efficiency reduction. Capacity control is one way to reduce the cycling rate and improve the efficiency.
Additional capacity control methods used on other refrigeration systems (unloading, multiple compressors) are not as likely to be seen on residential heat pumps.
With a single-stage heat pump, the compressor is normally controlled by the first stage and the auxiliary heat by the second stage. The T874G, N and R Thermostats are used for this purpose.
With a two-stage compressor, the two thermostat switches control the individual compressor stages. Auxiliary heat is controlled along with the compressor stage-two, by the thermostat second stage. It comes on with the compressor high speed if an outdoor thermostat�wired in series with it�is made. See Fig. 35.
Fig. 35. Two-stage heat pump with two-stage thermostat.
The outdoor thermostat is set at the balance point with both heat pump stages running. So if the heat pump can control the heating load down to +20°F (-7°C), the auxiliary heat comes on with the second stage of the compressor.
In effect, this control strategy changes the heat input of the second stage, depending on the amount of heat needed. Additional stages of auxiliary heat can be added with or without the control of more outdoor thermostats, See Auxiliary Heat section.
Another way to control a two stage heat pump is with a three-stage thermostat. The T874W is designed for this application as well as others. See Fig. 36.
The advantage of this system is that no auxiliary heat is used until there is an actual demand from the controlled space.
Fig. 36. Two-stage heat pump with three-stage thermostat.
Two speed Heat PumpOne way to control capacity is to use a two-speed compressor. The compressor runs at low speed for stage-one heating and cooling. The compressor runs at the low speed instead of cycling the heat pump on and off under some light load conditions.
The high speed is stage-two cooling. The compressor runs on high speed when loads increase so the low speed can no longer handle the cooling load. This reduces cycling rate and improves capacity.
M5838
THERMOSTAT
HEAT 2 HEAT 1
OUTDOORTHERMOSTAT
COMP. STAGE 2
AUXILIARYHEAT
COMP. STAGE 1
M5837
COMP. STAGE 2
THERMOSTAT
HEAT 2 HEAT 1
AUXILIARYHEAT
HEAT 3
COMP. STAGE 1
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 26
Defrost ControlIn some regions, during half or more of the heating season, the outdoor coil operates below 32°F (0°C) Frost or ice builds up on the outdoor coil of a heat pump similarly to the frost buildup in a household refrigerator. Eventually, this accumulation of ice interferes with efficient heat transfer from the outdoor air to the coil and refrigerant. Defrosting is occasionally required to remove this ice, and restore the heat pump ability to absorb heat from the air.
DefrostingA heat pump defrosts its outdoor coil by temporarily switching to the cooling mode, which causes hot gas from the compressor to be directed to the outdoor coil instead of to the indoor coil so the heat pump is taking heat from the home to warm up the outdoor coil. Defrosting is the greatest detriment to heat pump efficiency.
Defrost Control FunctionsBesides changing over to the cooling mode, defrosting requires several more control initiated actions that follow.
OUTDOOR FANWhen defrosting has begun, it is standard practice to turn off the outdoor fan to speed up the melting process. A separate defrost relay is required to control that fan. See Fig. 37. Other contacts can be needed on the defrost relay to power the changeover valve or power part of the auxiliary heat.
Fig. 37. Outdoor fan with defrost control.
AUXILIARY HEAT DURING DEFROSTMost pump manufacturers bring on some auxiliary heat during defrost, although this is not a universal practice. Some rely on the second stage of the thermostat to call for auxiliary heat as needed. Since the heat pump is operating in the cooling mode to defrost, it is delivering cold air to the living space. Auxiliary heat is used to offset this cooling. It requires another normally open contact on the defrost relay. See Fig. 38.
Fig. 38. Auxiliary heat with defrost control.
WHEN TO DEFROSTTimely defrosting is an essential component of effective heat pump operation. Failure to defrost often enough permits too much ice to accumulate on the coil. At the very least, this hurts efficiency; at worst, it results in compressor damage. Insufficient defrosting is a condition the heat pump manufacturer wants very much to avoid.
A 50 percent reduction in outdoor airflow is the maximum that would be tolerated. So the designer of a heat pump would select a control point that puts the system into defrost when airflow through the outdoor coil approaches half its normal level. Restricted airflow causes a greater load on the compressor; the outdoor coil runs colder, suction pressure is lower and the motor runs hotter.
At the other end of the scale, defrosting too often hurts the overall energy efficiency of the system. Consider that in terms of heating the building, defrosting is a big loss. Not only does the system stop heating, but it actually moves heat out of the building. If electric strip heat is used, it is a further waste because its COP is 1.0 and not the 2.0 or more COP realized if the heat is provided by the heat pump.
So, concern for equipment safety suggests fairly frequent defrosting while economy of operation argues for fewer defrost cycles. Since the equipment manufacturer chooses, the balance is usually tipped in favor of more frequent defrosting to avoid the possibility of damaging the compressor.
Auxiliary HeatExcept in warm climates, all air-to-air heat pump installations require auxiliary heat capability. Electric resistance heaters can provide this auxiliary heat.
The electric heaters (sometimes called strip heaters) usually are supplied in 5 kW units or strips (about 17,000 Btu). The indoor unit of the heat pump is designed to accommodate various electric heat units so it can be used in variously sized buildings in different parts of the country.
Two-Stage ThermostatThe most common heat pump control strategy is for the thermostat first stage to switch the compressor and the second stage to switch the auxiliary heat. See Fig. 39.
M5839
COMPRESSOR MOTORCONTACTOR
CONTROLLED BYDEFROST RELAY
OUTDOORFAN MOTOR
M5835
THERMOSTAT
HEAT 2 HEAT 1
DEFROSTRELAYCONTACT
AUXILIARYHEAT RELAY
L1(HOT)
L2
TRANSFORMER
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
27 60-2485�8
Fig. 39. Auxiliary heat in two-stage thermostat.
This method keeps the auxiliary heat off until the heating load is large enough to demand 100 percent heat pump operation. That demand is measured by the thermostat and is the actual heat requirement of the space. The two-stage thermostat requires about a 2°F (1.1°C) room temperature drop to bring on the second stage.
Stage or Time Modulated ControlThere are two different ways to control auxiliary heat, staged or time modulated control.
Outdoor thermostats are used to switch additional increments of electric heat into the thermostat circuit as the outdoor temperature gets lower. All increments of auxiliary heat are still controlled by stage-two of the thermostat but only if the outdoor temperature requires the additional capacity. See Fig. 40.
Fig. 40. Outdoor thermostats for auxiliary heat.
The rationale for this system is that it very closely matches the system capacity to the heating load of the building. By calculating the heat loss of a building, the installing contractor can pick the theoretical outdoor temperature at which to permit each additional unit of electric heat to be operated by the second stage of the room thermostat.
The disadvantage of this system is that it can require several outdoor thermostats. Also, since the unit is operating most often at nearly full capacity, the thermostat is on longer which results in more droop, with a little more offset from the thermostat setpoint.
In addition, the capacity is tied to theoretical load, based on heat loss calculations. Normally this is very close to the actual load, but there are times where the second stage is switched on too soon (no harm done) or too late (the building gets cold).
The T874 Thermostat produces time modulated control, which is the on time of the thermostat changing during each cycle as the load changes. The on time of the heating system is directly proportional to the heating load of the building. As an example of the quality of time modulated control, consider the typical gas furnace. It can have a capacity of 100,000 Btu (293 kW), which is controlled On-Off. The output is 100,000 Btu (293 kW) or nothing. A quality thermostat controls so closely that the occupants rarely detect changes in room temperature.
The same is true with 50,000 or 60,000 Btu (146.5 or 178.8 kW) of heat pump auxiliary electric heat. The T874 can provide the same high quality control.
This scheme also eliminates the need for outdoor thermostats and thus offers the manufacturer an opportunity to reduce unit cost. One disadvantage is that a thermostat jiggler can be demanding more kW of strip heat when chilly.
The method any particular manufacturer selects depends on which arguments it finds persuasive and the opinions of its distributors and dealers.
Three-Stage ThermostatA definite improvement in quality of control and economy can be achieved with a three-stage thermostat (T874W), which is especially true with heat pumps using dual compressors.
Three-stage control permits both the heat pump and the auxiliary heat to be tied directly to the demand of the controlled space. With a two-stage compressor, maximum (100 percent) heat pump operation is required before auxiliary heat is brought on.
Emergency HeatSome provision is generally required to back up the compressor in the event of a failure during the heating season. In fact, it is quite common to find that local building codes or electric utilities require that a specified percent of the building heating requirements be available from emergency heat�a source other than the heat pump compressor. Almost universally, the source is electric resistance heaters. Typically, the requirement is for 70 or 80 percent of the building heating needs.
Switching to Emergency HeatConventional heat pump control (thermostat logic) usually includes a manual subbase switch to bring on the emergency heat.
In one control strategy, the emergency heat relay is turned on by the EM.HT. selector switch on the thermostat subbase. The compressor is prevented from running. The electric heaters are cycled as they normally would be by the second stage of
M5836
COMPRESSORCONTRACTOR
THERMOSTAT
HEAT 2 HEAT 1
AUXILIARYHEAT RELAY
CONTROLSAT 65°F (18°C)
CONTROLS AT 63°F (17°C)
M5834
COMPRESSORCONTACTOR
THERMOSTAT
HEAT 2 HEAT 1
AUXILIARYHEAT RELAY 1
AUXILIARYHEAT RELAY 2
AUXILIARYHEAT RELAY 3
OUTDOORTHERMOSTATS
20°F(-7°C)
5°F(-15°C)
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 28
the thermostat. A set of contacts on the emergency heat relay is used to bypass each outdoor thermostat so that all electric heat is under immediate thermostat stage-two control. So the emergency heat relay simply bypasses the outdoor thermostats. See Fig. 41.
In the second method, the emergency heat relay is cycled directly by the thermostat mercury bulb. In this hookup, the relay is controlled by the thermostat first stage. The emergency heat relay energizes all of the auxiliary heat relays on a call for heat. See Fig. 42.
So the emergency heat is controlled by the first stage of the thermostat. The emergency heat relay energizes all of the electric strip heaters so the heat and the indoor fan come on together as soon as the first stage calls for heat.
With the first method, the fan remains on (being controlled by the first stage of the thermostat) and the electric heaters cycle on and off with the second stage.
In either case, a subbase indicator light is turned on whenever the function switch is in the emergency heat (EM.HT.) position.
Fig. 41. Emergency heat relay that bypasses the outdoor thermostats.
Fig. 42. Emergency heat relay that energizes all of the auxiliary heat relays on a call for heat.
Crankcase HeatIn any mechanical refrigeration system, refrigerant tends to migrate to the coldest part of the equipment and condense there. In a heat pump, this coldest spot could be the compressor because it is usually outdoors. In addition, the oil in the com-pressor crankcase is capable of absorbing a high concentration of refrigerant. On compressor startup, there are two risks: (1) the liquid refrigerant, which is noncompressible, can be drawn into the cylinder, and (2) considerable oil can be entrained in the refrigerant and swept out of the crankcase through the changeover valve and dispersed in the piping and coils.
So the migration of refrigerant to the crankcase is undesirable because it can interfere with system lubrication and because the liquid refrigerant must be kept from going through the compressor.
Adding a crankcase heater creates enough temperature differential to prevent this migration because the compressor is no longer the coldest part of the system so refrigerant does not migrate to it.
Compressor Fault RelayAnother very simple method of detecting a compressor failure has been developed. It uses the voltage developed across the capacitor in a permanent split capacitor compressor motor.
The principle involved is that virtually all serious problems reduce the voltage across the motor capacitor. By carefully selecting the correct coil voltage, the normally closed relay does not pull in unless the proper voltage builds up across the capacitor, which brings on the SERVICE LED. See Fig. 43.
Here is how it works:� On a call for cooling, the thermostat makes R to Y, the
contactor coil is powered, and the compressor motor turns on.� At the same time, the indicator light is energized.� As the motor gets up to speed�about one second, the
fault relay sees enough voltage to pull in. Its normally closed contact opens and the indicator light goes out.
� Anything that prevents the motor from running prevents the fault relay from pulling in.
Fig. 43. Compressor fault relay schematic.
M5833
COMPRESSOR
THERMOSTAT
FUNCTIONSWITCH
HEAT 2 HEAT 1
EMERGENCY HEAT RELAY CONTACT EMERGENCY
HEAT RELAY
AUXILIARYHEAT RELAY 1
AUXILIARYHEAT RELAY 2
OUTDOORTHERMOSTAT
M5832
COMPRESSOR
THERMOSTAT
FUNCTIONSWITCH
HEAT 2 HEAT 1
EMERGENCYHEAT RELAYCONTACT
24 V
EMERGENCYHEAT RELAY
AUXILIARYHEAT RELAY
RISE
L1 (HOT)
L2
M5831
COMPRESSOR MOTOR FAULT RELAY
Y R L X
LED
CAP.
RUN
START S
R
C
L1
L3
CONTACTORTHERMOSTAT-SUBBASE
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
29 60-2485�8
CROSS REFERENCEThe following section lists the current T874 Trade replace-ments for T872 and T874 Multistage Thermostats. It also lists the Q674 Trade replacements for Q672 and Q674 Subbases.
All thermostats listed carry the Honeywell logo unless otherwise noted.
When using the Cross Reference Charts, refer to the following instructions:
1. Locate and identify the existing thermostat and subbase model.
2. Refer to the Model Number column to find the model that matches the existing thermostat and subbase.
3. The Description column identifies certain characteristics of the existing device.
4. The Trade Replacement column identifies the correct replacement device.
5. The Remarks column lists any characteristics or adjust-ments to be made on the Trade replacement model.
6. The Fig. No. column lists the wiring hookup used for the specific model number. The wiring diagrams follow the Cross Reference section.
7. Refer to the circuit illustration that corresponds with the appropriate number. This figure illustrates the internal electric circuit for the desired model number.
Table 6. T872-T874 Thermostat Cross Reference.
Model Number DescriptionT874 Trade
Replacementa RemarksT872A 1-stage heat, 1-stage cool
A1006 Standard OEM T874A1036A1014 72-78°F (22-26°C) stop; locking cover; no
thermometerT874A1010 Use T874A1176 for Dept. of
Defense (DoD) application.A1022 Heat anticipator set at 0.45A T874A1036A1030 0.4A heat anticipator setting T874A1036A1048 TRADELINE T874A1036A1055 AAF logo; locking cover T874A1036A1063 Climatrol logo T874A1036A1071 Lennox logo; 0.5A heat anticipator setting T874A1036A1089 Melco logo T874A1036A1097 Westinghouse logo T874A1036A1105 Amana logo; 1.2A heat anticipator setting T874A1036A1113 Trane logo T874A1036A1121 Airtemp (Chrysler) logo T874A1036A1139 Singer logo; no. 02005384 T874A1036A1147 American Standard logo T874A1036A1154 Carrier logo and color; no. HH07AT074 T874A1036A1162 General Electric logo; no. AY28X097 T874A1036A1170 Sears logo; no. 4291441 T874A1036A1188 Command-Aire logo T874A1036A1196 Singer logo; Celsius scale; no. 02005521 T874A1036A1204 Carteret logo T874A1036A1212 General Electric; no. AY28X114; 72-78°F
(22-26°C) stopT874A1010 Use T874A1176 for Dept. of
Defense (DoD) application.A1220 Singer logo; no. 050240-01 T874A1036A1238 Celsius scale T874A1036A1246 TRADELINE; locking cover and adjustable locking
lever stopsT874A1150
A1253 Trane Comfort Corp T874A1036A1261 TRADELINE; 72-78°F (22-26°C) stop; locking
cover; no thermometer; meets DoD specs T874A1176
a When replacing a T872 Thermostat and Q672 Subbase, always replace both the thermostat and the subbase.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 30
A1279 General Electric logo; no. AY28X114A; 75°F stop; locking cover; no thermometer.
T874A1010 Use T874A1176 for Dept. of Defense (DoD) application.
A1287 General Electric; no. AY28X097A; fan current shunt for auto fan in heating; heat anticipator set at 0.4A.
T874A1036/Q674B1018
Set thermostat stage 1 heat anticipator for total of fan and stage 1 primary control current draw.
A1295 Lennox; Celsius scale T874A1036A1303 Lennox logo; no. 64A0601; meets DoD specs T874A1176A1311 Envirotron special; Celsius scale T874A1010A1329 Carrier logo; Celsius scale; no. HH07AT074C T874A1036A1337 Square D; no. HCD-3; heat anticipator set at 0.2A T874A1036A1345 TRADELINE; Celsius scale T874A1010A1352 Heat anticipator set 1.2A T874A1036A1360 Friedrich logo; heat anticipator set at 0.2A T874A1036A1378 Wesco logo; heat anticipator set at 0.8A T874A1036
T872B 1-stage heat, 2-stage coolB1005 Standard OEM T874B1019B1013 0.4A heat anticipator setting T874B1019B1021 TRADELINE T874B1019B1039 Westinghouse logo T874B1019B1047 American Standard logo T874B1019B1054 Climatrol logo T874B1019B1062 Carrier logo T874B1019B1070 Trane logo T874B1019B1088 Fedders logo T874B1019B1096 Climatrol logo T874B1019B1104 Carteret logo T874B1019B1112 Singer logo; no. 050240-03 T874B1019B1120 Celsius scale T874B1019B1138 Singer logo; no. 02005711; locking cover and
lever.T874B1019
B1146 Lennox logo; no. P-8-8895 T874B1019B1153 Lennox logo; Celsius scale T874B1019
T872C 2-stage heat, 1-stage coolC1004 Standard OEM T874C1018C1012 Heat anticipator set at 0.4A T874C1018C1020 72-78°F (22-26°C) stop; locking cover; no
thermometer; 42-88°F (6-31°C) setpoint range.T874C1141 Use T874C1141 for Dept. of
Defense (DoD) application.C1038 TRADELINE T874C1018C1046 American Standard logo T874C1018C1053 Friedrich logo T874C1018C1061 Lennox logo; no. P-8-8896 T874C1018C1079 Westinghouse logo; stage 1 heat anticipator set at
0.75A; stage 2 anticipator set at 1.2AT874C1018
C1087 Fast cycle performance on both heat stages; anticipator range 0.12-0.6A
T874C1018 Adjust anticipator faster for correct performance.
C1095 Payne logo; no. 0.1-0.175 T874C1018
Table 6. T872-T874 Thermostat Cross Reference.
Model Number DescriptionT874 Trade
Replacementa Remarks
a When replacing a T872 Thermostat and Q672 Subbase, always replace both the thermostat and the subbase.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
31 60-2485�8
C1103 Amana logo; anticipator set at 1.2A T874C1018C1111 Airtemp (Chrysler) logo T874C1018C1129 Day and Night logo; no. 0.1-0.174 T874C1018C1137 Fast cycle performance on both heat stages T874C1018 Adjust anticipator faster for correct
performance.C1145 Rheem logo T874C1018C1152 Ruud logo T874C1018C1160 Climatrol logo T874C1018C1178 Wesco logo T874C1018C1186 Sears logo T874C1018C1194 First Co. logo T874C1018C1202 Carrier logo T874C1018C1210 Carrier logo; Celsius scale T874C1018C1228 0.4A heat anticipator setting T874C1018C1236 Carrier logo; no. HH07AT070 T874C1018C1244 Fraser-Johnson logo T874C1018C1251 Trane logo T874C1018C1269 Fedders logo T874C1018C1277 Climatrol special T874C1018C1285 Autogas logo T874C1018C1293 Fedders logo T874C1018C1301 Climatrol logo T874C1018C1319 Command-Aire logo T874C1018C1327 Melco logo; lock cover and levers T874C1018C1335 Singer logo (Carteret) T874C1018C1343 Singer logo; no. 050240-04 T874C1018C1350 Celsius scale T874C1018C1368 12°F (67°C) differential between heat 1 and
heat 2T874C1125
C1376 AAF logo; locking cover; 72-78°F (22-26°C) stop T874C1018C1384 Servel logo T874C1018C1392 TRADELINE; fast cycle performance on both heat
stages.T874C1018 Adjust anticipator faster for correct
performance.C1400 72-78°F (22-26°C) stop; locking cover; no
thermometer; meets DoD specsT874C1141
C1418 Solaron logo T874C1018C1426 Lennox logo; no. 42C04; four LEDs NoneC1434 Carrier logo; no. HH07AT070C; Celsius scale T874C1018C1442 Goettl logo T874C1018C1459 Goettl logo; used with Q672N1001, N1019 NoneC1467 Lennox logo; Celsius scale T874C1018C1475 Tappan logo; no. 080-13708-37 T874C1018C1483 Fasco logo; no. 1230-8161 T874C1018C1491 Lennox logo; no. 64A0501; locking cover; no
thermometer; meets DoD specsT874C1141
Table 6. T872-T874 Thermostat Cross Reference.
Model Number DescriptionT874 Trade
Replacementa Remarks
a When replacing a T872 Thermostat and Q672 Subbase, always replace both the thermostat and the subbase.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 32
C1509 Fedders logo; used with Q672L1102 Y594R1425 Wiring differences (old=new): C=X, K=E; remove Y-W1 jumper.
C1517 Climatrol logo; used with Q672L1102 Y594R1425 Wiring differences (old=new): C=X, K=E; remove Y-W1 jumper.
C1525 Square D logo; no. HCD-2 T874C1018C1533 Airtemp logo T874C1018C1541 Airtemp logo; used with Q672L1102 Y594R1425 Wiring differences (old=new): C=X,
K=E; remove Y-W1 jumper.C1566 TRADELINE; Celsius scale T874C1018 Replacement has °F scaleplate.C1574 Whalen special; used with Q672B1269 NoneC1582 Lennox; meets DoD NoneC1590 Singer; 8°F (4.4°C) differential between stage
1 and stage 2T874C1125 Replacement has 2°F (1° C)
differential between H1 and H2.C1608 Singer logo; no. 02005784 8°F (4.4°C) differential
between stage 1 and stage 2T874C1125 Replacement has 2°F (1°C)
differential between H1 and H2.C1616 Celsius scale; stop set at 23°C None Add 4074ECK adjustable stop.C1624 Heat Wave logo; no. 0360-116 T874C1018C1632 York logo; heat anticipator set at 0.2A T874C1018C1640 Heat anticipator set at 0.4A T874C1018C1665 Wesco logo; heat anticipator set at 0.8A T874C1018C1673 Wards logo; used with Q672B1285, B1293 Gas systems:
T874C1018/ Q674B1034 Electric systems: T874C1018/ Q674B1075
Adjust anticipator faster for correct performance.
C1681 Lechauffage Urbain logo; Celsius scale T874C1018C1699 Duotherm logo; used with Q672E1068 or
Q672F1000T874C1018 See subbase description for
replacement information.C1707 Sigler logo; used with Q672N1027 NoneC1715 Westinghouse logo T874C1018
T872D 2-stage heat, 2-stage coolD1003 Standard OEM T874D1165D1011 TRADELINE T874D1165D1029 Westinghouse logo T874D1165D1037 Climatrol logo T874D1165D1045 Lennox logo; no. P-8-8897; used with Q672E1191. T874D1165D1052 York logo T874D1165D1060 Singer logo; no. 02005385 T874D1165D1078 Rheem logo T874D1165D1086 Rudd logo T874D1165D1094 York logo; locking cover T874D1165D1102 American Standard logo T874D1165D1110 ITT logo T874D1165D1128 Carrier logo T874D1165D1136 No anticipator on stage 1 cool; used with
Q672C1029T874D1165
Table 6. T872-T874 Thermostat Cross Reference.
Model Number DescriptionT874 Trade
Replacementa Remarks
a When replacing a T872 Thermostat and Q672 Subbase, always replace both the thermostat and the subbase.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
33 60-2485�8
D1144 Carrier logo; no. HH07AT072 T874D1165D1151 General Electric logo; no. AY28X098; 0.4 heat
anticipator settingT874D1165
D1169 Airtemp (Chrysler) logo; used with Q672E1118 T874D1165/Q674E1049
Wiring differences (old=new): A=W1; set H1 anticipator to 1.2A.
D1177 Trane logo T874D1165D1185 Dunham-Bush logo T874D1165D1193 Fedders logo T874D1165D1201 Climatrol logo T874D1165D1219 Command-Aire logo T874D1165D1227 Singer logo; no. 02005522; Celsius scale T874D1165D1235 Singer logo; (Carteret) T874D1165D1243 Friedrich logo T874D1165D1250 Singer logo; no. 050240-02 T874D1165D1268 Airtemp logo T874D1165D1276 Celsius scale T874D1165D1284 Solaron T874D1165D1292 Tokyo Carrier logo; no. HH07AT072C; Celsius
scaleT874D1165
D1300 SUPER TRADELINE T874D1165D1318 General Electric logo; no. AY28X098A; fan current
shunt for auto fan in heating.T874D1165/Q674B1075
D1326 General Electric logo; locking cover 72-78°F (22-26°C) stop; fan current shunt for auto fan in heating.
T874D1165
D1334 Lennox logo; Celsius scale T874D1165D1342 Tappan logo; no. 080-13708-32 T874D1165D1359 Singer logo; no. 02005740; Celsius scale; 6.6°C
differential between H1 and H2.T874D1165 Only 2°F (1°C) differential between
H1 and H2.D1367 Friedrich logo; no. 600-580-23 T874D1165D1375 Singer logo; no. 02005713; Celsius scale; controls
2 separate heat/cool circuits; used with Q674G1017
None
D1383 TRADELINE; Celsius scale T874D1165D1391 Singer logo; no. 02005712; controls two separate
heat/cool circuits; used with Q674G1017None
D1409 12°F (7°C) differential between H1 and H2 T874D1165D1417 Fedders logo T874D1165D1425 Climatrol logo T874D1165D1433 Singer logo; no. 02005785; 8°F (4.4°C) differential
between H1 and H2T874D1165
D1441 American Air Filter T874D1165D1474 Carrier; no. HH07AT072-03; Celsius scale T874D1165
T872E 2-stage coolE1002 Standard OEM T874E1016E1010 TRADELINE T874E1016E1028 Westinghouse logo T874E1016
Table 6. T872-T874 Thermostat Cross Reference.
Model Number DescriptionT874 Trade
Replacementa Remarks
a When replacing a T872 Thermostat and Q672 Subbase, always replace both the thermostat and the subbase.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 34
E1036 American Standard logo T874E1016E1044 York logo; locking cover T874E1016E1051 ITT logo T874E1016E1069 Climatrol logo T874E1016E1077 Airtemp (Chrysler) logo T874E1016E1085 Lennox logo T874E1016E1093 Trane logo T874E1016E1101 Dunham-Bush logo T874E1016E1119 Fedders logo T874E1016E1127 Climatrol logo T874E1016E1135 General Electric logo; no. AY28X108 T874E1016E1143 Lennox logo; Celsius scale T874E1016E1150 Celsius scale T874E1016E1168 Airtemp logo T874E1016T872F 2-stage heatF1001 Standard OEM T874F1015F1019 TRADELINE T874F1015F1027 Lennox logo; fast cycle heat anticipator T874C1018F1035 Luxaire logo; fast cycle performance on both heat
stages.T874C1018 M839 draws 0.72A; set adjustable
heat anticipator to setting of 0.9A for proper cycle rate.
F1043 York logo; locking cover; used with M839. T874C1018F1050 Raehco logo T874F1015F1068 Fast cycle performance on both heat stages. T874C1018F1076 Wesco logo T874F1015F1084 Lennox logo T874F1015F1092 Auto Gas logo T874F1015F1100 Celsius scale T874F1015F1118 Lennox logo; Celsius scale T874F1015F1126 Stages 1 and 2 heat electrically isolated; used with
Q672D1002None
F1134 Square D logo; HCD-4 T874F1015F1159 Wesco logo; heat anticipator set at 0.8A T874F1015F1167 York logo T874F1015F1175 Oneida Heater logo; no. 30A0287-01; used with
Q672K1012.T874F1015/Q674K1026
T872G Heat pump models; 2-stage heat, 1-stage cool, 1-stage changeover.
G1000 Fast cycle performance stage 2 heat; fixed anticipator stage 1 heat and cool; changeover with cooling; used with Q672F1018.
Y594G1252 Wiring differences (old=new): W=W2, X1=X.
G1018 Adjustable anticipator stage 2 heat; fixed anticipator stage 1 heat and cool; changeover with cooling; used with Q672E1027.
Y594G1393 Wiring differences (old=new): Y1=O, Y2=Y.
Table 6. T872-T874 Thermostat Cross Reference.
Model Number DescriptionT874 Trade
Replacementa Remarks
a When replacing a T872 Thermostat and Q672 Subbase, always replace both the thermostat and the subbase.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
35 60-2485�8
G1026 Lennox logo; fast cycle performance; stage 2 heat; fixed anticipator stage 1 heat and cool; changeover with cooling; used with Q672E1019, F1067.
None See subbase description for replacement information.
G1034 Westinghouse logo; adjustable anticipator stage 2 heat; fixed anticipator stage 1 heat and cool; changeover with cooling; used with Q672F1091, F1141, F1257 or Q672J1013, J1062.
Y594G1252 Wiring differences (old=new): W=W2.
G1042 York logo; fixed anticipator on all stages heat and cool; changeover with cooling; used with Q672J1021.
Y594G1567
G1059 TRADELINE; no anticipator stage 2 heat; fixed anticipator stage 1 heat and cool; changeover with cooling; used with Q672J1039 outdoor reset.
Y594G1161 Designed for use on General Electric heat pumps.
G1067 Lennox logo; no. P-8-11222; fast cycle performance; stage 2 heat; fixed anticipator stage 1 heat and cool; changeover with cooling; used with Q672E1142, F1083.
See subbase description for replacement information.
G1075 Carrier logo; adjustable anticipator stage 2 heat; fixed anticipator stage 1 heat and cool; changeover with cooling; used with Q672J1054, L1052.
See subbase description for replacement information.
G1083 Adjustable anticipator stage 2 heat; fixed anticipator stage 1 heat and cool; changeover with cooling; includes shunt to bypass stage 2 anticipator with auxiliary heat relays; used with Q672F1158.
Y594G1252
G1091 Lennox logo; same as T872G1026 except meets DoD specs.
See subbase description for replacement information.
G1109 Tappan logo; no. 080-13708-52; adjustable anticipator stage 1 heat and cool; changeover with cooling; used with Q672F1117.
Y594G1252 Wiring differences (old=new): C=X.
G1117 Changeover; used with Q672F1125. Y594G1252 Wiring differences (old=new): C=X.G1125 Lennox logo; no. 63A0401; Celsius scale; isolated
auxiliary heat power circuit; fast cycle anticipator stage 2 heat.
None
G1133 Rheem logo; no. RXMT-B71; adjustable anticipator stage 2 heat; fixed anticipator stage 1 heat and cool; changeover with cooling; includes shunt to bypass stage 2 anticipator with auxiliary heat relays; used with Q672F1158, F1232.
Y594G1252
G1141 Ruud logo; adjustable anticipator stage 2 heat; fixed anticipator stage 1 heat and cool; changeover with cooling; includes shunt to bypass stage 2 anticipator with auxiliary heat relays; used with Q672F1158.
Y594G1252
G1158 Carrier logo; same as T872G1075. Except DoD styling.
See subbase description for replacement information.
G1166 BDP used with Q672F1125. Y594G1252 Wiring differences (old=new): C=X.G1174 BDP used with Q672F1125. Y594G1252 Wiring differences (old=new): C=X.G1182 Carrier; no. HH07AT071C; Celsius scale; used
with Q672L1052, J1054. See subbase description for
replacement information.G1190 Tappan; no. B13708-57; used with Q672L1078 for
8 and 10 ton heat pumps with 2 compressors.None
Table 6. T872-T874 Thermostat Cross Reference.
Model Number DescriptionT874 Trade
Replacementa Remarks
a When replacing a T872 Thermostat and Q672 Subbase, always replace both the thermostat and the subbase.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 36
G1208 Marvair logo; special for Crispaire; used with Q672F1166, F1323.
Y594G1393
G1216 Janitrol logo; no. 26G05; stage 2 heat anticipator set at 1.2A; used with Q672F1117.
Y594G1252 Wiring differences (old=new): C=X.
G1224 TRADELINE; adjustable anticipator stage 2 heat; fixed anticipator stage 1 heat and cool; changeover in cool; used with Q672F1208.
Y594G1419
G1232 Heat Wave (Southwest Mfg.) logo; stage 2 heat anticipator set at 1.2A; used with Q672F1224.
G1240 Lennox; fast cycle anticipator stage 2 heat; used with Q672F1240.
None
G1257 Carrier logo; no. HH07AT073; used with Q672L1169 (HH93AZ071).
None
G1265 Addison logo; used with Q672F1265. Y594G1252 Wiring differences (old=new): C=X.G1273 Carrier logo; (DoD model); 68°F (20°C) maximum
heating; 78°F (26°C) minimum cooling; used with Q672L1052, J1054
See subbase description for replacement information.
G1281 Wesco logo; used with Q672F1265. Y594G1252 Wiring differences (old=new): C=X.G1299 York logo; meets DoD specs; used with
Q672L1177.Y594G1567
G1307 Carrier; no. 38EQ1900; Celsius; used with Q672J1054, L1052.
See subbase description for replacement information.
G1315 Luxaire special; stage 2 heat anticipator set to 1.2A; used with Q672F1281.
Y594G1252
G1323 Lennox special; used with Q672L1201 and C815A1013.
None
G1331 York; used with Q672J1021. Y594G1567 Wiring differences (old=new): X=X1, L=X2, W=E; Y1-W1 and Y2-W2 jumpers required.
G1356 Westinghouse; used with Q672L1219. T874D1165/Q674F1022
Wiring differences (old=new): X=X1, L=X2, W=E; Y1-W1 and Y2-W2 jumpers required.
G1364 York; used with Q672D1077. NoneG1372 Tappan/Janitrol logo; no. B-13708-521;
used with Q672F1117.Y594G1252 Wiring differences (old=new): C=X.
G1398 York logo; no. 025-21454C; used with Q672J1021. Y594G1567T872H Heat pump model; 1 stage heat,
1 stage cool, 1 stage changeover.H1009 Command-Aire logo; fixed anticipator stage 1 heat
and cool; changeover with cooling; used with Q672C1086.
Y594H1012
H1017 Friedrich logo. Y594H1012H1025 Friedrich logo; Celsius. Y594H1012T872M 1 stage heat, 1 stage cool with stage 2 heat factory
set at 60°F (16°C).M1003 Standard OEM; used with Q672D and external
switching means.T874C1125 T874C1125 has 12°F (6.7°C)
differential between stage 1 and stage 2 heat.
T872N Heat pump model; 2-stage heat, 1-stage cool plus changeover, changeover in heat mode.
N1002 None
Table 6. T872-T874 Thermostat Cross Reference.
Model Number DescriptionT874 Trade
Replacementa Remarks
a When replacing a T872 Thermostat and Q672 Subbase, always replace both the thermostat and the subbase.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
37 60-2485�8
N1010 Williamson logo; adjustable anticipator stage 1 and 2 heat; fixed anticipator stage 1 cool; used with Q672F1133 or F1315.
T874N1016/Q674F1220
N1028 TRADELINE heat mode changeover; used with Q672F1216.
T874N1016
N1036 Bard; used with Q672F1299. T874N1016/Q674F1220
N1044 Thermotron logo; 1st stage changeover heat mode; used with Q672F1299.
T874N1016/Q674F1220
T872Q 1-stage heat; used with another T872 for heating setback.
Q1009 Standard OEM T874C1125Q1017 York logo T874C1125 Replacement only good for
1-stage heat and 1-stage cool applications.
Q1025 ITT logo NoneQ1033 Lennox logo; no. P-8-8899. NoneQ1041 Lennox logo; no. 63A6401. None
T872R Heat pump model; 2-stage heat, 1-stage cool, manual changeover.
R1008 Fixed anticipator stage 1 heat and cool; no anticipator stage 2 heat; changeover with cooling; used with Q672B1046.
Y594R1425 Wiring differences (old=new): W=W2; W1-Y1 jumper required.
R1016 Addison same as T872R1008; used with Q672B1103.
Y594R1425 Wiring differences (old=new): W=W2; W1-Y1 jumper required.
R1024 Lennox logo; fast cycle stage 2 heat; fixed anticipator stage 1 heat and cool; changeover with cooling; used with Q672B1160 and Q672L1003.
See subbase description for replacement information.
R1032 York logo; fixed anticipator stage 1 and 2 heat and stage 1 cool; changeover with cooling; used with Q672L1011.
Y594R1664
R1040 Lennox logo; fast cycle stage 2 heat; fixed anticipator stage 1 heat and cool; isolated stage 2 heat switch; changeover with cooling; used with Q672B1202 no. P-8-11221, Q672L1029
See subbase description for replacement information.
R1057 TRADELINE; fixed anticipator stage 1 heat and cool; no anticipator stage 2 heat; changeover on cooling; used with Q672L1037; outdoor reset.
Y594R1763 Designed for use on General Electric heat pumps. Wiring differences (old=new): A=T.
R1065 Adjustable anticipator stage 2 heat; fixed anticipator stage 1 heat and cool; changeover on cooling; used with Q672L1045.
Y594R1243
R1073 Lennox logo; no. 63A0301; Celsius scale; separate auxiliary heat power circuit; fast cycle stage 2 heat antic.
None
R1081 Ruud logo; same circuit as T872R1065; used with Q672L1045, L1136.
Y594R1243
R1099 Dunham Bush special; used with Q672L1060, L1383.
Y594R1243
R1107 Rheem; no. RXMT-B70; used with Q672L1045, L1136.
Y594R1243
R1115 Friedrich logo; fixed anticipator; used with Q672B1244, L1086.
See subbase description for replacement information.
Table 6. T872-T874 Thermostat Cross Reference.
Model Number DescriptionT874 Trade
Replacementa Remarks
a When replacing a T872 Thermostat and Q672 Subbase, always replace both the thermostat and the subbase.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 38
R1123 York logo; no. 025-21453C; Celsius scale. Y594R1664R1131 Lennox logo; separate auxiliary heat power circuit;
fast cycle stage 2 heat anticipator; outdoor reset; used with Q672L1144, C815A1013.
None
R1149 Westinghouse logo; adjustable stage 2 heat anticipator; cooling changeover; fixed anticipator stage 1 heat and cool; used with Q672L1110, L1128, L1151.
Y594R1243 Wiring differences (old=new): W=W2.
R1156 Marvair logo; used with Q672L1094, L1250. Y594R1243 Replacement has auto fan in Emergency Heat mode.
R1164 Bard; used with Q672L1185. Y594R1243R1172 Heil Quaker; used with Q672L1193. Y594R1243 Wiring differences (old=new): B=X,
W=W2.R1180 York; Celsius; used with Q672L1011. Y594R1664R1198 TRADELINE; used with Q672L1227 Y594R1243R1206 For use with W89; used with Q672L1235. NoneR1214 Intertherm logo; used with Q672L1276. Y594R1300 Wiring differences (old=new):
W1=B, Z=L, K=E.R1222 York logo; used with C815A1039; adjustable
anticipator stage-2 heat; used with Q672L1284Y594R1672
R1230 Amana logo; no. C62397-1; used with Q672L1300, W89.
None
R1255 Singer logo; used with Q672L1326 and W89. NoneR1271 Westinghouse logo; used with Q672L1375 and
W89.Y594R1664
R1297 York; Celsius scale; used with Q672L1011. NoneR1305 Used with Q672L1235 and W89. NoneR1321 Duotherm logo; used with Q672L1409, and W89. NoneR1339 Williamson; used with Q672L1391. Y594R1243
T872S Heat pump model; 2-stage heat plus changeover, 1-stage cool.
S1005 Westinghouse logo; adjustable anticipator stage 1 and 2 heat; fixed anticipator stage 1 heat; changeover with heating: used with Q672C1045
T874C1018/Q674C1058
Wiring differences (old=new): V=RC-RH, F=G, C=Y1, Z=B, H2=W2; W1-Y1 jumper required.
T872T 1-heat stage, 1-vent and 2-cool stages.T1004 Trane logo; used with Q672B1129. None
T872W 3-heat stages, 2-cool stages, manual changeoverW1019 Lennox logo; no. 52C7501; used with Q672L1342
and C815A1013.None
W1027 Westinghouse logo; used with Q672L1268 and C815A1021.
None
W1035 TRADELINE; used with C815A1043 and Q672B1251.
Y594W1014
Table 6. T872-T874 Thermostat Cross Reference.
Model Number DescriptionT874 Trade
Replacementa Remarks
a When replacing a T872 Thermostat and Q672 Subbase, always replace both the thermostat and the subbase.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
39 60-2485�8
Table 7. Q672-Q674 Subbase Cross Reference.
Model Number DescriptionQ674 Trade
Replacementa RemarksQ672A System: HEAT-AUTO-COOL, Fan: AUTO-ON
A1005 Standard OEM Q674A1019A1013 TRADELINE Q674A1019A1021 RC-RH jumper Q674A1019 RC-RH jumper required.A1039 RC-RH jumper; Chek Lite Q674A1019 RC-RH jumper required.
Q672B System: HEAT-OFF-COOL, Fan: AUTO-ONB1004 Standard OEM Q674B1034B1012 Isolated G terminal. Q674B1018B1020 System: HEAT-OFF-RESET-COOL Q674B1034 Used system off as reset position.B1038 TRADELINE Q674B1034B1046 Heat pump circuit; used with T872R1008. Y594R1425 Wiring differences (old=new):
W1=Y1, W=W2.B1053 RC-RH jumper Q674B1034 RC-RH jumper required.B1061 Chek Lite Q674B1034B1079 Auto fan operation in heat and cool. Q674B1075B1087 Carrier no. HH93AZ078; RC-RH jumper. Q674B1075B1095 Carrier no. HH93AZ084; RC-RH jumper. Q674B1034B1103 Addison; heat pump circuit; used with
T872R1016.Y594R1425 Wiring differences (old=new):
W=W2; W1-Y1 jumper required.B1111 Carrier no. HH93AZ080; isolated G terminal. Q674B1018B1129 Trane special circuit; used with T872T1004. NoneB1137 RC-RH jumper; isolated G terminal. Q674B1018 RC-RH jumper required.B1145 Fedders special Q674B1034 RC-RH jumper required.B1152 Fedders special; auto fan operation in heat
and cool.Q674B1075
B1160 Lennox; heat pump circuit; used with T872R1024; includes compressor lockout in EM. HT.
Y594R1243 Wiring differences (old=new): V-VR=R, M=Y, Y=W2, F=G, R=O.
B1178 General Electric no. AY28X107; auto fan operation in heat and cool.
Q674B1075
B1186 Trane; isolated G terminal; Filter LED. Q674B1018B1194 General Electric no. AY28X124; auto fan
operation in heat and cool.Q674B1075 Set T874 stage-1 anticipator for
combined load of heat relay and fan relay.
B1202 Lennox no. P-8-11223; heat pump circuit; used with T872R1040.
Y594R1243 Wiring differences (old=new): V-VR=R, M=Y, Y=W2, F=G, R=O.
B1210 NoneB1228 General Electric no. BAY28X137; isolated
G terminal.Q674B1018
B1236 Carrier no. HH-93AZ079; RC-RH jumper; LOCKOUT LED indicates compressor lockout switch activated.
Q674B1034 RC-RH jumper; LED cannot be provided in TRADELINE model.
B1244 Friedrich; heat mode changeover; used with T872R1115.
T874C1018/Q674B1034
Wiring differences (old=new): C=no connection; RC-RH and W1-Y1 jumpers required.
B1251 Used with T872W1035 and C815A1043. Y594W1014a When replacing a T872 Thermostat and Q672 Subbase, always replace both the thermostat and subbase.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 40
B1269 Whalen; Hi-Lo fan switch; constant fan in heat and cool system switch positions; used with T872C1574.
None
B1277 Square D no. HCB-5. Q674B1034B1285 Wards; RC-RH and F-W3 jumpers; used with
T872C1673.Gas Furnace: T874C1018/Q674B1034Electric Furnace: T874C1018/Q674B1075
Adjust anticipator faster for correct performance.
B1293 Lennox no. 41C96; used with T872C1673. Same as Q672B1285
Q672C System: OFF-AUTO, Fan: AUTO-ONC1003 Standard OEM Q674C1058C1011 Westinghouse; RC-RH jumper. Q674C1058 RC-RH jumper required.C1029 W1-Y2 jumper; for heat pump; used with
T872D1136.Q674E1049 Replacement has heat/cool system
switching.C1037 Chrysler Airtemp; System: COOL-OFF-AUTO. Q674C1058C1045 Westinghouse; heat pump; used with
T872S1005.T874C1018/Q674C1058
Wiring differences (old=new): V=RC-RH, F=G, C=Y1, Z=B, H2=W2; W1-Y1 jumper required.
C1052 Isolated stage 2 heat circuit for dc electric heat relay.
Recontrol Use T874G1246/Q674F1212 which adds HEAT-COOL-EM.HT. system switch.
C1060 Fedders special. Q674C1058C1078 General Electric no. AY28X109. Q674C1058C1086 Command-Aire; heat pump; used with
T872H1009.Y594H1012
C1102 TRADELINE Q674C1058Q672D System: None. Fan: None.
D1002 Standard OEM; used with T872F1126. Q674D1040D1010 Lennox special. NoneD1028 Carrier; RC-RH jumper. NoneD1036 Carrier no. HH93AZ070; RC-RH jumper. Q674D1040 RC-RH jumper required.D1044 General Electric no. AY-28X100. NoneD1069 Square D no. HCB-4. NoneD1077 York; used with T872G1364. NoneD1085 TRADELINE Q674D1040
Q672E System: OFF-HEAT-AUTO-COOL Fan: AUTO-ON
E1001 Standard OEM Q674E1049E1019 Lennox no. P-8-8892; heat pump; cool mode
changeover; used with T872G1026.T874D1165/Q674B1075
E1027 Heat pump circuit; W1-Y2 jumper; cool mode changeover; used with T872G1018.
Y594G1393 Wiring differences (old=new): Y1=O, Y2=Y.
E1035 Heat pump circuit; W1-Y2 jumper; cool mode changeover.
Y594G1393 Wiring differences (old=new): Y1=O, Y2=Y.
E1043 Heat pump circuit; heat mode changeover. Q674E1049 Wiring differences (old=new): W1=B, W2=W1; W1-Y1 jumper.
Table 7. Q672-Q674 Subbase Cross Reference.
Model Number DescriptionQ674 Trade
Replacementa Remarks
a When replacing a T872 Thermostat and Q672 Subbase, always replace both the thermostat and subbase.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
41 60-2485�8
E1050 TRADELINE Q674E1049E1068 RC-RH jumper; used with T872C1699. Q674E1049 RC-RH jumper required.E1076 RC-RH internal jumper; EM. HT. LED. Q674E1049 RC-RH jumper required.E1084 Carrier no. HH93AZ076; RC-RH jumper. Q674E1049 RC-RH jumper required.E1092 Carrier no. HH93AZ082; RC-RH jumper; B
terminal; isolated G terminal.Q674E1049
E1100 General Electric no. AY28X099. Q674E1049E1118 Airtemp; heat pump; used with T872D1169. T874D1165/
Q674E1049Wiring differences (old=new): A=W1; set H1 anticipator to 1.2A.
E1126 Common R terminal. Q674E1049 RC-RH jumper required.E1134 ITT Nesbitt; RC-RH jumper; O and B terminals;
isolated G terminal.Q674E1049
E1142 Lennox no. P-8-11224; heat pump; V-VR jumper; cool mode changeover; used with T872G1067.
Y594G1252 Wiring differences (old=new): V-VR=R, Y=W2, R=O, M=Y, F=G.
E1159 Carrier no. HH93AZ077; RC-RH jumper; LOCKOUT LED indicates activation of compressor lockout switch.
Q674E1049 RC-RH jumper required; no LED in TRADELINE model.
E1167 Square D no. HCB-2; Chek Lite. Q674E1049E1183 Square D no. HCB-3. Q674E1049E1191 Lennox; HIGH and LOW LEDs; used with
T872D1045.Q674E1049 No LEDs on replacement.
Q672F System: EM. HT.-HEAT-AUTO-COOL-OFFFan: AUTO-ON.
F1000 With EM. HT. LED; used with T872C1699. Q674F1022 Remove W3-X2 jumper to E-X2.F1018 Heat pump; heat mode changeover; Chek Lite;
used with T872G1000.Y594G1252 Wiring differences (old=new):
W=W2, X1=X.F1026 Chek Lite; W2-X2 jumper. Q674F1022F1034 Airtemp; EM. HT. LED; RC-RH and X2-E
jumpers.Q674F1022 If RC-RH jumper removed on
Q672F1034, Q674F1022 does not replace.
F1042 W2-X2 jumper; Chek Lite. Q674F1022F1059 Carrier no. HH93AZ074; EM. HT. LED. Q674F1022 Remove W2-X2 jumper to E-X2; X
terminal same as C.F1067 Lennox; heat pump; cool mode changeover;
EM. HT. LED; used with T872G1026.None
F1075 Heat pump circuit; EM. HT. LED; 2 terminal; RC-RH jumper.
None
F1083 Lennox no. P-8-11225; heat pump;V-VR jumper; cool mode changeover; EM. HT. LED; used with T872G1067.
None
F1091 Westinghouse; heat pump; EM. HT. LED; cool mode changeover; compressor lockout in EM. HT.; used with T872G1034.
Y594G1252 Wiring differences (old=new): W=W2.
F1109 Airtemp no. 3778567ACC; R-X2 jumper; EM. HT. LED.
Q674F1022 R-X2 jumper required.
F1117 Tappan no. 080-13708-53; heat pump; EM. HT. LED; cool mode changeover; compressor lockout and auto fan in EM. HT.; used with T872G1109, G1216, G1372.
Y594G1252 Wiring differences (old=new): C=X.
Table 7. Q672-Q674 Subbase Cross Reference.
Model Number DescriptionQ674 Trade
Replacementa Remarks
a When replacing a T872 Thermostat and Q672 Subbase, always replace both the thermostat and subbase.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 42
F1125 BDP no. 3442DP90; used with T872G1117, G1166, G1174.
Y594G1252 Wiring differences (old=new): C=X.
F1133 Williamson; heat pump; EM. HT. LED; heat mode changeover; compressor lockout in EM. HT.; used with T872N1010.
T874N1016/Q674F1220
F1141 Westinghouse; EM. HT. LED; auto fan in EM. HT.; used with T872G1034.
Y594G1252 Wiring differences (old=new): W=W2.
F1158 Rheem Ruud; heat pump; EM. HT. LED; cool mode changeover; compressor lockout in EM. HT.; used with T872G1083, G1133, G1141; auto fan in EM. HT.
Y594G1252
F1166 Crispaire; EM. HT. LED; used with T872G1208. Y594G1252F1174 Carrier no. HH93AZ081; EM. HT. LED. Q674F1022F1182 Square D no. HCB-1; Chek Lite; R-X2 jumper;
System: Aux. Heat replaces EM. HT.Q674F1022 R-X2 jumper; add monitor switch
between X1 and low side of power.F1190 EM. HT. LED; X2-E and RC-RH jumpers. NoneF1208 TRADELINE; cool mode changeover; EM. HT.
LED; used with T872G1224.Y594G1419
F1216 TRADELINE; heat mode changeover; EM. HT. LED; used with T872N1028.
T874N1016/Q674F1220
F1224 Heatwave (Southwest Mfg.); compressor lockout in EM. HT.; EM. HT. LED; used with T872G1232.
Y594G1252
F1232 Rheem; cool mode changeover; EM. HT. and AUX. HEAT LEDs; compressor lockout in EM. HT.; used with T872G1133.
Y594G1252
F1240 Lennox; cool mode changeover; EM. HT. and SERVICE LEDs; used with T872G1240.
None
F1257 Westinghouse; cool mode changeover; EM. HT. and AUX. HEAT LEDs; auto fan in EM. HT; used with T872G1034.
Y594G1252 Wiring differences (old=new): W=W2.
F1265 Wesco Addison; Chek and EM. HT. LEDs; used with T872G1281, G1265.
Y594G1252 Wiring differences (old=new): C=X.
F1273 Southwest special; no. 0361-136; W2-X2 jumper.
None
F1281 Luxaire special; used with T872G1315. Y594G1252F1299 Bard special; used with T872N1036, N1044. T874N1016/
Q674F1220F1315 Williamson special; used with T872N1010. T874N1016/
Q674F1220F1323 Crispaire special; used with T872G1208. Y594G1252
Q672G System: OFF-AUTO. Fan: None.G1009 Standard OEM Q674G1070G1017 Singer; O-B jumper; used with T872D1375. Q674G1070G1025 Includes O and B terminals. Q674G1070G1033 General Electric no. AY28X102. Q674G1070G1041 Singer no. 02005649; French wording; O-B
jumper.Q674G1070 Less French wording.
G1066 SLI-Mammoth; heat pump; heat mode changeover.
Q674G1070 Connect fan (G) wire to Y1 terminal; B-O and RC-RH jumpers.
Table 7. Q672-Q674 Subbase Cross Reference.
Model Number DescriptionQ674 Trade
Replacementa Remarks
a When replacing a T872 Thermostat and Q672 Subbase, always replace both the thermostat and subbase.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
43 60-2485�8
G1074 Singer no. 02005754; X1 and X2 terminals for field-added indicator lights; used with T872D1375.
None
G1082 Singer no. 02005792; X1 and X2 terminals for field-added indicator lights; used with T872D1375.
None
G1090 TRADELINE; B and O terminals. Q674G1070Q672H System: OFF-ON
Fan: NIGHT INT.-DAY CONT.H1008 Used with T872. None
Q672J System: EM. HT.-AUTO-OFFFan: AUTO-ON.
J1005 With EM. HT. LED; used with T872C or D. NoneJ1013 Westinghouse; heat pump; EM. HT. LED; cool
mode changeover; compressor lockout in EM. HT.; used with T872G1034.
Y594G1252
J1021 York; heat pump; EM. HT. LED; cool mode changeover; compressor lockout and auto fan in EM. HT.; E-W jumper; used with T872G1042, G1331, G1398.
Y594G1567
J1039 Heat pump; EM. HT. and AUX. HEAT LEDs; cool mode changeover; compressor lockout and auto fan in EM. HT.; used with T872G1059.
Y594G1161 Designed for use on General Electric heat pumps.
J1047 Singer no. 02005699; heat pump; EM. HT. LED; heat mode changeover.
Q674F1022
J1054 Carrier no. HH93AZ073A; heat pump; EM. HT. LED; cool mode changeover; compressor lockout in EM. HT.; used with T872G1075, G1182, G1307.
Y594G1252 Wiring differences (old=new): C=X.
J1062 Westinghouse; EM. HT. and AUX. HEAT LEDs; used with T872G1034.
Y594G1252 Wiring differences (old=new): W=W2.
Q672K System: OFF-HEAT-AUTO-COOL. Fan: None.K1004 Carrier no. HH93AZ072. Q674E1049 Fan switch does not function.K1012 Oneida Heater no. 30A0288-01; System: OFF-
WOOD-WOOD/OIL-OIL; used with T872F1175.T874F1155/Q674K1026
Q672L System: EM. HT.-HEAT-OFF-COOL. Fan: ON-AUTO.
L1003 Lennox; heat pump; EM. HT. LED; cool mode changeover; used with T872R1024.
Y594R1425
L1011 York; heat pump; EM. HT. LED; cool mode changeover; compressor lockout and auto fan in EM. HT.; used with T872R1032, R1180, R1297.
Y594R1664
L1029 Lennox no. P-8-11226; heat pump; EM. HT. LED; V-VR jumper; cool mode changeover; compressor lockout in EM. HT.; used with T872R1040.
Y594R1425 Wiring differences (old=new): V-VR=R, M=Y, Y=W2, F=G, R=O.
L1037 Heat pump; EM. HT. and AUX. HT. LEDs; cool mode changeover; compressor lockout and auto fan in EM. HT.; used with T872R1057.
Y594R1763 Wiring differences (old=new): A=T; designed for used on General Electric heat pumps.
L1045 Rheem; heat pump; EM. HT. LED; cool mode changeover; compressor lockout in EM. HT.; auto fan in EM. HT; used with T872R1065, R1081, R1107.
Y594R1243
Table 7. Q672-Q674 Subbase Cross Reference.
Model Number DescriptionQ674 Trade
Replacementa Remarks
a When replacing a T872 Thermostat and Q672 Subbase, always replace both the thermostat and subbase.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 44
L1052 Carrier no. HH93AZ075; heat pump; EM. HT. LED; cool mode changeover; compressor lockout in EM. HT.; used with T872G1075, G1182, G1273, G1307.
Y594R1615 Wiring differences (old=new): C=X.
L1060 Dunham Bush; EM. HT. LED; used with T872R1099.
Y594R1243
L1078 Tappan no. B13708-58; heat pump; EM. HT. LED; cool mode changeover; compressor lockout in EM. HT.; EM. HT. relay provides fan operation in EM. HT.; used with T872G1190.
None
L1086 Friedrich; heat mode changeover; EM. HT. LED; used T872R1115 with L terminal.
Y594R1243 Wiring differences (old=new): X2=E, C=X.
L1094 Crispaire; W2-H jumper; EM. HT. LED; used with T872R1065, R1156.
Y594R1243 Replacement has auto fan in Emergency Heat mode.
L1102 Fedders; heat mode changeover; EM. HT. LED; used with T872C1509, C1517, C1541.
Y594R1425 Wiring differences (old=new): K=E, C=X; remove Y-W1 jumper.
L1110 Westinghouse; EM. HT. LED; used with T872R1149.
Y594R1243 Wiring differences (old=new): W=W2.
L1128 Westinghouse; EM. HT. LED; used with T872R1149.
Y594R1243 Wiring differences (old=new): W=W2.
L1136 Rheem no. 41-20796-07; cool mode changeover; EM. HT. and AUX. HT. LEDs; used with T872R1081, T872R1107.
Y594R1243
L1144 Lennox; V-VR jumper; EM. HT. and SERVICE LEDs; isolated stage 2 heat; used with T872R1131, C815A1013.
None
L1151 Westinghouse; AUX. HT. and EM. HT. LEDs; used with T872R1149.
Y594R1243 Wiring differences (old=new): W=W2.
L1169 Carrier no. HH93AZ071; EM. HT. LED; used with T872G1257 (HH07AT073).
None
L1177 York; DoD; EM. HT. LED; used with T872G1299. Y594G1567L1185 Bard; used with T872R1164. Y594R1243L1193 Heil Quaker no. NAXA001TS01; used with
T872R1172.Y594R1243 Wiring differences (old=new): B=X,
W=W2.L1201 Lennox special; no. 1485701; used with
T872G1323.None
L1219 Westinghouse special; used with T872G1356. T874D1165/Q674F1022
Wiring differences (old=new): X=X1, L=X2, W=E; Y1-W1 and Y2-W2 jumpers required.
L1227 Heat pump; used with T872R1198. Y594R1243L1235 Intertherm; used with T872R1206, R1305. NoneL1250 Crispaire special; used with T872R1156 and
C815A1021.Y594R1243
L1268 Westinghouse special; used with T872W1027 and C815A1021.
None
L1276 Intertherm special; used with T872R1214. Y594R1300 Wiring differences (old=new): W1=B, Z=L, K=E.
L1284 York special; used with T872R1222. Y594R1672 L1300 Amana special; no. C62345-1; used with
T872R1230.None
L1326 Singer; used with T872R1255. None
Table 7. Q672-Q674 Subbase Cross Reference.
Model Number DescriptionQ674 Trade
Replacementa Remarks
a When replacing a T872 Thermostat and Q672 Subbase, always replace both the thermostat and subbase.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
45 60-2485�8
L1342 Lennox no. 52C7601; used with T872W1019 and C815A1013.
None
L1375 Westinghouse; used with T872R1271, W89. NoneL1383 Dunham Bush; used with T872R1099. Y594R1243L1391 Williamson; used with T872R1339. Y594R1243L1409 Duotherm special; used with T872R1321, W89. None
Q672N System: OFF-HEAT-COOL-EVAP.N1001 Goettl; heat pump; heat mode changeover;
evaporative cooler circuit; Fan: AUTO-ON; System: AUTO; used with T872C1459.
None
N1019 Goettl; heat pump; heat mode changeover; evaporative cooler circuit; W1-Y1 jumper; used with T872C1459.
None
N1027 Siegler special; used with T872C1707. NoneQ672P System: EM. HT.-HEAT-COOL.
P1009 Carrier special; no. HH93AZ069; used with T872G1075 (HH07AT071).
Y594R1243 Replacement has OFF system switch position
Table 7. Q672-Q674 Subbase Cross Reference.
Model Number DescriptionQ674 Trade
Replacementa Remarks
a When replacing a T872 Thermostat and Q672 Subbase, always replace both the thermostat and subbase.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 46
Table 8. T874 Cross Reference.
Model Number
Fig. No. Description
Trade Model Replacement Remarks
T874A 1-stage heat, 1-stage cool. A1002 44, 65 Honeywell logo; Standard OEM; used with Q674B1331. T874A1036A1010 44 Honeywell logo; includes Allen wrench and screws to
lock cover; non-adjustable range stops set at 72°F (max. heat) and 78°F (min. cool) (22-26°C); field adjustable locking levers.
T874A1010
A1028 44 Honeywell logo; heat anticipator factory set at 0.4A. T874A1036A1036 44 Honeywell logo; TRADELINE® model; includes Allen
wrench and screws to lock cover; field adjustable locking levers.
T874A1036
A1044 44 Obsolete. AAF/Snyder General logo; part no. 4ELN-3006C; °F/°C scaleplate.
T874A1036 Replacement has °F scaleplate.
A1051 44 Lennox logo; part no. 12F9901; °F/°C scaleplate; heat anticipator set at 0.45A.
T874A1036 Replacement has °F scaleplate.
A1069 44 Obsolete. Westinghouse logo; used with Q674A-E,G. T874A1036A1077 46, 82 Obsolete. Amana Air Conditioning logo; part no.
D68535-1; heat anticipator factory set at 1.2A; used with Q674B1075, E1056; used in Y594A1001, A1019.
T874A1036
A1085 44, 46,55, 66
Obsolete. Trane logo; part no. 13510451; used with Q674B1018, B1075, D1008.
T874A1036
A1093 44 Obsolete. McQuay logo; part no. 02005935; °F/°C scaleplate.
T874A1036 Replacement has °F/°C scaleplate.
A1101 51, 53 Carrier logo; part no. HH07AT174; used with Q674B. Y594C1421 or T874A1036a
When using the T874C1036, set stage 1 heat anticipator for total current draw of fan and stage 1 heat primary.
A1119 82 Obsolete. Sears logo; part no. 541. 91441/49. 9144; °F/°C scaleplate; used with Q674E1007; used in Y594A1068.
T874A1036 Replacement has °F scaleplate.
A1127 44 Obsolete. Climate Control logo; part no. 02005936; °C scaleplate.
T874A1036 Replacement has °F scaleplate.
A1135 44 Fedders multi-logo; part no. THTX-110-WCHA, 88-58-00500-001.
T874A1036
A1143 44 Honeywell logo; °C scaleplate. T874A1036 Replacement has °F scaleplate.
A1150 44 Honeywell logo; TRADELINE model; includes Allen wrench and screws to lock cover; field adjustable locking levers (68°F max. heat, 78°F min. cool).
T874A1150
A1168 44 Obsolete. Trane Comfort Corps logo. T874A1036A1176 44 Honeywell logo; meets DoD specs; includes Allen
wrench and screws to lock cover; no thermometer; non-adjustable range stops set at 72°F (max. heat) and 78°F (min. cool) (22-26°C); field adjustable locking levers.
T874A1176
A1184 51, 53 Trane logo; part no. BAY28X182; °F/°C scaleplate; automatic fan in heating and cooling modes; heat anticipator set at 0.4A; used with Q674B1141, E1080.
T874A1036a When used with Q674E1080, set stage 1 heat anticipator for total current draw of fan and stage 1 heat primary; replacement has °F scaleplate.
A1192 44 Obsolete. Lennox logo; part no. 13F0001; °C scaleplate; heat anticipator factory set at .458A.
T874A1036 Replacement has °F scaleplate.
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
47 60-2485�8
A1200 51, 53 Obsolete. Carrier logo; part no. HH07AT164; °C scaleplate; includes Allen wrench and screws to lock cover; used with Q674B.
T874A1036a Set stage 1 heat anticipator for total current draw of fan and stage 1 heat primary; replacement has °F scaleplate.
A1226 44 Honeywell logo; Honeywell Canada TRADELINE model; °C scaleplate; includes Allen wrench and screws to lock cover.
T874A1036 Replacement has °F scaleplate.
A1234 44 Obsolete. Friedrich Climate Master logo; heat anticipator factory set 1.2A.
T874A1036
A1242 44 Obsolete. Friedrich Climate Master logo. T874A1036A1259 44 Obsolete. Wesco logo; heat anticipator set at 0.8A. T874A1036A1267 59 Obsolete. McQuay logo; used with Q674Q1004. T874A1036A1275 44 Obsolete. Lennox logo; part no. 13F0101; meets DoD
specifications. T874A1176
A1283 75 McQuay Air Conditioning logo; part no. 03005047; used with Q674C1132 and thermistor to display outdoor temperature.
T874A1036 Replacement does not have ability to display external temperature or momentary system switch position.
A1291 64 No logo; three-speed fan; one setpoint lever for heat and cool setpoints; used with Q674Q1012; used in Y594A1126.
T874A1036/Q674B1075a
Replacement has two levers and 1 speed fan.
A1309 44 Obsolete. Arcoaire Air Conditioning and Heating logo; part no. AO2076; includes Allen wrench and screws to lock cover.
T874A1036
A1317 44 Obsolete. McQuay logo; part no. 60685301; no scaleplate; used with Q674A-E,G.
T874A1036
A1325 75 Obsolete. McQuay logo; part no. 60685401; no scaleplate; used with Q674C1306 and outdoor thermistor to display outdoor temperature.
T874A1036 Replacement does not have ability to display external temperature or momentary system switch position.
A1341 44 Obsolete. Trane logo; part no. THT-0577; meets DoD specifications.
T874A1176
A1358 44 York-Miraco logo. T874A1036A1366 51, 53 Obsolete. BDP Multi-logo; part no. HH07AT182. T874A1036a Set stage 1 heat anticipator for
total current draw of fan and stage 1 heat primary.
A1374 44 American Standard logo; part no. ASYSTAT610; heat anticipator factory set at 0.4A.
T874A1036a
A1390 44 Obsolete. Climate Control logo; part no. 654958804; °F/°C scaleplate.
T874A1036 Replacement has °F scaleplate.
A1416 44 Obsolete. Reznor logo; part no. 654758803; °F/°C scaleplate.
T874A1036 Replacement has °F scaleplate.
A1424 214 Obsolete. Carrier Olympia Series Split System logo; part no. HH07AT194; used with Q674B1455 (HH93AZ208).
See OEM for replacement.
A1440 91 Obsolete. Simplex System 2000 logo; heat anticipator factory set at 1.2A; used with Q674G1005; used in Y594A.
T874A1036
A1465 212 Honeywell Trol-A-Temp� logo; Premier White® color; heat anticipator factory set at 0.10A; used with Q674E1379.
None See Trol-A-Temp for replacement.
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 48
A1481 44 Obsolete. Honeywell logo; Carrier part no. HH621602; includes locking cover and non-adjustable range stops set at 72°F (max. heat) and 78°F (min. cool).
T874A1036
A1507 44 Obsolete. Climate-Tel logo; includes Allen wrench and screws to lock cover and non-adjustable range stops set at 72°F (max. heat) and 78°F (min. cool).
T874A1176
A1523 224, 225
Obsolete. AAF/Snyder General logo; part no. 066804404; °F/°C scaleplate; no cooling anticipation; used with Q674E1312, C1298.
See OEM for replacement.
A1549 224, 225
Obsolete. McQuay logo; part no. 066816601; no cooling anticipation; used with Q674E1312, C1298.
See OEM for replacement.
A1556 51, 53 Carrier logo; part no. HH07AT164-W; °C scaleplate; Premier White® color; includes Allen wrench and screws to lock cover; used with Q674B.
T874A1036a Replacement has °F scaleplate; replacement is beige.
A1572 224, 225
Obsolete. McQuay logo; part no. 066816611; Premier White® color; °F/°C scaleplate; no cooling anticipation.
See OEM for replacement.
A1580 91 California Economizer logo; Premier White® color; heat anticipator factory set at 1.2A.
T874A1036
A1598 224, 225
McQuay logo; part no. 073319001; Premier White® color; °F/°C scaleplate; includes Allen wrench, screws to lock cover and AAF insert.
See OEM for replacement.
A1614 44 Honeywell logo; TRADELINE® model; °C scaleplate; Premier White® color; includes Allen wrench and screws to lock cover; used with Q674B.
T874A1036 Replacement has °F scaleplate; replacement is beige.
A1622 44 Obsolete. York logo; part no. 2TH04703224A; includes Allen wrench and screws to lock cover and non-adjustable range stops set at 72°F (max. heat) and 78°F (min. cool).
T874A1010
T874B 1-stage heat, 2-stage cool. B1001 44 Obsolete. Honeywell logo. T874B1019B1019 44 Honeywell logo; TRADELINE model; includes Allen
wrench and screws to lock cover. T874B1019
B1027 44 Obsolete. Westinghouse logo. T874B1019B1035 44, 46 Obsolete. Trane logo; used with Q674B1018, B1075;
used in Y594B1026, B1034. T874B1019
B1043 44 Obsolete. Honeywell logo; °C scaleplate. T874B1019 Replacement has °F scaleplate.
B1050 44 Lennox logo; part no. 13F0201; °F/°C scaleplate. T874B1019 Replacement has °F scaleplate.
B1068 44 Honeywell logo; Honeywell Canada TRADELINE model; °C scaleplate; includes Allen wrench and screws to lock cover.
T874B1019 Replacement has °F scaleplate.
B1076 88 Obsolete. Lennox Power Saver Two-Speed logo; part no. 91C7401; °F/°C scaleplate; used with Q674E1155.
T874B1019 Replacement has °F scaleplate.
B1084 44 Obsolete. Lennox Two-Speed logo; part no. 13F0301; °C scaleplate.
T874B1019 Replacement has °F scaleplate.
B1092 44 Obsolete. Honeywell logo; Heil Quaker part no. HQ521389HW.
T874B1019
B1100 88 Obsolete. Janitrol logo; part no. CHTS36-60; °F/°C scaleplate; used with Q674E1338; used in Y594B1042.
T874B1019 Replacement has °F scaleplate.
B1118 44 Honeywell logo; °C scaleplate; used with Q674A-E, G.
T874B1019 Replacement has °F scaleplate.
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
49 60-2485�8
B1134 222 Obsolete. Carrier Synergy 2000 logo; part no. HH07AT199; °C scaleplate; used with Q674E1395 (HH93AZ209).
T874B1019/Q674E1049a
Wiring differences (old=new): W1=W; RC-RH jumper required; replacement has no LEDs.
T874C 2-stage heat, 1-stage cool. C1000 44, 76 Honeywell logo; used with Q674B1075, C1181; used in
Y594C1058. T874C1018
C1018 60, 61, 81, 92
Honeywell logo; TRADELINE model; includes Allen wrench and screws to lock cover; used with Q674C1074.
T874C1018
C1026 44 Obsolete. AAF logo; °C scaleplate; includes Allen wrench and screws to lock cover; non-adjustable range stops set at 23°C (max. heat and min. cool) (73°F).
T874C1018 Replacement has °F scaleplate.
C1034 44 Lennox logo; part no. 13F0401; °F/°C scaleplate. T874C1018 Replacement has °F scaleplate.
C1042 44 Obsolete. Westinghouse logo; H1 anticipator factory set at.75A; H2 anticipator factory set at 1.2A; used with Q674A-E,G.
T874C1018
C1059 44, 142 Obsolete. Amana Air Conditioning logo; part no. D68535-2; H1 anticipator factory set at 1.2A; used with Q674E1056, Q674B1059, Q674F1022; used in Y594C1009, Y594C1017, Y594C1256, Y594C1330.
T874C1018
C1067 44 Obsolete. Sears logo; part no. 42. 9297; °F/°C scaleplate.
T874C1018 Replacement has °F scaleplate.
C1075 51, 53 Carrier logo; part no. HH07AT170; used with Q674B1166.
Y594C1421 or T874C1018a
When using the T874C1018, set stage 1 heat anticipator for total current draw of fan and stage 1 heat primary.
C1083 44 Obsolete. Trane logo; used with Q674E1007; used in Y594C1082.
T874C1018
C1117 44 Honeywell logo; °C scaleplate. T874C1018 Replacement has °F scaleplate.
C1125 60, 61, 92
Obsolete. Honeywell logo; 12°F (6.7°C) differential between stage 1 heat and stage 2 heat; used with Q674G1047.
T8611M2025
C1133 96 Obsolete. AAF/Snyder General logo; part no. 4ELN7546; no H1 heat anticipation; used with Q674A-G,N and Q674C1173.
T874C1018 Must have H1 anticipator set to maximum value.
C1141 44 Obsolete. Honeywell logo; meets DoD specs; includes Allen wrench and screws to lock cover; no thermometer; non-adjustable range stops set at 72°F (max. heat) and 78°F (min. cool) (22-26°C); field adjustable locking levers.
T874C1141
C1158 44 Obsolete. Solaron special. T874C1018C1166 51, 53 Obsolete. Carrier logo; part no. HH07AT160; °C
scaleplate; includes Allen wrench and screws to lock cover; used with Q674B.
T874C1018a Replacement has °F scaleplate; set stage 1 heat anticipator for total current draw of fan and stage 1 heat primary.
C1174 44 Obsolete. Goettl logo. T874C1018C1182 60 Obsolete. Goettl logo; H1 anticipator factory set at 0.8A;
used with Q674N1015. T874C1018
C1190 44 Obsolete. Lennox logo; part no. 13F0501; °C scaleplate. T874C1018 Replacement has °F scaleplate.
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 50
C1216 44 Obsolete. Fasco part no. 1230-8197. T874C1018C1224 105 Obsolete. Square D logo. T874C1018C1240 44 Honeywell logo; Honeywell Canada TRADELINE model;
°C scaleplate; includes Allen wrench and screws to lock cover.
T874C1018 Replacement has °F scaleplate.
C1257 44 Obsolete. Singer part no. 0200-5931; 8°F (4.4°C) differential between H1 and H2 heat.
T874C1125 Replacement has 12°F differential between H1 and H2 heat.
C1265 44 Obsolete. Singer special; °C scaleplate; 5°C (8°F) differential between H1 and H2 heat.
T874C1125 Replacement has 12°F differential between H1 and H2 heat; replacement has °F scaleplate.
C1273 44 Honeywell logo; °C scaleplate; includes Allen wrench and screws to lock cover; non-adjustable range stops factory set at 23°C (max. heat and min. cool) (73°F).
T874C1018 Replacement has °F scaleplate.
C1281 44 Obsolete. Heat Wave special. T874C1018C1307 44 Obsolete. Friedrich Climate Master logo. T874C1018C1315 44 Obsolete. Wesco logo; heat anticipator factory set at
0.8A. T874C1018
C1323 44 Obsolete. Le Chauffage Urbain special; °C scaleplate. T874C1018 Replacement has °F scaleplate.
C1331 82, 141 Obsolete. Duotherm logo; used with Q674E or Q674F. T874C1018C1349 61 Obsolete. Sigler logo; used with Q674N1023. T874C1018C1372 52 Obsolete. Honeywell logo; used with Q674B1190. T874C1018/
Q674B1034For systems requiring automatic fan in cooling mode only.
T874C1018/Q674B1075
For systems requiring automatic fan in heating and cooling.
C1398 105 Obsolete. Fedders logo; °F/°C scaleplate; used with Q674L1090.
Y594R1425a Wiring differences (old=new): K=E, C=X; replacement has °F scaleplate.
C1406 105 Obsolete. Climatrol logo; °F/°C scaleplate; used with Q674L1090.
Y594R1425a Wiring differences (old=new): K=E, C=X; replacement has °F scaleplate.
C1414 105 Obsolete. Airtemp logo; °F/°C scaleplate; used with Q674L1090.
Y594R1425a Wiring differences (old=new): K=E, C=X; replacement has °F scaleplate.
C1422 187 Obsolete. Honeywell logo; used with Q674B1208. NoneC1430 49 Obsolete. Lennox Zone Master Two-Speed logo; part
no. 25F7201; used with Q674B1224. T874C1018
C1448 110, 190
Obsolete. Lennox logo; part no. 24F5101; meets DoD specifications; requires outdoor reset; used with Q674L1165, L1355.
Y594R1763a Wiring differences (new=old): R=V-VR, Y=M, G=F, B-X, W=Y, T=A, O=R, X2=E; Emergency Heat becomes stage 1 heat source.
C1455 127 Obsolete. Williamson logo; used with Q674L1322. Y594R1243a
C1463 82 Obsolete. AAF logo; °C scaleplate. T874C1018 Replacement has °F scaleplate.
C1471 56 Obsolete. Mammoth logo; part no. 71120102; used with Q674B1257; used in Y594C1314.
T874C1018
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
51 60-2485�8
C1489 121 Obsolete. Honeywell logo; non-adjustable range stops set at 75°F (max. heat and min. cool) (24°C); used with Q674L1157.
Y594C1322a
C1497 121 Obsolete. Honeywell logo; meets DoD specifications; used with Q674L1157.
Y594C1322a
C1513 44 Obsolete. Borg-Warner multi-logo; part no. 6TH11703124A.
T874C1018
C1562 44 Obsolete. Honeywell logo; Heil Quaker part no. HQ712001HW.
T874C1018
C1570 45 Obsolete. Williamson logo; used with Q674B1000; used in Y594C1280.
T874C1018
C1638 121 Obsolete. Honeywell logo; meets DoD specifications; includes Allen wrench and screws to lock cover; no thermometer; non-adjustable range stops set at 72°F (max. heat) and 78°F (min. cool) (22-26°C); field adjustable locking levers; used with Q674L1561; used in Y594C1322.
Y594C1322a
C1653 70 Obsolete. Fiberglas Canada; °C scaleplate; no H1, H2, or C1 anticipation; used with Q674S1000; used in Y594C1348.
See OEM for replacement.
C1661 99 Obsolete. McQuay logo; part no. 61202401; °F/°C scaleplate; includes momentary system switch position with spring release; used with Q674C1363.
T874C1125/ Q674B1075a
Replacement has HEAT-OFF-COOL system switching; no momentary system switch position; no LEDs.
C1695 45 Obsolete. Miller logo; used with Q674B1000; used in Y594C1355.
T874C1018
C1703 45 Obsolete. Intertherm logo; used with Q674B1000; used in Y594C1363.
T874C1018
C1737 44 Obsolete. Honeywell logo; Carrier part no. HH621603. T874C1018C1745 44 Obsolete. AAF/Snyder General logo; part no.
4ELN7919.T874C1018
C1752 219 Obsolete. McQuay/Snyder General logo; part no. 061202402; 12°F offset between H1 and H2; °F/°C scaleplate; no C1 anticipation; used with Q674C1363.
T8611M2025
C1760 44 Bard logo. T874C1018C1778 219 Obsolete. AAF/Snyder General logo; part no.
066804405; 12°F offset between H1 and H2; °F/°C scaleplate; no C1 anticipation; used with Q674C1363.
See OEM for replacement.
C1794 53 Obsolete. Carrier logo; Canada; part no. HH07AT160-W; Premier White® color; °C scaleplate; includes locking cover.
T874C1018 Set stage 1 heat anticipator for total current draw of fan and stage 1 heat primary.
C1802 246 Obsolete. California Economizer logo; °F/°C scaleplate; used with Q674G1005; used in Y594C1371.
T874C1018
C1810 237 Obsolete. Honeywell logo; TRADELINE model; Premier White® color; used with Q674B1547; used in Y594C1389.
Y594C1389
C1844 238 Energy Night logo; used with Q674F1592; used in Y594C1413.
Y594R1425 Jumper E-W2; system switch: EM.HT.-HEAT-OFF-COOL.
C1851 60 Obsolete. Whalen logo. T874C1018C1869 219 McQuay logo; part no. 0073318801 Premier White®
color; °F/°C scaleplate. See OEM for replacement.
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 52
C1877 53 Obsolete. Honeywell logo; TRADELINE model; used with Q674B1554; used in Y594C1421.
Y594D1347 Jumper RC-RH; system switch: OFF-HEAT-AUTO-COOL
T874D 2-stage heat, 2-stage cool. D1009 166, 82 Obsolete. Honeywell logo; used with Q674F1337,
E1007; used in Y594D1222, D1339. T874D1165
D1017 44, 88 Obsolete. Honeywell logo; TRADELINE model; includes Allen wrench and screws to lock cover; used with Q674A-G and Q674E1155.
T874D1165
D1025 44 Obsolete. Westinghouse logo; H1 anticipator factory set at 0.75A; H2 anticipator factory set at 1.2A.
T874D1165
D1033 44 Lennox logo; part no. 13F0601; °F/°C scaleplate. T874D1165 Replacement has °F scaleplate.
D1041 53 York logo; part no. 2TH04701524A; used with Q674B1125.
T874D1165
D1058 44 Obsolete. Shiger special. T874D1165D1066 44 Obsolete. ITT logo. T874D1165D1074 51, 53,
146Carrier logo; part no. HH07AT172; used with Q674F1030 (HH93AZ174), F1063 (HH93AZ181) or Q674B.
T874D1165a Set H1 anticipator for current draw of fan and stage 1 heat primary.
D1082 44, 46, 48, 72
Trane logo; used with Q674B1018, C1009, B1075, B1133; used in Y594D1024, D1040.
T874D1165
D1090 44 Obsolete. Dunham-Bush logo. T874D1165D1108 44 Obsolete. Westinghouse logo. T874D1165D1116 76, 89,
94Obsolete. Comfortmaker logo; part no. 1505-682; °F/°C scaleplate; used with Q674C1116, E1197, G1104.
T874D1165 Replacement has °F scaleplate.
D1124 44 Obsolete. Airtemp special. T874D1165D1132 44 Honeywell logo; °C scaleplate. T874D1165 Replacement has °F
scaleplate. D1140 44 Obsolete. Solaron special. T874D1165 Replacement has °F
scaleplate. D1157 51, 53,
146Carrier logo; part no. HH07AT172; °C scaleplate; used with Q674B or Q674F1030, F1063.
T874D1165a Replacement has °F scaleplate; set H1 anticipator for current draw of fan and stage 1 heat primary.
D1165 82 Honeywell logo; SUPER TRADELINE® model; includes Allen wrench and screws to lock cover, field-adjustable range stops, field-adjustable locking levers.
T874D1165
D1173 51, 53 Trane logo; part no. BAY28X183; heat anticipator factory set at 0.4A.
T874D1165a Set H1 anticipator for current draw of fan and stage 1 heat primary.
D1181 51, 53 Obsolete. General Electric logo; locking cover includes Allen wrench and screws to lock cover and range stops set at 72°F (max. heat) and 78°F (min. cool).
T874D1165a Set H1 anticipator for current draw of fan and stage 1 heat primary.
D1199 44 Obsolete. Lennox logo; part no. 13F0701; °C scaleplate. T874D1165 Replacement has °F scaleplate.
D1207 114 Obsolete. Lennox logo; part no. 24F5201; used with Q674L1199 and C815A1013 or Q674L1389.
T8611M2025 (programmable)
Wiring differences (old=new): V-VR=R, Y=W3, X=C, R=O, M=Y, M2=Y2-W2, F=G; jumper Y2-W2; no outdoor reset needed; use only one system transformer.
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
53 60-2485�8
D1215 44 Obsolete. Friedrich Climate Master logo; part no. AT5415; °F/°C scaleplate.
T874D1165 Replacement has °F scaleplate.
D1223 44 Honeywell logo; Honeywell Canada TRADELINE model; Celsius scale.
T874D1165 Replacement has °F scaleplate.
D1231 44 Obsolete. Honeywell logo; 12°F (7°C) differential between H1 and H2.
T874D1165 Replacement has 2°F differential between H1 and H2.
D1249 44 Obsolete. Fedders special. T874D1165D1256 44 Obsolete. Climatrol special. T874D1165D1264 107 Obsolete. Carrier Heat Pump System Control logo; part
no. HH07AT173; used with Q674L1116 (HH93AZ171). See OEM for replacement.
D1272 51, 53 Obsolete. Carrier logo; part no. HH07AT162-03; °C scaleplate; used with Q674B.
T874D1165a Replacement thermostat has °F scaleplate; set H1 anticipator for current draw of fan and stage 1 heat primary.
D1280 44 Obsolete. Command-Aire logo. T874D1165D1298 90, 232 Obsolete. Singer special; °C scaleplate; controls two
separate heat/cool circuits; used with Q674D or Q674G1054, G1062.
See OEM for replacement.
D1306 90, 186 Obsolete. Trane special; part no. 02005949; controls two separate heat/cool circuits; used with Q674G1013.
See OEM for replacement.
D1314 44 Obsolete. McQuay logo; part no. 02005941; 12°F (6.6°C) differential between H1 and H2.
T874D1165 Replacement has °F scaleplate; 2°F differential between H1 and H2.
D1322 46 Obsolete. Amana logo; part no. D68535-03; used with Q674B1075; used in Y594D1149.
T874D1165
D1330 44 Obsolete. Trane logo; part no. 13080242; °C scaleplate. T874D1165 Replacement has °F scaleplate.
D1355 44 Obsolete. Climate Control special; part no. 02005942; °C scaleplate; 6°C (11°F) differential between H1 and H2.
T874D1165 Replacement has 2°F differential between H1 and H2.
D1363 44 Obsolete. McQuay logo; part no. 02005943; 12°F (6.6°C) differential between H1 and H2; 6°F (3.3°C) differential between C1 and C2.
T874D1165 Replacement has 2°F differential between H1 and H2; 2°F differential between C1 and C2.
D1405 44 Obsolete. Trane logo; part no. 02005952; 12°F (6.6°C) differential between H1 and H2; 6°F (3.3°C) differential between C1 and C2.
T874D1165 Replacement has 2°F differential between H1 and H2; 2°F differential between C1 and C2.
D1413 44 Obsolete. Trane logo; part no. 02005956; 12°F (6.6°C) differential between H1 and H2.
T874D1165 Replacement has 2°F differential between H1 and H2.
D1421 44 Obsolete. Climate Control special; part no. 02005938; °C scaleplate.
T874D1165 Replacement has °F scaleplate.
D1439 90 McQuay logo; part no. 02005935; used with Q674G1096.
T874D1165
D1447 90 Obsolete. Climate Control special; part no. 02005940; °C scaleplate; used with Q674G1096.
T874D1165 Replacement has °F scaleplate.
D1454 51, 53 Obsolete. Carrier logo. T874D1165a Set H1 anticipator for current draw of fan and stage 1 heat primary.
D1462 80 Obsolete. Fedders multi-logo; part no. THTX-220-A0HB, 88-58-00550-001; used with Q674E1205.
T874D1165
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 54
D1470 44 Obsolete. York logo; part no. 2TH04701624A; includes Allen wrench and screws to lock cover; °C scaleplate.
T874D1165 Replacement has °F scaleplate.
D1488 44 Obsolete. Risco special. T874D1165D1496 44 Obsolete. Borg Warner multi-logo; part no.
6TH04701524A; includes Allen wrench and screws to lock cover.
T874D1165
D1504 82 York logo; part no. 025-23321-000; °C scaleplate; used with Q674E1007; used in Y594D1180.
T874D1165 Replacement has °F scaleplate.
D1512 44 Honeywell logo; Heil Quaker part no. HQ712002HW. T874D1165D1520 44 Obsolete. Bard logo; adjustable lever stops set 68°F
(max. heat) and 78°F (min. cool). T874D1165
D1538 44 Obsolete. McQuay logo; part no. 02005937. T874D1165D1553 44 Obsolete. Climate Control special; part no. 02005944;
°C scaleplate; 6°C differential between H1 and H2; 3°C differential between C1 and C2.
T874D1165 Replacement has 2°F differential between H1 and H2; 2°F differential between C1 and C2; replacement has °F scaleplate.
D1561 44 Obsolete. General Electric logo; used with Q674 A-G. T874D1165D1587 44 Obsolete. Stiles Four Seasons logo. T874D1165D1595 139 Obsolete. Nepco logo; used with Q674F1394. T874D1165/
Q674B1018aReplacement has HEAT-OFF-COOL system switching; no LEDs.
D1603 44 Obsolete. Arcoaire logo. T874D1165D1611 44 Obsolete. No logo; Friedrich part no. AT5411; °F/°C
scaleplate. T874D1165 Replacement has °F
scaleplate. D1629 82 Obsolete. Reznor logo; °F/°C scaleplate; used with
Q674E1007; used in Y594D1248. T874D1165 Replacement has °F
scaleplate. D1678 44 Obsolete. Honeywell logo; Saudi Oger special; °C
scaleplate; one setpoint lever; used with Q674A-K. T874D1165 Replacement has °F
scaleplate; separate heating and cooling setpoint levers.
D1686 98 Obsolete. McQuay logo; part no. 60685501; 8°F (4.4°C) differential between H1 and H2; 6°F (3.3°C) differential between C1 and C2; used with Q674E1312.
T874D1165 Replacement has 2°F differential between H1 and H2; 2°F differential between C1 and C2.
D1694 202 Obsolete. McQuay logo; part no. 60685201; used with Q674G1120.
See OEM for replacement.
D1702 44 Obsolete. McQuay logo; part no. 60685101. T874D1165D1710 44 Trane logo. T874D1165D1728 44 York-Miraco logo. T874D1165D1744 44 American Standard logo; heat anticipator factory set at
0.4A. T874D1165
D1751 44 Obsolete. Goettl logo; part no. 372080; range stops set at 68°F (max. heating) and 78°F (min. cooling).
T874D1165
D1769 82 Obsolete. Arcoaire logo; part no. 1506753; °F/°C scaleplate; used with Q674E1346; used in Y594D1297.
T874D1165 Replacement has °F scaleplate.
D1777 44 Obsolete. Climate Control logo; part no. 65495806; °F/°C scaleplate.
T874D1165 Replacement has °F scaleplate.
D1785 82 Obsolete. Comfortmaker logo; part no. 1505753; °F/°C scaleplate; used with Q674E1346; used in Y594D1305.
T874D1165 Replacement has °F scaleplate.
D1793 44 Obsolete. McQuay logo; part no. 65495805; °F/°C scaleplate.
T874D1165 Replacement has °F scaleplate.
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
55 60-2485�8
D1801 45, 208 Trol-A-Temp by Honeywell logo; H1 and H2 anticipators set at 0.10A; used with Q674B1463, D1115.
None See Trol-A-Temp for replacement.
D1819 44 Marv Air Com Stat logo; part no. 50059; adjustable interstage between H1 and H2 and between C1 and C2; includes Allen wrench and screws to lock cover; field adjustable range stops; °F/°C scaleplate.
T874D1165 Replacement has a 2°F fixed interstage differential between H1 and H2 and between C1 and C2; replacement has °F scaleplate.
D1827 45, 208 Trol-A-Temp by Honeywell logo; Premier White® color; H1 and H2 heat anticipators set at 0.10A; used with Q674B1471, D1123.
None See Trol-A-Temp.
D1843 45 Obsolete. Janitrol logo; Goodman part no. CHT 90-120; used with Q674B1000; used in Y594D1321.
T874D1165
D1850 44 Honeywell logo; Carrier part no. HH621606. T874D1165D1868 44 Bard logo; part no. 8405-031; H1 and H2 heat
anticipators factory set at 0.25A; 5°F interstage differential between H1 and H2 and between C1 and C2; includes Allen wrench and screws to lock cover; field adjustable range stops.
T874D1165 Replacement has 2°F fixed interstage differential between H1 and H2 and between C1 and C2.
D1876 44 Obsolete. AAF/Snyder General logo; part no. 4ELN6981A; °F/°C scaleplate.
T874D1165 Replacement has °F scaleplate.
D1892 44 Obsolete. Climate-Tel logo. T874D1165D1918 224,
225Obsolete. AAF/Snyder General logo; °F/°C scaleplate; no cooling anticipation; used with Q674E1312, C1298; 66804407.
See OEM for replacement.
D1926 226 Obsolete. AAF/Snyder General logo; °F/°C scaleplate; no cooling anticipation; used with Q674G1120; 66804406.
See OEM for replacement.
D1934 44 Bard logo. T874D1165D1942 82 Honeywell logo; TRADELINE model; used with
Q674E1403; used in Y594D1347; designed to replace York part no. 2TH04701024.
Y594D1347a
D1959 44 Rheem part no. 41-21444-01. T874D1165D1967 44 Obsolete. Desert Aire logo. T874D1165D1975 224,
225Obsolete. McQuay part no. 066816603; °F/°C scaleplate; no cooling anticipation.
See OEM for replacement.
D1983 226 Obsolete. McQuay part no. 066816602; °F/°C scaleplate; no cooling anticipation; used with Q674G1120.
See OEM for replacement.
D1991 51, 53 Carrier logo; Premier White® color; °C scaleplate. T874D1165a Set H1 anticipator for total current draw of fan and stage 1 primary; replacement has °F scaleplate.
D2007 44 Ultra-Zone logo. T874D1165D2023 44 Honeywell logo; TRADELINE model; Premier White®
color; °C scaleplate; includes locking cover; used with Q674A-K.
T874D1165 Replacement has °F scaleplate and is beige.
D2031 82 Obsolete. Honeywell logo; no cover; used with Q674E1049 and TG504A1025; used in Y594D1354.
T874D1165 or Y594D1354
D2049 45, 72, 55, 66,
184
Obsolete. Carrier Heat Pump System Control logo; part no. HH07AT236; °F/°C scaleplate; used with Q674B-D, Q674G; used in Y594D.
T874D1165 Replacement has °F scaleplate.
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 56
D2056 44 Obsolete. ComStat logo; part no. 50056; °F/°C scaleplate; adjustable interstage on both heating and cooling; includes locking cover and field-adjustable locking levers.
T874D1165 Replacement has °F scaleplate and 2°F fixed differential in heating and cooling.
D2064 53 Obsolete. Carrier Weathermaker; part no. HH07AT209; stage 1 and 2 heat anticipator factory set 0.1A; taupe color; used with Q674E1445; used in Y594D1412.
T874D1165 Set stage 1 heat anticipator for total current draw of fan and stage 1 heat primary. Replacement is beige.
D2072 53 Obsolete. Carrier Zone Perfect; part no. HH07AT208; taupe color; used with Q674E1445; used in Y594D1420.
T874D1165 Set stage 1 heat anticipator for total current draw of fan and stage 1 heat primary. Replacement is beige.
D2080 139 Obsolete. Hydroheat logo. T874D1165/Q674B1018a
Replacement system switch: HEAT-OFF-COOL; no LEDs.
D2098 44 Obsolete. Honeywell logo; °F scaleplate; one setpoint lever; used with Q674D1008; used in Y594D1438.
T874D1165 Replacement has °F scaleplate and two setpoint levers
D2106 44 Obsolete. Honeywell logo; °C scaleplate; one setpoint lever; used with Q674D1008; used in Y594D1446.
T874D1165 Replacement has °F scaleplate and two setpoint levers.
D2114 44 Obsolete. Bard logo; °C scaleplate. T874D1165 Replacement has °F scaleplate.
D2122 224, 225
Obsolete. McQuay T874D2023 Replacement has °C scaleplate.
T874D1165 Replacement has °F scaleplate.
D2130 226 Obsolete. McQuay See OEM for replacement.
D2148 44 Obsolete. Dry Aire Systems logo; °F/°C scaleplate. T874D1165D2155 139 Hydroheat logo; Premier White® color; °F/°C scaleplate;
used with Q674F1634.T874D1165/Q674B1018a
Replacement system switch: HEAT-OFF-COOL; no LEDs.
D2163 208 Obsolete. Amana logo; part no. P1217501F; °F/°C scaleplate.
T874D1165
D2171 44 Obsolete. Amana logo; part no. P1217701F; °F/°C scaleplate.
T874D1942
D2189 44 Armstrong logo; part no. 01142A024; °F/°C scaleplate; includes Air Ease insert.
T874D1165
D2197 44 Liebert logo; part no. 138968P3; °F/°C scaleplate; interstage differential between H1 and H2 and between C1 and C2; includes Allen wrench and screws to lock cover; field-adjustable locking levers.
T874D1165
D2205 44 Aaon logo; Premier White® color; °F/°C scaleplate. T874D1165T874E 0-stage heat, 2-stage cool.
E1008 44 Obsolete. Honeywell logo. T874E1016E1016 44 Honeywell logo; TRADELINE model; includes Allen
wrench and screws to lock cover; field-adjustable locking levers.
T874E1016
E1024 44 Obsolete. Westinghouse logo. T874E1016E1032 44 Lennox logo; part no. 13F0901; °F/°C scaleplate. T874E1016 Replacement has °F
scaleplate. E1040 72 Obsolete. Trane logo; used with Q674C1009; used in
Y594E1015. T874E1016
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
57 60-2485�8
E1081 44 Trane logo; part no. BAY28X186; °F/°C scaleplate. T874E1016 Replacement has °F scaleplate.
E1099 44 Obsolete. Lennox logo; part no. 13F1001; °C scaleplate. T874E1016 Replacement has °F scaleplate.
E1107 44 Honeywell logo; °C scaleplate. T874E1016 Replacement has °F scaleplate.
E1123 44 Obsolete. Amana logo; part no. D68535-4. T874E1016E1149 44 Obsolete. York logo; part no. 2TH04701724A. T874E1016E1156 44 Obsolete. Borg Warner multi-logo; part no.
6TH04701724A. T874E1016
E1164 44 Obsolete. E. A. Juffali & Bros. logo. T874E1016E1206 44 Obsolete. Trane logo. T874E1016E1230 44 Obsolete. Climar logo. T874E1016
T874F 2-stage heat, 0-stage cool. F1007 44 Honeywell logo. T874F1015F1015 44 Honeywell logo; TRADELINE model; includes Allen
wrench and screws to lock cover; field-adjustable locking levers.
T874F1015
F1023 44 Obsolete. Lennox logo; part no. 13F1101. T874F1015F1031 44 Obsolete. Honeywell logo; °C scaleplate; used with
40003440-001 wallplate; used in Y594F1022. T874F1015 Replacement has °F
scaleplate. F1049 44 Obsolete. Lennox logo; °C scaleplate. T874F1015 Replacement has °F
scaleplate. F1056 55,
66Obsolete. Honeywell logo; stages 1 and 2 heat electrically isolated; used with Q674D1008.
None
F1072 44 Obsolete. Wesco logo; heat anticipator factory set at 0.8A.
T874F1015
F1098 189 Obsolete. Lennox logo; used with Q674D1008 to control an M839.
T874F1015 Set H1 and H2 anticipators to lowest settings.
F1106 95 Obsolete. Oneida logo; part no. 30A0287-02; used with Q674K1018 on combination wood and oil applications.
T874F1155
F1114 44 Honeywell logo; Honeywell Canada TRADELINE model; °C scaleplate; includes Allen wrench and screws to lock cover; field-adjustable locking levers.
T874F1015 Replacement has °F scaleplate.
F1122 62 Obsolete. Honeywell logo; two heat setpoint levers; used with Q674B1307.
T874F1015/ Q674D1040
Replacement has no LED.
F1130 72, 91 Obsolete. Reznor logo; °F/°C scaleplate; used with Q674C, D, or G; used with Q674C1009, G1005; used in Y594F1048.
T874F1015 Replacement has °F scaleplate.
F1148 44 Obsolete. Trane logo; part no. THT 0584. T874F1015F1155 95 Honeywell logo; used with Q674K1026 on combination
wood and oil applications. T874F1155
T874G Heat pump models; 2-stage heat, 1-stage cool; 1�stage changeover.
G1006 84, 155 Obsolete. Honeywell logo; used with Q674E1015. Y594G1252a Wiring differences (old=new): R=O, M=Y, F=G, V=R, Y=W2; E-W2 jumper required.
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 58
G1014 86, 150 Obsolete. Lennox logo; part no. 24F5801; °F/°C scaleplate; H2 anticipator factory set at 0.25A for fast cycle performance; changeover in cooling mode; independent heating and cooling circuits; used with Q674E1148, F1113.
Y594G1252a Wiring differences (old=new): R=O, M=Y, F=G, Y=W2, V-VR=R (must use single transformer).
G1022 86, 150 Obsolete. Lennox logo; part no. 24F5701; °F/°C scaleplate; H2 anticipator factory set at 0.25A for fast cycle performance; changeover in cooling mode; independent heating and cooling circuits; used with Q674E1148, F1113.
Y594G1252a Wiring differences (old=new): R=O, M=Y, F=G, Y=W2, V-VR=R (must use single transformer).
G1048 153, 159
Obsolete. Westinghouse logo; H2 anticipator factory set at 1.2A; used with Q674F1121, J1019.
Y594G1252a Wiring differences when replacing T874G/Q674J1019 (old=new): W=W2.
G1055 161 Carrier Heat Pump System Control logo; part no. HH07AT171; H2 anticipator factory set at 0.8A; changeover in cooling mode; used with Q674J1035 (HH93AZ173).
None See subbase description for replacement information.
G1071 50, 103, 126, 183
Obsolete. Carrier Heat Pump System Control logo; meets DoD specifications; H2 anticipator factory set at 0.8A; used with Q674P1005 (HH93AZ169), L1041 (HH93AZ175), B1158, or J1050.
Y594G1419 Wiring differences (old=new): C=X; jumper Y1-W1.
G1089 154 Obsolete. Marvair logo; special for Crispaire; H2 anticipator factory set at 1.2A; used with Q674F1204; used in Y594G1153.
Y594G1393a Wiring differences (old=new): A=L.
G1097 155 Obsolete. Honeywell logo; Rheem part no. ZXMT-B79; used with Q674F1238 (41-20797-14).
Y594G1252a
G1105 153 Obsolete. Heat Wave (Southwest Mfg.) logo; H2 anticipator factory set at 1.2A; used with Q674F1170.
Y594G1252a
G1113 103 Obsolete. Carrier Heat Pump System Control logo; meets DoD specifications; H2 anticipator factory set at 0.8A; used with Q674L1041.
Y594G1419a Wiring differences (old=new): C=X; jumper Y1 -W1.
G1121 103 Obsolete. Carrier Heat Pump System Control logo; part no. HH07AT161; °C scaleplate; H2 anticipator factory set at 0.8A; includes Allen wrench and screws to lock cover.
Y594G1419a Wiring differences (old=new): C=X; jumper Y1-W1.
G1139 143, 234
Obsolete. Honeywell logo; used with Q674B1240, C1108.
None See subbase description for replacement information.
G1147 148 Obsolete. Honeywell logo; changeover in cooling mode; used with Q674F1139.
Y594G1252a Wiring differences (old=new): C=X.
G1154 84, 139 Obsolete. Lennox logo; used with Q674E1015, F1105. Y594G1252a See subbase description for replacement information.
G1162 155 Obsolete. Lennox logo; meets DoD specifications; used with Q674F.
Y594G1419a W1-Y1 jumper required.
G1170 160 Obsolete. York logo; part no. 2TH11702424A; H2 anticipator is fixed; used with Q674J1027; used in Y594G1013.
Y594G1567a
G1188 147 Obsolete. Honeywell logo; Keeprite/Westinghouse special; H2 anticipator factory set 1.2A; °C scaleplate; changeover in cooling mode; used with Q674F1295.
Y594G1252a Wiring differences (old=new): S=L.
G1196 160 Obsolete. York logo; °C scaleplate; changeover in cooling mode; used with Q674J1027; used in Y594G1138.
Y594G1567a
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
59 60-2485�8
G1204 162 Honeywell logo; designed for use on Trane heat pumps; no H2 anticipation; changeover in cooling mode; used with Q674J1043 and C815A1005; used in Y594G1161.
Y594G1161a Designed for use on Trane heat pumps.
G1212 155 Obsolete. Honeywell logo; H2 anticipator factory set at 0.2A; changeover in cooling mode; includes shunt to bypass H2 anticipator with W3 heat relays; used with Q674F1238.
Y594G1252a
G1220 235 Obsolete. Rheem logo; part no. RXMT-C71; changeover in cooling mode; used with Q674F1238.
Y594G1252a
G1238 155 Obsolete. Ruud logo; part no. UXMT-C71; changeover in cooling mode; used with Q674F1238.
Y594G1252a
G1246 Obsolete. Honeywell logo; changeover in cooling mode. 155 Used with Q674F1212; used in Y594G1195, G1252,
G1369. Y594G1252a
170 Used with Q674F1410; used in Y594G1393. Y594G1393a
G1261 58, 157 Obsolete. Borg-Warner; used with Q674D1032, F1253. None See subbase description for replacement information.
G1279 58, 157 Obsolete. Bryant logo; used with Q674D1032, F1253. None See subbase description for replacement information.
G1287 58, 157 Obsolete. Wesco logo; used with Q674D1032, F1253. None See subbase description for replacement information.
G1295 58 Obsolete. York logo; part no. 2TH11702724A; used with Q674D1032.
T874D1165/Q674D1040
Wiring differences (old=new): Y=Y2, O=Y1, W=W2; jumper W1-Y2.
G1345 160 Obsolete. York logo; part no. 2TH11702624A; °C scaleplate; used with Q674J1027.
Y594G1575a
G1352 73 Obsolete. Command-Aire logo; 12°F differential between H1 and H2 for night setback; used with Q674C1066.
Y594H1012a Wiring differences (old=new): Y1=O, Y2=Y, L=R, R=none; R-L jumper required; no night setback.
T8600D1004 (programmable)
Wiring differences (old=new): Y1=O, Y2=Y, L=RH; RC-RH jumper required; includes night setback.
G1378 79 Obsolete. Mammoth logo; H2 anticipator factory set at 0.8A; 12°F differential between H1 and H2 for night setback; °F/°C scaleplate; used with Q674C1124; used in Y594G1294.
Y594H1012a Wiring differences (old=new): R1=none, R2=L; R-L jumper required; no night setback.
T8090A1007/Q682A1038a
(programmable)
Includes night setback; W-Y jumper required.
G1402 129 Obsolete. York part no. 2TH11702824A; meets DoD specifications; used with Q674L1363.
Y594R1425a Wiring differences (old=new): W=W2, X=E, B=X; jumper Y-W1.
G1410 155 Obsolete. Borg-Warner multi-logo; part no. 6TH11703024A; used with Q674F1311.
T874G1246a or Y594G1252a
G1428 160 Obsolete. Borg-Warner multi-logo; part no. 6TH11702424A; used with Q674J1027; used in Y594G1229.
Y594G1567a
G1436 58 Obsolete. Borg-Warner multi-logo; part no. 6TH11702724A.
T874D1165/ Q674D1040
Wiring differences (old=new): Y=Y2, O=Y1, W=W2; jumper W1-Y2.
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 60
G1444 160 Obsolete. ROCA logo; °C scaleplate; used with Q674J1027.
Y594G1567a Replacement has °F scaleplate.
G1451 155 Obsolete. BDP multi-logo; part no. HH641502; used with Q674F1212; used in Y594G1245.
T874G1246a or V594G1252a
G1469 194 Obsolete. No logo; Addison special; used with Q674F1345; used in Y594G1344.
Y594G1252a Wiring differences (old=new): Y1=O, C=X, W1=Y1, X=L.
G1485 163 Obsolete. AAF logo; part no. 4ELN-7839; °F/°C scaleplate; 10°F differential between H1 and H2 for night setback and momentary RESET system switch position; used with Q674C1199.
Y594G1393a No night setback or momentary reset switch.
T8611G1004 (programmable)
Includes night setback; no momentary reset switch.
G1493 167 Obsolete. Honeywell logo; Rheem part no. 41-20797-18; used with Q674F1360.
Y594G1526a
G1501 195 Obsolete. Coleman logo; part no. 3600-375; changeover in cooling mode; used with Q674F1378.
Y594G1252a Wiring differences (old=new): L1=L; changeover in cooling only.
G1535 163 Obsolete. AAF/Snyder General logo; 4ELN7839 °F/°C scaleplate; 10°F differential between H1 and H2 for night setback and momentary RESET system switch position; used with Q674C1199.
Y594G1393a No night setback or momentary reset switch.
T8611G1004 (programmable)
Includes night setback.
G1543 194 Obsolete. Addison logo; Weather King part no. 8403-197; used with Q674F1345; used in Y594G1328.
Y594G1252a Wiring differences (old=new): Y1=O, C=X, W1=Y, X=L.
G1568 160 Obsolete. Luxaire logo; part no. 026-00068-000; °C scaleplate; used with Q674J1126; used in Y594G1351.
Y594G1367a Replacement has °F scaleplate.
G1576 169 Obsolete. Coleman logo; part no. 3600-373; changeover in heating and cooling mode; used with Q674F1402; used in Y594G1377.
Y594G1633a
G1584 73 Obsolete. No logo; Friedrich part no. AT5784; 8°F (4.4°C) differential between H1 and H2; used with Q674C1223.
Y594H1012a Wiring differences (old=new): Y1=O, Y2=Y, L=R, R=none; L-R jumper required; no night setback.
T8611G1004 (programmable)
Includes night setback.
G1592 155 Obsolete. Arcoaire logo; used with Q674F1212; used in Y594G1385.
T874G1246a or Y594G1252a
G1600 199 Obsolete. Honeywell logo; meets DoD specifications; used with Q674F1428; used in Y594G1401.
Y594G1419a Wiring differences (old=new): jumper W1-Y1.
G1618 73 Obsolete. Honeywell logo; 12°F differential between H1 and H2 for night setback; used with Q674C1256.
Y594H1012a Wiring differences (old=new): Y1=O, Y2=Y, L=R, R=none; L-R jumper required; no night setback.
T8600C1162 (programmable)
Wiring differences (old=new): L=R, W=O; W-Y jumper required; includes night setback.
G1626 167 Honeywell logo; used with Q674F1436; used in Y594G1526.
None
G1642 227 Honeywell logo; TRADELINE model; meets DoD specifications; used with Q674F1444; used in Y594G1419.
Y594G1419a
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
61 60-2485�8
G1659 177 Obsolete. Mammoth logo; 0.8A maximum current through B or O terminal; 12°F differential between H1 and H2 for night setback; used with Q674C1330; used in Y594G1427.
Y594H1012a Wiring differences (old=new): R2=L, R1=none; L-R jumper required; no night setback.
T8611G1004 (programmable)
Includes night setback.
G1675 174 Obsolete. American Standard logo; part no. ASYSTAT650; used with Q674J1142; used in Y594G1443.
Y594G1161a
G1691 176 Obsolete. Command Aire logo; part no. P1013-0060; 12°F (6.6°C) differential between H1 and H2 for night setback; used with Q674C1389, C1397.
Y594H1012a Wiring differences (old=new): Y1=O, Y2=Y, R=none; L-R jumper required; no night setback.
T8611G1004 (programmable)
Includes night setback.
G1717 175 Obsolete. Carrier Heat Pump System Control logo; part no. HH07AT102N; used with Q674J1167; used in Y507J1201.
Y594G1252a Wiring differences (old=new): C=X, D=L; replacement has AUX. HEAT and EM. HEAT LEDs.
G1741 227 Honeywell logo; TRADELINE model; includes factory set range stops at 68°F (max. heat) and 78°F (min. cool); Premier White® color; used with Q674F1477; used in Y594G1476.
Y594G1476a
G1758 211 Trol-A-Temp by Honeywell logo; Premier White® color; changeover is provided by Trol-A-Temp zone panel; used with Q674F1485; used in Y594G1492.
None See Trol-A-Temp for replacement.
G1774 216 Obsolete. Comfortmaker logo; part no. 1505756; used with Q674J1175; used in Y594G1500.
Y594G1252a Wiring differences (old=new): E=W2, W1=W3, X=E, C=X.
G1782 216 Obsolete. Arcoaire logo; part no. 1506756; used with Q674J1175; used in Y594G1518.
Y594G1252a Wiring differences (old=new): E=W2, W1=W3, X=E, C=X.
G1790 161 Obsolete. Carrier logo; Premier White® color; °C scaleplate; includes Allen wrench and screws to lock cover; used with Q674J1191.
Y594G1252a Wiring differences (old=new): C=X; replacement has °F scaleplate.
G1816 163 Climate Master logo; part no. AT5716; °F/°C scaleplate; 10°F differential between H1 and H2 and momentary RESET system switch position.
Y594G1393a No momentary reset switch.
G1824 227 Honeywell logo; Australian TRADELINE model; Premier White® color; °C scaleplate; used with Q674F1477; used in Y594G1534.
Y594G1476a
G1832 231 Obsolete. Intertherm logo; used with Q674F1519; used in Y594G1542.
Y594G1252a Replacement has auto changeover in cooling mode only.
G1840 231 Obsolete. Miller logo; used with Q674F1519; used in Y594G1559.
Y594G1252a Replacement has auto changeover in cooling mode only.
G1857 229 Obsolete. Lennox logo; °C scaleplate; Premier White® color; used with Q674F1535; used in Y594G1583.
Y594G1161a Wiring differences (old=new): E=X2, C=B, L=F.
G1865 160 Honeywell logo; TRADELINE model; designed to replace Y594G1013 (York part no. 2TH11702424), Y594G1229 (York part no. 6TH11702424), and York part no. 2TH117704124); used with Q674J1209; used in Y594G1567.
Y594G1567a
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 62
G1873 160 Obsolete. Honeywell logo; TRADELINE model; Premier White® color; designed to replace Y594G1013 (York part no. 2TH11702424), Y594G1229 (York part no. 6TH11702424), and York part no. 2TH117704124); used with Q674J1225; used in Y594G1575.
Y594G1567a Replacement is beige.
G1881 167 Rheem; part no. 41-20797-18. Y594G1526a
G1899 169 Obsolete. Amana; part no. 10574101; used with Q674F1550; used in Y594G1591.
Y594G1633a
G1915 155 Econar logo; used with Q674F1212; used in Y594G1609.
Y594G1252a
170 Used with Q674F1410. Y594G1393a
G1923 176 Trane logo; part no. X13510599010; H2 make 12°F below H1 make.
Y594H1012a Wiring differences (old=new): Y1=O, Y2=Y, R=none; L-R jumper required; no night setback.
T8611G1004(programmable)
Includes night setback.
G1931 155, 170
Obsolete. Honeywell logo; Premier White® color; °C scaleplate; used with Q674F1568.
None See subbase description for replacement information.
G1949 73 Obsolete. Carrier Heat Pump System Control logo; part no. HH07AT204; °F/°C scaleplate; H2 make 8°F below H1 make; used in Y594.
Y594H1012a Wiring differences (old=new): Y1=O, Y2=Y, L=R, R=none; R-L jumper required; no night setback.
T8600D1004 (programmable)
Wiring differences (old=new): Y1=O, Y2=Y, L=RH; RC-RH jumper required; includes night setback.
G1956 30, 103,126, 183
Obsolete. Carrier logo; Canada; Premier White® color; °C scaleplate; includes locking cover.
Y594G1476 Replacement has °F scaleplate.
G1964 160 York logo; Canada; Premier White® color; °C scaleplate; used in Y594G1625.
Y594G1575a Replacement has °F scaleplate.
G1972 169 Honeywell logo; TRADELINE model; used with Q674F1584; used in Y594G1633.
Y594G1633a
G1980 169 Obsolete. Amana logo; part no. 10574103; used with Q674F1600; used in Y594G1641.
Y594G1633a Wiring differences (old=new): W3=W2.
G1998 155 Obsolete. Tempstar logo (Inter-City Products); used in Y594G1658; used with Q674F1212.
Y594G1252a
G2004 103 Honeywell logo; TRADELINE model; used with Q674L; used in Y594G.
Y594G1666
161 Used with Q674J1274; used in Y594G1674. Y594G1674G2046 155,
170WaterFurnace logo; part no. TA21H03; Premier White® color; °F/°C scaleplate; used with Q674F1667; used in Y594G1716.
Y594G1716
T874H Heat pump model; 1-stage heat, 1-stage cool, 1-stage changeover in cool.
H1005 74 Obsolete. Command Aire logo; used with Q674C1041. Y594H1012a Wiring differences (old=new): Y1=O, Y2=Y; L-R jumper required.
H1013 74 Obsolete. Friedrich part no. AT5813; °C scaleplate; used with Q674C1041.
Y594H1012a Wiring differences (old=new): Y1=O, Y2=Y; L-R jumper required; replacement has °F scaleplate.
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
63 60-2485�8
H1021 74 Obsolete. Friedrich Climate Master logo; part no. AT5821; °F/°C scaleplate; used with Q674C1041.
Y594H1012a Wiring differences (old=new): Y1=O, Y2=Y; L-R jumper required; replacement has °F scaleplate.
H1039 79 Obsolete. Mammoth logo; °F/°C scaleplate; used with Q674C1124; used in Y594H1004.
Y594H1012a Wiring differences (old=new): R1=R, R2=L.
H1054 74 Obsolete. No logo; Friedrich part no. AT5854; used with Q674C1041.
Y594H1012a Wiring differences (old=new): Y1=O, Y2=Y; L-R jumper required.
H1062 164 Honeywell logo; used with Q674C1249; used in Y594H1012.
Y594H1012a
H1070 172, 173
Obsolete. Carrier Heat Pump System Control logo; part no. HH07AT166; °C scaleplate; used with Q674B1406 (HH93AZ200) or Q674C1322 (HH93AZ199).
None See subbase description for replacement information.
H1088 172, 173
Obsolete. Carrier Heat Pump System Control logo; part no. HH07AT167; used with Q674B1406 (HH93AZ200) or Q674C1322 (HH93AZ199).
None See subbase description for replacement information.
H1096 177 Obsolete. Mammoth Water Source Heat Pump logo; °F/°C scaleplate; changeover stage 0.8A maximum; used B or O terminal; used with Q674C1330.
Y594H1012a Wiring differences (old=new): R1=R, R2=L; L-R jumper required.
H1112 74 No logo; Friedrich part no. AT5812; used with Q674C1355.
Y594H1012a Wiring differences (old=new): Y1=O, Y2=Y; L-R jumper required.
H1120 205 Obsolete. Command Aire logo; part no. P1013-0055; used with Q674C1389, C1397.
Y594H1012a Wiring differences (old=new): Y1=O, Y2=Y.
H1138 221 Obsolete. Climate Master logo; part no. AT5838; used with Q674C1470.
Y594H1012a Wiring differences (old=new): Y1=O, Y2=Y; replacement has MALFUNCTION LED only.
H1146 205 Trane logo; part no. X13510598010. Y594H1012a Wiring differences (old=new): Y1=O, Y2=Y.
H1153 173 Obsolete. Carrier Heat Pump System Control logo; part no. HH07AT167; °F/°C scaleplate; used with Q674C1322; used in Y594H1053.
None See subbase description for replacement information.
H1161 74 Obsolete. Carrier Heat Pump System Control logo; part no. HH07AT203; °F/°C scaleplate; used with Q674C1496; used in Y594H1038.
Y594H1012a Wiring differences (old=new): Y1=O, Y2=Y; L-R jumper required.
T874J Heat pump model. 2-stage heat, 1-stage cool. J1002 124,
144, 206, 207
Obsolete. Carrier Heat Pump System Control logo; part no. HH07AT175; used with Q674J1068 (HH93AZ183), Q674J1159 (HH93AZ196), Q674L1074 (HH93AZ186), Q674L1637 (HH93AZ195).
None See subbase description for replacement information.
J1010 124, 171
Obsolete. BDP multi logo; part no. 34427DP124/P272-2471; used with Q674J1084, L1371.
None See subbase description for replacement information.
J1028 124, 144, 206, 207
Obsolete. Carrier Heat Pump System Control logo; part no. HH07AT165; °C scaleplate; used with Q674J1068 (HH93AZ183), Q674J1159 (HH93AZ196), Q674L1074 (HH93AZ186), Q674L1637 (HH93AZ195).
None See subbase description for replacement information.
J1036 124, 171
Obsolete. Miller logo; part no. 9132230; used with Q674J1217.
T8511G1021
J1044 124, 171
Obsolete. Intertherm logo; part no. 9132240; used with Q674J1217.
T8511G1021
J1051 124, 144
Obsolete. Carrier logo; part no. HH07AT165-W; Premier White® color; °C scaleplate.
None See subbase description for replacement information.
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 64
J1069 124, 144, 206, 207
Obsolete. Honeywell logo; TRADELINE model; used with Q674J1282; used in Y594J1019.
T8511G1021
J1077 124, 171
Obsolete. Nordyne logo; part no. 9148300; °F/°C scaleplate.
T8511G1021
T874K Heat pump model; 2-stage heat, 1-stage cool, automatic changeover in heat.
K1001 77 Obsolete. LSI Mammoth logo; used with Q674C1090. Y594G1419a Wiring differences (old=new): RH-RC=R, W1=B, W3=W2, W2=W1; remove Y1-W1 jumper.
K1019 181 Obsolete. McQuay/Snyder General logo; part no. 60687301; °F/°C scaleplate; H1 anticipator set at 0.83A; 8°F interstage differential between H1 and H2 for night setback; used with Q674C1280.
Y594G1252a Wiring differences (old=new): C=X, W=B, A=L; jumper E-W2; no night setback.
T8611G1004 (programmable)
Wiring differences (old=new): C=X, W=B, A=X2; jumper X2-R; remove external time clock; includes night setback.
K1027 181 Obsolete. AAF/Snyder General logo; part no. 066804403; °F/°C scaleplate; H1 anticipator set at 0.83A; 8°F interstage differential between H1 and H2 for night setback; used with Q674C1280.
Y594G1252a Wiring differences (old=new): C=X, W=B, A=L; jumper E-W2; no night setback.
T8611G1004 (programmable)
Wiring differences (old=new): C=X, W=B, A=X2; jumper X2-R; remove external time clock; includes night setback.
T874L Heat pump model; 2-stage heat, 1-stage cool, changeover in cool.
L1000 198 Obsolete. Carrier logo; part no. HH07AT176; used with Q674E1270 (HH93AZ189).
Y594G1419a E-W2 jumper required.
L1018 138, 165
Obsolete. Carrier Multiplex System logo; part no. HH07AT178; used with Q674B1356 (HH93AZ192) or Q674C1264 (HH93AZ193).
See OEM for replacement.
L1026 198 Obsolete. Honeywell logo; BDP part no. P272-2786; used with Q674E1304.
Y594G1419a E-W2 jumper required.
L1034 203 Obsolete. McQuay logo; part no. 60687201; °F/°C scaleplate; H1 anticipator factory set at 0.83A; used with Q674C1280.
Y594G1419a Wiring differences (old=new): Y=Y1, W=B, A=X1; remove Y1-W1 jumper.
L1059 215, 213
Obsolete. Carrier logo; part no. HH07AT192; used with Q674B1448 (HH93A2202) or Q674C1413 (HH93AZ204).
See OEM for replacement.
L1067 203 Obsolete. AAF/Snyder General logo; part no. 066804402; H1 anticipator factory set at 0.83A; used with Q674C1280.
Y594G1419a Wiring differences (old=new): Y=Y1, W=B, A=X1; remove Y1-W1 jumper.
L1075 203 Obsolete. McQuay logo; part no. 073318601; Premier White® color; °F/°C scaleplate; includes AAF insert.
See OEM for replacement.
T874N Heat pump model; 2-stage heat; 1-stage cool plus changeover; changeover in heat mode.
N1008 178 Obsolete. Williamson logo; used with Q674F1196; used in Y594N1007.
T874N1016
N1016 178 Honeywell Heat Pump Thermostat logo; used with Q674F1220.
T874N1016
N1024 179, 217
Bard logo; H1 and C1 anticipation fixed; used with Q674F1261.
None See subbase description for replacement information.
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
65 60-2485�8
N1040 179 Obsolete. Honeywell logo; H1 and C1 anticipation fixed; used with Q674F1261; used in Y594N1015.
None
N1057 178 Obsolete. Intertherm logo; part no. 9111882; used with Q674F1220; used in Y594N1023.
T874N1016
N1065 178 Obsolete. Miller logo; Nordyne part no. 9122240; used with Q674F1220; used in Y594N1031.
T874N1016
T874P Heat pump model; 2-stage heat, 1-stage cool, automatic changeover in cool.
P1006 57, 78 Obsolete. McQuay logo; part no. 860-442725B-00; 8°F (4.4°C) interstage differential between H1 and H2; used with Q674B1273, C1140.
None See subbase description for replacement information.
P1014 78 Obsolete. Friedrich/Climate Master logo; °F/°C scaleplate; 8°F (4.4°C) differential between H1 and H2 for night setback; used with Q674C1207.
T8600D2028 (programmable)
Wiring differences (old=new): L=R, W=O; W-Y jumper required; includes night setback.
P1022 97 Obsolete. Friedrich/Climate Master logo; part no. AT5922; °F/°C scaleplate; 8°F (4.4°C) differential between H1 and H2 for night setback; used with Q674C1215.
None See subbase description for replacement information.
P1030 97 Obsolete. No logo; Friedrich part no. AT5930; 8°F (4.4°C) differential between H1 and H2 for night setback; used with Q674C1215.
None See subbase description for replacement information.
P1055 68, 97 Obsolete. Carrier Heat Pump System Control logo; part no. HH07AT205; °F/°C scaleplate; heat interstage differential 8°F (4.4°C).
None See subbase description for replacement information.
T874Q 1-stage heat; used with another T874 for night setback. Q1005 44 Honeywell logo. T874A1036Q1013 44 Obsolete. Lennox logo; part no. 13F1201; °F/°C
scaleplate. T874A1036 Replacement has °F
scaleplate. Q1021 44 Obsolete. Lennox logo; part no. 13F1301; °C scaleplate. T874A1036 Replacement has °F
scaleplate. T874R Heat pump model; 2-stage heat, 1-stage cool, manual
changeover. R1004 47 Obsolete. Honeywell logo; used with Q674B1042; used
in Y594R1029. Y594R1243a Wiring differences (old=new):
W1=W2. R1012 47 Obsolete. Honeywell logo; Addison heat pump; used
with Q674B1109. Y594R1243a Wiring differences (old=new):
W1=W2. R1020 102 Obsolete. Lennox logo; part no. 24F5401; °F/°C
scaleplate; H1 and C1 anticipators are fixed; auxiliary heat circuit powered by separate transformer; used with Q674L1025.
Y594R1243a Wiring differences (old=new): M=Y, F=G, V-VR=R, Y=W2, R=O; replacement has °F scaleplate.
R1038 102 Obsolete. Lennox logo; °C scaleplate; H1 and C1 anticipators are fixed; auxiliary heat circuit powered by separate transformer; used with Q674L1025.
Y594R1243a Wiring differences (old=new): M=Y, F=G, V-VR=R, Y=W2, R=O; replacement has °F scaleplate.
R1046 120, 101
Obsolete. York logo; part no. 2TH11702224A; H2 anticipator is fixed; used with Q674L1272 in Y594R1011 or with Q674L1094.
Y594R1664a
R1053 109 Obsolete. Honeywell logo; H2 anticipator is fixed; used with Q674L1140; used in Y594R1136.
Y594R1763a Designed for use on Trane heat pumps.
R1061 104 Obsolete. Honeywell logo; H2 anticipator is field adjustable; changeover in cooling; used with Q674L1082.
Y594R1243a Replacement has auto fan in Emergency Heat mode.
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 66
R1079 123 Obsolete. Ruud logo; part no. UXMT-C70; used with Q674L1157.
Y594R1243a
R1087 120 Obsolete. Honeywell logo; Special for Dunham Bush; use with Q674L.
Y594R1664a
R1095 123 Obsolete. Rheem logo; part no. RXMT-C70; used with Q674L1157.
T874R1152/Y594R1243a
R1103 104 Obsolete. Westinghouse logo; used with Q674L. Y594R1243a
R1111 116, 104
Obsolete. Marvair logo; H2 anticipator factory set at 1.2A; used with Q674L1215, L1082; used in Y594R1128.
Y594R1243a Replacement has auto fan in Emergency Heat mode.
R1129 113 Bard logo; used with Q674L1181. Y594R1243a Wiring differences (old=new): X1=X.
R1137 108, 125
Obsolete. Honeywell logo; Heil Quaker part no. HQ711597HW; used with Q674L1132; used in Y594R1110.
Y594R1292a
R1145 120 Obsolete. York logo; °C scaleplate; H2 anticipator is fixed; used with Q674L1272; used in Y594R1102.
Y594R1664a
R1152 115 Honeywell logo; used with Q674L1207, L1033; used in Y594R1243.
Y594R1243a
R1160 182 Obsolete. Honeywell Advanced Heat Pump System logo; used with Q674L1298 and W89.
None
R1178 110, 111
Obsolete. Lennox logo; part no. 24F5601; °F/°C scaleplate; auxiliary heat circuit powered by separate transformer; fast cycle stage H2 anticipator; requires outdoor reset and independent circuits; used with Q674L1165, L1355.
Y594R1763a Wiring differences (old=new): V-VR=R, M=Y, F=G, X=B, Y=W, A=T, R=O, E=X2.
R1186 182 Obsolete. Honeywell Advanced Heat Pump System logo; used with Q674L1231 and W89.
None
R1194 115 Obsolete. Amana logo; used with Q674L1249 and W89. Y594R1243a
R1202 201 Obsolete. Intertherm logo; part no. 9111871; used with Q674L1264 or Q674L1595; used in Y594R1185.
Y594R1672a Wiring differences (old=new): W2=W, Z=no connection, K=X, W=G, W1=H, X=B.
R1210 101 Obsolete. Roca logo; °C scaleplate; used with Q674L1017.
Y594R1243a Wiring differences (old=new): W=W2, X=L, B=X.
R1228 120 Obsolete. York logo; part no. 2TH11702524A; °C scaleplate; used with Q674L1272 and C815A1005; used in Y594R1144.
Y594R1672a
R1236 115 Obsolete. Williamson logo; includes Allen wrench and screws to lock cover; used with Q674L1348.
T874R1152
R1244 115 Obsolete. Westinghouse logo; used with Q674L1314 and W89.
T874R1152/Y594R1243a
R1251 120 Obsolete. York logo; part no. 2TH11702324A; H2 anticipator is fixed; used with Q674L1272 and C815A1039.
Y594R1672a
R1269 122 Obsolete. Fedders multi logo; part no. THTX-120-HEHB 88-58-00540-001; used with Q674L1066; used in Y594R1037.
Y594R1615a Wiring differences (old=new): K=E, C=X, W1=B, Z=L.
R1285 123 Obsolete. Honeywell logo; Rheem part no. 41-20796-15; used with Q674L1157.
Y594R1243a
R1301 113 Obsolete. Comfortmaker logo; part no. 1505-714; used with Q674L1181; used in Y594R1417.
Y594R1243a Wiring differences (old=new): X1=X.
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
67 60-2485�8
R1319 191 Obsolete. Carrier part no. 42QH400083; used with Q674B1281 on two speed fan applications.
See OEM for replacement.
R1327 120 Obsolete. Borg-Warner multi-logo; part no. 6TH11702224A; used with Q674L1272; used in Y594R1193.
Y594R1672a
R1335 106 Obsolete. BDP multi-logo; part no. HH641501; H2 anticipator factory set 1.2A; used with Q674L1405; used in Y594R1201.
Y594R1243a
R1343 133 Obsolete. Fedders multi-logo; part no. THTX-120-HEHC 88-58-0056-001; used with Q674L1413; used in Y594R1219.
Y594R1425a Wiring differences (old=new): K=E, C=X1, Z=L; remove Y1-W1 jumper.
R1350 113 Obsolete. Honeywell logo; used with Q674L1181. Y594R1243a Wiring differences (old=new): X1=X.
R1368 125 Obsolete. Coleman logo; part no. 3600-368; used with Q674L1421; used in Y594R1235.
Y594R1797a
R1376 115 Honeywell logo; °C scaleplate; used with Q674L1207. T874R1152R1384 131,
135Obsolete. Carrier Heat Pump System Control logo; part no. HH07AQ170; used with Q674L (HH93AZ187), Q674L (HH93AZ197), or Q674L (HH93AZ198).
Y594G1243a Wiring differences (old=new): C=X.
R1392 128 Obsolete. Williamson logo; used with Q674L1447; used in Y594R1250.
Y594R1425a Wiring differences (old=new): A=L.
R1400 113 Obsolete. LSI part no. 104710001; used with Q674L1181, L1462.
See subbase description for replacement information.
R1426 136 Obsolete. Trane Weathertron Heat Pump logo; part no. BAYSTAT339 (WY28X0112); °F/°C scaleplate; used with Q674L1496; used in Y594R1284.
Y594R1763a
R1434 134 Ruud logo; part no. 41-20796-32; used with Q674L1504; used in Y594R1649.
Y594R1300a
R1442 134 Rheem logo; part no. 41-20796-28; used with Q674L1504; used in Y594R1631.
Y594R1300a
R1459 134 Obsolete. Honeywell logo; Rheem part no. 41-20796-25; used with Q674L1504.
Y594R1300a
R1467 108 Honeywell logo; used with Q674L1512; used in Y594R1292.
Y594R1292a
R1475 123 Honeywell logo; scale range 42°F to 88°F; used with Q674L1520; used in Y594R1300.
Y594R1300a
R1483 130 Obsolete. Comfortmaker logo; °F/°C scaleplate; used with Q674L1538 and C815A1005; used in Y594R1318.
Y594R1763a Wiring differences (old=new): W1=W, E=X2, X=F, C=B.
R1491 137 Obsolete. Honeywell logo; TRADELINE model; used with Q674L1553; used in Y594R1326.
Y594R1615a
R1509 47 Obsolete. Slant/Fin logo; used with Q674B1042; used in Y594R1334.
Y594R1243a Wiring differences (old=new): W1=W2.
R1517 130 Obsolete. Arcoaire logo; part no. 150671; used with Q674L1538 and C815A1005; used in Y594R1342.
Y594R1763a Wiring differences (old=new): W1=W, E=X2, X=F, C=B.
R1525 113 Obsolete. Arcoaire logo; used with Q674L1181; used in Y594R1359.
Y594R1243a Wiring differences (old=new): X1=X.
R1541 67 Obsolete. Goettl logo; part no. 372071; used with Q674B1349.
Y594R1300a
R1558 134 Obsolete. Universal Parts logo; part no. 41-20796-45; used with Q674L1504; used in Y594R1623.
Y594R1300a
R1566 130 Obsolete. Honeywell logo; used with Q674L1538 and C815A1005; used in Y594R1375.
Y594R1763a Wiring differences (old=new): W1=W, E=X2, X=F, C=B.
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 68
R1574 132 Obsolete. Comfortmaker logo; part no. 1505739; used with Q674L1538; used in Y594R1383.
Y594R1243a Wiring differences (old=new): C=X, X=L, W=W2.
R1582 132 Obsolete. Arcoaire logo; part no. 150739; used with Q674L1538; used in Y594R1391.
Y594R1243a Wiring differences (old=new): C=X, X=L, W=W2.
R1590 115 Obsolete. Refac logo; used with Q674L1207. T874R1152/Y594R1243a
Replacement has °F scaleplate.
R1608 119 Obsolete. Honeywell logo; Intertherm heat pump; used with Q674L1264; used in Y594R1409.
Y594R1763a Wiring differences (old=new): W2=W, X=B, Z=F, K=X2, W1=O.
R1616 168 Honeywell logo; SUPER TRADELINE® model; used with Q674L1587; used in Y594R1425.
Y594R1425a
R1624 200 Obsolete. Honeywell logo; used with Q674L1595; used in Y594R1433.
Y594R1243a Wiring differences (old=new): X=B, Z=F, W2=W, K=X2, W1=O.
R1632 134 Obsolete. Honeywell logo; used with Q674L1603. Y594R1243a R1640 115 Obsolete. Hitecsa logo; °C scaleplate; H2 anticipator
factory set at 1.2A; used with Q674L1207. Y594R1243a Replacement has °F
scaleplate. R1657 136 Obsolete. American Standard logo; part no.
ASYSTAT651; requires outdoor reset; used with Q674L1611; used in Y594R1441.
Y594R1763a
R1673 108 Heil logo; part no. 1060321, HAXB004TW01; used with Q674L1132; used in Y594R1466.
Y594R1292a
R1699 119 Obsolete. Miller logo; used with Q674L1264; used in Y594R1482.
Y594R1763a Wiring differences (old=new): W2=W, X=B, Z=F, K=X2, W1=O.
R1707 209 Trol-A-Temp by Honeywell logo; Premier White® color; used with Q674L1678; used in Y594R1490.
None See Trol-A-Temp for replacement.
R1715 209 Trol-A-Temp by Honeywell logo; used with Q674L1186; used in Y594R1508.
None See Trol-A-Temp for replacement.
R1723 218 Obsolete. No logo; Snyder General part no. 654958B07; °F/°C scaleplate; used with Q674L1702 and C815A1005; used in Y594R1516.
Y594R1672a Wiring differences (old=new): W1=W, X=X2, C=B.
R1731 108 Obsolete. Inter-City Products logo; part no. HQ11477909HW; used with Q674L1132; used in Y594R1524.
Y594R1292a
R1749 108 Tempstar logo; part no. 1060322, TAXB004TW01; used with Q674L1132; used in Y594R1532.
Y594R1292a
R1814 108 Obsolete. Honeywell logo; Keeprite part no. THPC; °C scaleplate; used with Q674L1132; used in Y594R1607.
Y594R1292a Replacement has °F scaleplate.
R1822 230 Honeywell logo; TRADELINE model; used with Q674L1710; used in Y594R1615.
Y594R1615a
R1830 134 Obsolete. Addison logo; WeatherKing part no. 41-20796-61; used with Q674L1504; used in Y594R1656.
Y594R1300a
R1855 228 Obsolete. Lennox logo; Premier White® color; °C scaleplate; outdoor reset required (use C815A1005); used with Q674L1728; used in Y594R1714.
Y594R1763a Wiring differences (old=new): Y1=Y, L=F, W1=W, E=X2, C=B; replacement has °F scaleplate.
R1871 120 Honeywell logo; designed to replace Y594R1011 (York part no. 2TH11702224); used with Q674L1736; used in Y594R1664.
Y594R1664a
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
69 60-2485�8
R1889 120 Honeywell logo; designed to replace Y594R1151 (York part no. 2TH11702324), Y594R1193 (York part no. 6TH11702224), and York part no. 2TH11704024; used with Q674L1736 and C815A1054; used in Y594R1672.
Y594R1672a
R1897 230 Honeywell logo; Premier White® color; used with Q674L1751; used in Y594R1680.
Y594R1680a
R1905 120 Obsolete. Honeywell logo; Premier White® color; designed to replace Y594R1151 (York part no. 2TH11702324), Y594R1193 (York part no. 6TH11702224), and York part no. 2TH11704024; used with Q674L1777 and C815A1054; used in Y594R1698.
Y594R1672a Replacement is beige.
R1913 120 Obsolete. Honeywell logo; Premier White® color; designed to replace Y594R1011 (York part no. 2TH11702224); used with Q674L1777; used in Y594R1706.
Y594R1664a Replacement is beige.
R1921 115 Obsolete. Econar logo; used with Q674L1207; used in Y594R1722.
Y594R1243a
R1939 197 American Standard logo (Trane); part no. ASYSTAT651A; includes outdoor reset; used with Q7674L1801; used in Y594R1748.
Y594R1763a
R1947 168 Obsolete. Inter-City Products logo; part no. HQ1149406HW; used with Q674L1819; used in Y594R1755.
Y594R1425a
R1954 197 Honeywell logo; TRADELINE model; includes outdoor reset; used with Q674L1827; used in Y594R1763.
Y594R1763a Direct replacement for Y594R1748 (T874R1939/Q674L1801) American Standard logo (ASYSTAT 651A) and Y594R1136 (T874R1053/Q674L1140).
R1962 115 Obsolete. Consolidated Industries logo; part no. 9036100; Premier White® color; used with Q674L1843; used in Y594R1771.
Y594R1680a Includes CHECK LED.
R1970 120 York logo; Canada; Premier White® color; °C scaleplate; used in Y594R1789; used with C815A1039.
Y594R1672a Replacement has °F scaleplate.
R1988 125 Honeywell logo; TRADELINE model; used with Q674L1868; used in Y594R1797.
Y594R1797 Direct replacement for Y594R1235 (T874R1368/Q674L1421) Evcon/Coleman part no. 3600-368.
R2002 245 Obsolete. Amana Air Conditioning logo; part no. 10574102; used in Y594R1805.
Y594R1797 Wiring differences (old=new): C/X=X.
R2010 245 Obsolete. Amana Air Conditioning logo; part no. 10574104.
Y594R1797 Wiring differences (old=new): C/X=X, W3=W2.
R2028 209 Obsolete. York logo; part no. 2TH11703424A; used with Q674L1918 in Y594R1821.
Y594R1797
R2036 134 Ruud logo; °C scaleplate; used with Q674L1504. See OEM for replacement.
T874S 2-stage heat, 3-stage cool. S1001 223 Obsolete. Carrier Synergy 2000 Heat Pump System
Control logo; used with Q674F1501. T8611M2025
(programmable) or see OEM for
direct replacement.
Includes night setback.
T874V 1-stage cool. V1008 69 Obsolete. No logo; Carrier part no. HH07AT177; used
with Q674R1003. T874A1036
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 70
T874W 3-stage heat, 2-stage cool, manual changeover. W1007 118 Obsolete. Honeywell logo; Westinghouse special; used
with Q674L1256. T8611M2025
(programmable)Includes night setback.
W1015 54 Honeywell logo; used with Q674B1216 and C815A1005; used in Y594W1014.
T874W1015
W1023 233 Obsolete. Lennox Advanced Heat Pump System logo; used with Q674L1280 and W89.
T874W1015
W1031 140 Obsolete. No logo; Rheem part no. 41-20797-20; used with Q674L1546 and C815A1005; used in Y594W1022.
T8611M2025 (programmable)
Includes night setback.
W1049 100 Obsolete. McQuay logo; part no. 61202501; 12°F interstage differential between H2 and H3 for night setback; used with Q674C1363.
T8611M2025 (programmable)
Includes night setback.
W1056 220 Obsolete. McQuay/Snyder General logo; part no. 1202501; 12°F differential between H2 and H3 for night setback; used with Q674C1363 (61202502).
See OEM for replacement.
W1064 220 Obsolete. AAF/Snyder General logo; part no. 066804408; 12°F differential between H2 and H3 for night setback; used with Q674C1363 (66804408).
See OEM for replacement.
W1072 140 Obsolete. Honeywell logo (Inter-City Products); used in Y594W1030.
T8611M2025 (programmable)
Includes night setback.
W1080 220 McQuay logo; part no. 073318901; Premier White® color; 12°F differential between H2 and H3 for night setback.
None
W1106 247 Obsolete. Addison logo; part no. 843-277; °F/°C scaleplate; used with Q674L1934 in Y594W1055.
T8611M2025
T874Y Heat pump model; 2-stage heat, 2-stage cool, heat or cool auto changeover.
Y1005 210 Obsolete. Mammoth Water Source Heat Pump logo; used with Q674E1353; used in Y594Y1004.
See OEM for replacement.
Y1013 248 Obsolete. WaterFurnace logo; part no. TA21H03; Premier White® color; °F/°C scaleplate; used with Q674F1675 (32003081).
See OEM for replacement.
Table 8. T874 Cross Reference.Model
NumberFig. No. Description
Trade Model Replacement Remarks
aBoth the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
71 60-2485�8
Table 9. Q674 Subbase Cross Reference.
Model Number
Fig. No. Description
Q674 Trade Replacement Remarks
Q674A System: HEAT-AUTO-COOL; Fan: AUTO-ONA1001 71 Standard OEM. Q674A1019A1019 71 TRADELINE® model; used with T874A-D. Q674A1019A1035 71 Obsolete. Trane part no. BAS-0435; used with T874A-D. Q674A1019A1043 71 Honeywell logo; TRADELINE model; Q674A1019A1050 71 Obsolete. Standard OEM. Q674A1043
Q674B System: HEAT-OFF-COOL; Fan: AUTO-ONB1000 45 Standard OEM; used with T874C1570, C1695, C1703,
D1843; used in Y594C1363.Q674B1034
B1018 44 Standard OEM; used with T874B1035, D1082; used in Y594B1026, D1016.
Q674B1018
B1026 45 Obsolete. System: HEAT-OFF-RESET-COOL. Q674B1034B1034 45 TRADELINE Q674B1034B1042 47 Obsolete. Used with T874R1004, R1509; used in
Y594R1029, R1334.Y594R1243a Wiring differences (old=new):
W1=W2.B1059 45 Obsolete. Factory installed RC-RH jumper; used with
T874C1059; used in Y594C1256.Q674B1034 Field wire RC-RH.
B1075 46 Auto fan in heating and cooling mode; used with T874B1035, C1000, D1082; used in Y594D1040.
Q674B1075
B1083 51 Obsolete. Carrier part no. HH93AZ178; factory installed RC-RH jumper.
Q674B1075a One system transformer only.
B1091 45 Obsolete. Carrier part no. HH93AZ184; factory installed RC-RH jumper.
Q674B1034
B1109 47 Obsolete. Addison heat pump; used with T874R1012. Y594R1243a Wiring differences (old=new): W1=W2.
B1117 44 Obsolete. Carrier part no. HH93AZ180; factory installed RC-RH jumper.
Q674B1018a
B1125 53 Obsolete. York part no. 2TB04700324A; used with T874D1041.
Q674B1075a Jumper RC-RH; replacement has no LOCKOUT LED.
B1133 48 Obsolete. Includes FILTER LED; used with T874D1082; used in Y594D1156.
Q674B1018
B1141 51 Trane part no. BAY28X185; automatic fan operation in heat and cool mode.
Q674B1075 Set T874 H1 anticipator for combined load of heat relay and fan relay.
B1158 50 Obsolete. Used with T874G1071. T874C1018/ Q674B1018a
W1-Y1 and RH-RC jumpers required.
B1166 249 Carrier part no. HH93AZ179; factory installed RC-RH jumper; LOCKOUT LED; used with T874C1075 (HH07AT170).
Y594C1421 or Q674B1075a
Replacement only requires one transformer and has no LOCKOUT LED.
B1190 52 Obsolete. Wards special; factory installed RH-RC and F-W3 jumpers; used with T874C1372.
Gas Furnace: Q674B1034
Electric Furnace: Q674B1075
B1208 187 Obsolete. Used with T874C1422. NoneB1216 54 Used with T874W1015 and C815A1005; used in
Y594W1014.Q674B1216
B1224 49 Obsolete. Lennox part no. 25F7301; four LEDs; used with T874C1430.
Q674B1034 Replacement has no LEDs.
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 72
B1240 234 Obsolete. Northrup heat pump; AUX HEAT LED; used with T874G1139.
Y594G1252a Wiring differences (old=new): Y1=Y2, W1=W2; EM HT system switch position is not operational.
B1257 56 Obsolete. LSI-Mammoth; RESET LED; automatic fan operation in heat and cool modes; used with T874C1471; used in Y594C1314.
Q674B1075 Replacement has no LED.
B1273 57 Obsolete. McQuay part no. 860-442727B-00; System: OVERRIDE-HEAT-OFF-COOL; used with T874P1006.
T874A1036/ Q674B1075a
Wiring differences (old=new): Y=Y1, L=R, W=O; jumper Y1-W1; no night setback.
T8600D2028 (programmable)
Wiring differences (old=new): L=R, W=O; W-Y jumper required; night setback.
B1281 191 Obsolete. Carrier no. 42QH400103; System: HEAT-OFF-COOL; Fan: LOW-HI-CONT; international symbols on switches; used with T874R1319.
See OEM for replacement.
B1299 46 Obsolete. Heil Quaker part no. HQ521714HW. Q674B1075B1307 62 Obsolete. Includes two LEDs; used with T874F1122. T874F1015/
Q674D1040aReplacement has no LEDs.
B1315 68 Obsolete. Friedrich part no. AQ5215; OVERRIDE and SERVICE LEDs; used with T874P1022, P1030.
T8600D2028 (programmable)
Wiring differences (old=new): L=R, W=O; W-Y jumper required; set dual fuel switch to electric heat; night setback.
B1331 65 Obsolete. Includes two LEDs; used with T874A1002. Q674B1034 Replacement has no LEDs.B1349 67 Obsolete. Goettl part no. 372072; used with
T874R1541.Y594R1300a
B1356 138 Obsolete. Carrier part no. HH93AZ192; used with T874L1018 (HH07AT178).
See OEM for replacement.
B1372 44 Obsolete. Trane part no. BAS-0427; used with T874A-D. Q674B1018B1380 46 Obsolete. Trane part no. BAS-0426; used with T874A-D. Q674B1075B1398 48 Obsolete. Trane part no. BAS-0431; FILTER LED; used
with T874A-D.Q674B1034 Replacement has no LEDs.
B1406 172 Obsolete. Carrier part no. HH93AZ200; FAULT and CHECK FILTER LEDs; used with T874H1070 (HH07AT166), T874H1088 (HH07AT167) or T874H1153 (HH07AT167); used in Y594H1046.
T874A1150/Q674B1075a
Wiring differences (old=new): Y=Y1; jumper W1-Y1; replacement has no LEDs.
B1414 51 American Standard (Trane) part no. ASYSTAT1617. Q674B1075B1448 215 Obsolete. Carrier part no. HH93A2202; Fan: Lo-Med-
High-On; used with T874L1059.See OEM for replacement.
B1455 214 Obsolete. Carrier part no. HH93AZ208; Fan: Lo-Med-High-On; used with T874A1424 (HH07AT194).
See OEM for replacement.
B1463 45 Trol-A-Temp; used with T874D1801. None See Trol-A-Temp.B1471 45 Trol-A-Temp; used with T874D1827. None See Trol-A-Temp.B1513 53 Obsolete. TRADELINE; exact replacement for
Q674B1125 (York part no. 2TB04700324).Q674B1075 Jumper RC-RH; replacement
has no LOCKOUT LED.B1521 53 Obsolete. Carrier Canada part no. HH93AZ179-W;
gray color; includes LOCKOUT LED and removable jumpers between RC and RH terminals.
Q674B1075 Jumper RC-RH; replacement has no LOCKOUT LED; beige color.
B1539 45 Obsolete. Carrier part no. HH93AZ139; used with T874D2049; used in Y594D1370.
Q674B1034
B1547 237 Obsolete. TRADELINE; gray color; used with T874C1810; used in Y594C1389.
Y594C1389
Table 9. Q674 Subbase Cross Reference.Model
NumberFig. No. Description
Q674 Trade Replacement Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
73 60-2485�8
B1554 82 Obsolete. TRADELINE; includes LOCKOUT LED and removable jumpers between RC and RH terminals; used with T874C1877; used in Y594C1421.
Y594D1347 Jumper RH-RC; system switch: Off-HEAT-AUTO-COOL.
B1562 45 Obsolete. Amana logo; part no. P1217701F; removable jumpers between RC and RH terminals.
Q674B1034
B1570 45 Obsolete. Armstrong logo; part no. 03299A18. Q674B1034 Replacement is beige.B1588 45 Obsolete. Standard OEM. Q674B1034 Replacement is beige.
Q674C System: OFF-AUTO; Fan: AUTO-ONC1009 72 Standard OEM; used with T874D1082; used in
Y594D1024.Q674C1058
C1017 Obsolete. Includes factory-installed RC-RH jumper; used with T874A,F,Q.
Q674C1058
C1033 72 Trane part no. BAY28X187. Q674C1058C1041 74 Obsolete. Command Aire heat pump; used with
T874H1005, H1054.Y594H1012a Wiring differences (old=new):
Y1=O, Y2=Y; W-Y jumper required.
C1058 72 TRADELINE Q674C1058C1066 73 Obsolete. Command Aire heat pump; used with
T874G1352.Y594H1012a Wiring differences (old=new):
Y1=O, Y2=Y, L=R, R=none; R-L jumper required; no night setback.
T8600D2028 (programmable)
Wiring differences (old=new): Y1=O, Y2=Y, L=R; W-Y jumper required; night setback.
C1074 81 Obsolete. Used with T874C1018. Q674C1058 Jumper W2-Y1 and RH-RC.C1090 77 Obsolete. LSI-Mammoth heat pump; used with
T874K1001.Y594R1419a Wiring differences (old=new):
RH-RC=R, W1=B, W3=W2, W2=W1; remove Y1-W1 jumper.
C1108 143 Obsolete. Northrup special; AUX HEAT LED; used with T874G1139.
Y594R1243a Wiring differences (old=new): Y1=Y, W1=W2, C=X.
C1116 76 Obsolete. McQuay part no. 02005959; two LEDs; used with T874D1116.
Q674C1058 Replacement has no LEDs.
C1124 79 Obsolete. LSI-Mammoth heat pump; RESET LED; used with T874G-H; used in Y594G-H.
Y594G1294 T8600D2028
C1132 75 Obsolete. McQuay part no. 03005049; spring return momentary system switch position; used with T874A1283.
See OEM for replacement.
C1140 78 Obsolete. McQuay no. 860-442728B-00; System: OVERRIDE-AUTO-OFF; used with T874P1006.
T8600D2028 (programmable)
Wiring differences (old=new): L=R, W=O; W-Y jumper required; night setback.
C1157 72 Obsolete. York part no. 2TB04700124A. Q674C1058C1165 192 Obsolete. McQuay part no. 03005050; spring return
momentary system switch position.See OEM for replacement.
C1173 96 Obsolete. American Air Filter part no. 4ELN-8787; used with T874C1133.
Q674C1058 Replacement has no LEDs.
C1181 76 Obsolete. California heat pump; used with T874C1000. Q674C1058C1199 163 Obsolete. American Air Filter part no. 4ELN-8788; two
LEDs; spring return momentary system switch position; used with T874G1485, G1535.
T8600D2028 No momentary reset switch.
Table 9. Q674 Subbase Cross Reference.Model
NumberFig. No. Description
Q674 Trade Replacement Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 74
C1207 78 Obsolete. Friedrich; System: OVERRIDE-AUTO-OFF; used with T874P1014.
T8600D2028 (programmable)
Wiring differences (old=new): L=R, W=O; W-Y jumper required; night setback.
C1215 97 Obsolete. Friedrich part no. AQ5315; System: OVERRIDE-AUTO-OFF; OVERRIDE and SERVICE LEDs; used with T874P1022, P1030.
T8600D2028 (programmable)
Wiring differences (old=new): L=R, W=O; W-Y jumper required; night setback.
C1223 73 Obsolete. Friedrich part no. AQ5323; used on systems requiring night setback contacts; used with T874G1584.
Y594H1012a Wiring differences (old=new): Y1=O, Y2=Y, L=R, R=none; R-L jumper required; no night setback.
T8600D2028 (programmable)
Wiring differences (old=new): L=R, W=O; W-Y jumper required; night setback.
C1249 164 Includes MALFUNCTION LED; used with T874H1062; used in Y594H1012.
Y594H1012a
C1256 73 Obsolete. Used with T874G1618. Y594H1012a Wiring differences (old=new): Y1=O, Y2=Y, L=R, R=none; R-L jumper required; no night setback.
T8600D2028 (programmable)
Wiring differences (old=new): L=R, W=O; W-Y jumper required; night setback.
C1264 165 Obsolete. Carrier part no. HH93AZ193; used with T874L1018 (HH07AT178).
See OEM for replacement.
C1280 181, 203
Obsolete. McQuay heat pump; part no. 60687401; COMP FAULT LED; used with T874K1019, L1034.
T8600D2028 See thermostat description for replacement information.
C1298 76, 225
Obsolete. McQuay part no. 60684801; SERVICE LED; used with T874A1523, A1549, D1918.
See OEM for replacement.
C1306 75 Obsolete. McQuay part no. 60685001; SERVICE LED; spring return momentary system switch position; used with T874A1325.
See OEM for replacement.
C1314 72 Obsolete. Trane part no. BAS-0429; used with T874A-F. Q674C1058C1322 173 Obsolete. Carrier part no. HH93AZ199; FAULT and CK
FILTER LEDs; used with T874H1070 (HH07AT166), T874H1088 (HH07AT167) or T874H1153 (HH07AT167); used in Y594H1053.
Y594H1012a Wiring differences (old=new): 2=X.
C1330 177 Obsolete. LSI-Mammoth part no. 71115201; RESET LED; used on systems with night setback contacts; used with T874G1659, H1096; used in Y594G1427, H1020.
Y594H1012a Wiring differences (old=new): R1=R; R2=L.
C1355 74 Friedrich part no. AQ355; SERVICE LED; used with T874H1112.
Y594H1012a Wiring differences (old=new): Y1=O, Y2=Y; L-R jumper required.
C1363 99 Obsolete. McQuay part no. 61202601; SERVICE LED; auto fan in heat and cool mode; used with T874C.
T874C1125/Q674B1075a
Replacement has HEAT-OFF-COOL.
219 Obsolete. Used with T874C. See OEM for replacement.
220 Obsolete. Used with T874W. See OEM for replacement.
100 Obsolete. Used with T874W. T8611M2025 (programmable)
Includes night setback.
C1371 72 American Standard part no. ASYSTAT616. Q674C1058
Table 9. Q674 Subbase Cross Reference.Model
NumberFig. No. Description
Q674 Trade Replacement Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
75 60-2485�8
C1389 205, 176
Obsolete. Command Aire part no. P1099-0021; two LEDs; used with T874G-H.
None See thermostat description for replacement information.
C1397 205, 171
Obsolete. Command Aire part no. P1099-0023; used with T874G-H.
None See thermostat description for replacement information.
C1413 213 Obsolete. Carrier part no. HH93AZ204; Fan: Lo-Med-High-On; used with T874L1059.
See OEM for replacement.
C1439 217 Obsolete. Bard part no. 8404-016; used with T874N1024.
See OEM for replacement.
C1454 163 Obsolete. Climate Master part no. AQ5354; two LEDs; spring return momentary system switch position.
Y594G1393a No momentary reset switch.
C1462 25 Climate Master Special. Q674C1058 Replacement has no LEDs.C1470 221 Obsolete. Climate Master part no. RQ5370; used with
T874H1138.Y594H1012a Wiring differences (old=new):
Y1=O, Y2=Y; replacement has MALFUNCTION LED only.
C1496 74 Obsolete. Carrier part no. HH93AZ213; includes SERVICE LED; used with T874H1161; used in Y594H1038.
Y594H1012a Wiring differences (old=new): Y1=O, Y2=Y; L-R jumper required.
C1504 83 Obsolete. Carrier part no. HH93AZ214; used in Y594. Y594H1012a Wiring differences (old=new): Y1=O, Y2=Y, L=R, R=none; R-L jumper required; no night setback.
T8600D2028 (programmable)
Wiring differences (old=new): Y1=O, Y2=Y, L=R; W-Y jumper required; night setback.
C1512 97 Obsolete. Carrier part no. HH93AZ216; System: Override-Auto-Off; includes two LEDs; used in Y594.
T8600D2028 (programmable)
Wiring differences (old=new): L=R, W=O; W-Y jumper required; night setback.
C1520 72 Obsolete. Carrier part no. HH93AZ210; used with T874D2049; used in Y594D1388.
Q674C1058
C1538 163 Climate Master part no. AQ5354; System: Off-Auto-Override; includes two LEDs and momentary spring position.
Y594G1393 No momentary reset switch.
C1546 76, 225
Obsolete. McQuay part no. 060684802; gray color; includes one LED.
Q674C1058 Replacement has no LEDs; beige color
C1553 181, 203
Obsolete. McQuay logo; part no. 073319901; includes one LED.
Q674C1058 Replacement is beige.
C1561 76 McQuay logo; part no. 073319701; includes one LED. See OEM for replacement.
C1579 99, 100
McQuay logo; part no. 073320001; includes one LED. See OEM for replacement.
C1595 72 Obsolete. Standard OEM. Q674C1058Q674D System: None; Fan: None
D1008 55, 66 Obsolete. Used with T874D1082, F1056; used in Y594D1057.
Q674D1040
D1016 55 Obsolete. Carrier part no. HH93AZ170; RC-RH jumper. Q674D1040 RC-RH jumper required.D1032 58 Obsolete. Borg-Warner; used with T874G. T874D1165/
Q674D1040aWiring differences (old=new): Y=Y2, O=Y1, W=W2; jumper W1-Y2 required.
D1040 55 TRADELINE Q674D1040D1057 55, 66 Obsolete. York part no. 2TB04700424A. Q674D1040
Table 9. Q674 Subbase Cross Reference.Model
NumberFig. No. Description
Q674 Trade Replacement Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 76
D1065 63 Obsolete. Includes two LEDs; used with T874F1122. T874F1015/Q674D1040a
Replacement has no LEDs.
D1099 55, 66 Obsolete. Trane part no. BAS-0430; used with T874A-F. Q674D1040D1107 55, 66 Obsolete. Snyder General part nos. 654958801/
1520503/ 4ELN30070.Q674F1040.
D1115 208 Trol-A-Temp; used with T874D1801. None See Trol-A-Temp.D1123 208 Trol-A-Temp; gray color; used with T874D1827. None See Trol-A-Temp.D1156 55 Obsolete. Gray color; includes removable jumper
between RC and RH terminals.Q674D1040 Replacement is beige color.
D1164 66 Obsolete. Carrier part no. HH93AZ211; used in Y594D1440.
Q674D1040
D1172 208 Obsolete. Amana logo; part no. P121501F; removable jumpers between RC and RH terminals.
Q674D1040
D1180 55 Obsolete. York logo; part no. 2TH04703224A. Q674D1040D1198 55, 66 Obsolete. Standard OEM. T874D1165/
Q674D1040Replacement is beige color.
Q674E System: OFF-HEAT-AUTO-COOL; Fan: AUTO-ONE1007 82 Used with T874D1504; used in Y594D1180. Q674E1049E1015 84 Obsolete. Lennox heat pump; used with T874G1006,
G1154.Y594G1252a Wiring differences (old=new):
R=O, M=Y, F=G, V=R, Y=W2; E-W2 jumper required.
E1049 193 TRADELINE; used with T874D2031 and TG504A1025; used in Y594D1354.
Q674E1049
E1056 82 Obsolete. Amana part no. D68535-7; used with T874C1059, C1331; used in Y594C1009.
Q674E1049 RC-RH jumper required.
E1064 83 Obsolete. RC-RH jumpered internally; EM HEAT LED. Q674E1049E1072 82 Carrier part no. HH93AZ176; RC-RH jumpered
internally.Q674E1049 RC-RH jumper required.
E1080 82 Trane part no. BAY28X184. Q674E1049E1098 85 Obsolete. Used with T874A-D. Q674E1049 RC-RH jumper required.E1106 185 Obsolete. ITT Nesbitt. See OEM for
replacement.E1114 87 Carrier part no. HH93AZ177; RC-RH jumper;
LOCKOUT LED to indicate compressor lockout; used with HH07AT series thermostats.
Q674E1049 RC-RH jumper required; replacement has no LED.
E1122 83 Obsolete. Square D part no. 63600-002-10; CHECK LED.
Q674E1049 Replacement has no LED.
E1148 86 Obsolete. Lennox heat pump; used with T874G1014, G1022.
Y594G1252a Wiring differences (old=new): R=O, M=Y, F=G, Y=W2, V-VR=R; must use single transformer.
E1155 88 Obsolete. Lennox part no. 91C7501; HIGH and LOW LEDs; used with T874B1076, D1017.
Q674E1049 Replacement has no LEDs.
E1197 89 Obsolete. McQuay part no. 02005961; two LEDs; used with T874D1116.
Q674E1049 Wiring differences (old=new): D=O; replacement has no LEDs.
E1205 80 Obsolete. Fedders special; SERVICE LED; used with T874D1462.
Q674E1049 Replacement has no LEDs.
E1213 82 York part no. 2TB04700224A. Q674E1403E1221 82 Heil Quaker part no. HQ712003HW. Q674E1049
Table 9. Q674 Subbase Cross Reference.Model
NumberFig. No. Description
Q674 Trade Replacement Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
77 60-2485�8
E1262 82 Lennox part no. 13F1701. Q674E1049E1270 198 Obsolete. Carrier part no. HH93AZ189; used with
T874L1000 (HH07AT176).Y594G1419a E-W2 jumper required.
E1304 82 Obsolete. BDP part no. P272-1887; used with T874L1026.
Y594G1419a E-W2 jumper required.
E1312 224 Obsolete. McQuay part no. 60684901; one LED; used with T874A1523, A1549, D1686, D1918.
Q674E1049 Replacement has no LEDs.
E1320 82 Obsolete. Trane part no. BAS-0434. Q674E1049E1338 88 Obsolete. Goodman part no. CHTS36-60; HIGH and
LOW LEDs; used with T874B1100; used in Y594B1042.
Q674E1049 Replacement has no LEDs.
E1346 82 Obsolete. Snyder General part nos. 1505753/1506753/ 654958B02; used with T874D1769; used in Y594D1297.
Q674E1049
E1353 210 Obsolete. Mammoth; used with T874Y1005; used in Y594Y1004.
T8611M2025
E1379 212 Trol-A-Temp by Honeywell; used with T874A1465. None See Trol-A-Temp.E1395 222 Obsolete. Carrier part no. HH93AZ209; used with
T874B1134 (HH07AT199).T874B1019/ Q674E1049a
Wiring differences (old=new): W1 =W; RC-RH jumper required; replacement has no LEDs.
E1403 82 TRADELINE; designed to replace York 2TH04701024; used with T874D1942; used in Y594D1347.
Y594D1347a
E1411 82 Obsolete. Carrier Canada part no. HH93AZ176-W; gray color; removable jumper between RC and RH terminals.
Q674E1049 RC-RH jumper required. Replacement is beige color.
E1429 87 Carrier Canada part no. HH93AZ177-W; gray color; includes LOCKOUT LED; removable jumper between RC and RH terminals.
Q674E1049 RC-RH jumper required. Replacement has no LOCK-OUT LED and is beige color.
E1445 82 Obsolete. Carrier part no. HH93AZ217-W; gray color; removable jumper between RC and RH terminals.
Q674E1049 RC-RH jumper required. Replacement is beige color.
E1460 224 McQuay logo; part no. 073319801; includes one LED.E1478 82 Obsolete. Armstrong logo; part no. 03299A19. Q674E1049 RC-R jumper required.
Replacement is beige color.E1486 82 Obsolete. Standard OEM. Q674E1049 RC-R jumper required.
Replacement is beige color.Q674F System: EM.HT.-HEAT-AUTO-COOL-OFF;
Fan: AUTO-ONF1006 141 Obsolete. Includes EM HEAT LED; used with
T874C1331.Q674F1022 Jumper E-X2.
F1022 142 Includes LED and field selectable inserts; used with T874C1059; used in Y594C1017, C1330.
Q674F1022
F1030 146 Carrier part no. HH93AZ174; SUPL HEAT LED; used with T874D1074 (HH07AT172).
Q674F1022 Wiring differences (old=new): C=X1, X=X2.
F1048 149 Obsolete. Includes EM HEAT LED and auxiliary power terminal Z.
Q674F1022 Replacement does not include Z terminal and only requires one transformer.
F1063 146 Obsolete. Carrier part no. HH93AZ181; SUPL HEAT LED; used with T874D1074 (HH07AT172).
Q674F1022 Wiring differences (old=new): C=X1, X=X2.
F1071 142 Obsolete. Square D part no. 63600-002-11; CHECK LED.
Q674F1022
Table 9. Q674 Subbase Cross Reference.Model
NumberFig. No. Description
Q674 Trade Replacement Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 78
F1089 152 Obsolete. Includes EM HEAT LED; X2-E and RC-RH jumpers.
Q674F1022
F1097 142 Obsolete. Southwest special; W2-X2 jumper. Q674F1022F1105 145 Obsolete. Lennox heat pump; EM HEAT LED; used
with T874G1154.Y594G1252a Wiring differences (old=new):
V=R, Y=W2, F=G, X2=X, R=O, M=Y; L-E jumper required.
F1113 150 Obsolete. Lennox heat pump; part no. 24F6201; V-VR jumper; EM HEAT LED; changeover in cooling; used with T874G1014, G1022.
Y59461252a Wiring differences (old=new): R=O, M=Y, F=G, Y=WC, V=VR=R; must use single transformer.
F1121 153 Obsolete. Westinghouse heat pump; EM HEAT LED; used with T874G1048.
Y594G1252a
F1139 148 Obsolete. Tappan heat pump; EM HEAT LED; auto fan in emergency heat mode; used with T874G1147.
Y594G1252a Wiring differences (old=new): C=X.
F1162 151 Obsolete. Crispaire heat pump; EM HEAT LED; used with T874G.
Y594G1393a
F1170 153 Obsolete. Heatwave (Southwest Mfg.) heat pump; EM HT LED; used with T874G1105.
Y594G1252a
F1188 153 Obsolete. Luxaire heat pump. Y594G1252a
F1196 178 Obsolete. Williamson; EM HEAT and SERVICE LEDs; used with T874N1008; used in Y594N1007.
Q674F1220
F1204 154 Obsolete. Special for Crispaire; EM HEAT and COMP FAULT LEDs; used with T874G1089; used in Y594G1153.
Y594G1393a Wiring differences (old=new): A=L.
F1212 155 Includes AUX HEAT and EM HEAT LEDs; used with T874G1246, G1451, G1592, G1915; used in Y594G1252.
Q674F1212 or Y594G1252a
F1220 178 Used with T874N1016; used in Y594N. Q674F1220F1238 155 Obsolete. Rheem part no. 41-20797-14; AUX HEAT
and EM HEAT LEDs; used with T874G1097, G1212, G1220, G1238.
Y594G1252a
F1246 156 Obsolete. Westinghouse heat pump; EM HEAT and AUX HEAT LEDs; auto fan in emergency heat mode; changeover in cooling mode.
Y594G1252a
F1253 157 Obsolete. Wesco/Addison heat pump; used with T874G1261, G1279, G1287.
Y594G1252a Wiring differences (old=new): Y1=O, C=X, W1=Y, X=L.
F1261 179 Includes two LEDs; used with T874N1024; used in Y594N.
Y594G1419a Wiring differences (old=new): L=X2, Y=Y1.
F1279 158 Obsolete. Westinghouse heat pump; two LEDs; used with T874G.
Y594G1252a Wiring differences (old=new): L1=L.
F1295 147 Obsolete. Keeprite/Westinghouse heat pump; SERVICE, AUX HEAT and EM HEAT LEDs; used with T874G1188.
Y594G1252a Wiring differences (old=new): S=L; replacement does not include A or T terminals.
F1311 155 York heat pump; AUX HEAT and EM HEAT LEDs; used with T874G1410.
Y594G1252a
F1329 142 Obsolete. Heil Quaker part no. HQ712005HW; one LED and field selectable inserts.
Q674F1022
F1337 166 Obsolete. WeatherKing heat pump; two LEDs and field selectable inserts; used with T874D1009; used in Y594D1222.
Q674F1022 Wiring differences (old=new): R=RC-RH; replacement has no LEDs.
F1345 194 Obsolete. Addison heat pump; EM HEAT and CHECK LEDs; used with T874G; used in Y594G.
Y594G1252a Wiring differences (old=new): Y1=O, C=X, W1=Y, X=L.
Table 9. Q674 Subbase Cross Reference.Model
NumberFig. No. Description
Q674 Trade Replacement Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
79 60-2485�8
F1360 167 Obsolete. Rheem part no. 41-20797-17; AUX HEAT and EM HEAT LEDs; used with T874G1493.
Y594G1526a
F1378 195 Obsolete. Includes EM HEAT and AUX HEAT LEDs; used with T874G1501.
Y594G1252a Wiring differences (old=new): L1=L; changeover in cooling only.
F1394 139 Obsolete. Nepco heat pump; HEAT PUMP and AUX HEAT LEDs; System: AUX HEAT-HEAT PUMP-2 STAGE HEAT-OFF-COOL; used with T874D1595.
T874D1165/Q674B1018a
Replacement has HEAT-OFF-COOL system switching and no LEDs.
F1402 169 Obsolete. Coleman heat pump; two LEDs; used with T874G1576; used in Y594G1377.
Y594G1633a
F1410 170 Used with T874G1246, G1915; used in Y594G1393. Y594G1393a
F1428 199 Obsolete. Used with T874G1600; used in Y594G1401. Y594G1419a Wiring differences (old=new): jumper W1-Y1.
F1436 167 Includes AUX HEAT and EM HEAT LEDs; changeover in heating mode; used with T874G1626; used in Y594G1526.
None
F1444 227 Includes AUX HEAT, EM HEAT and CHECK LEDs; used with T874G1642; used in Y594G1419.
Y594G1419a
F1451 204 Obsolete. York part no. 2TB047700524A; one LED and field selectable inserts.
Q674F1012 Wiring differences (old=new): X2=X; X1=B.
F1477 227 TRADELINE; gray color; used with T874G1741, G1824; used in Y594G1476, G1534.
Y594G1476a
F1485 211 Trol-A-Temp by Honeywell; changeover is provided by Trol-A-Temp zone panel; used with T874G1758; used in Y594G1492.
None See Trol-A-Temp.
F1501 223 Obsolete. Carrier two-speed compressor heat pump; used with T874S1001.
T8611M2025 (programmable)
Includes night setback.
F1519 231 Obsolete. Nordyne; used with T874G1832, G1840; used in Y594G1542, G1559.
Y594G1252a Replacement has auto changeover in cooling mode only.
F1535 229 Obsolete. Lennox heat pump; gray color; used with T874G1857; used in Y594G1583.
Y594G1161a Wiring differences (old=new): E=X2, C=B, L=F.
F1543 204 Obsolete. TRADELINE Q674F1022 Wiring differences (old=new): X2=X, X1=B.
F1550 243 Obsolete. Amana part no. 10573901; includes two LEDs; used with T874G1899; used in Y594G1591.
Y594G1633
F1568 155 Obsolete. Gray color; includes two LEDs; used with only T874G1931.
Y594G1476 Y1-W1 jumper required.
F1584 169 TRADELINE; includes two LEDs; used with T874G1972; used in Y594G1633. Direct replacement for Coleman/Evcon Y594G1377 (T874G1576/ Q674D1402); Coleman part no. 3600-373.
Y594G1633a
F1592 238 Heat Controller; Fan: AUTO-ON; System: AUX HEAT- HEAT PUMP- 2 STAGE HEAT-OFF-COOL; includes two LEDs; used with T874C1844; used in Y594C1413.
Y594R1425 E-W2 jumper required; system switch: EM.HT.-HEAT-OFF-COOL.
F1600 169 Obsolete. Amana part no. 10573903; includes two LEDs; used with T874G1980; used in Y594G1641.
Y594G1633 Wiring differences (old=new); W3=W2.
F1634 139 Standard OEM; System: AUX HEAT-HEAT PUMP-2 STG HEAT-OFF-COOL; includes two LEDs; used with T874D2155.
Y594G1716
F1667 155 WaterFurnace logo; part no. TA21H03; System: OFF-AUTO-HEAT-EM HT; includes two LEDs; used with T874G2046.
Y594G1716
Table 9. Q674 Subbase Cross Reference.Model
NumberFig. No. Description
Q674 Trade Replacement Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 80
F1675 248 Obsolete. WaterFurnace logo; part no. TA21H03; includes four LEDs.
See OEM for replacement.
Q674G System: OFF-AUTO; Fan: NoneG1005 184 Obsolete. Used in Y594F1063. Q674G1070G1013 186 Obsolete. Climate Control; used with T874D1298. See OEM for
replacement.G1021 91 Obsolete. Includes O and B terminals; used with
T874A-F,Q or T874D1082; used in Y594D1032.Q674G1070
G1047 92 Obsolete. Used with T874C1018, C1125. T8611G1054 188 Obsolete. Singer part no. 0200-5963; used with
T874D1298.See OEM for replacement.
G1062 232 Obsolete. Singer; used with T874D1298. See OEM for replacement.
G1070 91 TRADELINE Q674G1070G1088 92 Obsolete. LSI-Mammoth part no. 71120201; used with
T874C.See OEM for replacement.
G1096 90 Obsolete. Climate Control part no. 02005958; used with T874D1439, D1447.
See OEM for replacement.
G1104 94 Obsolete. McQuay part no. 0200-5963; two LEDs; used with T874D1116.
See OEM for replacement.
G1120 202, 226
Obsolete. McQuay part no. 60684701; two SERVICE LEDs; no fan switching; used with T874D1694, G1926.
See OEM for replacement.
G1138 91 Obsolete. Trane part no. BAS-0433; used with T874A-F. Q674G1070G1153 184 Obsolete. Carrier part no. HH93AZ212; used in
Y594D1396.Q674G1070
G1161 184 Gray color. Q674G1070 Replacement is beige color.G1179 202 Obsolete. McQuay logo; part no. 073319601; includes
two LEDs.Q674G1161 Replacement has no LEDs.
Q674J System: EM.HT.-AUTO-OFF; Fan: AUTO-ONJ1001 180 Obsolete. Singer heat pump part no. 02005964; EM
HEAT LED; changeover heat mode.See OEM for replacement.
J1019 159 Obsolete. Westinghouse heat pump; EM HT LED; System: EM.HT.-ON-OFF; used with T874G1048.
Y594G1252a Wiring differences (old=new): W=W2.
J1027 160 Obsolete. York part no. 025-22291; EM HEAT LED; auto fan in emergency heat mode; changeover in cool mode; used with T874G1170, G1196, G1428, G1345, G1444; used in Y594G1013, G1138, G1229.
Y594G1567a
J1035 161 Carrier heat pump; part no. HH93AZ173; System: SUPL.HT.-ON-OFF; SUPL HEAT LED; used with T874G1055 (HH07AT171).
Y594G1674a
J1043 162 TRADELINE heat pump model; designed for use on Trane heat pumps; AUX HT and EM HT LEDs; auto fan in emergency heat; changeover in cooling mode; used with T874G1204 and C815A1008; used in Y594G1161.
Q674J1043 or Y594G1161a
Designed for use on Trane heat pumps.
J1050 183 Obsolete. Westinghouse heat pump; EM HEAT and AUX HEAT LEDs; used with T874G1071.
Y594G1674a
J1068 144 Obsolete. Carrier heat pump; part no. HH93AZ183; used with T874J1002 (HH07AT175) or T874J1028 (HH07AT165).
Y594J1019
J1076 180 Obsolete. McQuay part no. 02005964; two LEDs; used with T874A,D.
Q674F1022 Replacement has no LEDs.
Table 9. Q674 Subbase Cross Reference.Model
NumberFig. No. Description
Q674 Trade Replacement Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
81 60-2485�8
J1084 171 Obsolete. BDP heat pump; part no. 34427DP126, P272-1879; EM HEAT LED; used with T874J1010.
Y594J1019 Wiring differences (old=new): W1=W2, F=L.
J1118 196 Obsolete. Carrier heat pump; part no. HH93AZ188; SUPL HEAT LED; System: SUPL.HT.-ON-OFF; used with T874G1055 (HH07AT171).
Y594G1674 Wiring differences (old=new): C=X;Y1=W1; jumper required; no auto fan in emergency heat.
J1126 160 Obsolete. Luxaire no. 026-00068-000; EM HEAT LED; used with T874G1568; used in Y594G1351.
Y594G1567a
J1142 174 Obsolete. American Standard part no. WY28X0250; AUX HEAT and EM HEAT LEDs; used with T874G1675; used in Y594G1443.
Y594G1161a
J1159 206 Obsolete. Carrier heat pump; part no. HH93AZ196; used with T874J1002 (HH07AT175) or T874J1028 (HH07AT165).
Y594J1019
J1167 175 Obsolete. Carrier heat pump; MANUAL, AUTO, HEAT PUMP and DEFROST LEDs; System: SUPL HEAT-ON-OFF; used with T874G1717; used in Y507J1201.
Y594G1252a Wiring differences (old=new): C=X, D=L; replacement has AUX HEAT and EM HEAT LEDs.
J1175 216 Obsolete. Snyder General part nos. 1505756, 1506756; CHECK, AUX HEAT and SYSTEM LEDs; used with T874G1774, G1782; used in Y594G1500, G1518.
Y594G1252a Wiring differences (old=new): E=W2, W1=W3, X=E, C=X.
J1191 161 Obsolete. Carrier heat pump; gray color; used with T874G1790.
Y594G1252a Wiring differences (old=new): C=X; replacement has °F scaleplate.
J1209 160 TRADELINE; designed to replace Y594G1013 (York part no. 2TH11702424), Y594G1229 (York part no. 6TH11702424) and York part no. 2TH11704124; used with T874G1865; used in Y594G1567.
Y594G1567a
J1217 171 Obsolete. Nordyne part no. 9132250; used with T874J1036, J1044.
Y594J1019 Wiring differences (old=new): F=L.
J1225 160 Obsolete. TRADELINE; gray color; designed to replace Y594G1013 (York part no. 2TH11702424), Y594G1229 (York part no. 6TH11702424) and York part no. 2TH11704124; used with T874G1873; used in Y594G1575.
Y594G1567a Replacement is beige.
J1241 144 Obsolete. Carrier Canada part no. HH93AZ183-W; gray color; System: SUPL HT-ON-OFF; includes one LED.
See OEM for replacement.
J1258 161 Obsolete. Carrier Canada part no. HH93AZ173-W; gray color; System: SUPL HT-ON-OFF; includes one LED.
Y594G1674a Replacement is beige color.
J1266 160 York Canada; gray color; includes EM HT LED; used in Y594G1625.
Y594G1567a
J1274 161 TRADELINE; System: SUPL HT-ON-OFF; includes one LED; used with T874G2004; used in Y594G1674.
Y594G1674
J1282 244 Obsolete. TRADELINE; System: SUPL HT-ON-OFF; includes SUPL HT LED; used with T874J1069; used in Y594J1019.
(Recontrol)T8511G1021
Q674K System: OFF-HEAT-AUTO-COOL; Fan: NoneK1000 93 Obsolete. Carrier part no. HH93AZ172; RC-RH jumper. Q674E1049 Fan switch is not operational.K1018 95 Obsolete. Oneida Heater part no. 3040284-02;
System: OFF-WOOD-WOOD/OIL-OIL; used with T874F1106.
Q674K1026
Table 9. Q674 Subbase Cross Reference.Model
NumberFig. No. Description
Q674 Trade Replacement Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 82
K1026 95 System: OFF-WOOD-WOOD/ OIL-OIL; used with T874F1155.
Q674K1026
K1034 93 Obsolete. Snyder General part no. 4ELN-7920. Q674E1049 Fan switch is not operational.K1042 93 Obsolete. Carrier part no. HH93AZ172-W; gray color;
includes removable jumper between RC and RH terminals.
Q674E1049 Fan switch is not operational.
Q674L System: EM.HT.-HEAT-OFF-COOL; Fan: ON-AUTOL1017 101 Obsolete. York heat pump; EM HEAT LED; cooling
mode changeover; compressor lockout; auto fan in EM.HT; used with T874R1046.
Y594R1243a Wiring differences (old=new): W=W2, X=L, B=X.
L1025 102 Obsolete. Lennox heat pump; part no. 24F6101; EM. HEAT LED; V-VR jumper; used with T874R1020, J1038.
Y594R1243a Wiring differences (old=new): M=Y, F=G, V-VR=VR, Y=W2, R=O.
L1033 115 Obsolete. Rheem heat pump; EM HEAT LED; used with T874R1152.
Y594R1243a
L1041 103 Obsolete. Carrier heat pump; part no. HH93AZ175; SUPL HEAT LED; used with T874G1055 (HH07AT171), G1071 (HH93AZ175), G1113.
Y594G1419 Wiring differences (old=new): C=X, jumper Y1=W1.
L1066 122 Obsolete. Fedders heat pump; used with T874R1269; used in Y594R1037.
Y594R1615a Wiring differences (old=new): K=E, C=X, W1=B, Z=L.
L1074 124 Obsolete. Carrier heat pump; part no. HH93AZ186; SUPL HT LED; used with T874J1002 (HH07AT175) or T874J1028 (HH07AT165).
Y594J1001
L1082 104 Obsolete. Crispaire heat pump; W2-H jumper; EM HEAT LED; used with T874R1061, R1111.
Y594R1243a Replacement has auto fan in emergency heat mode.
L1090 105 Obsolete. Fedders heat pump; EM HEAT LED; changeover in heat mode; used with T874C1398, C1406, C1414.
Y594R1425a Wiring differences (old=new): K=E, C=X.
L1108 106 Obsolete. Westinghouse; EM HEAT LED. Y594R1243a
L1116 107 Obsolete. Carrier part no. HH93AZ171; SUPL HEAT LED; used with T874D1264 (HH07AT173).
See OEM for replacement.
L1132 108 Heil Quaker part no. HQ711598; used with T874R1137, R1673, R1731, R1749, R1814; used in Y594R1110, R1466, R1524, R1532, R1607.
Y594R1292a
L1140 109 Obsolete. Includes EM HEAT and AUX HEAT LEDs; used with T874R1053; used in Y594G1136.
Y594R1763a Designed for use on Trane heat pumps.
L1157 115 Obsolete. Rheem part no. 41-20796-14; EM HEAT and AUX HEAT LEDs; used with T874R.
Q674L1207a
121 Obsolete. Used with T874C. Y594C1322a
123 Obsolete. Used with T874R. Y594R1243a
L1165 110 Obsolete. Lennox no. 24F5901; factory installed V-VR jumper; EM HEAT and SERVICE LEDs; stage 2 heat is isolated; used with T874C1448, R1178 and C815A1013.
Y594R1763a Wiring differences (old=new): V-VR=R, M=Y, F=G, X=B, Y=W, A=T, R=O, E=X2.
L1173 112 Obsolete. Westinghouse; AUX HEAT and EM HEAT LEDs.
Y594R1243a
L1181 113 Used with T874R1129; used in Y594R. Y594R1243a Wiring differences (old=new): X1=X.
Table 9. Q674 Subbase Cross Reference.Model
NumberFig. No. Description
Q674 Trade Replacement Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
83 60-2485�8
L1199 114 Obsolete. Lennox no. 24F6001; used with T874D1207 and C815A1013.
T8611M2025 (programmable)
Wiring differences (old=new): V-VR=R, Y=W3, X=C, R=O, M=Y, M2=Y2-W2, F=G; jumper Y2-W2; no outdoor reset needed; use only one system transformer.
L1207 115 Used with T874R1152, R1590, R1640, R1921; used in Y594R1243, R1706.
Q674L1207 or Y594R1243a
L1215 116 Obsolete. Crispaire heat pump; used with T874R1111; used in Y594R1128.
Y594R1243a Replacement has auto fan in emergency heat mode. Wiring differences (old=new): A=L; set anticipator to 1.2.
L1223 117 Obsolete. Westinghouse special. See OEM for replacement.
L1231 182 Obsolete. Used with T874R1186 and W89. NoneL1249 115 Obsolete. Used with T874R1194 and W89. Y594R1243a
L1256 118 Obsolete. Westinghouse special; used with T874W1007.
T8611M2025 (programmable)
Includes night setback.
L1264 119 Obsolete. Intertherm heat pump; EM HEAT and SERV LEDs; used with T874R1202, R1608, R1699; used in Y594R1185, R1409, R1482.
Y594R1672a or Y594R1763a
Wiring differences (old=new): W2=W, X=B, Z=no connection, K=X, W1=H.
L1272 120 Obsolete. York part no. 025-22290; used with T874R1046, R1145; used in Y594R1011, R1102; used with T874R1228, R1251 R1327 and C815A1039; used in Y594R1144, R1151, R1193.
Y594R1672a
L1280 233 Obsolete. Lennox no. 52C7601; used with T874W1023 and W89.
Y594W1014a
L1298 182 Obsolete. Singer heat pump; used with T874R1160 and W89.
See OEM for replacement.
L1314 115 Obsolete. Westinghouse heat pump; used with T874R1244 and W89.
Q674L1207 or Y594R1243a
L1322 127 Obsolete. EM HEAT and AUX HEAT LEDs; used with T874C1455.
Y594R1243a
L1330 120 Obsolete. York heat pump; used with T874R. Y594R1664a Wiring differences (old=new): L=X, X=B.
L1348 115 Obsolete. Williamson heat pump; used with T874R1236.
Q674L1207
L1355 111, 190
Obsolete. Lennox part no. 31F3201; V-VR jumper; used with T874C1448, R1178 and C815A1015.
Y594R1763a Wiring differences (old=new): V-VR=R, M=Y, F=G, X=B, Y=W, A=T, R=O, E=X2.
L1363 129 Obsolete. York heat pump; EM HEAT LED; used with T874G1402.
Y594R1425a Wiring differences (old=new): W=W2, X=E, B=X; jumper Y-W1.
L1371 124 Obsolete. BDP heat pump; part no. 34427DP125, P272-1878; EM HEAT LED; used with T874J1010.
Y594J1001 Wiring differences (old=new): W1=W2, F=L.
L1389 114 Obsolete. Lennox part no. 41F6501; V-VR jumper; used with T874D1207.
T8611M2025 (programmable)
Wiring differences (old=new): V-VR=R, Y=W3, X=C, R=O, M=Y, M2=Y2-W2, F=G; jumper Y2-W2; no outdoor reset needed; use only one system transformer.
L1397 103 Obsolete. Carrier part no. HH93AZ185A; SUPL HEAT LED.
Y594G1393a Wiring differences (old=new): C=X.
Table 9. Q674 Subbase Cross Reference.Model
NumberFig. No. Description
Q674 Trade Replacement Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 84
L1405 106 Obsolete. BDP heat pump; part no. HH641501; used with T874R1335; used in Y594R1201.
Y594R1243a
L1413 133 Obsolete. Fedders heat pump; used with T874R1343; used in Y594R1219.
Y594R1425a Wiring differences (old=new): K=E, C=X, Z=L; remove W1-Y jumper.
L1421 125 Obsolete. Coleman heat pump; used with T874R1368; used in Y594R1235.
Y594R1797a
L1439 131 Obsolete. Carrier part no. HH93AZ187; SUPL HEAT LED; System: SUPL HT-HEAT- COOL; used with T874R1384 (HH07AQ170).
Q674L1207 or Y594G1393a
Wiring differences (old=new): C=X.
L1447 128 Obsolete. Williamson heat pump; three LEDs; used with T874R1392; used in Y594R1250.
Y594R1425a Wiring differences (old=new): A=L.
L1454 131 Obsolete. Carrier part no. HH93AZ197; SUPL HEAT LED; used with T874R1384 (HH07AQ170).
Y594R1393a Wiring differences (old=new): C=X.
L1462 113 Obsolete. LSI heat pump; part no. 104710002; used with T874R1400.
Y594R1243a Wiring differences (old=new): X1=X.
L1496 136 Obsolete. Trane heat pump; used with T874R1426; used in Y594R1284.
Y594R1763a
L1504 134 Rheem part no. 41-20796-24; used with T874R1442, R1434, R1459; used in Y594R1631, R1649, R1854.
Y594R1300a
L1512 108 Includes two LEDs; used with T874R1467; used in Y594R1292.
Y594R1292a
L1520 123 Includes EM HEAT and AUX HEAT LEDs; used with T874R1475; used in Y594R1300.
Y594R1300a
L1538 130 Obsolete. Snyder General heat pump; used with T874R1483, R1517, R1566 and C815A1005; used in Y594R1318, R1342, R1375.
Y594R1763a Wiring differences (old=new): C=B, W1=W, E=X2, X=F.
132 Obsolete. Used with T874R1574, R1582; used in Y594R1383, R1391.
Y594R1243a Wiring differences (old=new): C=X, X=L, W=W2.
L1546 140 Obsolete. Rheem part no. 41-20797-21; three LEDs; used with T874W1031 and C815A1005; used in Y594W1022.
T8611M2025 (programmable)
Includes night setback.
L1553 137 Obsolete. Includes three LEDs; used with T874R1491; used in Y594R1326.
Y594R1615a
L1561 121 Obsolete. Used with T874C1638; used in Y594C1322. Y594C1322a Use Y594C1322 when T874C is used.
123 Obsolete. Used with T874R. Y594R1243a Use Y594R1243 when T874R is used.
L1579 135 Obsolete. Carrier heat pump; part no. HH93AZ198; SUPL HEAT LED; used with T874R1384 (HH07AQ170).
Y594R1243a Wiring differences (old=new): C=X.
L1587 168 Used with T874R1616; used in Y594R1425. Y594R1425a
L1595 200,201
Obsolete. Miller heat pump; used with T874R1624 or T874R1202; used in Y594R1433.
Y594R1243a or Y594R1763a
L1603 134 Obsolete. Used with T874R1632. Y594R1243a
L1611 136 Obsolete. American Standard heat pump; part no. WY28X235; used with T874R1657; used in Y594R1441.
Y594R1763a
L1637 207 Obsolete. Carrier heat pump; part no. HH93AZ195; used with T874J1002 (HH07AT175) or T874J1010 (HH07AT165).
Y594J1001a
Table 9. Q674 Subbase Cross Reference.Model
NumberFig. No. Description
Q674 Trade Replacement Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
85 60-2485�8
L1678 209 Trol-A-Temp by Honeywell; gray color; used with T874R1707; used in Y594R1490.
None See Trol-A-Temp.
L1686 209 Trol-A-Temp by Honeywell; used with T874R1715; used in Y594R1508.
None See Trol-A-Temp.
L1702 132 Obsolete. Snyder General heat pump; part no. 654958B07; used with T874R1723 and C815A1005; used in Y594R1516.
Y594R1672a Wiring differences (old=new): C=B, W1=W, X=X2.
L1710 230 Used with T874R1822; used in Y594R1615. Y594R1615a
L1728 228 Obsolete. Lennox; gray color; used with T874R1855; used in Y594R1714.
Y594R1763a Wiring differences (old=new): Y1=Y, L=F, W1=W, E=X2, C=B.
L1736 120 Designed to replace Y594R1011 (York part no. 2TH11702224); used with T874R1871; used in Y594R1664.
Y594R1664a
Designed to replace Y594R1151 (York part no. 2TH11702324), Y594R1193 (York part no. 6TH11702224) and York part no. 2TH11704024; used with T874R1889 and C815A1054; used in Y594R1672.
Y594R1672a
L1751 230 Gray color; used with T874R1897, used in Y594R1680.
Y594R1680a
L1769 124 Obsolete. Nordyne part no. 9132260; used with T874J. See OEM for replacement.
L1777 120 Obsolete. Gray color; designed to replace Y594R1151 (York part no. 2TH11702324), Y594R1193 (York part no. 6TH11702224) and York part no. 2TH11704024; used with T874R1905 and C815A1059; used in Y594R1698.
Y594R1672a Replacement is beige.
Designed to replace Y594R1011 (York part no. 2TH11702224); used with T874R1913; used in Y594R1706.
Y594R1664a Replacement is beige.
L1785 103 Obsolete. Carrier part no. HH93AZ175-W; Canada; gray color; System: Supl Ht-Heat-Off-Cool; includes one LED.
Y594G1476a Wiring differences (old=new): C=X; Y1-W1 jumper required.
L1793 124 Obsolete. Carrier Canada part no. HH93AZ186-W; gray color; Fan: Auto-On; System: Supl Ht-Heat-Off-Cool; includes one LED.
Y594J1019a
L1801 197 American Standard (Trane) part no. THT1225; includes two LEDs; used with T874R1939; used in Y594R1748.
Y594R1763a
L1819 168 Obsolete. Inter-City Products part no. HQ1149407HW; includes three LEDs; used with T874R1947; used in Y594R1755.
Y594R1425a
L1827 197 TRADELINE; includes two LEDs; used with T874R1954; used in Y594R1763; direct replacement for Trane/American Standard Y594R1748 (T874R1939/Q674L1801) Trane part no. ASYSTAT 631A, Y594R1136 (T874R1053/Q674L1140).
Y594R1763a
L1835 140 Obsolete. Inter-City Products; includes three LEDs; used in Y594W1030.
T8611M2025a (programmable)
Includes night setback.
L1843 115 Obsolete. Consolidated Industries part no. 9036100; gray color; includes two LEDs; used with T874R1962; used in Y594R1771.
Y594R1680a Includes CHECK LED.
L1850 120 York Canada; gray color; includes one LED; used with T874R1970; used in Y594R1789.
Y594R1672a
Table 9. Q674 Subbase Cross Reference.Model
NumberFig. No. Description
Q674 Trade Replacement Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 86
L1868 125 TRADELINE; includes two LEDs; used with T874R1988; used in Y594R1797; direct replacement for Evcon/Coleman Y594R1235 (T874R1368/ Q674L1421) Coleman part no. 3600-368.
Y594R1797a
L1876 245 Obsolete. Amana part no. 10573902; includes two LEDs; used with T874R2002; used in Y594R1805.
Y594R1797 Wiring differences (old=new): C/X=X.
L1884 245 Obsolete. Amana part no. 10573904; includes two LEDs; used with T874R2010; used in Y594R1813.
Y594R1797 Wiring differences (old=new): C/X=X, W3=W2.
L1892 103 Obsolete. TRADELINE; System: SUPL HT-HEAT-OFF-COOL; includes one LED; used with T874G2004; used in Y594G1666; direct replacement for Carrier Y507J1011 (T874G1055/Q674L1041) Carrier part no. HH07AT171/HH93AZ175.
Y594G1674 Replacement has auto changeover.
L1900 241 Obsolete. TRADELINE; System: SUPL HT-HEAT-OFF-COOL; includes SUPL HT LED; used with T874J1069; used in Y594J1001; direct replacement for Carrier T874J1028/Q674J1068 (Carrier part no. HH07AT165/HH93AZ183), Carrier T874J1002/ Q674J1068 (Carrier part no. HH07AT175/ HH93AZ183).
Y594J1019 Replacement has auto changeover.
L1918 125 Obsolete. York logo; part no. 2TH11703424A; includes two LEDs; used with T874R2028 in Y594R1821.
Y594R1797a
L1934 123 Obsolete. Addison logo; part no. 843-277; includes three LEDs; used with T874W1106 in Y594W1055.
T8611M2025
Q674N System: OFF-HEAT-COOL-EVAP; Fan: AUTO-ONN1015 60 Obsolete. Goettl heat pump; changeover in heat mode;
evaporative cooler circuit; used with T874C1182.See OEM for replacement.
N1023 61 Obsolete. Sigler heat pump; evaporative cooler circuit; used with T874C1349.
See OEM for replacement.
Q674P System: SUPL HT-HEAT-COOL; Fan: AUTO-ONP1005 126 Obsolete. Carrier heat pump; part no. HH93AZ169;
used with T874G1071 (HH07AT171).Y594G1419a Wiring differences (old=new):
C=X; jumper Y1-W1; replacement has OFF-EM HT-HEAT-AUTO-COOL system switching.
Q674Q System: HEAT-OFF-COOL; Fan: LOW-MED-HI-ONQ1004 59 Obsolete. McQuay special; used with T874A1267. See OEM for
replacement.Q1012 64 Used with T874A1291. None
Q674R System: OFF-COOL; Fan: LO-HI-CONTR1003 69 Obsolete. Carrier part no. HH93AZ190; international
symbols on fan and switches; used with T874V1008 (HH07AT177).
See OEM for replacement.
Q674S System: HEAT-COOL; Fan: NoneS1000 70 Obsolete. Fiberglas; Canada; SERVICE LED; used
with T874C1653; used in Y594C1348.See OEM for replacement.
Q674W System: OFF-ON; Fan: LO-MED-HIW1006 240 Obsolete. Snyder General part no. 044271801. See OEM for
replacement.
Table 9. Q674 Subbase Cross Reference.Model
NumberFig. No. Description
Q674 Trade Replacement Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
87 60-2485�8
Table 10. Y594 Cross Reference.
Model Number
Fig. No. Description
Trade Model Replacementa Remarks
Y594AA1001 46 Obsolete. Amana part no. D68535-11; contains
T874A1077, Q674B1075.T874A1036/ Q674B1075
A1019 82 Obsolete. Amana part no. P68535-12; contains T874A1077, Q674E1056.
T874A1036/ Q674E1049
A1035 44 Obsolete. Trane part no. 268-0187-1; contains T874A1085, Q674B1018.
T874A1036/ Q674B1018
A1043 46 Obsolete. Trane part no. 268-0201-5; contains T874A1085, Q674B1075.
T874A1036/ Q674B1075
A1050 55, 66 Obsolete. Trane part no. 268-0201-3; contains T874A1085, Q674D1008.
T874A1036/ Q674D1040
A1068 82 Obsolete. Sears part no. 42-9144; contains T874A1119, Q674E1007.
T874A1036/ Q674E1049
A1126 64 Contains T874A1291, Q674Q1012. NoneA1159 91 Obsolete. Contains T874A1440, Q674G1005. T874A1150/
Q674G1070A1167 184 California Economizer; Premier White® color;
contains T874A1580 and Q674G1161.T874A1036/ Q674G1070
Replacement is beige color.
A1175 55 Obsolete. York logo; part no. 2TH04703224; contains T874A1622, Q674D1180.
T874A1010/Q674D1040
A1191 46 Obsolete. Amana logo: part no. P6853524R; contains T874A1002, Q674B1075.
T874A1036/Q674B1075
Y594BB1026 44 Trane part no. BAYSTAT012; contains T874B1035,
Q674B1018.T874B1019/ Q674B1018
B1034 46 Obsolete. Trane part no. 163-552-1; contains T874B1035, Q674B1075.
T874B1019/ Q674B1075
B1042 88 Obsolete. Goodman part no. CHTS36-60; contains T874B1100, Q674E1338.
T874B1019/ Q674E1049
No LEDs on replacement.
Y594CC1009 82 Obsolete. Amana part no. D68535-9; contains
T874C1059, Q674E1056.T874C1018/ Q674E1049
Jumper RC-RH.
C1017 142 Obsolete. Amana part no. D68535-10; contains T874C1059, Q674F1022.
T874C1018/ Q674F1022
C1058 46 Obsolete. Contains T874C1000, Q674B1075. T874C1018/ Q674B1075
C1082 82 Obsolete. Trane part no. 166-162-1; contains T874C1083, Q674E1007.
T874C1018/ Q674E1049
C1256 45 Obsolete. Amana part no. D68535-16; contains T874C1059, Q674B1059.
T874C1018/ Q674B1034
Jumper RC-RH.
C1280 45 Obsolete. Williamson; contains T874C1570, Q674B1000.
T874C1018/ Q674B1034
C1314 56 Obsolete. LSI; contains T874C1471, Q674B1257. T874C1018/ Q674B1018
Jumper RC-RH; no RESET LED on replacement.
C1322 121 Obsolete. Contains T874C1638, Q674L1561. Y594C1322C1330 142 Obsolete. Amana part no. D68535-21; contains
T874C1059, Q674F1022.T874C1018/ Q674F1022
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 88
C1348 70 Obsolete. Fiberglas; contains T874C1653, Q674S1000.
T874C1000/ Q674B1075
Wiring differences (old=new): Y=Y1; jumper RC-RH and Y1-W1; replacement has no SERVICE LED; replacement has fan switching and HEAT-OFF-COOL system switching.
C1355 45 Obsolete. Nordyne �Miller� part no. 9122250; contains T874C1695, Q674B1000.
T874C1018/ Q674B1034
C1363 45 Obsolete. Nordyne �Intertherm� part no. 911100001; contains T874C1703, Q674B1000.
T874C1018/ Q674B1075
Wiring differences (old=new): Y=Y1; jumper RC-RH; Y1-W; replacement has no SERVICE LED.
C1371 184 Obsolete. California Economizer; contains T874C1802 and Q674G1005.
T874C1018/ Q674G1070
C1389 237 Obsolete. TRADELINE; Premier White® color; contains T874C1810 and Q674B1547.
Y594C1389
C1413 238 Heat Controller �Energy Night� logo; contains T874C1844 and Q674F1592.
Y594R1425 E-W2 jumper required; system: EM.HT.-Heat-Off-Cool.
C1421 249 Obsolete. TRADELINE; contains T874C1877 and Q674B1554.
Y594D1347 Replacement has auto changeover; jumper RH-RC.
C1439 T874C1869 and Q674C1579. NoneY594D
D1016 44 Obsolete. Trane part no. 268-0201-2; contains T874D1082, Q674B1018.
T874D1165/ Q674B1018
D1024 72 Trane part no. BAYSTAT010; contains T874D1082, Q674C1009.
T874D1165/ Q674C1058
D1032 91 Obsolete. Trane part no. BAYSTAT011; contains T874D1082, Q674G1021.
T874D1165/ Q674G1070
D1040 46 Amana part no. P68535-19R; contains T874D1082, Q674B1075.
T874D1165/ Q674B1075
D1057 55, 66 Obsolete. Trane part no. BAYSTAT007; contains T874D1082, Q674D1008.
T874D1165/ Q674D1040
D1149 46 Obsolete. Amana part no. P68535-20C; contains T874D1322, Q674B1075.
T874D1165/ Q674B1075
D1156 48 Obsolete. Trane part no. BAYSTAT013; contains T874D1082, Q674B1133.
T874D1165/ Q674B1018
Replacement has no FILTER LED.
D1180 82 York part no. 025-23321-000; contains T874D1504, Q674E1007.
T874D1165/ Q674E1049
D1222 166 Obsolete. WeatherKing; contains T874D1009, Q674F1337.
T874D1165/ Q674F1022
Wiring differences (old=new): R=RH; jumper RC-RH; replacement has no EM.HT. or AUX. HT. LEDs.
D1248 82 Obsolete. Reznor part no. 93437; contains T874D1629, Q674E1007.
T874D1165/ Q674E1049
D1297 82 Obsolete. ArcoAire part no. 1506753; contains T874D1769, Q674E1346.
T874D1165/ Q674E1049
D1305 82 Obsolete. Comfortmaker part no. 1505753; contains T874D1785, Q674E1346.
T874D1165/ Q674E1049
D1321 45 Obsolete. Goodman part no. CHT 90-120; contains T874D1843, Q674B1000.
T874D1165/ Q674B1034
D1339 82 Obsolete. Nordyne part no. 5471180; contains T874D1009, Q674E1007.
T874D1165/ Q674E1049
Table 10. Y594 Cross Reference.
Model Number
Fig. No. Description
Trade Model Replacementa Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
89 60-2485�8
D1347 82 TRADELINE® contains T874D1942, Q674E1403. Y594D1347D1354 82 SUPER TRADELINE® contains T874D2031 (no
cover), Q674E1049, and TG504A with two keys.Y594D1354
D1370 45 Obsolete. Carrier part no. 50QE90022101; contains T874D2049 and Q674B1539.
T874D1165/Q674B1034
Replacement has °F scaleplate.
D1388 72 Obsolete. Carrier part no. 50QE90023101; contains T874D2049 and Q674C1520.
T874D1165/Q674C1058
Replacement has °F scaleplate.
D1396 184 Obsolete. Carrier part no. 50QE90025101; contains T874D2049 and Q674G1153.
T874D1165/Q674G1070
Replacement has °F scaleplate.
D1404 55, 66 Obsolete. Carrier part no. 50QE90024101; contains T874D2049 and Q674D1164.
T874D1165/Q674D1040
Replacement has °F scaleplate.
D1412 82 Obsolete. Carrier �Weathermaker� part no. HH07AT209; taupe color; contains T874D2064 and Q674E1445.
T874D1165/Q674E1049
Replacement is beige color.
D1420 82 Obsolete. Carrier �Zone Perfect� part no. HH07AT208; taupe color; contains T874D2072 and Q674E1445.
T874D1165/Q674E1049
Replacement is beige color.
D1438 55, 66 Obsolete. Contains T874D2098 and Q674D1008. T874D1165/Q674D1040
Replacement has 2 setpoint levers.
D1446 55, 66 Obsolete. Contains T874D2106 and Q674D1008. T874D1165/Q674D1040
Replacement has °F scaleplate and 2 setpoint levers.
D1453 208 Obsolete. Amana logo; part no. P1217501F; contains T874D2163 and Q674D1172.
T874D1165/Q674D1040
D1461 45 Obsolete. Amana logo; part no. P1217701F; contains T874D2171 and Q674B1562.
T874D1942/Q674B1034
Y594EE1015 72 Obsolete. Trane part no. BAYSTAT015; contains
T874E1040, Q674C1009.T874B1019/ Q674C1058
Y594FF1022 44 Obsolete. Contains T874F1031 and 40003440-001
wallplate with installed diode.T874F1015
F1048 72 Obsolete. Reznor part no. 93436; contains T874F1130, Q674C1009.
T874F1015/ Q674C1058
F1063 91 Obsolete. Reznor part no. 93435; contains T874F1130, Q674G1005.
T874F1015/ Q674G1070
Y594GG1013 160 Obsolete. York part no. 2TH11702424; contains
T874G1170, Q674J1027.Y594G1567
G1138 160 Obsolete. York part no. 025-22286; contains T874G1196, Q674J1027.
Y594G1567
G1153 154 Obsolete. Crispaire part no. HP10-51; contains T874G1089, Q674F1204.
Y594G1252 Wiring differences (old=new): A=L.
G1161 162 Contains T874G1204, Q674J1043. Y594G1161G1195 155 Obsolete. Heil Quaker part no. HQ521387HW;
contains T874G1246, Q674F1212.Y594G1252
G1229 160 Obsolete. York part no. 6TH11702424; contains T874G1428, Q674J1027.
Y594G1567
G1245 155 Obsolete. BDP part no. HH641502; contains T874G1451, Q674F1212.
Y594G1252
G1252 155 TRADELINE; contains T874G1246, Q674F1212. Y594G1252
Table 10. Y594 Cross Reference.
Model Number
Fig. No. Description
Trade Model Replacementa Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 90
G1294 79 Obsolete. LSI; contains T874G1378, Q674C1124. See OEM for replacement.
H2 is night setback.
G1328 194 Obsolete. Addison part no. 8403-197; contains T874G1543, Q674F1345.
Y594G1252 Wiring differences (old=new): Y1=O, X=L, C=X.
G1344 194 Obsolete. Heat Controller part no. 7601-110B; contains T874G1469, Q674F1345.
Y594G1252 Wiring differences (old=new): Y1=O, X=L, C=X; W1=Y.
G1351 160 Obsolete. Luxaire part no. 026-00068-000; contains T874G1568, Q674J1126.
Y594G1567
G1369 155 Obsolete. Contains T874G1246, Q674F1212. Y594G1252G1377 169 Obsolete. Coleman part no. 3600-373; contains
T874G1576, Q674F1402.Y594G1633
G1385 155 Obsolete. ArcoAire; contains T874G1592, Q674F1212.
Y594G1252
G1393 170 Obsolete. Contains T874R1393, Q674L1454. Y594G1393G1419 227 TRADELINE; contains T874G1642, Q674F1444. Y594G1419G1427 177 Obsolete. Mammoth part no. 73034101; contains
T874G1659, Q674C1330.See OEM for replacement.
H2 is night setback.
G1443 174 Obsolete. American Standard (Trane) part no. ASYSTAT650; contains T874G1675, Q674J1142.
Y594G1161
G1476 227 TRADELINE; same as Y594G1419 except Premier White® color; contains T874G1741, Q674F1477.
Y594G1476
G1492 211 Trol-A-Temp; contains T874G1758, Q674F1485. None See Trol-A-Temp for replacement.
G1500 216 Obsolete. Comfortmaker part no. 1505756; contains T874G1774, Q674J1175.
See OEM for replacement.
G1518 216 Obsolete. ArcoAire part no. 1506756; contains T874G1782, Q674J1175.
See OEM for replacement.
G1526 167 TRADELINE; contains T874G1626, Q674F1436. NoneG1534 227 TRADELINE; °C; white; Australia; contains
T874G1824, Q674F1477.None
G1542 231 Obsolete. Intertherm part no. 9129290; contains T874G1832, Q674F1519.
Y594G1252 Cooling changeover only.
G1559 231 Obsolete. Miller part no. 9129310; contains T874G1840, Q674F1519.
Y594G1252 Cooling changeover only.
G1567 160 TRADELINE; contains T874G1865, Q674J1209. Y594G1567G1575 160 Obsolete. TRADELINE; same as Y594G1567
except Premier White® color; contains T874G1873, Q674J1225; direct replacement for York 2TH11702424 (Y594G1013 contains T874G1170/Q674J1027) and 6TH11702424 (Y594G1229 contains T874G1428/Q674J1027).
Y594G1567 Replacement is beige.
G1583 229 Obsolete. Lennox Canada part no. 97E78; contains T874G1857, Q674F1535.
Y594G1161 Wiring differences (old=new): E=X2, C=B, L=F.
G1591 243 Obsolete. Amana part no. 10636701; contains T874G1899 and Q674F1550.
Y594G1633
G1609 155 Obsolete. Econar; contains T874G1915 and Q674F1212.
Y594G1252
Table 10. Y594 Cross Reference.
Model Number
Fig. No. Description
Trade Model Replacementa Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
91 60-2485�8
G1617 73 Obsolete. Carrier part no. 50QE90020101; contains T874G1949 and Q674C1504.
Y594H1012a Wiring differences (old=new): Y1=O, Y2=Y, L=R, R=none; R-L jumper required; no night setback.
T8600D2028 (programmable)
Wiring differences (old=new): Y1=O, Y2=Y, L=R; W-Y jumper required; night setback.
G1625 160 York Canada part no. 2TH11702524; contains T874G1964 and Q674J1266.
Y594G1567a Replacement has °F scaleplate.
G1633 169 TRADELINE; contains T874G1972 and Q674F1584; direct replacement for Y594G1377 (T874G1576/Q674F1402) Evcon/Coleman part no. 3600-373.
Y594G1633a
G1641 169 Obsolete. Amana part no. 10636703; contains T874G1980 and Q674F1600.
Y594G1633 Wiring differences (old=new): W3=W2.
G1658 155 Obsolete. Tempstar �Inter-City Products� part no. 1149910; contains T874G1998 and Q674F1212.
Y594G1252
G1666 103 Obsolete. TRADELINE; manual changeover; contains T874G2004 and Q674L1892; direct replacement for Y507J1011 (T874G1055/Q674L1041) Carrier part no. 99TZ90041106 (HH07AT171/HH93AZ1750).
Y594G1674 Replacement has auto changeover.
G1674 161 TRADELINE; automatic changeover; contains T874G2004 and Q674J1274; direct replacement Y507J1003 (T874G1055/Q674J1035) Carrier part no. 99TZ90040106 (HH07AT171/HH93AZ173).
Y594G1674
G1716 155 WaterFurnace logo; part no. TA21H03; contains T874G2046 and Q674F1667.
Y594G1716
Y594HH1004 79 Obsolete. LSI part no. 73033901; contains
T874H1039 and Q674C1124.T8600D2028 H2 is night setback.
H1012 164 Contains T874H1062 and Q674C1249; replaces T874H1005/Q674C1041.
Y594H1012
H1020 177 Obsolete. Mammoth part no. 71117101; contains T874H1096 and Q674C1330.
Y594H1012 Wiring differences (old=new): R1=R, R2=L; use jumper provided.
H1038 74 Obsolete. Carrier part no. 50QE90019101; contains T874H1161 and Q674C1496.
Y594H1012a Wiring differences (old=new): X1=O, Y2=Y; L-R jumper required.
H1046 172 Obsolete. Carrier part no. 50QE90026101; contains T874H1153 and Q674B1406.
T874A1130/ Q674B1075a
Wiring differences (old=new): Y=Y1; W1-Y1 jumper required; replacement has no LEDs.
H1053 173 Obsolete. Carrier part no. 50QE90027101; contains T874H1153 and Q674C1322.
Y594H1012a Wiring differences (old=new): Z=X.
Y594JJ1001 241 Obsolete. TRADELINE; manual changeover;
contains T874J1069 and Q674L1900; direct replacement for T874J1002 or T874A1028 used with Q674L1074 or Q674L1637 (HH07AT175 or HH07AT165 used with HH93AZ186 or HH93AZ195).
(Recontrol)T8511G1021
Table 10. Y594 Cross Reference.
Model Number
Fig. No. Description
Trade Model Replacementa Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 92
J1019 244 Obsolete. TRADELINE; automatic changeover; contains T874J1069 and Q674J1282; direct replacement for T874J1002 or T874J1028 used with Q674J1068 or Q674J1159 (HH07AT175 or HH07AT165 used with HH93AZ183 or HH93AZ196).
(Recontrol)T8511G1021
Y594NN1007 178 Obsolete. Williamson part no. 75-189; contains
T874N1008 and Q674F1196.T874N1016/ Q674F1196
N1015 179 Obsolete. Contains T874N1040 and Q674F1261. Y594G1419a Wiring differences (old=new): L=X2, Y=Y1.
N1023 178 Obsolete. Intertherm part no. 9111882; contains T874N1057 and Q674F1220.
T874N1016/ Q674F1220
N1031 178 Obsolete. Nordyne �Miller� part no. 9122240; contains T874N1065 and Q674F1220.
T874N1016/ Q674F1220
Y594PP1005 97 Obsolete. Carrier part no. 50QE90021101; contains
T874P1055 and Q674C1512.T8600D2028 Wiring differences (old=new):
Y=Y1, W=O; Y1-W1 jumper required.
Y594RR1011 120 Obsolete. York part no. 2TH11702224; contains
T874R1046 and Q674L1272.Y594R1664
R1029 47 Obsolete. Bryant; contains T874R1004 and Q674B1042.
Y594R1243 Wiring differences (old=new): W1=W2.
R1037 122 Obsolete. Fedders part no. 88-58-00540-001; contains T874R1269 and Q674L1066.
Y594R1615 Wiring differences (old=new): K=E, C=X, W1=B, Z=L.
R1102 120 Obsolete. York part no. 025-22285-000; contains T874R1145 and Q674L1272.
Y594R1664
R1110 108 Obsolete. Heil Quaker part no. HQ712004HW; contains T874R1137 and Q674L1132.
Y594R1292
R1128 116 Obsolete. Crispaire part no. HP9-51; contains T874R1111 and Q674L1215.
Y594R1243 Wiring differences (old=new): A=L.
R1136 109 Obsolete. Contains T874R1053 and Q674L1140. Y594R1763R1151 120 Obsolete. York part no. 2TH11702324; contains
T874R1251, Q674L1272 and C815A1039.Y594R1672
R1185 201 Obsolete. Intertherm part no. 9111871; contains T874R1202 and Q674L1264.
Y594R1672 Wiring differences (old=new): W2=W, X=B, Z=no connection, K=X, W1=H.
R1193 120 Obsolete. York part no. 6TH11702224; contains T874R1327 and Q674L1272.
Y594R1664
R1201 106 Obsolete. BDP part no. HH641501; contains T874R1335 and Q674L1405.
Y594R1243
R1219 133 Obsolete. Fedders part no. 88-58-00560-001; contains T874R1343 and Q674L1413.
Y594R1425 Wiring differences (old=new): K=E, C=X, Z=L; remove factory installed jumper.
R1235 125 Obsolete. Coleman part no. 3600-368; contains T874R1368 and Q674L1421.
Y594R1797
R1243 115 TRADELINE; contains T874R1152 and Q674L1207. Y594R1243R1250 128 Obsolete. Williamson part no. 75-191; contains
T874R1392 and Q674L1447.Y594R1425 Wiring differences (old=new):
A=L.R1284 136 Obsolete. Trane part no. BAYSTAT339; contains
T874R1426 and Q674L1496.Y594R1763
Table 10. Y594 Cross Reference.
Model Number
Fig. No. Description
Trade Model Replacementa Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
93 60-2485�8
R1292 108 Contains T874R1467 and Q674L1512; replaces Y594R1110 (T874R1137/Q674L1132).
Y594R1292
R1300 123 Contains T874R1475 and Q674L1520. Y594R1300R1318 130 Obsolete. Comfortmaker part no. 1505721; contains
T874R1483, Q674L1538 and C815A1005.Y594R1763 Wiring differences (old=new):
W1=W, E=X2, X=F, C=B.R1326 137 Obsolete. SUPER TRADELINE; contains
T874R1491 and Q674L1553.Y594R1615
R1334 47 Obsolete. Slant Fin; contains T874R1509 and Q674B1042.
Y594R1243 Wiring differences (old=new): W1=W2.
R1342 130 Obsolete. ArcoAire part no. 1506721; contains T874R1517, Q674L1538 and C815A1005.
Y594R1763 Wiring differences (old=new): W1=W, E=X2, X=F, C=B.
R1359 113 Obsolete. ArcoAire part no. A02074; contains T874R1525 and Q674L1181.
Y594R1243 Wiring differences (old=new): X1=X.
R1375 130 Obsolete. Contains T874R1566, Q674L1538 and C815A1005.
Y594R1763 Wiring differences (old=new): W1=W, E=X2, X=F, C=B.
R1383 132 Obsolete. Comfortmaker part no. 1505739; contains T874R1574 and Q674L1538.
Y594R1243 Wiring differences (old=new): W=W2, C=X, X=L.
R1391 132 Obsolete. ArcoAire part no. 1506739; contains T874R1582 and Q674L1538.
Y594R1243 Wiring differences (old=new): W=W2, C=X, X=L.
R1409 119 Obsolete. Intertherm part no. 6244630; contains T874R1608 and Q674L1264.
Y594R1763 Wiring differences (old=new): W2=W, X=B, Z=F, K=X2, W1=O.
R1417 113 Obsolete. Comfortmaker part no. 1505-735; contains T874R1301 and Q674L1181.
Y594R1243 Wiring differences (old=new): X1=X.
R1425 168 SUPER TRADELINE; contains T874R1616 and Q674L1587.
Y594R1425
R1433 200 Obsolete. Miller part no. 9115900; contains T874R1624 and Q674L1595.
Y594R1243 Wiring differences (old=new): W2=W, X=B, Z=F, K=X2, W1=O.
R1441 136 Obsolete. American Standard (Trane) part no. ASYSTAT651; contains T874R1657 and Q674L1611.
Y594R1763
R1466 108 Heil Quaker part no. 1060321; model no. HAXB004TW01; contains T874R1673 and Q674L1132.
Y594R1292
R1482 119 Obsolete. Nordyne �Miller� part no. 9122230; contains T874R1699 and Q674L1264.
Y594R1763 Wiring differences (old=new): W2=W, X=B, Z=F, K=X2, W1=O.
R1490 209 Trol-A-Temp; contains T874R1707 and Q674L1678. None See Trol-A-Temp for replacement.
R1508 209 Trol-A-Temp; contains T874R1715 and Q674L1686. None See Trol-A-Temp for replacement.
R1516 132 Obsolete. Snyder General part no. 654958B07; contains T874R1723, Q674L1702 and C815A1005.
Y594R1763 Wiring differences (old=new): W1=W, C=B, X=X2.
R1524 108 Obsolete. Inter-City Products part no. HQ1147925HW; contains T874R1731 and Q674L1132.
Y594R1292
R1532 108 Heil Quaker part no. 1060322; model no. TAXB004TW01; contains T874R1749 and Q674L1132.
Y594R1292
R1607 108 Obsolete. Keeprite THPC; contains T874R1814 and Q674L1132.
Y594R1292
Table 10. Y594 Cross Reference.
Model Number
Fig. No. Description
Trade Model Replacementa Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 94
R1615 230 TRADELINE; contains T874R1822 and Q674L1710; replaces Y594R1326 (T874R1491/Q674L1553).
Y594R1615
R1623 134 Obsolete. Rheem Universal Parts part no. 41-20796-46; contains T874R1558 and Q674L1504.
Y594R1300
R1631 134 Rheem part no. 41-20796-29; contains T874R1442 and Q674L1504.
Y594R1300
R1649 134 Ruud part no. 41-20796-33; contains T874R1434 and Q674L1504.
Y594R1300
R1656 134 Obsolete. WeatherKing part no. 41-20796-64; contains T874R1830 and Q674L1504.
Y594R1300
R1664 120 TRADELINE; contains T874R1871 and Q674L1736; direct replacement for York 2TH11702224 (Y594R1011 contains T874R1046/Q674L1272).
Y594R1664
R1672 120 TRADELINE; contains T874R1889, Q674L1736 and C815A1054; direct replacement for York 2TH11702324 (Y594R1151 contains T874R1251/Q674L1272/C815A1039) and 6TH11702224 (Y594R1193 contains T874R1327/Q674L1272).
Y594R1672
R1680 230 TRADELINE; same as Y594R1615 except Premier White® color; contains T874R1897 and Q674L1751; direct replacement for Y594R1326 (T874R1491/Q674L1553).
Y594R1680
R1698 120 Obsolete. TRADELINE; Premier White® color; contains T874R1905, Q674L1777 and C815A1054.
Y594R1672 Replacement is beige.
R1706 120 Obsolete. TRADELINE; same as Y594R1664 except Premier White® color; contains T874R1913 and Q674L1777; direct replacement for Y594R1011 (T874R1046/Q674L1272) York part no. 2TH11702224.
Y594R1664 Replacement is beige.
R1714 228 Obsolete. Lennox part no. 97E79; Canada; Premier White® color; contains T874R1855 and Q674L1728.
Y594R1763 Wiring differences (old=new): Y1=Y, L=F, W1=W, E=W2, C=B.
R1722 115 Obsolete. Econar; contains T874R1921 and Q674L1207.
Y594R1243a
R1748 197 American Standard (Trane) part no. ASYSTAT651A; contains T874R1939 and Q674L1801.
Y594R1763a
R1755 168 Obsolete. Inter-City Products part no. HQ1149376HW; contains T874R1947 and Q674L1819.
Y594R1425a
R1763 197 TRADELINE: contains T874R1954 and Q674L1827; direct replacement for Y594R1136 (T874R1053/Q674L1140), Y594R1748 (T874R1939/Q674L1801) Trane part no. ASYSTAT651A, Y594R1441 (T874R1657/Q674L1611) Trane part no. ASYSTAT651.
Y594R1763
R1771 115 Obsolete. Consolidated Industries part no. 9036100; contains T874R1962 and Q674L1843.
Y594R1680a Includes CHECK LED.
R1789 120 York Canada part no. 2TH11701524; contains T874R1970 and Q674L1850.
Y594R1672a Replacement has °F scaleplate.
Table 10. Y594 Cross Reference.
Model Number
Fig. No. Description
Trade Model Replacementa Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
95 60-2485�8
R1797 125 TRADELINE; contains T874R1988 and Q674L1868; direct replacement for Y594R1235 (T874R1368/Q674L1421) Evcon/Coleman part no. 3600-368).
Y594R1797a
R1805 245 Obsolete. Amana part no. 10636702; contains T874R2002 and Q674L1876.
Y594R1797 Wiring differences (old=new): C/X=X.
R1813 245 Obsolete. Amana part no. 10636704; contains T874R2010 and Q674L1884.
Y594R1797 Wiring differences (old=new): C/X=X, W3=W2.
R1821 125 Obsolete. York logo; part no. 2TH11703424A; contains T874R2028 and Q674L1918.
Y594R1797
R1839 134 Rudd logo; part no. 41-20796-48; contains T874R2036 and Q674L1504.
See OEM for replacement.
R1854 123 Obsolete. Rheem logo; part no. 41-20796-47; contains T874R1996 and Q674L1504.
Y594R1300
Y594WW1014 54 Contains T874W1015, Q674B1216 and
C815A1005.Y594W1014
W1022 140 Obsolete. Rheem part no. 41-20797-19; contains T874W1031, Q674L1546 and C815A1005.
T8611M2025.
W1030 68 Obsolete. Inter-City Products part no. 1072350; contains T874W1072, Q674L1835 and C815A1005 Outdoor Thermistor.
T8611M2025 (programmable)
Includes night setback.
W1055 247 Obsolete. Addison logo; part no. 843-277; contains T874W1106, Q674L1934 and C815A1005.
T8611M2025
Y594YY1004 210 Obsolete. Mammoth part no. 71117301; contains
T874Y1005 and Q674E1353.See OEM for replacement.
Y1012 248 Obsolete. WaterFurnace logo; part no. TA21H03; contains T874Y1013 and Q674F1675.
Table 10. Y594 Cross Reference.
Model Number
Fig. No. Description
Trade Model Replacementa Remarks
a Both the thermostat and subbase must be replaced.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 96
WIRING DIAGRAMS
Fig. 44. Schematic and hookup of T874A,B,C,D,E,F with Q674B. Used in standard applications.
Fig. 45. Schematic and hookup of T874C,D with Q674B. Used in standard applications.
H1
FALL
L1 (HOT)L2
1
RH
W1
W2
O
G
Y2
Y1
RC
HEAT RELAY 2
HEAT RELAY 1
HEAT
OFF
COOL
SYSTEMSWITCH
H1 ANTICIPATOR
C1 ANTICIPATOR
AUTO
ON
FANSWITCH
2
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED.
JUMPER RH, RC FOR SINGLE TRANSFORMER.
2
M2903
B
HEAT CHANGEOVERVALVE
L1 (HOT)
L2
1
COOL CHANGEOVERVALVE
FAN RELAY
COMPRESSORCONTACTOR 2
COMPRESSORCONTACTOR 1
1
4
6
8
9
10
11
H2
FALL
C2 ANTICIPATOR
RISE
RISE
C1
C2
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H2 ANTICIPATOR
NOTE:Model Heating Cool-ingNo. Bulbs BulbsT874A H1 C1T874B H1 C1,C2T874C H1,H2 C1T874D H1,H2 C1,C2T874E C1,C2T874D H1,H2
H1
FALL
L1 (HOT) L2
1
RH
W1
W2
O
G
Y2
Y1
RC
HEAT RELAY 2
HEAT RELAY 1
HEAT
OFF
COOL
SYSTEMSWITCH
H1 ANTICIPATOR
C1 ANTICIPATOR
AUTO
ON
FANSWITCH
2
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED.
JUMPER RH, RC FOR SINGLE TRANSFORMER.
2
M933C
B
HEAT CHANGEOVERVALVE
L1 (HOT)
L2
1
COOL CHANGEOVERVALVE
FAN RELAY
COMPRESSORCONTACTOR 2
COMPRESSORCONTACTOR 1
1
4
6
8
9
10
11
H2
FALL
C2 ANTICIPATOR
RISE
RISE
C1
C2
X1
3 OPTIONAL LED ON SOME MODELS.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
3
H2 ANTICIPATOR
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
97 60-2485�8
Fig. 46. Schematic and hookup of T874A,B,D with Q674B. Used in standard applications.
.
Fig. 47. Schematic and hookup of T874R with Q674B. Used in heat pump applications.
H1
FALL
W1
W2
O
G
Y2
Y1
HEAT RELAY 2
HEAT RELAY 1
HEAT
OFF
COOL
SYSTEMSWITCH
H1 ANTICIPATOR
C1 ANTICIPATOR
AUTO
ON
FANSWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED.
M2904
B
HEAT CHANGEOVER VALVE
COOL CHANGEOVERVALVE
FAN RELAY
COMPRESSORCONTACTOR 2
COMPRESSORCONTACTOR 1
1
4
6
8
9
10
11
H2
FALL
C2 ANTICIPATOR
RISE
RISE
C1
C2
L1 (HOT)L2
1
R
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H2 ANTICIPATOR
L1 (HOT)
L21
COOL
HEAT
FALL
O
G
R
W1
Y
H1/C1 ANTICIPATOR
H2
SYSTEMSWITCH
FAN RELAY
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED. M2906
OFF
COOL CHANGEOVERVALVE
H1
FALL
C1
FANSWITCH
AUTO
ON
THERMOSTAT SUBBASE SYSTEM COMPONENTS
1
2
3
4
5
6
AUX. HT. RELAY
COMPRESSORCONTACTOR
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 98
Fig. 48. Schematic and hookup of T874D with Q674B. Used in standard applications.
H1
FALL
W1
G
W2
B
RH
X1
O
FAN RELAY
HEAT RELAY 1
HEAT
OFF
COOL
SYSTEMSWITCH
H1 ANTICIPATOR
C1 ANTICIPATOR
AUTO
ON
FANSWITCH
2
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED.
CLOGGED FILTER, SERVICE SWITCH. M2905
THERMOSTAT SUBBASE SYSTEM COMPONENTS
RC
HEAT CHANGEOVERVALVE
L1 (HOT)
L2
1
COOL CHANGEOVERVALVE
COMPRESSORCONTACTOR 2
COMPRESSORCONTACTOR 1
1
4
6
8
9
10
11
H2
FALL
C2 ANTICIPATOR
RISE
RISE
C1
C2Y1
Y2
HEAT RELAY 2
EXTERNAL FAN SWITCH
2
L1 (HOT)L2
1
FILTERLED (RED)
H2 ANTICIPATOR
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
99 60-2485�8
Fig. 49. Schematic and hookup of T874C with Q674B. Used in standard applications.
Fig. 50. Schematic and hookup of T874G with Q674B. Used in heat pump applications.
L1 (HOT)L2
1
H1
FALL
H2
FALL
C1
RISE
L1 (HOT)L2
1
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
HEAT RELAY 1
BLOWER RELAY
HEAT RELAY 2
COMPRESSOR CONTACTOR
HSIICONTROL PANEL
LO SPEEDLED (GREEN)
HI SPEEDLED (GREEN
COOL LED(YELLOW)
HEAT LED (RED)
FAN SWITCH
AUTO
ON
SYSTEMSWITCH
HEAT
OFF
COOL
C1 ANTICIPATOR
H2 ANTICIPATOR
H1 ANTICIPATOR
1
4
6
8
9
10
W1
G
R
W2
T
Y1
L
C
HM5945
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1 FALL
H2
FALL
CO
RISE
C1 RISE
L1 (HOT)
L2
1
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
10
9
8
6
4
2
1
FANSWITCH
AUTO
ON
SYSTEMSWITCH
HEAT
OFF
COOL
R
W2
AUX. HT. RELAY
G
FAN RELAY
Y
COMPRESSORCONTRACTOR
O
COOL CHANGEOVERVALVE
M8000
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 100
Fig. 51. Schematic and hookup of T874D with Q674B. Used in standard applications.
Fig. 52. Schematic and hookup of T874C with Q674B. Used in standard applications.
C2
RISE
L1 (HOT)L2
1
L1 (HOT)
L2
1
3
3
C1
RISE
H2
FALL
H1
FALL
M5944
H1 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
C2 ANTICIPATOR
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
FIELD WIRE JUMPER TO ALLOW SINGLE SYSTEM TRANSFORMER.
B, O TERMINALS ON SOME MODELS.
1
2
3
1
3
4
6
8
9
10
11 Y2
Y1
O
RH
B
W2
RC
G
W1
2
SYSTEMSWITCH
HEAT
OFF
COOL
ON
AUTO
FANSWITCH
HEAT RELAY 1
FAN RELAY
HEAT RELAY 2
HEAT CHANGEOVER VALVE
COOL CHANGEOVER VALVE
COMPRESSOR CONTACTOR 1
COMPRESSOR CONTACTOR 2
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1
FALL
H2
FALL
C1 RISE
L1 (HOT)
L21
2
3
1
2
3
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
OPTIONAL FIELD WIRE JUMPER. W3 AND F TO BE JUMPERED EXCEPT FOR TWO STAGE GAS APPLICATION.
FIELD WIRE JUMPER TO ALLOW SINGLE SYSTEM TRANSFORMER.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
SYSTEMSWITCH
HEAT
OFF
COOL
10
9
8
6
5
4
1FAN SWITCH
AUTO
ON
HEAT RELAY 1 FAN RELAY
HEAT RELAY 2
W1
G
RC
W3
W2
F
RH
B
O
Y1
COMPRESSORCONTACTOR
M5999
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
101 60-2485�8
Fig. 53. Schematic and hookup of T874D with Q674B. Used in standard applications.
Fig. 54. Schematic and hookup of T874W with Q674B. Used in standard applications.
H1FALL
W1
W2
G
Y2
Y1
HEAT RELAY 2
HEAT RELAY 1H1 ANTICIPATOR
C1 ANTICIPATOR
AUTO
ON
FAN SWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED. M3202A
L1 (HOT)
L2
1
FAN RELAY
COMPRESSORCONTACTOR 2
COMPRESSORCONTACTOR 1
1
4
6
8
9
10
11
H2
FALL
C2 ANTICIPATOR
RISE
RISE
C1
C2
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H2 ANTICIPATORRSYSTEM
SWITCH
HEAT
OFF
COOL
L1 (HOT)
L2
1
W1
T
W2
HEAT RELAY 3
FAN RELAY
W3
HEAT CHANGEOVER VALVE
COMPRESSOR CONTACTOR 2
B
Y2
Y1
SYSTEMSWITCH
HEAT
OFF
COOL
H1 ANTICIPATOR
C1
H1FALL
H3
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
M3674
AUTO
ON
FAN SWITCH
FALL
R
COMPRESSOR CONTACTOR 1
HEAT RELAY 2
HEAT RELAY 1
G
C815A THERMISTOR
H2 ANTICIPATOR
FALL
H3 ANTICIPATOR
H2
C2 ANTICIPATOR
C2
RISE
RISE
COOL CHANGEOVER VALVE
O
C1 ANTICIPATOR
RESET HEATER
THERMOSTAT SUBBASE SYSTEM COMPONENTS
1
2
3
4
5
6
8
10
11
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 102
Fig. 55. Schematic and hookup of T874A,D,F with Q674D. Used in standard applications.
Fig. 56. Schematic and hookup of T874C with Q674B. Used in standard applications.
M3667A
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
JUMPER RC, RH FOR SINGLE TRANSFORMER.
B AND 5 TERMINALS AVAILABLE ON SOME MODELS.
COMPRESSORCONTACTOR 1
H2 ANTICIPATOR
C1
C1 ANTICIPATOR
C2
H1 ANTICIPATOR
H1
HEAT RELAY 1
HEAT RELAY 2
COMPRESSORCONTACTOR 2
FALLL1(HOT)
L2
RH
W2
Y2
Y1
L1(HOT)
L2
RC
FALLH2
RISE
C2 ANTICIPATOR
RISE
NOFANSWITCH
NOSYSTEMSWITCH
W1
B
1
1
3
2
3
2
1
4
5
6
8
9
10
11
3
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1
FALL
L1 (HOT)L2
1
H2FALL
C1 RISE
FANSWITCH
SYSTEMSWITCH
AUTO
ON
HEAT
OFF
COOL
COMPRESSORCONTACTOR 1
O RELAY
B RELAY
AUX. HT. RELAY
FAN RELAY
RESET
RESET LED (RED)
C1 ANTICIPATOR
H2 ANTICIPATOR
H1 ANTICIPATOR
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
1
4
6
8
9
10
11Y1
Y2
O
B
W2
R
G
X
1
SUBBASE SYSTEM COMPONENTS
M5975
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
103 60-2485�8
Fig. 57. Schematic and hookup of T874P with Q674B. Used in heat pump applications.
Fig. 58. Schematic and hookup of T874G with Q674D. Used in standard applications.
H2
FALL
H1RISECO
L1 (HOT)
L2
1
C1
RISE
2
1
2
POWERSUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
JUMPER HONEYWELL SUPPLIED, FIELD INSTALLED.
C1 ANTICIPATOR
H1 ANTICIPATOR
FAN SWITCH
AUTO
ON
SYSTEM SWITCH
OVERRIDE
HEAT
OFF
COOL
1
2
3
4
5
6
8
9
10 T
W
P
S
L
B
R
G
Y
COMPRESSORCONTACTOR
FAN RELAY
CLOSED-DAYOPEN-NITE
B RELAY
JUMPER
COOL CHANGEOVER VALVE
M8004
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1 ANTICIPATOR
H1FALL
M3722C1
H2 ANTICIPATOR
H2
FALL
ECONOMIZERPACKAGE
RISE
RISE
CO
C1 ANTICIPATOR
CONTROL PANEL
W
RH
B
RC
Y
O
O
W2
O
Y
THERMOSTAT SUBBASE SYSTEM COMPONENTS
2
3
4
6
8
9
10
NO FANSWITCH
NO SYSTEMSWITCH
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 104
Fig. 59. Schematic and hookup of T874A with Q674Q. Used in fan coil applications.
Fig. 60. Schematic and hookup of T874C with Q674N. Used in evaporative cooler applications.
L1 (HOT)L2
1
K2 RELAY
SYSTEMSWITCH
ON
HIGH
H1 ANTICIPATOR
H1FALL
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED. M3729
HEAT
COOL
FAN SWITCH
R
COMPRESSOR CONTACTOR
Y1
B
O
G1
MEDG2
K1 RELAY
W1
C1 ANTICIPATOR
C1RISE
HEAT RELAY 1
OFF
K2
K1
K2
K1
K2
HI LOMED
3 SPEED FAN SCHEMATIC
LO L2 L1
THERMOSTAT SUBBASE SYSTEM COMPONENTS
1
4
8
9
10
L1 (HOT) L2 1
H2 ANTICIPATOR
M2863
H1 ANTICIPATOR
C1 ANTICIPATOR
FALL
H1
R
W2
W1
G
ELEC. HT. RELAY
FAN RELAYCOOL RELAYCONTACT
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
AUTO
ON
FANSWITCH
SYSTEMSWITCH
EVAP
HEAT
OFF
COOL
CHANGEOVERVALVE
COMPRESSORCONTACTOR
EVAPORATORRELAY
RISE
C1
FALL
H2
Y1
B
Y2
THERMOSTAT SUBBASE SYSTEM COMPONENTS
1
4
6
8
9
10
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
105 60-2485�8
Fig. 61. Schematic and hookup of T874C with Q674N. Used in evaporative cooler applications.
Fig. 62. Schematic and hookup of T874F with Q674B. Used in wood/coal applications.
L1 (HOT)
L2
EVAPORATORRELAY
ELEC. HT. RELAY
FAN RELAY
COMPRESSORCONTACTOR
CHANGEOVERRELAY
O
Y2
W2
G
RH2ANTICIPATOR
AUTO
ON
FANSWITCH
H1 ANTICIPATOR
C1
RISE
FALL
H2
FALL
H1
SYSTEMSWITCH
EVAP.
HEAT
COOL
OFF
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
C1ANTICIPATOR
Y1
M2862
1
THERMOSTAT SUBBASE SYSTEM COMPONENTS
1
4
6
8
9
10
L1 (HOT)
L2
1
FAN RELAY
SYSTEMSWITCH
OFF
H2 ANTICIPATOR
H1
H2
FALL
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
M3723A
AUTO
ON
FAN SWITCH
R
COMPRESSOR CONTACTOR
G
W2
H1 ANTICIPATOR
X2
AUX. HT. RELAY
HEAT
X1
EXTERNAL COOLINGTHERMOSTAT (SUCH AS T87 F)
COOL
W1
RY
CWOOD/COALRELAY
FALL
YELLOW
GREEN
THERMOSTAT SUBBASE SYSTEM COMPONENTS
1
4
8
9
10
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 106
Fig. 63. Schematic and hookup of T874F with Q674D. Used in wood/coal applications.
Fig. 64. Schematic and hookup of T874A with Q674Q. Used in fan coil applications.
L1 (HOT)
L2
1
NOSYSTEMSWITCH
H2 ANTICIPATOR
H1
H2FALL
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.M3725
NO FAN SWITCH
R
W2
H1 ANTICIPATOR
AUX. HT. RELAY
W1
C
WOOD/COALRELAY
FALL
YELLOW
GREEN
1
4
8
9
10
THERMOSTAT SUBBASE SYSTEM COMPONENTS
HEAT/COOLSWITCH
H1
FALL
L1 (HOT)L2
1
C1RISE
M8005
2
1
2
H1 ANTICIPATOR
C1 ANTICIPATOR
5
4
2
1 W1
B
R
G1
G2
O
Y1 HIMED
LO
K2
K1
K2 K2
K1
COMPRESSOR CONTACTOR
O RELAY
K2 RELAY
K1 RELAY
B RELAY
HEAT RELAY 1
SYSTEM SWITCH
HEAT
OFF
COOL
FANSWITCH
LO
MED
HIGH
ON
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
SINGLE SETPOINT LEVER AND BIMETAL.
3
L2 L1
THERMOSTAT SUBBASE SYSTEM COMPONENT
3-SPEED FAN SCHEMATIC
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
107 60-2485�8
Fig. 65. Schematic and hookup of T874A with Q674B. Used in standard applications.
Fig. 66. Schematic and hookup of T874A,D,F with Q674D. Used in standard applications.
C1RISE
L1 (HOT)L2
1
L1 (HOT)L2
1
H1
FALL
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED. M5976
C1 ANTICIPATOR
H1 ANTICIPATOR
SYSTEM SWITCH
HEAT
OFF
COOL
FAN SWITCH
AUTO
ON
NO. 1 HEAT RELAY
HEAT DAMPER
COOL DAMPER
FAN RELAY
NO. 1 COMP. RELAY
FILTER LED (RED)
SERVICE LED (YELLOW)
X2
X1
Y1
Y2
G
RC
RH
B
W2
W11
4
6
8
9
10
11
O
THERMOSTAT SUBBASE SYSTEM COMPONENTS
W2
W1
M7011
THERMOSTAT SUBBASE SYSTEM COMPONENTS
Y2
RH
RC
Y1
H1 ANTICIPATOR
H2 ANTICIPATOR
H1 FALL
FALLH2
1
4
5
6
8
9
10
11
NO FANSWITCH
NO SYSTEMSWITCH
L1 (HOT)L2
1
L1 (HOT)L2
1
HEAT RELAY 1
HEAT RELAY 2
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 108
Fig. 67. Schematic and hookup of T874R with Q674B. Used in heat pump applications.
Fig. 68. Schematic and hookup of T874P with Q674B. Used in heat pump applications.
M5998
H2
FALL
H1
FALL
C1L1 (HOT)
L21
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1/C1 ANTICIPATOR
FAN SWITCH
AUTO
ON
SYSTEMSWITCH
HEAT
OFF
COOL COMPRESSORCONTACTOR
AUX. HT. RELAY
HEAT CHANGEOVERVALVE
FAN RELAY
6
5
4
3
2
1 X
G
R
B
W2
Y
H2
FALL
H1
RISECO
L1 (HOT)
L2
1
C1
RISE
COMPRESSOR CONTACTOR
FAN RELAY
CLOSED-DAYOPEN-NITE
B RELAY
SERVICELED (RED)
OVERRIDELED (RED)
FAN SWITCH
AUTO
ON
H1 ANTICIPATOR
SYSTEM SWITCH
JUMPER
COOL CHANGEOVER VALVE
OVERRIDE
HEAT
OFFC1 ANTICIPATOR
1
2
3
4
5
6
8
9
10
W
P
S
X
L
B
R
C
G
Y
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
JUMPER HONEYWELL SUPPLIED, FIELD INSTALLED.
H2 MAKE OFFEST 8˚ F BELOW H1 MAKE.
3
2
1
2
3 M101A
THERMOSTAT SUBBASE SYSTEM COMPONENTS
T
COOL
COMPRESSORFAULT
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
109 60-2485�8
Fig. 69. Schematic and hookup of T874V with Q674R. Used in fan coil applications.
Fig. 70. Schematic and hookup of T874C with Q674S. Used in heat pump applications.
C1
RISE L1 (HOT)L2
1
M107A
FAN SWITCHLO
AUTOHI
CONT.
SYSTEM SWITCH
OFF
COOL
C1 ANTICIPATOR
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
COOL RELAY
FAN RELAY
Z RELAY
8
9
10
Y
R
G
Z
1
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1 FALL
L1 (HOT)
L2
1
H2FALL
H1
FALL
1
4
6
8
9
S
W2
R
Y
NO FANSWITCH
SYSTEMSWITCH
HEAT
COOL
THERMOSTAT SUBBASE SYSTEM COMPONENTS
SERVICELED (RED)
AUX. HT. RELAY
COMPRESSOR CONTACTOR M1402A
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
1
COMPRESSORFAULT
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 110
Fig. 71. Schematic and hookup of T874A-D with Q674A. Used in standard applications.
Fig. 72. Schematic and hookup of T874D,E,F with Q674C. Used in standard applications.
H1FALL
L1 (HOT) L2
1
RH
W1
W2
G
Y2
Y1
RC
HEAT RELAY 2
HEAT RELAY 1
HEAT
AUTO
COOL
SYSTEMSWITCH
H1 ANTICIPATOR
C1 ANTICIPATOR
AUTO
ON
FAN SWITCH
2
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED.
JUMPER RH, RC FOR SINGLE TRANSFORMER.
2
M932B
L1 (HOT)
L2
1
FAN RELAY
COMPRESSORCONTACTOR 2
COMPRESSORCONTACTOR 1
1
4
6
8
9
10
11
H2
FALL
C2 ANTICIPATOR
RISE
RISE
C1
C2
X1
3 OPTIONAL LED ON SOME MODELS.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
3
H2 ANTICIPATOR
CHECK
L1 (HOT)L2
1
H2 ANTICIPATOR
H1 ANTICIPATOR
C1 ANTICIPATOR
C2 ANTICIPATOR
FALLH1 W2
W1
B
G
RH
1
2
3
3
2
2POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
JUMPER TERMINALS RC-RH FOR SINGLE SYSTEM TRANSFORMER ONLY.
B,O TERMINALS ON SOME MODELS.
AUTO
ON
FANSWITCH
SYSTEMSWITCH
AUTO
OFFRISE
C2
C1
FALL
RISE
H2O
Y2
Y1
RC
HEAT DAMPER
COOL DAMPER
FAN RELAY
COMPRESSORCONTACTOR 2
COMPRESSORCONTACTOR 1
L1 (HOT)
L21
HEAT RELAY 1
HEAT RELAY 2
M5122A
THERMOSTAT SUBBASE SYSTEM COMPONENTS
1
4
6
8
9
10
11
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
111 60-2485�8
Fig. 73. Schematic and hookup of T874G with Q674C. Used in heat pump applications.
Fig. 74. Schematic and hookup of T874H with Q674C. Used in heat pump applications.
H1
FALL
G
Y1
R
FAN RELAY
REVERSINGVALVE RELAY
OFF
AUTO
SYSTEMSWITCH
H ANTICIPATOR
C ANTICIPATOR
AUTO
ON
FAN SWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED. M7008
THERMOSTAT SUBBASE SYSTEM COMPONENTS
Y2
OPEN-NIGHTCLOSED-DAY
3
4
6
8
10
SETBACK
FALL
RISE
COL1 (HOT)
L2
1
2
L
COMPRESSORCONTACTOR
SETBACKRELAY
9
RISEC1
L1 (HOT)
L21
FAN RELAY
Y2SYSTEMSWITCH
OFF
AUTO
H1 ANTICIPATOR
CO
H1
FALL
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
SERVICE LED ON SELECT MODELS. M3680A
AUTO
ON
FAN SWITCH
R
COMPRESSOR CONTACTOR
COOL CHANGEOVERVALVE
G
C1
RISE
RISE
O
C1ANTICIPATOR
B
Y1
THERMOSTAT SUBBASE SYSTEM COMPONENTS
2
3
4
8
9
10
SERVICE LED (YELLOW)
X
C2
2
COMPRESSOR FAULT
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 112
Fig. 75. Schematic and hookup of T874A with Q674C. Used in standard applications.
Fig. 76. Schematic and hookup of T874A-D with Q674C. Used in standard applications.
C1
RISE
L1 (HOT)L2
1
3
H1 FALL
2
THERMOSTAT SUBBASE SYSTEM COMPONENTS
SYSTEM SWITCHOFF
AUTO
FAN SWITCH
AUTO
ON
HEAT RELAYFILTER LED(YELLOW)
SERVICELED (RED)
FAN RELAY
W1
X
A
G
R
O
O
Y
T
T12
11
10
9
8
4
1H1ANTICIPATOR
THERMISTOR
C1ANTICIPATOR
EXTERNALTEMP.READOUT
COMPRESSOR CONTACTOR
MOMENTARYCIRCUIT
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
MOMENTARY POSITION. SPRING RETURN TO "ON" UPON SWITCH RELEASE.
FILTER LED ON SELECT MODELS.
1
2
3 M5731
Y1
RC
1
M7025
THERMOSTAT SUBBASE SYSTEM COMPONENTS
B
Y2
W2
RH
X
H1 ANTICIPATOR
H2 ANTICIPATOR
C1
RISE
H1FALL
FALL
H2
C2
RISE
C2 ANTICIPATOR
C1 ANTICIPATOR
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED.
FOR T874C, DELETE C2.
O
A
1
6
9
10
11
4
8
AUTO
ON
FANSWITCH
SYSTEMSWITCH
OFF
HEAT CHANGEOVER VALVE
HEAT RELAY 1
COMPRESSORCONTACTOR 1
HEAT RELAY 2
L1 (HOT)
L21
COMPRESSORCONTACTOR 2
AUTO
FILTERLED (YEL)
SERVICELED (RED)
W1
G
L1 (HOT)
1L2COOL CHANGEOVER VALVE
FAN RELAY
FILTER LED ON SELECT MODELS.2 3
3
2
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
113 60-2485�8
Fig. 77. Schematic and hookup of T874K with Q674C. Used in heat pump applications.
Fig. 78. Schematic and hookup of T874P with Q674C. Used in heat pump applications.
C1RISE
H1
H2
CO
FALL
FALL
FALL
L1 (HOT)L2 1
1
2
L1 (HOT)L2 12
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
JUMPER RH AND RC FOR SINGLE TRANSFORMER SYSTEM.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1 ANTICIPATOR
C1 ANTICIPATOR
SYSTEMSWITCH
FANSWITCH
AUTO
ON
OFF
AUTO
FAN RELAY
HEAT CHANGEOVERVALVE
COMPRESSORCONTACTOR
M4729
1
3
4
6
8
9
10
Y1
O
RC
B
W3
W2
W1
RH
G
X1RESET LED (RED)
"O" RELAY
"B" RELAY
HEAT RELAY 1
HEAT RELAY 2
B
1
THERMOSTAT SUBBASE SYSTEM COMPONENTS
C
G
R
H1ANTICIPATOR
C1
RISE
H2FALL
C1 ANTICIPATOR
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED.
JUMPER HONEYWELL SUPPLIED, FIELD INSTALLED.
W
1
4
9
10
3
8
AUTO
ON
FANSWITCH
SYSTEMSWITCH
OFF
COMPRESSORCONTACTOR
AUTO
Y
L1 (HOT)
1L2
2
FAN RELAY
SETBACKCONTACT
M7026
HEATCHANGEOVER VALVE
L
S
P
2
REVERSINGVALVE
JUMPER
2
H1
RISE
CO
5
6
OVERRIDE
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 114
Fig. 79. Schematic and hookup of T874G,H with Q674C. Used in standard applications.
Fig. 80. Schematic and hookup of T874D with Q674E. Used in standard applications.
O
1
THERMOSTAT SUBBASE SYSTEM COMPONENTS
R1
G
R2
H1 ANTICIPATOR
CO
RISE
H1FALL
FALLH2
C1
C1 ANTICIPATOR
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED.
SETBACK CONTACT ON Q674C1124.
Y
1
6
9
10
4
8
AUTO
ON
FANSWITCH
SYSTEMSWITCH
OFF COMPRESSORCONTACTOR
AUTO
X
L1 (HOT)
1L2
COOL CHANGEOVER VALVE
2 3
RESET
FAN RELAY
SETBACKCONTACT
RISE
RESETLED (RED)
H2 ON T874G. M7027
3
2
H1
FALL
FALL
L1 (HOT)L2
1
2
2
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
OPTIONAL FIELDWIRE JUMPER TO ALLOW SINGLE SYSTEM TRANSFORMER.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
M5997
HEAT RELAY 1
CONTACTORCOMPRESSOR 1
FAN RELAY
HEAT RELAY 2
COMPRESSORFAULT COMPRESSOR
CONTACTOR 2
SERVICE LED (RED)
SYSTEMSWITCH
OFF
HEAT
AUTO
COOL
C2 ANTICIPATOR
C1 ANTICIPATOR
C2
RISE
RISE
C1
H2 ANTICIPATOR
H1 ANTICIPATOR
H2
4
6
8
10
11 Y2
Z
C
W2
RC
G
Y1
W1
FAN SWITCHAUTO
ON
1
RH
9
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
115 60-2485�8
Fig. 81. Schematic and hookup of T874C with Q674C. Used in heat pump applications.
Fig. 82. Schematic and hookup of T874A,C,D with Q674E. Used in standard applications.
H1
FALL
L1 (HOT)
L2
1
H2 ANTICIPATOR
OFF
AUTO
FANSWITCH
CHANGEOVERRELAY
M5981POWER SUPPLY. PROVIDE DISCONECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
1
SYSTEM COMPONENTSSUBBASETHERMOSTAT
1
4
6
8
9
10
W1
B
H2
FALL
C1RISE
G
R
W2
Y1
C1 ANTICIPATOR
AUTO
ON
FANRELAY
COMPRESSORCONTACTOR
SYSTEMSWITCH
H1FALL
H2
FALL
C1
RISE
C2
RISE
L1 (HOT)L2
L1 (HOT)
L21
1
1
2
3
POWER SUPPLY. PROVIDE DISCONNECTMEANS AND OVERLOAD PROTECTION AS REQUIRED.
JUMPER RC, RH FOR SINGLE TRANSFORMER.
O AND B TERMINALS ON SELECTED MODELS.
2
3
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1 ANTICIPATOR
H2 ANTICIPATOR
C2 ANTICIPATOR
C1 ANTICIPATOR
SYSTEMSWITCH
FANSWITCH
AUTO
ON
OFF
HEAT
AUTO
COOL
HEAT RELAY 2
HEAT RELAY 1
COMPRESSORCONTACTOR 1
COMPRESSORCONTACTOR 2
FAN RELAY
1
4
6
8
9
10
11
RC
Y1
Y2
G
B
O
W2
W1
RH
M934
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 116
Fig. 83. Schematic and hookup of T874G with Q674C. Used in standard applications.
Fig. 84. Schematic and hookup of T874G with Q674E. Used in heat pump applications.
H1
FANSWITCH
ON
AUTO
CHECK LED(RED)
M5982
POWER SUPPLY. PROVIDE DISCONECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
1
4
6
8
9
10
11
H2 ANTICIPATOR
FALL
H2
RISE
C1
C1 ANTICIPATOR
RISE
C2
FALL
H1 ANTICIPATOR
1
RH
SYSTEM COMPONENTSSUBBASETHERMOSTAT
L1 (HOT)
L2
1
L1 (HOT)
L2 1
COMPRESSORCONTACTOR 1
C2 ANTICIPATOR
AUTO
COOL
HEAT
OFF
X1
RC
W2
G
Y1
W1
HEAT RELAY 1
FAN RELAY
HEAT RELAY 2
COMPRESSORCONTACTOR 2
Y2
H1FALL
H2FALL
CO
RISE
C1RISE
L1 (HOT)
L21
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
SYSTEMSWITCH
1
2
4
6
8
9
10Y
V
F
M
R
FANSWITCH
AUTO
ON
OFF
HEAT
AUTO
COOL
AUX. HT.RELAY
DEFROSTRELAY
DEFROSTRELAY
FAN RELAY
HIGH PRESSURESWITCH
DEFROSTSWITCH
COOL CHANGEOVERVALVE OUTDOOR
FAN RELAY
COMPRESSORCONTACTOR
DEFROSTRELAY
M4666
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
117 60-2485�8
Fig. 85. Schematic and hookup of T874A-D with Q674E. Used in standard applications.
Fig. 86. Schematic and hookup of T874G with Q674E. Used in heat pump applications.
H1
FALL
4
H1 ANTICIPATOR
W2
HEAT RELAY 2
L1 (HOT)
L2 1
COMPRESSORCONTACTOR 1
M5983POWER SUPPLY. PROVIDE DISCONECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.1
SYSTEM COMPONENTSSUBBASETHERMOSTAT
FAN RELAY
H2
RISEC1
RISE
C2
OFF
SYSTEMSWITCH
FANSWITCH
HEAT
AUTO
COOL
ON
AUTO
R
Y1
W1
Y2
FALL
6
8
10
9
11
1
H2 ANTICIPATOR
C1 ANTICIPATOR
C2 ANTICIPATOR
HEAT RELAY 1
G
COMPRESSORCONTACTOR 2
H1
FALL
H2 FALL
CO
RISE
C1 RISE
L1 (HOT)L2
1
L1 (HOT)
L2
1
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
SYSTEMSWITCH
FANSWITCH
AUTO
ON
OFF
HEAT
AUTO
COOL
AUX. HT. RELAYDEFROST RELAYCONTACT
COOL CHANGEOVERVALVE
COMPRESSORCONTACTOR
DEFROSTRELAY
M4667
1
2
3
5
6
8
9
10
VR
Y
V
F
M
R
HIGHPRESSURESWITCH
DEFROST RELAYCONTACT
FAN RELAY
DEFROSTSWITCH
D. F. O.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 118
Fig. 87. Schematic and hookup of T874D with Q674E. Used in standard applications.
Fig. 88. Schematic and hookup of T874B,D with Q674E. Used in standard applications.
C2
RISE
C1
RISE
H2
FALL
H1 FALL
L1 (HOT)L2
1
L1 (HOT)
L21
2
1
2
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
FIELDWIRE JUMPER TO ALLOW SINGLE SYSTEM TRANSFORMER.
H1 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
C2 ANTICIPATOR
SYSTEMSWITCH
FANSWITCH
AUTO
ON
OFF
HEAT
AUTO
COOL
COMPRESSORCONTACTOR 1
COMPRESSORCONTACTOR 2
M4668
1
SYSTEM FAULT CONTACT
FAN RELAY
HEAT RELAY 1
HEAT RELAY 2
LOCKOUT LED(RED)
THERMOSTAT SUBBASE SYSTEM COMPONENTS
W1
Y1
RC
W2
B
G
RH
C
X
Y211
10
9
8
6
4
C2
RISE
C1
RISE
H2
FALL
H1 FALL
L1 (HOT)
L2
1
L1 (HOT)
L21
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
H1 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
C2 ANTICIPATOR
SYSTEMSWITCH
FANSWITCH
AUTO
ON
OFF
HEAT
AUTO
COOL
COMPRESSORCONTACTOR 1
COMPRESSORCONTACTOR 2
M4669
1
FAN RELAY
HEAT RELAY 1
HEAT RELAY 2
HIGH LED (RED)
LOW LED (GREEN)
THERMOSTAT SUBBASE SYSTEM COMPONENTS
W1
Y1
RC
W2
G
RH
X
Y211
10
9
8
6
4
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
119 60-2485�8
Fig. 89. Schematic and hookup of T874D with Q674E. Used in standard applications.
Fig. 90. Schematic and hookup of T874D with Q674G. Used in standard applications.
Y1
W1
RC
1 M7023
THERMOSTAT SUBBASE SYSTEM COMPONENTS
B
Y2
G
W2
RH
X
H1 ANTICIPATOR
H2 ANTICIPATOR
C1
RISE
H1FALL
FALLH2
C2 RISEC2 ANTICIPATOR
C1 ANTICIPATOR
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED.
O
A
1
6
9
10
11
4
8
AUTO
ON
FANSWITCH
SYSTEMSWITCH
HEAT
OFF
COOL
HEAT CHANGEOVER VALVE
HEAT RELAY 1
COMPRESSORCONTACTOR 1
FAN RELAY
HEAT RELAY 2
L1 (HOT)
L2 1
L1 (HOT)
L21
COOL CHANGEOVERVALVE
COMPRESSORCONTACTOR 2
AUTO
FILTERLED (YEL)
SERVICELED (RED)
W1
A2
A1
OFF
AUTO
SYSTEMSWITCH
1 M7022
THERMOSTAT SUBBASE SYSTEM COMPONENTS
X2
L1 (HOT)
L21
B
X1
W2
T
RC
H1 ANTICIPATOR
H2 ANTICIPATOR
C1RISE
H1FALL
FALLH2
C2 RISEC2 ANTICIPATOR
C1 ANTICIPATOR
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED.
NO FANSWITCH
RH
O
1
6
9
10
11
4
7
Y2
Y1
HEAT RELAY 1
HEAT RELAY 2T RELAY
HEAT CHANGEOVERVALVE
COMPRESSORCONTACTOR 2
COMPRESSORCONTACTOR 1
L1 (HOT)
L21
5
8
12
FILTER LED (YEL)
SERVICELED (RED)
FILTERLED (YEL)
SERVICELED (RED)
COOLCHANGEOVERVALVE
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 120
Fig. 91. Schematic and hookup of T874A-F,Q with Q674G. Used in standard applications.
Fig. 92. Schematic and hookup of T874C with Q674G. Used in heat pump applications.
H1FALL
L1 (HOT) L2
1
RH
W1
W2
O
Y2
Y1
RC
HEAT RELAY 2
HEAT RELAY 1
OFF
AUTO
SYSTEMSWITCH
H1 ANTICIPATOR
C1 ANTICIPATOR
NO FAN SWITCH
2
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED.
JUMPER RH, RC FOR SINGLE TRANSFORMER.
2
M3201B
L1 (HOT)
L2
1
COOL DAMPER
HEAT DAMPER
COMPRESSORCONTACTOR 2
COMPRESSORCONTACTOR 1
1
4
6
8
9
10
11
H2
FALL
C2 ANTICIPATOR
RISE
RISE
C1
C2
B
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H2 ANTICIPATOR
L2
1OFF
H1 ANTICIPATOR
H2 ANTICIPATOR
H1
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED. M6008A
Y1
W1
C1 ANTICIPATOR
AUTO
FALL
FALL
CHANGEOVERRELAY
L1 (HOT)
R
FAN RELAY
COMPRESSORCONTACTOR
G
3
THERMOSTAT SUBBASE SYSTEM COMPONENTS
NO FAN SWITCH
SYSTEM SWITCH
RISE
H2
W2
B
1
4
6
8
9
10
C1
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
121 60-2485�8
Fig. 93. Schematic and hookup of T874D with Q674K. Used in standard applications.
Fig. 94. Schematic and hookup of T874D with Q674G. Used in standard applications.
H1FALL
H2 FALL
C1RISE
C2
RISE
L1 (HOT)
L2
L1 (HOT)
L2 1
1
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
NO FANSWITCH
SYSTEMSWITCH
11
10
9
8
6
4
1
OFF
HEAT
AUTO
COOL
C2 ANTICIPATOR
C1 ANTICIPATOR
H2ANTICIPATOR
H1 ANTICIPATOR
HEAT FAN RELAY
HEAT RELAY
COMPRESSORCONTACTOR 1
COMPRESSORCONTACTOR 2
W1
W2
RH
Y1
RC
Y2
M4664
W2
W1
RC
HEAT CHANGEOVERVALVE
OFF
AUTO
SYSTEMSWITCH
1 M7013
THERMOSTAT SUBBASE SYSTEM COMPONENTS
B
L1 (HOT)
L2 1
Y2
HEAT RELAY 2
RH
X
A
Y1
COMPRESSORCONTACTOR 1
COMPRESSORCONTACTOR 2
L1 (HOT)
L2 1
H1 ANTICIPATOR
H2 ANTICIPATOR
C1
RISE
H1FALL
FALLH2
C2 RISEC2 ANTICIPATOR
C1 ANTICIPATOR
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED.
NO FANSWITCH
HEAT RELAY 1
O
T
COOL CHANGEOVERVALVE
"T" RELAY
1
6
9
10
11
FILTERLED (YELLOW)
SERVICELED (RED)
4
8
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 122
Fig. 95. Schematic and hookup of T874F with Q674K. Used in wood/oil applications.
Fig. 96. Schematic and hookup of T874C with Q674C. Used in standard applications.
H1
FALL
1
OFF
WOOD
SYSTEMSWITCH
H1 ANTICIPATOR
WOOD/OIL
OIL
OIL LED(RED)
W2
M5984POWER SUPPLY. PROVIDE DISCONECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.1
SYSTEM COMPONENTSSUBBASETHERMOSTATS
2
3
4
5
6
H2
FALL
NO FANSWITCH
OIL RELAY
WOOD RELAY
L1 (HOT)
L21
X
W1
R
WOOD LED(GREEN)H2 ANTICIPATOR
H2
FALL
L1 (HOT)
L2
1
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
L1 (HOT)
L2
1
C1
RISE
H1FALL
FAN SWITCH
AUTO
ON
SYSTEM SWITCH
OFF
AUTO
C1 ANTICIPATOR
H2 ANTICIPATOR
NO. 1 HEAT RELAY
NO. 2 HEAT RELAY
HEAT DAMPER
COOL DAMPERFAN RELAY
NO. 1 COMPRESSORCONTACTOR
ON LED(YELLOW)
SERVICE LED (RED)
C
A
X
Y1
Y2
G
O
RC
RH
B
W2
W11
4
6
8
9
10
11
M104A
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
123 60-2485�8
Fig. 97. Schematic and hookup of T874P with Q674C. Used in heat pump applications.
Fig. 98. Schematic and hookup of T874D with Q674E. Used in standard applications.
H2
FALL
H1
RISE
CO
L1 (HOT)
L2
1
C1
RISE
COMPRESSOR CONTACTOR
FAN RELAY
CLOSED-DAYOPEN-NITE
B RELAY
SERVICELED (RED)
OVERRIDELED (RED)
FAN SWITCH
AUTO
ON
H1 ANTICIPATOR
SYSTEM SWITCH
JUMPER
COOL CHANGEOVER VALVE
OVERRIDE
AUTO
OFF
C1 ANTICIPATOR
1
2
3
4
5
6
8
9
10
W
P
S
X
L
B
R
C
G
Y
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
JUMPER HONEYWELL SUPPLIED, FIELD INSTALLED.
H2 MAKE OFFEST 8˚ F BELOW H1 MAKE.
3
2
1
2
3 M100A
THERMOSTAT SUBBASE SYSTEM COMPONENTS
COMPRESSURE FAILURE
Y1
RC
1M5106A
THERMOSTAT SUBBASE SYSTEM COMPONENTS
B
Y2
W2
RH
H1 ANTICIPATOR
H2 ANTICIPATOR
C1
RISE
H1FALL
FALL
H2
C2
RISE
C2 ANTICIPATOR
C1 ANTICIPATOR
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
T874A IS SINGLE-STAGE (NO W2 OR Y2).
O
A
AUTO
ON
FANSWITCH
SYSTEMSWITCH
OFF
CHANGEOVER RELAY
HEAT RELAY 1
COMPRESSORCONTACTOR 1
HEAT RELAY 2
L1 (HOT)
L21
COMPRESSORCONTACTOR 2
AUTO
HEAT
SERVICELED (RED)
W1
G
L1 (HOT)
1L2CHANGEOVER RELAY
FAN RELAY
2
SYSTEM MONITOR
COOL
1
6
9
10
11
4
8
2
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 124
Fig. 99. Schematic and hookup of T874C with Q674C. Used in standard applications.
L2
1
ON
H1 ANTICIPATOR
H2 ANTICIPATOR
H1
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
MOMENTARY POSITION. SPRING RETURN TO "ON" UPON SWITCH RELEASE.
H1 AND C1 ARE DPST SWITCHES.
M531
Y1
W1
C1 ANTICIPATOR
AUTO
FALL
FALL
HEAT RELAY 1
HEAT RELAY 2
COMPRESSOR RELAY
L1 (HOT)
RFAN RELAY
O
AUTO
OFF
SERVICELED (RED)
A
G
2
2
3
4
5
5
3
3
4
MOMENTARYCIRCUIT
T
T EXTERNALTEMP.READOUT
THERMOSTAT SUBBASE SYSTEM COMPONENTS
FAN SWITCH
SYSTEMSWITCH
RISE
H2
THERMISTER
W2
W3
Y2
1
2
4
5
6
7
8
9
10
C1
11
12
H3 OFFSET 12°F FROM H2 FOR NIGHT SETBACK.
THERMISTOR INTERNAL TO THERMOSTAT.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
125 60-2485�8
Fig. 100. Schematic and hookup of T874W with Q674C. Used in standard applications.
Fig. 101. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
L2
1
ON
H1 ANTICIPATOR
H2 ANTICIPATOR
H1
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
MOMENTARY POSITION. SPRING RETURN TO "ON" UPON SWITCH RELEASE.
H1 AND C1 ARE DPST SWITCHES.
M532
Y1
W1
C2 ANTICIPATOR
C2 ANTICIPATOR
AUTO
FALL
FALL
FALL
HEAT RELAY 1
HEAT RELAY 2
HEAT RELAY 3
COMPRESSOR RELAY
L1 (HOT)
RFAN RELAY
O
AUTO
OFF
SERVICELED (RED)
A
G
2
2
3
4
5
5
3
3
4
MOMENTARYCIRCUIT
T
T EXTERNALTEMP.READOUT
THERMOSTAT SUBBASE SYSTEM COMPONENTS
FAN SWITCH
SYSTEMSWITCH
H3
RISE
RISE
H2
THERMISTER
COMPRESSORCONTACTOR 2
W2
W3
Y2
1
2
4
5
6
7
8
9
10
C1
C2
11
12
H3 OFFSET 12°F FROM H2 FOR NIGHT SETBACK.
THERMISTOR INTERNAL TO THERMOSTAT.
L1 (HOT)
L2
1
COOL CHANGEOVERVALVE
W
SYSTEMSWITCH
OFF
HEAT
H1/C1 ANTICIPATORH1
FALL
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
M3718A
AUTO
ON
FAN SWITCH R
COMPRESSOR CONTACTOR
GC1
B
Y
EM. HT.LED (RED)
AUX. HT. RELAYX
EM. HT.H2 ANTICIPATOR
H2
FALL
COOL
O
FAN RELAY
2
3
4
5
6
THERMOSTAT SUBBASE SYSTEM COMPONENTS
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 126
Fig. 102. Schematic and hookup of T874J,R with Q674L. Used in heat pump applications.
H2FALL
H1
FALL
C1
L1 (HOT)
L2 1 L1 (HOT)
L2 1
2
POWER SUPPLY. PROVIDE DISCONNECTMEANS AND OVERLOAD PROTECTION AS REQUIRED.
FIELD WIRE JUMPER TO ALLOW SINGLE SYSTEM TRANSFORMER.
1
2
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1/C1 ANTICIPATOR
H2 ANTICIPATOR
SYSTEMSWITCH
FANSWITCH
AUTO
ON
OFF
HEAT
EM. HT.
COOL
INTERNAL THERMOSTAT
OVERLOADSWITCH
SUPPL. ELEC.HT. RELAY
COOL CHANGEOVERVALVE
COMPRESSORCONTACTOR
M4726
EM. HT.LED (RED)
EM. HT. RELAY
TIME DELAYFAN RELAY
OUTDOOR THERMOSTAT
EM. HT.RELAY CONTACT
FAN RELAY
HIGH PRESSURESWITCH
R
VR
X
E
Y
V
F
M1
2
3
4
5
6
7
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
127 60-2485�8
Fig. 103. Schematic and hookup of T874G with Q674L. Used in heat pump applications.
Fig. 104. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
H2 ANTICIPATOR
1
SUPL. HT.LED (RED)
M4665 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
1
SYSTEM COMPONENTSSUBBASETHERMOSTAT
L1 (HOT)
L2
1
H1 FALL
H2FALL
2
4
6
O
G
R
W2
E
L
C
Y
CORISE
C1 RISE
8
9
10
H1 ANTICIPATOR
C1 ANTICIPATOR
SYSTEMSWITCH
SUPL. HT.
COOL
OFF
FANSWITCH
AUTO
ONFAN RELAY
COOL CHANGEOVER VALVE
OUTDOORTHERMOSTAT
HEAT RELAY 1
HEAT RELAYCONTACT 1
HEAT RELAY 2
HEAT RELAYCONTACT 2
HEAT RELAY 32
COMPRESSORCONTACTOR 1
N.O. SWITCH – INSTALLER ADDED, TO LIGHT SUPL. HT. LEDWHEN COMPRESSOR OPERATION IS NOT NORMAL.
2
COMPRESSORFAULTHEAT
1
1
2
L1 (HOT)
L2
2
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
OPTIONAL FIELD WIRE JUMPER TO CYCLE AUXILIARY HEAT RELAY H1 INSTEAD OF H2 (FASTER RESPONSE).
THERMOSTAT SUBBASE SYSTEM COMPONENTS
M4728
FANSWITCH
AUTO
ON
EM. HT. LED(RED)
O
G
Y
H
W2
B
X
E2
3
4
H2FALL
H2 ANTICIPATOR5
6
COM
EH
R8233B
Y R
G
W
O
R
SYSTEMSWITCH
OFF
HEAT
EM. HT.
COOL
H1
FALL
C1
EM. HT. RELAY
AUX. HT. RELAY
"B" RELAY
COMPRESSORCONTACTOR
ELEC. HT. RELAY
H1/C1 ANTICIPATOR
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 128
Fig. 105. Schematic and hookup of T874C with Q674L. Used in heat pump applications.
Fig. 106. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
OFF
COOL
IHRI
RHI
FAN SWITCH
ON
SYSTEMSWITCH
SYSTEMMONITORSWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
M8384
EM. HT. RELAY
1
EM. HT. LED(RED)
W2
2
EM. HT.
HEAT
FAN RELAY
HEAT RELAY 2
HEAT RELAY 1
W1
AUTO
C
Y
H1 FALL
H2 ANTICIPATOR
H1 ANTICIPATOR
C1 ANTICIPATOR
H2
FALL
C1
RISE
COMPRESSORCONTRACTOR
8
10
L1 (HOT)
L2
1
G
K
L
R
THERMOSTAT SUBBASE SYSTEM COMPONENTS
4
6
H2
FALL
H1
FALL
C1
L1 (HOT)L2 1
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1/C1 ANTICIPATOR
H2 ANTICIPATOR
SYSTEMSWITCH
FAN SWITCH
AUTO
ON
OFF
HEAT
EM. HT.
COOL
AUX. HT. RELAY
EM. HT. RELAY
COOL CHANGEOVERVALVE
COMPRESSORCONTACTOR
FAN RELAY
M4724
2
3
4
5
6
E
Y
X
W2
R
G
O
EM. HT.LED (RED)
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
129 60-2485�8
Fig. 107. Schematic and hookup of T874D with Q674L. Used in heat pump applications.
Fig. 108. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
C2 RISE
C1
RISE
H2FALL
H1
FALL
L1 (HOT)
L2
1
1
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1 ANTICIPATOR
C2 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
SYSTEMSWITCH
FANSWITCH
AUTO
ON
OFF
HEAT
EM. HT.
COOL
M4727
Y
R
C
L
E
Y1
G
O
11
10
8
5
4
3
2
EM. HT.LED (RED)
COMPRESSORCONTACTOR 1
COMP. FAILURE
EM. HT.RELAY CONTACT
EM. HT. RELAY
COMPRESSORCONTACTOR 2
OUTDOORTHERMSTAT
SUPPL. HT. RELAY
FAN RELAY
COOL CHANGEOVER VALVE
H2
FALL
H1
FALL
C1
L1 (HOT)L2
1
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1/C1 ANTICIPATOR
H2 ANTICIPATOR
FANSWITCH
AUTO
ON
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
AUX. HT. RELAY
FAN RELAY
COOL CHANGEOVERVALVE
COMPRESSORCONTACTOR
M4725
2
3
4
5
6
R
G
W
B
X
O
Y
AUX. HT.LED (YELLOW)
EM. HT.LED (RED)
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 130
Fig. 109. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
H2FALL
L1 (HOT)L2
1
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1
FALLC1
H1/ C1ANTICIPATOR
SYSTEMSWITCH
FANSWITCH
AUTO
ON
OFF
HEAT
EM. HT.
COOL
AUX. HT. RELAY
FAN RELAY
AUX. HT.LED (GREEN)
COOL CHANGEOVERVALVE
COMPRESSORFAILURE
EM. HT.LED (RED)
OUTDOORTHERMOSTAT
OUTDOORTHERMISTOR
COMPRESSORCONTACTOR
Y
O
X2
T
R
F
B
W
G
1
2
3
4
5
6
RESETHEATER
M5071
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
131 60-2485�8
Fig. 110. Schematic and hookup of T87C,R with Q674L. Used in heat pump applications.
L1 (HOT)L2
1
F
EM. HT.LED (YELLOW)
R
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
H1 ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
M2854
VR
H1
FALL
E
AUTO
ON
FAN SWITCH
A
L
M
OUTDOORTHERMOSTAT
SUPL. ELEC.HT. RELAY
X
COMPRESSORCONTACTOR
OVERLOADSWITCH
INTERNALTHERMOSTAT
HI PRESSURESWITCHFAN
RELAY
EM. HT. RELAY CONTACT
TIME DELAYFAN RELAY
ELEC. HT. RELAY
H2
FALL
H2 ANTICIPATOR
C1RISE
C1ANTICIPATOR
REMOVE FACTORY INSTALLED V-VR JUMPER WHEN CONNECTING A TWO TRANSFORMER SYSTEM.
2
2
SERVICE
S
Y
C815A OUTDOORTHERMISTOR
COOL CHANGEOVER VALVE
V
SERVICELED (RED)
3
RESET
REMOVE FACTORY-INSTALLED S-Y JUMPER TO DISABLE SERVICE LIGHT.3
10
8
7
6
5
4
3
2
1
THERMOSTAT SUBBASE SYSTEM COMPONENTS
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 132
Fig. 111. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
L1 (HOT)
L2
1
COOL
HEATFALL
H2
SYSTEMSWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED. M2851
OFF
H1C1
2 REMOVE FACTORY INSTALLED V-VR JUMPER WHEN CONNECTING A TWO TRANSFORMER SYSTEM.
COMPRESSORCONTACTOR
OVERLOADSWITCH
INTERNALTHERMOSTAT
HIGH PRESSURESWITCH
2
V
VR
M
F
L
Y
E
X
A
R
FAN RELAY SERVICE
OUTDOORTHERMOSTAT
EM. HT.RELAY
SUPPL. ELEC.HT. RELAY
EM. HT.RELAY
EM. HT.RELAY
C815AOUTDOORTHERMISTOR
COOL CHANGEOVERVALVE
EM. HT. LED(YELLOW)
SERVICELED (RED)
EM. HT.
AUTO
ON
FANSWITCH
RESETHEATER
H1/ C1ANTICIPATOR
H2ANTICIPATOR
FALL
THERMOSTAT SUBBASE SYSTEM COMPONENTS
1
2
3
4
5
6
7
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
133 60-2485�8
Fig. 112. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
OFF
COOL
COMPRESSORFAILURE
FANSWITCH
ON
SYSTEMSWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
M8383
AUX. HT. RELAY
4
EM. HT. LED(RED)
AUX. HT. LED(GREEN)
EM. HT.
HEAT
COOL CHANGEOVERVALVE
FAN RELAY
EM. HT. RELAY
AUTO
Y
C1H1
FALL
H1/C1 ANTICIPATOR
H2 ANTICIPATOR
H2 FALL
COMPRESSORCONTACTOR
6
O
5
R
W2
L1 (HOT)
L2
1
G
2
3
E
X
L1
THERMOSTAT SUBBASE SYSTEM COMPONENTS
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 134
Fig. 113. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
H2
H1
FALL
C1
L1 (HOT)L2
1
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1/C1 ANTICIPATOR
FALL
H2 ANTICIPATOR
SYSTEMSWITCH
FANSWITCH
AUTO
ON
OFF
HEAT
EM. HT.LED (RED)
EM. HT.
COOL
EM. HT. RELAY
EM. HT. RELAY
EM. HT. RELAY
DEFROST RELAY
DEFROSTRELAY
FAN RELAY
M4720
COMPRESSORCONTACTOR
HIGH PRESSURESWITCH
COOL CHANGEOVERVALVE
LOW AMBIENTCUTOFF
O
Y
G
E
X1
X2
L
CHECK LED(GREEN)
OPTIONAL COMP.FAILURE DEVICE
B
W2
W3
RHEAT CONTRACTOR 3
HEAT CONTRACTOR 2
OUTDOORTHERMOSTAT
HEATCONTRACTOR 1
HIGH LIMITSWITCH
REVERSINGVALVE
1
2
3
4
5
6
7
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
135 60-2485�8
Fig. 114. Schematic and hookup of T874D with Q674L. Used in heat pump applications.
L1 (HOT)L2
1
F
E
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
H1 ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
M2
H1
FALL
R
AUTO
ON
FAN SWITCH
X
V
M
L
FANRELAY
H2
FALL
H2 ANTICIPATOR
C1RISE
C2RISE
C2ANTICIPATOR
REMOVE FACTORY INSTALLED V-VR JUMPER WHEN CONNECTINGA TWO TRANSFORMER SYSTEM.
2
2
VR
Y
A
OUTDOORTHERMOSTAT HIGH SPEED
COMPRESSORCONTACTOR
LOW SPEEDCOMPRESSORCONTACTOR
COOL CHANGEOVERVALVE
OUTDOORTHERMOSTAT
SUPPL. ELEC.HT. RELAY
SUPPL. ELEC.HT. RELAY
EM. HT.RELAY
C815A OUTDOORTHERMISTOR
M2853
EM. HT. LED(YELLOW)
EM. HT.RELAY
SERVICELED (RED)
RESETHEATER
C1ANTICIPATOR
SERVICE
1
2
3
4
5
6
7
8
10
11
THERMOSTAT SUBBASE SYSTEM COMPONENTS
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 136
Fig. 115. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
M5072A
(HOT) L1 L2
1
LACO CHPY
B
E
O
G
L
X
W2
W3
RODT 1
RTD 1 EHR 1 RTD 2
ODT 2
EHR 2 RTD 3
RDSYSTEM MONITOR
FAN RELAY
COMPRESSORCONTACTOR
COOL CHANGEOVERVALVE
EM. HT. RELAY
RTD 1AUX. HT.LED (GREEN)
EM. HT.LED (RED)
FAN SWITCH
ON
AUTO
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
H2
FALL
H1
FALL
C1
2
3
4
5
6
H1/C1ANTICIPATOR
H2ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
AUXILIARY HEAT LED AVAILABLE ON SOME MODELS.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
2
2
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
137 60-2485�8
Fig. 116. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
H2
FALL
H1
FALL
C1
Y R
COM
G
W
O EHO
G
Y
A
H
W2
R
B
X
E
L1 (HOT)L2
1
COMPRESSORCONTACTOR
AUX. HT. RELAY
EM. HT. RELAY
EM. HT.LED (RED)
EM. HT.
HEAT
OFF
COOL
COMP. FAULTLED (YELLOW)
SYSTEMSWITCH
FANSWITCH
AUTO
ON
1 POWER SUPPLY. PROVIDE DISCONNECTMEANS AND OVERLOAD PROTECTION AS REQUIRED.
OPTIONAL FIELD WIRE JUMPER TO CYCLE AUXILIARY HEAT RELAY WITH H1 INSTEAD OF H2 (FASTER RESPONSE).
2 ELEC.HT. RELAY
M2857
H1/C1 ANTICIPATOR
H2 ANTICIPATOR
2
R8233B
THERMOSTAT SYSTEM COMPONENTSSUBBASE
2
5
6
4
3
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 138
Fig. 117. Schematic and hookup of T874D with Q674L. Used in heat pump applications.
H1FALL
L1 (HOT) L2
R
B
2
3
4
5
6
G
Y1
Y2
W
X
L
O
ENTHALPYCONTROL RELAY
HEAT RELAYCONTACT 1
DEFROST RELAY
H1 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
C2 ANTICIPATOR
2
2
1
1
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED.
OPTIONAL ECONOMIZER HOOKUP (DOTTED LINES).
M7755
H2FALL
8
10
11
C1RISE
C2RISE
THERMOSTAT SUBBASE SYSTEM COMPONENTS
MOTOR3
MOTOR1
OUTDOOR FAN RELAY 1
DEFROST SWITCHRELAY
TM1 TM2
OUTDOORFAN RELAY 2
DEFROSTSWITCH
LOW AMBIENTTHERMOSTAT 1
OUTDOORFAN RELAY 3
1ST STAGESHORT CYCLECONTROL
2ND STAGESHORT CYCLECONTROL
1ST STAGE LOW PRESSURE LIMIT
2ND STAGE LOW PRESSURE LIMIT
TIME DELAYHEATER
ECONOMIZERRELAY
ENTHALPYCONTROL
ENTHALPYCONTROLRELAY 2
ENTHALPYCONTROLRELAY 1
TIME DELAY
DEFROSTRELAY
HEAT RELAY 1OUTDOOR
THERMOSTAT
SERVICE
DEFROSTRELAY
COOL CHANGEOVERVALVE
SYSTEM SWITCH
OFF
COOL
HEAT
EM. HT.LED(GREEN)
SERVICELED (RED)
FANSWITCH
AUTO
ON
MOTOR2
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
139 60-2485�8
Fig. 118. Schematic and hookup of T874W with Q674L. Used in heat pump applications.
H1
FALL
H2
FALL
L1 (HOT) L2
R
B2
1
3
4
5
6
G
Y1
Y2
O
X
E
A
ECONOMIZERRELAY
HEAT RELAYCONTACT 1
DEFROST RELAY
H2 ANTICIPATOR
H1 ANTICIPATOR
H3 ANTICIPATOR
C2 ANTICIPATOR
C1 ANTICIPATOR
RESET HEATER
2
2
1
1
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
OPTIONAL ECONOMIZER HOOKUP (DOTTED LINES).
M7756
H3FALL
8
9
10
11
12
C1RISE
C2RISE
THERMOSTAT SUBBASE SYSTEM COMPONENTS
MOTOR3
MOTOR1
MOTOR2
OUTDOOR FAN RELAY 1
DEFROST SWITCHRELAY
DEFROSTRELAY
TM1 TM2
OUTDOORFAN RELAY 2
DEFROSTSWITCH
OUTDOORTHERMOSTAT 1
OUTDOORFAN RELAY 3
1ST STAGESHORT CYCLECONTROL
2ND STAGESHORT CYCLECONTROL
1ST STAGE LOW PRESSURE LIMIT
2ND STAGE LOW PRESSURE LIMIT
TIME DELAYHEATER
ECONOMIZERRELAY
ENTHALPYCONTROL
ECONO-MIZERRELAY 2
ECONOMISERRELAY 1
TIME DELAYRELAY
DEFROSTRELAY
COOL CHANGEOVERVALVE
EMERGENCYHEAT RELAY
W
AUXILIARYHEAT RELAY
SYSTEM SWITCH
OFF
COOL
HEAT
EM. HT.
AUX. HEATLED (GREEN)
EM. HEATLED (RED)
FANSWITCH
AUTO
ON
DEFROSTRELAYCONTACT
DEFROSTRELAYCONTACT
C815 OUTDOORTHERMISTOR
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 140
Fig. 119. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
Fig. 120. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
H1
FALL
C1
L1 (HOT)
L2
1
H2FALL
SYSTEM SWITCH
EM. HT.
HEAT
OFF
COOL
H1 ANTICIPATOR
C1ANTICIPATOR
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
RESETHEATER
H2 ANTICIPATOR
FAN SWITCH
AUTO
ON
C815AOUTDOORTHERMISTOR
AUX. HT. RELAY
FAN RELAY
SERVICE
EM. HT. RELAY
COMPRESSORCONTACTOR
HEAT CHANGEOVER RELAY
12
6
5
4
3
2
1 T
W2
G
X
SERVICE LED(YELLOW)
EM. HT. LED (RED)
Z
K
Y
W1
R
11
1
THERMOSTAT SUBBASE SYSTEM COMPONENTS
M5955
H2FALL
H1FALL
C1
L1 (HOT)
L2
1
FAN SWITCH
AUTO
ON
FAN RELAY
AUX. HT. RELAY
"H" RELAY
EM. HT. RELAY
CHANGEOVER VALVE (COOL)
COMPRESSORCONTACTOR
C815A1039THERMISTOR
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
EM. HT. LED (RED)
G
R
W
H
B
X
T
O
Y
12
11
6
5
4
3
2
H1/C1ANTICIPATOR
H2ANTICIPATOR
RESET HEATER
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED. M3173B
THERMOSTAT SUBBASE SYSTEM COMPONENTS
1
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
141 60-2485�8
Fig. 121. Schematic and hookup of T874C with Q674L. Used in heat pump applications.
L1 (HOT)L2 1
R
L
X
W2
G
O
E
B
Y
ODT1
EHR1
ODT2
EHR2
RTD2
RTD3
RTD1
COMPRESSORFAILURE
HEAT CHANGEOVERVALVE
COMPRESSORCONTACTOR
LACO CHP
EM. HT.RELAY
COOL CHANGEOVERVALVE
FAN RELAYRD
RTD1
H1
FALL
H2
FALL
C1
RISE
2
3
4
5
6
8
10
AUX. HT.LED (GRN)
EM. HT.LED (RED)
AUTO
ON
FANSWITCH
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
H2 ANTICIPATOR
H1 ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED.
M7012
C1ANTICIPATOR
THERMOSTAT SUBBASE SYSTEM COMPONENTS
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 142
Fig. 122. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
H1C1
2
3
H2
FALL5
6
H1/C1ANTICIPATOR
H2ANTICIPATOR
AUTO
ON
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
FAN RELAY
G
R
K
L
1
C
Y
W1
SERVICELED (RED)
EM. HT. LED(YELLOW)
SERVICE
COMPRESSORCONTACTOR
EM. HT. RELAY
AUX. HT. RELAY
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED.
1
CO
L1(HOT)
L2
CHANGEOVERVALVE
FALL
4
W2
M8379
THERMOSTAT SUBBASE SYSTEM COMPONENTS
FANSWITCH
Z
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
143 60-2485�8
Fig. 123. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
H2
FALL
H1
FALL
C1
L1 (HOT)
L2
1
2
2
1
2
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
CONNECT CHANGEOVER RELAY TO B FOR HEAT CHANGEOVER, TO O FOR COOL CHANGEOVER.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
LACO CHP
ODT 1
RTD 1
EHR 1 RTD 2
ODT 2
EHR 2 RTD 3
COMPRESSORMONITOR
R
L
X
W2
G
O
E
Y
BHEATCHANGEOVER VALVE
COMPRESSORCONTACTOR
EM. HT. RELAY
COOLCHANGEOVER VALVE
FAN RELAY
RTD 1
RD
10
8
H2ANTICIPATOR
6
5
4
3
2
H1/C1 ANTICIAPTOR
FAN SWITCH
AUTO
ON
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
EM. HT.LED (RED)
AUX. HT.LED (GREEN)
M1030A
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 144
Fig. 124. Schematic and hookup of T874J with Q674L. Used in heat pump applications.
H1FALL
C1RISE
CO
H2
FALL
CO
RISE
L1 (HOT)
L2
1
THERMOSTAT SUBBASE SYSTEM COMPONENTS
COMPRESSOR CONTACTOR
FAN RELAY HEAT RELAY 1
OUTDOOR THERMOSTAT
HEAT RELAYCONTACT 1
HEAT RELAY 2
HEAT RELAYCONTACT 2 HEAT RELAY 3
"X" RELAY"P" RELAY
COOL CHANGEOVER VALVE
SYSTEMSWITCH
EM. HT. ORSUPL. HT.
HEAT
OFF
FANSWITCH
AUTO
ONH1 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
ON MODELS INCLUDING EXTERNAL JUMPER, W2=W1 AND L=F.
1
3
4
5
6
8
9
10
11O
P
X
E
C
L
G
Y
R
2
W2
EM. HT. OR SUPL. HT.LED (RED)
M8003
2
COOL
2
12
2
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
145 60-2485�8
Fig. 125. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
L1 (HOT)
L2
1
X
L
W2
EM. HT.LED (RED)
AUX. HT.LED (GRN)
AUX. HT.RELAY
FAN RELAY
"B" RELAY
G
COOL CHANGEOVERVALVE
EM. HT. RELAY
COMPRESSOR CONTACTOR
O
Y
E
B
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
H1/C1ANTICIPATOR
C1H1
FALL
H2
W3
AUX. HT.RELAY
H2ANTICIPATOR
1
2
3
2
3
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
TERMINAL LABELED C/X ON SOME MODELS.
W3 TERMINAL AVAILABLE ON SOME MODELS ONLY.
M3683A
AUTO
ON
FANSWITCH
FALL
R
2
3
4
6
THERMOSTAT SUBBASE SYSTEM COMPONENTS
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 146
Fig. 126. Schematic and hookup of T874G with Q674P. Used in heat pump applications.
Fig. 127. Schematic and hookup of T874C with Q674L. Used in heat pump applications.
H2
H1
FALL
CO
RISE
C1 RISE
L1 (HOT)L2
1
1
2
2
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
N.O. SWITCH INSTALLER ADDED, TO LIGHT EM. HT. LED WHEN COMPRESSOR OPERATION IS NOT NORMAL.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
SYSTEMSWITCH
FANSWITCH
AUTO
ON
SUPL. HT.
HEAT
COOL
FAN RELAY
COOL CHANGEOVERVALVE
COMPRESSORCONTACTOR 1
HEAT RELAY 2
HEAT RELAY 1
M4722
1
2
4
6
8
9
10
Y
C
L
E
W2
R
G
O
HEAT RELAYCONTACT 2
HEAT RELAYCONTACT 1
HEAT RELAY 3
OUTDOORTHERMOSTAT
FALL
SUPL. HT.LED (RED)
FALL
AUTO
ON
H1
HEAT
OFF
COOL
L2
M5652A
POWER SUPPLY. PROVIDE DISCONNECT MEANS ANDOVERLOAD PROTECTION AS REQUIRED.
FAN SWITCH
L1 (HOT)
SYSTEM SWITCH
COMPRESSORFAILURE
1
1
R
W3
Y
B
L
W2
X
E
FAN RELAY
G
O
LACO CHP
COMPRESSORCONTACTOR
EM. HT. RELAYCOOL CHANGEOVER
VALVE
RDEM. HT.LED (RED)
AUX.HT.LED (GREEN)
RISE
C1
H2
FALL
C1 ANTICIPATOR
EM. HT.
ODT1RTD1
EHR1
RTD2ODT2
EHR2 RTD3RTD1
H2 ANTICIPATOR
H1 ANTICIPATOR
2
3
4
5
6
8
10
THERMOSTAT SUBBASE SYSTEM COMPONENTS
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
147 60-2485�8
Fig. 128. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
Fig. 129. Schematic and hookup of T874G with Q674L. Used in heat pump applications.
FALL
AUTO
ON
H1
HEAT
OFF
COOL
L2
M5653A
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
FANSWITCH
L1 (HOT)
SYSTEMSWITCH
SYSTEM MONITOR
1
1
R
W3
Y
B
L
W2
X
E
FAN RELAY
G
O
LACO CHP
COMPRESSORCONTACTOR
EM. HT. RELAYCOOL CHANGEOVERVALVE
RD
EM. HT. LED (YELLOW)
AUX. HT.LED (GREEN)
H2
FALL
EM. HT.
RD
RTD1 EHR1
RTD2ODT2
EHR2 RTD3RTD1
H1/C1ANTICIPATOR
ODT1
A
SERVICELED (RED)
C1
H2 ANTICIPATOR
2
3
4
5
6
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1FALL
L1 (HOT)L2
1
H2
FALL
CO
RISE
C1
RISE
H1 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
COMPRESSORCONTACTOR
M102A
COOL CHANGEOVER VALVE
EM. HT. RELAYAUX. HT. RELAY
FAN RELAY
G
R
W
X
EM. HT. LED (RED)
B
O
Y
SYSTEM SWITCH
EM. HT.
HEAT
OFF
COOL
FAN SWITCH
AUTO
ON
2
3
4
6
8
9
10
1
THERMOSTAT SUBBASE SYSTEM COMPONENTS
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 148
Fig. 130. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
H2
FALL
H1
FALL
C1
L1 (HOT)L2
1
2
2
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
FACTORY-INSTALLED JUMPER.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1/C1 ANTICIPATOR
H2 ANTICIPATOR
SYSTEMSWITCH
FANSWITCH
AUTO
ON
OFF
HEAT
EM. HT.
COOL
FAN RELAY
EM. HT. RELAY
COOL CHANGEOVER VALVE
COMPRESSORCONTACTOR
M1628A
COMPRESSORFAILURE
C815A OUTDOORTHERMISTOR
SYSTEMLED (GREEN)
CHECK LED (RED)
AUX. HT.LED (YELLOW)
2
3
4
5
6
11
12RESET
Y
T
C
X
E
W1
R
G
O
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
149 60-2485�8
Fig. 131. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
H2 FALL
H1
FALL
C1
L1 (HOT)L2
1
1
2
2
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
FOR Q674L1454, IS "OFF".
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1/C1 ANTICIPATOR
H2 ANTICIPATOR
SYSTEMSWITCH
FANSWITCH
AUTO
ON
SUPL. HT.
HEAT
COOL
COOL CHANGEOVERVALVE
COMPRESSORCONTACTOR
FAN RELAY
M4723
2
3
4
6
R
W2
L
SUPL. HT.LED (RED)
C
G
O
E
Y
HCR 1 HCR 2
HCR 2 HCR 3
ODT
HCR 1RESETHEATER
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 150
Fig. 132. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
Fig. 133. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
H2
FALL
H1
FALL
C1
L1 (HOT)
L21
1
2
2
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
REMOVE JUMPER FOR INDEPENDENT CONTROL OF W1 AND E TERMINALS.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1/C1 ANTICIPATOR
H2 ANTICIPATOR
RESET
SYSTEMSWITCH
FANSWITCH
AUTO
ON
OFF
HEAT
EM. HT.
COOL
COMPRESSORCONTACTOR
FAN RELAY
M1858
2
3
4
5
6
11
12
Y
T
C
X
E
R
G
O
COOL CHANGEOVERVALVE
3R
SEQ 1
SEQ 2
EM. HT. RELAY
4R4R
5R
HPS 4R
4R
C815A OUTDOORTHERMISTOR
SYSTEMLED (GREEN)
EM. HT.LED(RED)
W1
AUX. HT.LED(YELLOW)
H2
FALL
H1
FALL
C1
L1 (HOT)
L2 1
G
R
K
W2
L
C
Z
W1
2
3
4
6
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
1
THERMOSTAT SUBBASE SYSTEM COMPONENTS
FANSWITCH
AUTO
ON
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
M2018
H1/C1ANTICIPATOR
H2 ANTICIPATOR
Y
FANRELAY
EM. HT.RELAY
AUX. HT.RELAY
CO W1 RELAY
COMPRESSORCONTACTOR
1
5
EM. HT.LED (YEL)
RESETLED (RED)
COMPRESSORFAILURE
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
151 60-2485�8
Fig. 134. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
H2FALL
H1
FALLC1
LACO CHP
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
L1 (HOT)L2
1
H1/C1 ANTICIPATOR
H2ANTICIPATOR
SYSTEM SWITCH
EM. HT.
HEAT
OFF
COOL
FAN SWITCH
AUTO
ON
AUX. HT.LED (GREEN)
EM. HT. LED (RED)
COMP.FAILURE
CHANGEOVER VALVE (HEAT)
COMPRESSOR CONTACTOR
Y
X
B
L
E
W2
R
G
O
6
5
4
3
2
1
EM. HT. RELAY
RD
RTD 1
FAN RELAY
RTD 1 ODT 1
EHR 1 RTD 2
ODT 2
EHR 2 RDT 3
CHANGEOVER VALVE (COOL)
M106A1
8
10
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 152
Fig. 135. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
Fig. 136. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
H2
FALL
H1
FALL
C1
L1 (HOT)
L2 1
R
W2
L
C
G
O
E
Y
2
3
4
6
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
1
THERMOSTAT SUBBASE SYSTEM COMPONENTS
FANSWITCH
AUTO
ON
SYSTEMSWITCH
SUPL. HT.
HEAT
OFF
COOL
M2017
HCR 1
ODT HCR 1 HCR 2
FAN RELAY
COOLCHANGEOVER VALVE
HCR 2 HCR 3
COMPRESSORCONTACTOR
SUPL. HT.LED (RED)
H1/C1ANTICIPATOR
RESETHEATER
H2 ANTICIPATOR
H2
FALL
H1
FALL
C1
L1 (HOT)
L2
1
G
W
U
B
F
R
T
X2
O
Y
2
1
3
4
5
6
FAN RELAY
AUX. HEATRELAY
COMP.FAILURE
O.D.STAT
C815A OUTDOORTHERMISTOR
COOL CHANGEOVERVALVE
COMPRESSORCONTACTOR
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
FIELD REMOVABLE JUMPER1
2
2
THERMOSTAT SUBBASE SYSTEM COMPONENTS
RESET
FANSWITCH
AUTO
ON
AUX. HT.LED (GRN)
EM. HT.LED (RED)
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
M2012
C1ANTICIPATOR
H1ANTICIPATOR
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
153 60-2485�8
Fig. 137. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
H2FALL
H1
FALLC1
LACO CHP
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
L1 (HOT)L2
1
H1/C1 ANTICIPATOR
H2ANTICIPATOR
SYSTEM SWITCH
EM. HT.
HEAT
OFF
COOL
FAN SWITCH
AUTO
ON
AUX. HT.LED (GREEN)
EM. HT. LED(RED)
CHECK LED (RED)
COMP.FAILURE
CHANGEOVER VALVE (HEAT)
COMPRESSOR CONTACTOR
Y
X
B
L
E
W2
R
G
W3
O
6
5
4
3
2
1
EM. HT. RELAY
RD
RTD 1
FAN RELAY
RTD 1 ODT 1
EHR 1 RTD 2
ODT 2
EHR 2 RDT 3
CHANGEOVER VALVE (COOL)
M105A
1
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 154
Fig. 138. Schematic and hookup of T874L with Q674B. Used in heat pump applications.
Fig. 139. Schematic and hookup of T874D with Q674F. Used in heat pump applications.
M103A
R1 NO2 S1 RELAY
S1 NC
SOLIENOIDRELAY
FAN RELAYFAN SWITCH
AUTO
ON
J
S
G
R
C
H2
H1
O
AUX. HT. RELAY
COMPRESSORCONTACTORR1 NC1
R2 NO1
REVERSING VALVE
R1 RELAY
SYSTEM SWITCH
HEAT
OFF
COOL
H1 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
10
9
8
7
5
4
3
2
1
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
FIELD REMOVABLE JUMPER
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H2
FALL
H1
FALL
L1 (HOT)L2
1
RISE
C1
2
2
1
H1FALL
H2 FALL
C1RISE
C2 RISE
L1 (HOT)L2
1
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
C2 ANTICIPATOR
SYSTEMSWITCH
FANSWITCH
AUTO
ON
OFF
2 STG. HEAT
HEAT PUMP
AUX. HT.
COOL
FAN RELAY
AUX. HT. RELAY
COOL CHANGEOVERVALVE
COMPRESSORCONTACTOR 1
COMPRESSORRELAY
COMPRESSORCONTACTOR 2 M4730
HEAT PUMPLED (GREEN)
AUX. HTLED (RED)
1
2
4
6
8
10
11 Y2
Y1
C
W2
W1
B
R
G
O
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
155 60-2485�8
Fig. 140. Schematic and hookup of T874W with Q674L. Used in heat pump applications.
1
T
W3
U
G
R
E
L
X
B
O
Y1
Y2
C815A OD THERMISTOR
AUX. HT. RELAY
FAN RELAY
EM. HT. RELAYCOMPRESSORMONITOR
HEAT CHANGEOVERRELAY
COOL CHANGEOVERRELAY
COMPRESSORCONTACTOR 1
COMPRESSORCONTACTOR 2
EM.HT.
AUTO
ON
FAN SWITCH
H1 ANTICIPATOR
H2 ANTICIPATOR
H3 ANTICIPATOR
RESET
FALL
FALL
FALL
H1
H3
H2
AUX. HT.LED (GREEN)
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
CONNECT CHANGEOVER RELAY TO 'O' TERMINAL FOR CHANGEOVER IN COOLING OR TO 'B' TERMINAL FOR CHANGEOVER IN HEATING. M156A
C1 ANTICIPATOR
RISE
RISEC2 ANTICIPATOR
C1
C2
EM. HT.LED (RED)
CHECK LED(RED)
HEAT
OFF
COOL
SYSTEMSWITCH
2
2
THERMOSTAT SUBBASE SYSTEM COMPONENTS
1
2
3
4
5
6
8
9
10
11
12
L1 (HOT)L2
1
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 156
Fig. 141. Schematic and hookup of T874C with Q674F. Used in standard applications.
Fig. 142. Schematic and hookup of T874C,D with Q674F. Used in standard applications.
H1
FALL
H2
FALL
C1RISE
L1 (HOT)L2
1
H1 ANTICIPATOR
4
1
C2RISE
C1 ANTICIPATOR
C2 ANTICIPATOR
8
9
10
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
1
R
AUTO
ON
FANSWITCH
SYSTEM SWITCH
OFF
EM. HT.
HEAT
AUTO
COOL
HEAT RELAY 1
HEAT RELAY 2
EM. HT. LED(RED)
EM. HT. RELAY
FAN RELAY
COMPRESSOR CONTACTOR 1
COMPRESSOR CONTACTOR 2
M8376
THERMOSTAT SUBBASE SYSTEM COMPONENTS
E
G
Y2
Y1
6
11
X2
W2
W1
H2 ANTICIPATOR
H1
FALL
1
EM. HT.
HEAT
SYSTEMSWITCH
H1 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
C2 ANTICIPATOR
AUTO
COOL
W2
M5985POWER SUPPLY. PROVIDE DISCONECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.1
SYSTEM COMPONENTSSUBBASETHERMOSTAT
4
6
8
9
10
11
OFF
AUTO
ON
FANSWITCH
L1 (HOT)
L2 1
B
X2
X1
E
G
O
Y2
Y1
R
EM. HT. RELAY
FAN RELAY
COMPRESSORCONTACTOR 2
COMPRESSORCONTACTOR 1
W1
HEAT RELAY 1
HEAT RELAY 2
C1
C2
RISE
RISE
H2FALL
CHECKLED (RED)
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
157 60-2485�8
Fig. 143. Schematic and hookup of T874G with Q674B. Used in heat pump applications.
Fig. 144. Schematic and hookup of T874J with Q674J. Used in heat pump applications.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
M8378
H1
FALL1
H1 ANTICIPATOR
2
FANSWITCH
AUTO
ON4
R
COMPRESSORCONTACTOR
FAN RELAY
H2
FALL
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
CO
RISE
H2ANTICIPATOR
8
L1 (HOT)
1
10
9
C1
RISE
G
AUX. HT. RELAY
L2
W1
CAUX. HT. LED(RED)
6SYSTEMSWITCH
OFF
AUTO
C1 ANTICIPATOR
O
Y1
COOL CHANGEOVER VALVE
H1
FALL
C1RISE
CO
H2 FALL
CO
RISE
L1 (HOT)
L2
1
THERMOSTAT SUBBASE SYSTEM COMPONENTS
COMPRESSOR CONTACTOR
FAN RELAY
HEAT RELAY 1
OUTDOOR THERMOSTAT
HEAT RELAYCONTACT 1
HEAT RELAY 2
HEAT RELAYCONTACT 2
HEAT RELAY 3
"X" RELAY"P" RELAY
COOL CHANGEOVERVALVE
SYSTEMSWITCH
SUPL. HT.
ON
OFF
FANSWITCH
AUTO
ON
H1 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.1
3
4
5
6
8
9
10
11 O
P
X
E
C
L
G
Y
R
2
W2
SUPP. HT.LED (RED)
M5956
12
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 158
Fig. 145. Schematic and hookup of T874G with Q674F. Used in heat pump applications.
Fig. 146. Schematic and hookup of T874D with Q674F. Used in heat pump applications.
OFF
COOL
OUTDOORTHERMOSTATON
SYSTEMSWITCH
FANSWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
M8375
EM. HT. RELAYTIME DELAYFAN RELAY4
EM. HT.LED (RED)EM. HT.
HEAT
AUTO
SUP. ELEC. HT. RELAY
DEFROSTRELAY
COMPRESSORCONTACTOR
INTERNALTHERMOSTAT
COOL CHANGEOVERVALVE
HIGHPRESSURESWITCH
OVERLOAD
AUTO
H1 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
C1RISE
FALL
EM. HT. RELAY6
V
9
8
10
CO
FALLH1
FALL
H2
F
L2 (HOT) L1
1
Y1
M
E
R
FAN RELAY
THERMOSTAT SUBBASE SYSTEM COMPONENTS
2
H1
FALL
Y1
G
W1
X
W2
R
AUTO
COOL
SYSTEMSWITCH
H1 ANTICIPATOR
AUTO
ON
FAN SWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
M7010
THERMOSTAT SUBBASE SYSTEM COMPONENTS
4
8
9
10
11
H2 ANTICIPATOR
SUPL. HEATLED (RED)
C
E
1
3
6
SUPL. HT.
HEAT
OFF
Y2
RVR RVR
EHR EHR
COMPRESSORCONTACTOR 1DFR 2
REVERSINGRELAY
FAN RELAY
L1 (HOT)L2
1
ODT 3
HEATRELAY 2
HEAT RELAY 1ODT 2
HEAT RELAY 3
SUPL. HT.RELAY
DFR 2 COMPRESSORCONTACTOR 2
LPCO
H2
FALL
C1
RISE
C1 ANTICIPATOR
C2 ANTICIPATORRISE
C2
EHT
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
159 60-2485�8
Fig. 147. Schematic and hookup of T874G with Q674F. Used in heat pump applications.
Fig. 148. Schematic and hookup of T874G with Q674F. Used in heat pump applications.
H1
FALL
1
G
A
X
W2
R
AUTO
COOL
SYSTEMSWITCH
H1 ANTICIPATOR
AUTO
ON
FAN SWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
CONNECT TO Y OR W TERMINAL WITH FACTORY INSTALLED JUMPER. M7024
THERMOSTAT SUBBASE SYSTEM COMPONENTS
4
8
9
10
H2 ANTICIPATOR
O
L
2
3
6
EM. HT.
HEAT
OFF
Y
H2FALL
CO
RISE
C1 ANTICIPATORRISE
C1
L1 (HOT)L2
1
2
S
W3
E
T
MODE SIGNAL
COOL CHANGEOVERVALVE
COMPRESSORCONTACTOR
EM. HT. RELAY
HEAT RELAY 1 HEAT RELAY 2
FAN RELAY
MODE SIGNAL
5
AUX. HT.LED (GRN)
EM. HT.LED (YEL)
SERVICELED (RED)
2
2
3 JUMPER FACTORY INSTALLED.
3
OFF
COOL
DEFROSTRELAY
FANSWITCH
ON
SYSTEMSWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.M8382
AUX. HT. RELAY
EM. HT. RELAY
4
EM. HT. LED (RED)EM. HT.
HEAT
AUTO
COOL CHANGEOVERVALVE
BLOWER SPEEDRELAY
DEFROSTRELAY
BLOWER RELAY
COOLCONTRACTOR
LOCKOUTTHERMOSTAT
AUTO
E
H1 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
C1 RISE
RISE
6
O
8
10
R
CO
FALLH1
FALL
H2 W2
L1 (HOT)
L2 1
G
1
Y
C
THERMOSTAT SUBBASE SYSTEM COMPONENTS
9
2
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 160
Fig. 149. Schematic and hookup of T874C with Q674F. Used in heat pump applications.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1
FALL
H1 ANTICIPATOR
1
H2
FALL
H2ANTICIPATOR
W1
EMR4 2R
1R
5R
3R
Y1
G
EMR4
EMR2
THERMAL SWITCHESFOR HEATINGELEMENTS
HTR 1
C1
RISE
HTR 3
HTR 2
OUTDOORTHERMOSTAT
EMR3
L1 (HOT)
L21
L1 (HOT) L2
1
C2
RISE
8
3
C1 ANTICIPATOR
C2 ANTICIPATOR
9
11
10EM. HT. LED
RC
X1
RH
EMR1
EMR1
Z
EM. HT. RELAY
2
1
2
3
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
OPTIONAL FIELD WIRE JUMPER TO ALLOW SINGLE SYSTEM TRANSFORMER.
FOR Q674F1048, DELETE C2 STAGE.
M8380
SYSTEMSWITCH
OFF
EM. HT.
HEAT
AUTO
COOL
E
FANSWITCH
AUTO
ON
W26
4
3R1
4R2 2R2
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
161 60-2485�8
Fig. 150. Schematic and hookup of T874G with Q674F. Used in heat pump applications.
L1 HOTL2
1
F
EM. HEATLED (RED)
V
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
H1 ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
M2852A
R
H1
FALL
E
AUTO
ON
FAN SWITCH
VR
Y
M
OUTDOORTHERMOSTAT
SUPL. ELEC. HT. RELAY
X
COOL CHANGEOVER VALVE
COMPRESSORCONTACTOR
OVERLOADSWITCH
INTERNALTHERMOSTAT
HI PRESSURESWITCH
FANRELAY
EM. HT. RELAY CONTACT
TIME DELAYFAN RELAY
TIME DELAYFAN RELAY
SYSTEMMONITOR
AUTO
H2
FALL
H2 ANTICIPATOR
CO
RISE
C1
RISE
C1ANTICIPATOR
REMOVE FACTORY INSTALLED V-VR JUMPER WHEN CONNECTINGA TWO TRANSFORMER SYSTEM.
2
2
L1 HOT
L21
1
2
3
5
6
8
9
10
THERMOSTAT SUBBASE SYSTEM COMPONENTS
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 162
Fig. 151. Schematic and hookup of T874G with Q674F. Used in heat pump applications.
H1FALL
H2FALL
CO
RISE
C1 RISE
L1 (HOT)
L2
11
2
1
L1 (HOT)
L2
2
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
OPTIONAL FIELD WIRE JUMPER TO CYCLE W2 WITH H1 IN EM. HT. (FASTER RESPONSE).
THERMOSTAT SUBBASE SYSTEM COMPONENTS
M4710
H1 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
SYSTEMSWITCH
FANSWITCH
AUTO
ON
OFF
HEAT
EM. HT.
AUTO
COOL
EM. HT. LED(RED)
EM. HT. RELAYCONTACT 1
T6031 REFRIGERATON/TEMPERATURE CONTROLLER
EM. HT.
EM. HT. RELAY
COMPRESSORCONTACTOR
SEQUENTIALRELAY
FANREVERSINGSOLENOID
COM
EM.HT.
FAN
R8233B
Y R
G
W
O
C DF RS
O
G
Y
H
X
W2
R1
2
4
6
8
9
10
E
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
163 60-2485�8
Fig. 152. Schematic and hookup of T874D with Q674F. Used in standard applications.
Fig. 153. Schematic and hookup of T874G with Q674F. Used in heat pump applications.
OFF
ON
SYSTEMSWITCH
FAN SWITCH
1
2
3
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
M8377
HEAT RELAY 2
COMPRESSORCONTRACTOR 1
EM. HEATLED (RED)
EM. HT.
HEAT
AUTO
HEAT RELAY
COMPRESSORCONTRACTOR 2
AUTOH1 ANTICIPATOR
H2 ANTICIPATOR
C2 ANTICIPATOR
C1
RISE
RISE
W1
FALL
H1
FALL
H2
RC
Y1
G
1
Y2
X2
O
B
X1
E
RH
FAN RELAY
EM. HT. RELAY
L1 (HOT)
L21
L1 (HOT)
L2
12 FACTORY SUPPLIED FIELD INSTALLED JUMPER TO E-X2 FOR CONSTANT POWER TO EM HT LIGHT IN EM HT POSITION.
3 OPTIONAL FIELDWARE JUMPER TO ALLOW SINGLE SYSTEM TRANSFORMER.
6
C1 ANTICIPATOR
C2
11
10
W2
8
THERMOSTAT SUBBASE SYSTEM COMPONENTS
COOL
9
4
OFF
COOL
OUTDOORTHERMOSTAT
FANSWITCH
ON
SYSTEMSWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED. M8381
AUX. HT. RELAYCONTACT
AUX. HT. RELAY
4
EM. HT. LED(RED)
EM. HT.
HEAT
AUTO
COOL CHANGEOVERVALVE
FAN RELAY
COMPRESSORCONTACTOR
AUTO
H1 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
C1 RISE
RISE
EM. HT.RELAY
6
O
9
10
R
CO
FALLH1
FALL
H2
W2
L1 (HOT)L2 1
G
1
2
E
X
THERMOSTAT SUBBASE SYSTEM COMPONENTS
8
Y
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 164
Fig. 154. Schematic and hookup of T874G with Q674F. Used in heat pump applications.
H2
FALL
Y R
COM
G
W
O
EH
O
G
Y
A
H
E
W2
R 1
COMPRESSORCONTACTOR
EM. HT.
HEAT
AUTO
COOL
COMP. FAULTLED (YELLOW)
SYSTEMSWITCH
FANSWITCH
AUTO
ON
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
OPTIONAL FIELD WIRE JUMPER TO CYCLE W2 WITH H1IN EM. HEAT(FASTER RESPONSE).
2
H2 ANTICIPATOR
2
X
C DF RS
FAN
L1(HOT)
L2
EM. HT. RELAY
FAN
REVERSINGSOLENOID
T6031 REFRIGERATIONTEMPERATURECONTROLLER
EM. HT. RELAYCONTACT 1
EM. HT.
L1(HOT)
L2
EM. HT.LED (RED)
H1 ANTICIPATOR
H1FALL
H1 ANTICIPATORCO
RISE
C1RISE
SEQUENTIALRELAY
M2858
R8233B
THERMOSTAT SUBBASE SYSTEM COMPONENTS
1
2
6
4
8
9
10
OFF
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
165 60-2485�8
Fig. 155. Schematic and hookup of T874G with Q674F. Used in heat pump applications.
H2
FALL
L1 (HOT)
L2 1
R
W3
W2
X
L
G
O
E
Y
RTD1 OTD1
EHR1
ODT2
EHR2
RTD2
RTD3
RTD1
SYSTEMMONITOR
FANRELAY
RD
COOL CHANGEOVER VALVE
EM. HT.RELAY
LACO
COMPRESSORCONTACTOR
CHP
2
3
4
5
6
8
9
10
H1 FALL
H1 ANTICIPATOR
H2ANTICIPATOR
CHANGEOVER
RISE
C1RISE
C1ANTICIPATOR
OFF
COOL
AUTO
HEAT
EM. HT.
SYSTEMSWITCH
AUTO
ON
FANSWITCH
AUX. HT.LED (GRN)
EM. HT.LED (RED)
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED.
W3 TERMINAL ON SELECT MODELS.
1
2
2
M1589
THERMOSTAT SUBBASE SYSTEM COMPONENTS
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 166
Fig. 156. Schematic and hookup of T874G with Q674F. Used in heat pump applications.
Fig. 157. Schematic and hookup of T874G with Q674F. Used in heat pump applications.
COMPRESSORFAILURE
H1
FALL
H2
FALL
L1 (HOT)
L2
1
CO
RISE
H1 ANTICIPATOR
1
2
4
6
9
8
C1
RISE
OFF
EM. HT.
SYSTEMSWITCH
FANSWITCH
10
C1 ANTICIPATOR
H2 ANTICIPATOR
HEAT
AUTO
COOL
ON
ON
EM. HT. LED(RED)
L1
E
AUX. HT.RELAYCONTACT
EM. HT.RELAY
R
G
O
COOLCHANGEOVER VALVE
FAN RELAY
OUTDOORTHERMOSTAT
EM. HT. LED(GREEN)
X
AUX. HT. RELAY
COMPRESSOR CONTACTOR
W2
Y
M5720POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.1
SYSTEM COMPONENTSSUBBASETHERMOSTAT
L2
1
COMPRESSORCONTACTOR
H2 ANTICIPATOR
M2860
AUTO
ON
FAN SWITCH
W1
C1
E
W2
H1 ANTICIPATOR
C1 ANTICIPATOR
CO
RISE
C1
FALL
H2
FALL
H1
R
X
Y1
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
AUTO
G
TIME DELAYRELAY 2
FAN RELAY
COOL CHANGEOVERVALVE
LOCKOUTRELAY
HI PRESSURESWITCH
EM. HT. LED (RED)
CHECK LED(GREEN)
TIME DELAYRELAY 1
DEFROSTRELAY
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
L1 (HOT)
RISE
2
3
4
6
8
9
10
THERMOSTAT SUBBASE SYSTEM COMPONENTS
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
167 60-2485�8
Fig. 158. Schematic and hookup of T874G with Q674F. Used in heat pump applications.
4
OFF
EM. HT.
SYSTEMSWITCH
HEAT
AUTO
COOL AUX. HT. LED (GREEN)
1
X
M5721
8
C1 ANTICIPATOR
POWER SUPPLY. PROVIDE DISCONNECT MEANSAND OVERLOAD PROTECTION AS REQUIRED.
1
CORISE
FALL
H2
6
9
C1RISE
H2 ANTICIPATOR
10
FALL
H1
H1 ANTICIPATOR1
2
AUTO
ON
FANSWITCH
EM. HT. LED(RED)
W2
L1 (HOT) L2
1
AUX. HT. RELAY
Y
COMPRESSOR CONTACTOR
2
B TERMINAL ON SELECT MODELS.
R
B
HEAT CHANGEOVER VALVE
G
FAN RELAY
E
EM. HT. RELAY
O
COOL CHANGEOVER VALVE
COMPRESSORFAILURE
2
L
SYSTEM COMPONENTSSUBBASETHERMOSTAT
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 168
Fig. 159. Schematic and hookup of T874G with Q674J. Used in heat pump applications.
Fig. 160. Schematic and hookup of T874G with Q674J. Used in heat pump applications.
L1 (HOT)
L2
1
H1 FALL
H1 ANTICIPATOR
H2
FALL
CO
RISE
C1
RISE
1
2
4
6
8
9
10
O
G
R
X
Y
W
C1 ANTICIPATOR
E
OFF
AUTO
SYSTEMSWITCH
FAN SWITCH
OUTDOORTHERMOSTAT
OFF
AUTO
EM.HT.EM. HT. LED(RED)
LIMITCOMPRESSORCONTACTOR
HEAT RELAYCONTACT
EM. HT.RELAY
AUX. HT. RELAY
COOL CHANGEOVER VALVE
FAN RELAY
M5722
HEAT RELAYCONTACT
SYSTEM COMPONENTSSUBBASETHERMOSTAT
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.1
H2 ANTICIPATOR
EM. HT.
AUX. HT. RELAY
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.1
RISE
CO
RISE
C1
6
8
9
10
X
B
Y
COMPRESSORCONTACTOR
FALL
H2
5 W
4
SYSTEM COMPONENTSSUBBASETHERMOSTAT
H1 ANTICIPATOR
2
L1 (HOT)
L21
FALL
H1
3
O
G
R
FAN RELAY
COOL CHANGEOVER VALVE
H2 ANTICIPATOR
C1 ANTICIPATOR
FANSWITCH
AUTO
ON
SYSTEMSWITCH
AUTO
OFF
EM. HT.LED (RED)
M5723
EM. HT. RELAY
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
169 60-2485�8
Fig. 161. Schematic and hookup of T874G with Q674J. Used in heat pump applications.
H2 ANTICIPATOR
1
SUPL. HT.LED (RED)
M5724POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
1
SYSTEM COMPONENTSSUBBASETHERMOSTAT
L1 (HOT)L2
1
H1
FALL
H2
FALL
2
4
6
O
G
R
W 2
E
L
C
Y
CO
RISE
C1
RISE
8
9
10
H1 ANTICIPATOR
C1 ANTICIPATOR
SYSTEMSWITCH
SUPL. HT.
ON
OFF
FANSWITCH
AUTO
ONFAN RELAY
COOL CHANGEOVER VALVE
OUTDOORTHERMOSTAT
EM. HT. RELAY 1
EM. HT. RELAYCONTACT 1
EM. HT. RELAY 2
EM. HT. RELAYCONTACT 2
EM.HT. RELAY 32
COMPRESSORCONTACTOR 1
N.O. SWITCH — INSTALLER ADDED, TO LIGHT EM. HT. LEDWHEN COMPRESSOR OPERATION IS NOT NORMAL.
2
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 170
Fig. 162. Schematic and hookup of T874G with Q674J. Used in heat pump applications.
H1
FALL
EM. HT. LED (RED)
L1 (HOT)L2
1
AUX. HT. LED(GREEN)
F
M5725POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.1
SYSTEM COMPONENTSSUBBASETHEROMSTAT
B
W
H2
FALL
CO
RISE
C1
RISE
O
G
T
R
1
2
3
4
5
6
8
9
10Y
X2
C1ANTICIPATOR
RESET HEATER
H1 ANTICIPATOR
SYSTEM SWITCH
EM. HT.
AUTO
OFF
FAN SWITCH
AUTO
ON
C815A OUTDOORTHERMISTOR
FAN RELAY
COOLCHANGEOVER VALVE
OUTDOORTHERMOSTAT
AUX. HT. RELAY
EM. HT. RELAY
COMPRESSORCONTACTOR
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
171 60-2485�8
Fig. 163. Schematic and hookup of T874G with Q674C. Used in standard applications.
H1FALL
H2FALL
CO
FALL
C1
RISE
L1 (HOT)
L2
1
1
1
1
2
3
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
H2 HAS 10¡F FIXED SETBACK FROM H1 ON T874G1485, 0-12¡F ADJUSTABLE ON T874G1535.
RESET IN MOMENTARY POSITION, SPRING RETURN TO OFF UPON SWITCH RELEASE.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
1
4
6
8
9
10
C1ANTICIPATOR
H2ANTICIPATOR
H1ANTICIPATOR
FANSWITCH
AUTO
ON
SYSTEMSWITCH
AUTO
OFF
RESET
RESET CIRCUIT
RESET CIRCUIT
COMPRESSORRELAY
SERVICE LED (RED)
ON LED (YELLOW)
COOL CHANAGEOVER VALVE
HEAT RELAY 2
FAN RELAY
HEAT RELAY 1
HEAT DAMPER
C
A
X
Y
S2
O
S1
R
W2
G
W1
B
M1820C
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 172
Fig. 164. Schematic and hookup of T874H with Q674C. Used in standard applications.
Fig. 165. Schematic and hookup of T874L with Q674C. Used in heat pump applications.
H1
FALL
L1 (HOT)L2
1
2
OFF
FAN SWITCH
SYSTEM SWITCH
C1ANTICIPATOR
AUTO
ON
M5726
POWER SUPPLY. PROVIDE DISCONNECT MEANSAND OVERLOAD PROTECTION AS REQUIRED.
1
SYSTEM COMPONENTSSUBBASETHERMOSTAT
3
4
6
8
9
10
O
Y
G
R
L
B
X
2
AUTO
CO
RISE
C1
RISE
R-L JUMPER SUPPLIED BY HONEYWELL.2
H1ANTICIPATOR
MALFUNCTIONLED (RED)
HEAT CHANGEOVERVALVE
MALFUNCTIONSWITCH
FAN RELAY
COMPRESSORCONTACTOR
COOL CHANGEOVERVALVE
L1 (HOT)
L21
RISE
C1
H1 ANTICIPATOR
1
FANSWITCH
ON
AUTO
M5727POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
1
SYSTEM COMPONENTSSUBBASETHERMOSTAT
SYSTEMSWITCH
AUTO
OFF
2
3
4
5
7
8
9
10
H2 ANTICIPATOR
J
S
G
C
R
O
H2
H1
FIELD REMOVABLE JUMPER.2
H1 AND C1 ARE DPST SWITCHES.3
H2
FALL
H1FALL
3
3
2
C1ANTICIPATOR
R1 N.O.2 S1 RELAY
SOLENOID RELAY S1 N.C.
FAN RELAY
AUX. HT. RELAY
R1 N.C.1COMPRESSORCONTACTOR
R2 N.O. 1
R1 RELAY
REV. VALVE
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
173 60-2485�8
Fig. 166. Schematic and hookup of T874D with Q674F. Used in standard applications.
H1
FALL
L1 (HOT)
L21
H1 ANTICIPATOR
1
OFF
EM. HT.
SYSTEMSWITCH
FANSWITCH
HEAT
AUTO
COOL
ON
AUTO
M5728
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.1
SYSTEM COMPONENTSSUBBASETHERMOSTAT
H2
FALL
C1
RISE
C2
RISE
4
6
8
9
10
11
X
W1
W2
Y2
L
RH
E
G
Y1
RC
L1 (HOT)L2 1
HEAT RELAY 1
HEAT RELAY 2
EM. HT. RELAY
FAN RELAY
COMRESSOR CONTACTOR 1
AUX. HT. LED(GREEN)
EM. HT. LED(RED)
COMRESSOR CONTACTOR 2
SYSTEM MONITOR
C1 ANTICIPATOR
C2 ANTICIPATOR
H2 ANTICIPATOR
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 174
Fig. 167. Schematic and hookup of T874G with Q674F. Used in heat pump applications.
M1592A
(HOT) L1 L2
1
LACO CHPY
B
E
G
L
X
W2
RODT 1
RTD 1 EHR 1 RTD 2
ODT 2
EHR 2 RTD 3
RDCOMPRESSORFAILURE
FAN RELAY
COMPRESSORCONTACTOR
HEAT CHANGEOVERVALVE EM. HT.
RELAY
RTD 1AUX. HT.LED (GREEN)
EM. HT.LED (RED)
FAN SWITCH
ON
AUTO
SYSTEMSWITCH
EM. HT.
HEAT
AUTO
OFF
COOL
H2
FALL
H1
FALL 2
3
4
5
H1 ANTICIPATOR
H2ANTICIPATOR
C1
RISE
FALL
7
8
9
10C1ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
EHT1
CHANGEOVER
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
175 60-2485�8
Fig. 168. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
H1
FALL
C
L1 (HOT)L2
1
EM. HT.LED (RED)
AUX. HT.LED (GRN)
W3
O
L
G
R
W2
E
X
X2
B
W1
Y
AUX. HT. RELAY
EM. HT. RELAY
HEATCHANGEOVERVALVE
W1 RELAY
COMPRESSORRELAY
W3 RELAY
COOL CHANGEOVERVALVE
COMPRESSORMONITOR
FAN RELAY
H2
FALL
H1ANTICIPATOR
C ANTICIPATOR
H2ANTICIPATOR
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED.
REMOVE JUMPER WHEN W1 RELAY IS USED.
FACTORY-INSTALLED JUMPER.
1
M5067
FANSWITCH
AUTO
ON
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
3
22
3
THERMOSTAT SUBBASE SYSTEM COMPONENTS
1
2
3
4
5
6
11
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 176
Fig. 169. Schematic and hookup of T874G with Q674F. Used in heat pump applications.
H1
FALL
RISE
CO
L1 (HOT)
L2
1
3
C1
RISE1
2
2
3
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
TERMINAL LABELED C/X ON SOME MODELS.
W3 TERMINAL ON SOME MODELS ONLY.
C1 ANTICIPATOR
H1 ANTICIPATOR FAN SWITCH
AUTO
ON
SYSTEM SWITCH
AUTO
HEAT
OFF
COOL
1
2
4
6
8
9
10
O
W2
X
E
L
B
W3
R
G
Y
AUX. HT. RELAY
FAN RELAY
EM. HT. RELAY
B RELAY
M5986A
THERMOSTAT SUBBASE SYSTEM COMPONENTS
11
12
COMPRESSORCONTACTOR
EM. HT.
EM. HT.LED (RED)
AUX. HT.LED (GREEN)
COOL CHANGEOVER VALVE
H2
FALL
H2 ANTICIPATOR
AUX HT. RELAY
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
177 60-2485�8
Fig. 170. Schematic and hookup of T874G with Q674F. Used in heat pump applications.
H1
FALL
RISE
CO
L1 (HOT)
L2
1
C1
RISE
1
2
3
3
2
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
ON SOME MODELS, Y TERMINAL MAY BE LABELED Y1.
EMERGENCY HEAT RUNS CONTINUOUSLY WHEN SWITCH IN IN EM. HT. POSITION.
C1 ANTICIPATOR
H1 ANTICIPATOR FAN SWITCH
AUTO
ON
SYSTEM SWITCH
AUTO
HEAT
OFF
COOL
2
4
8
9
10
W2
X
L
B
R
G
Y
AUX. HT. RELAY
FAN RELAY
EM. HT. RELAY
B RELAY
M5987A
THERMOSTAT SUBBASE SYSTEM COMPONENTS
COMPRESSORCONTACTOR
EM. HT.
EM. HT.LED (RED)
AUX. HT.LED (GREEN)
H2
FALL
H2 ANTICIPATOR
3
5
W3
W1W3 RELAY
W1 RELAY
COOL CHANGEOVER VALVE
COMPRESSOR FAULT
E
O
6
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 178
Fig. 171. Schematic and hookup of T874J with Q674J. Used in heat pump applications.
Fig. 172. Schematic and hookup of T874H with Q674B. Used in heat pump applications.
H1FALL
C1 RISECO
L1 (HOT)L2
1
H1 ANTICIPATOR
OFF
EM. HT.
SYSTEMSWITCH
FANSWITCH
AUTO
ON
AUTO
EM. HT. LED(RED)
2
FAN RELAY
M5729
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.1
SYSTEM COMPONENTSSUBBASETHERMOSTAT
H2FALL
CO
RISE
3
4
5
6
8
9
10
11
12
EXTERNAL JUMPER SUPPLIED BY HONEYWELL.2
R
Y
G
F
C
E
X
P
O
W1
2
H2 ANTICIPATOR
C1 ANTICIPATOR
COMPRESSORCONTACTOR
O.D.T.
HCR1
HCR1
"X" RELAY
"P" RELAY
COOL CHANGEOVERVALVE
HCR2
HCR2 HCR3
H1
FALL
CO
RISE
L1 (HOT)L2
1
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1 ANTICIPATOR
C1 ANTICIPATOR SYSTEMSWITCH
FANSWITCH
AUTO
ON
OFF
HEAT
COOL
COOL CHANGEOVER VALVE
COMPRESSORCONTACTOR M1401
FAULTLED (RED)
CHECKFILTERLED (YELLOW)
FAN RELAY
12
11
10
9
8
4
3
2
G
R
O
2
C
3
Y
RISE
C1
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
179 60-2485�8
Fig. 173. Schematic and hookup of T874H with Q674C. Used in heat pump applications.
Fig. 174. Schematic and hookup of T874G with Q674J. Used in heat pump applications.
H1
FALL
CO
RISE
L1 (HOT)L2
1
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1 ANTICIPATOR
C1 ANTICIPATOR SYSTEMSWITCH
FANSWITCH
AUTO
ON
OFF
AUTO
COOL CHANGEOVER VALVE
COMPRESSORCONTACTOR M1400
FAULTLED (RED)
CHECKFILTERLED (YELLOW)
FAN RELAY
12
11
10
9
8
4
3
2
G
R
O
2
C
3
Y
RISE
C1
H1
FALL
H2
FALL
C1
RISE
C2
RISE
L1 (HOT)L2
1
1
2
2
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
REMOVABLE JUMPER.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
HA
CA
ODA
SYSTEMSWITCH
FANSWITCH
AUTO
ON
OFF
EM. HT.
AUTO
EM.. HT. RELAY
AUX. HT. RELAY
M1403
1
2
3
4
5
6
8
9
10
X2
G
T
R
F
W
U
B
O
Y
COMPRESSORCONTACTOR
COOL CHANGEOVER VALVE
"F" RELAY
C815AOUTDOORTHERMISTOR
FAN RELAY
EM. HT.LED (RED)
AUX. HT.LED (GREEN)
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 180
Fig. 175. Schematic and hookup of T874G with Q674J. Used in heat pump applications.
Fig. 176. Schematic and hookup of T874G with Q674C. Used in standard applications.
FALLL1 (HOT)
L2 1
O
G
R
W2
E
L
C
Y
2
4
6
8
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
1
THERMOSTAT SUBBASE SYSTEM COMPONENTS
FANSWITCH
AUTO
ON
SYSTEMSWITCH
SUPL. HT.
ON
OFF
M2112A
H1 ANTICIPATOR
D
COOLCHANGEOVER VALVEFAN RELAY
H.C.R. 1
H.C.R. 1 H.C.R.2
H.C.R. 2 H.C.R.3
COMPRESSORCONTACTOR
1
9
10
FALL
CORISE
C1 ANTICIPATOR
H2 ANTICIPATOR
C1RISEHEAT PUMP(GRN)
DEFROST(RED)
MANUAL(RED)AUTO
(YEL)
O.D.T.
H1
FALL
L1 (HOT)
L21
H1 ANTICIPATOR
2
OFF
AUTO
SYSTEMSWITCH
FAN SWITCH
ON
AUTO
FAN RELAY
M5730
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
SETBACK STAGE OFFSET 12°F (7°C) FROM H1 STAGE.
LEDS ON SOME MODELS.
1
SYSTEM COMPONENTSSUBBASETHERMOSTAT
SETBACK
FALL
CO
RISE
C1RISE
3
4
6
8
10
9
Y2
G
R
L
2
2
Y1
COMPRESSORCONTACTOR
OPEN-NIGHTCLOSED-DAY
C1 ANTICIPATOR
SETBACK RELAY
COOL CHANGEOVER VALVE
LEDX1
C
X2LED
3
3
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
181 60-2485�8
Fig. 177. Schematic and hookup of T874G,H with Q674C. Used in standard applications.
Fig. 178. Schematic and hookup of T874N with Q674F. Used in heat pump applications.
H1FALL
L1 (HOT)L2
1FALL
M114C
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
USE EITHER 'B' OR 'O' ONLY FOR SYSTEM CHANGEOVER. 0.8A AT 30 VAC MAXIMUM LOAD CURRENT.
SECOND STAGE HEAT MAKES 12oF (7oC) AFTER FIRST STAGE HEAT TO PROVIDE SETBACK
1
2
2
THERMOSTAT SUBBASE SYSTEM COMPONENTS
1
R2
R1
B
O
Y
G
FANSWITCH
AUTO
ON
SYSTEM SWITCH
RESET LED(RED)
OFF
AUTO
C1
H2
H1 ANTICIPATOR
FAN RELAY
COOL CHANGEOVER VALVE
HEAT CHANGEOVERVALVE
COMPRESSORCONTACTOR
C1 ANTICIPATOR
RISE
2
3
3
RISE
CO
4
6
7
8
9
10
LOCKOUT(RESET) RELAY
X
H2
FALL
C0
RISE
H1
FALL
M18623
H1 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.1
1
3
4
6
8
9
10
K
L
W2
R
G
W1
SYSTEMSWITCH
HEAT
EM.HT.
OFF
COOL
AUTO
ON
AUTO
FANSWITCH
SERVICELED (RED)
EM, HT. LED (YELLOW)
AUX.HT. RELAY
FAN RELAY
CHANGEOVER RELAY
COMPRESSOR RELAY
EM.HT. RELAY
C
X
THERMOSTAT SUBBASE SYSTEM COMPONENTS
L1 (HOT)L2
1
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 182
Fig. 179. Schematic and hookup of T874N with Q674F. Used in heat pump applications.
L1 (HOT)L2
1
W1
W2
EM. HT.LED (RED)
CHECKLED
(GREEN)
FAN RELAY
G
EM. HT. RELAY
COMPRESSOR CONTACTOR
Y
ESYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
H1ANTICIPATOR
H1
H2
H2ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED. M3686
FALL
R
RISE L
C1
HEAT RELAY 3
EM.HT. RELAYCONTACT
OUTDOORTHERMOSTAT
AUTO
ON
FAN SWITCH
X
W3
OPTIONAL COMPRESSORFAILURE DEVICE
DEFROST RELAY
REVERSING VALVE
EM.HT. RELAYCONTACT
HIGH PRESSURESWITCH
HEAT RELAY 1
HEAT RELAY 2
AUTO
FALL
CO
C1ANTICIPATOR
1
2
4
5
6
8
9
10
THERMOSTAT SUBBASE SYSTEM COMPONENTS
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
183 60-2485�8
Fig. 180. Schematic and hookup of T874A,D with Q674J. Used in heat pump applications.
H1
FALL
L1 (HOT)
L2
1
H1
FALL
C1
RISE
C2
RISE
M5957POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
FILTER LED ON SOME MODELS.
C2 ANTICIPATOR
C1 ANTICIPATOR
SYSTEMSWITCH
EM. HT.
AUTO
OFF
FILTERLED (YELLOW)
R-3
R-6
RANDOM STARTR-8 (OPT.)
R-5
R-5 T2
(HEAT PUMP OPERATION) R-10
(BIOLERLESSOPERATION ) R-11
EM. HT. RELAY
ELEC. HT. RELAYSTG. 2R-10
R-2
R-1
FAN RELAYR-6
OVERLOADR-6COMPRESSORCONTACTORR-8R-10
R-11
R-11 CHANGEOVER VALVE ELEC. HT.RELAY STG. 1
FAN DELAY RELAY
W1
Y1
G
R
W2
EM. HT.LED (RED)
E
X2
Y2
X1
1
4
6
8
9
10
11
H1ANTICIPATOR
1
2
2
H2 ANTICIPATOR
SYSTEM COMPONENTSSUBBASETHERMOSTAT
FANSWITCH
AUTO
ON
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 184
Fig. 181. Schematic and hookup of T874K with Q674C. Used in heat pump applications.
Fig. 182. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
FALL
CO
L1 (HOT)
L2
1
1
H2 FALL
H1
FALL
C1
RISE
2
3
6
8
9
10
Y
G
R
W
W2
A
COMPRESSORFAULT
REVERSINGVALVE
FAN RELAY
COMPRESSORRELAY
TIMECLOCK
FANSWITCH
AUTO
ON
SYSTEM SWITCH
OFF
AUTO
COMPRESSORFAULT LED (RED)C1
ANTICIPATOR
H1ANTICIPATOR
THERMOSTAT SUBBASE SYSTEM COMPONENT
M18587
4
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
FAN
SYSTEM SWITCH
COOL
HEAT
H1/C ANTICIPATOR
H1
FALL
M3951
AUTO
ON
FAN SWITCH
R
G
L
Y
X
H2E
W2
B
EM. HT.LED (YELLOW)
1
2
3
5
4
6
SERVICELED (RED)
COMPRESSOR
FALL
AUX. HT.
O
T
OUTDOOR RESET
EM. HT.
OFF
EM. HT.
W89HEATPUMPCONTROLPANEL
COOL/HEAT
H2 ANTICIPATOR
RESET
SERVICE LIGHT
EM. HT. LIGHT
THERMOSTAT SUBBASE SYSTEM COMPONENTS
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
185 60-2485�8
Fig. 183. Schematic and hookup of T874G with Q674J. Used in heat pump applications.
Fig. 184. Schematic and hookup of T874A,F with Q674G. Used in standard applications.
L1(HOT)
L2
1
FAN RELAY
SYSTEM SWITCH
OFF
EM. HT.
H1 ANTICIPATOR
H1
FALL
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
M3950
AUTO
ON
FAN SWITCH
R
G
CO
W
Y
X
H2
RISE
E
O
C1 ANTICIPATOR
C1
RISE
L1
EM. HT.LED (RED)
ON
1
2
4
6
8
9
10
AUX. HT.LED (GREEN)
COMPRESSORCONTACTOR
COMPRESSORFAILURE
FALL COOL CHANGEOVER VALVE
2BH
O. D. S.
1BH SH
1BH
H2 ANTICIPATOR
THERMOSTAT SUBBASE SYSTEM COMPONENTS
L1 (HOT)
L2
1
SYSTEM SWITCH
OFF
H1 ANTICIPATOR
H1
FALL
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED. M3953
RH
C1
Y1
H2
RISE
W1
C1 ANTICIPATOR
C2
RISE
AUTO
1
4
6
8
9
10
COMPRESSORCONTACTOR 2
FALL
HEAT RELAY 1
RC
Y211
C2ANTICIPATOR
W2
HEAT RELAY 2
COMPRESSORCONTACTOR 1
L1 (HOT)
L2
1
H2 ANTICIPATOR
THERMOSTAT SUBBASE SYSTEM COMPONENTS
NOFAN SWITCH
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 186
Fig. 185. Schematic and hookup of T874D with Q674E. Used in standard applications.
Fig. 186. Schematic and hookup of T874D with Q674G. Used in standard applications.
L1 (HOT)
L2
1
SYSTEM SWITCH
AUTO
H1 ANTICIPATOR
H1
FALL
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
M3954
RH
C1
Y1
H2
RISE
W1
C1 ANTICIPATOR
C2
RISE
COOL
1
4
6
8
9
10
COMPRESSORCONTACTOR 2
FALL
HEAT RELAY
RC
Y211
C2ANTICIPATOR
W2
HEAT RELAY 2
COMPRESSORCONTACTOR 1
L1 (HOT)
L2
1
AUTO
ON
FAN SWITCH
FAN RELAY
IGNITIONRELAYOFF
HEAT B
G
H2 ANTICIPATOR
THERMOSTAT SUBBASE SYSTEM COMPONENTS
L1 (HOT)
L2
1
SYSTEM SWITCH
OFF
H1 ANTICIPATOR
H1
FALL
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED. M3955
RH
C1
Y1
H2
RISE
W1
C1 ANTICIPATOR
C2
RISE
AUTO
1
4
6
8
9
10
COMPRESSORCONTACTOR 2
FALL
HEAT RELAY 1
RC
Y211C2ANTICIPATOR
W2
HEAT RELAY 2
COMPRESSORCONTACTOR 1
L1 (HOT)
L2
1
12
B
5
7FAN RELAY
O
FAN RELAY
H2 ANTICIPATOR
THERMOSTAT SUBBASE SYSTEM COMPONENTS
NOFAN SWITCH
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
187 60-2485�8
Fig. 187. Schematic and hookup of T874C with Q674B. Used in standard applications.
Fig. 188. Schematic and hookup of T874D with Q674G. Used in standard applications.
L2
1
SYSTEM SWITCH
OFF
H1 ANTICIPATOR
H1
FALL
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED. M3956
C
C1
R3
H2
RISE
R1
C1 ANTICIPATOR COOL
3
4
8
10
FALL
HEAT RELAY 1
R
R2
R5
HEAT RELAY 2
L1 (HOT)
X
5
HI SPEEDFAN RELAY
LO SPEEDFAN RELAY
HIGHTEMP.SWITCH
HIGHPRESSURE SWITCH
R4
HIGH
LOW
FAN SWITCH
2
HEAT
H2ANTICIPATOR
COOLCONTACTOR
LOCKOUTRELAY
LR
THERMOSTAT SUBBASE SYSTEM COMPONENTS
L1 (HOT)
L2
1
SYSTEM SWITCH
H1 ANTICIPATOR
H1
FALL
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
M3958
RH
C1
Y1
H2
RISE
W1
C1 ANTICIPATOR
C2
RISE
AUTO
1
4
6
8
9
10
COMPRESSORCONTACTOR 2
FALL
HEAT RELAY 1
RC
Y211C2ANTICIPATOR
W2
HEAT RELAY 2
COMPRESSORCONTACTOR 1
L1 (HOT)
L2
1
12
B
5
7
FAN RELAY
O
T
H2ANTICIPATOR
THERMOSTAT SUBBASE SYSTEM COMPONENTS
NOFAN SWITCH
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 188
Fig. 189. Schematic and hookup of T874F with Q674D. Used in standard applications.
Fig. 190. Schematic and hookup of T874C with Q674L. Used in heat pump applications.
H1
FALL
M3960
Y1
H2
W11
4
6
8
9
10
FALL
Y2
11
W2
RH
B
R
Y
L1
L2
RC
5 ANTICIPATOR
M839MOTOR
THERMOSTAT SUBBASE SYSTEM COMPONENTS
NOFAN SWITCH
NOSYSTEMSWITCH
L1(HOT)
L2
1
FAN RELAY
SYSTEM SWITCH
OFF
EM. HT.
H1 ANTICIPATOR
H1
FALL
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
OPTIONAL REMOVABLE JUMPER TO ALLOW SINGLE SYSTEM TRANSFORMER.
WIRE JUMPER FOR SERVICE LIGHT. M3978
AUTO
ON
FAN SWITCH
L
F
X
A
Y
H2
E
M
C1 ANTICIPATOR
C1
RISE EM. HT. LED (YELLOW)
HEAT
2
3
4
6
8
10
SERVICELED (RED)
COMPRESSORCONTACTOR
FALL
O. D. S.H2 ANTICIPATOR
THERMOSTAT SUBBASE SYSTEM COMPONENTS
COOL
OG
COOL CHANGEOVERVALVE
C815A OUTDOOR THERMISTOR
5
1
7
R
VR
V
EM. HT.
EM. HT. RELAY
IN STAT
HI PRSERVICE RELAY
ELEC. HT. RELAY
ELEC. HT. RELAY
RESET
2
3
3
2
1
L1(HOT)
L2
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
189 60-2485�8
Fig. 191. Schematic and hookup of T874R with Q674B. Used in heat pump applications.
Fig. 192. Schematic and hookup of T874D with Q674C. Used in standard applications.
L2
1
OFF
H1/C1 ANTICIPATORH1
FALL
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED. M3965
Z
H2W2
HEAT
2
4
6
FALL
AUX. HT. RELAY
"Z" RELAY
L1 (HOT)
R
FAN RELAY
Y
AUTO
CONT.
FANSWITCH
C
G
H2 ANTICIPATOR
3
COOL RELAY
COOL
THERMOSTAT SUBBASE SYSTEM COMPONENTS
SYSTEMSWITCH
C1 LO
HI
O
W1
HEAT RELAY
COOL CHANGE-OVER VALVE
L2
1
ON
H1 ANTICIPATOR
H1
FALL
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
MOMENTARY POSITION. SPRING RETURN TO "ON" UPON SWITCH RELEASE.M3959
C1
Y1
H2
RISE
W1
C1 ANTICIPATOR
C2RISE
AUTO
1
4
6
8
9
10
COMPRESSORCONTACTOR 2
FALL
HEAT RELAY 1
Y211
C2ANTICIPATOR
W2
HEAT RELAY 2
COMPRESSORCONTACTOR 1
L1 (HOT)
RFAN RELAY
O
AUTO
OFF
SERVICELED (RED)
FILTERLED (YELLOW)
X
A
G
O
2
2
MOMENTARYCIRCUIT
H2 ANTICIPATOR
THERMOSTAT SUBBASE SYSTEM COMPONENTS
FAN SWITCH
SYSTEMSWITCH
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 190
Fig. 193. Schematic and hookup of T874D with Q674E. Used in standard applications.
Fig. 194. Schematic and hookup of T874G with Q674F. Used in heat pump applications.
H1FALL
L1 (HOT) L2
1
RH
W1
W2
G
Y2
Y1
RC
HEAT RELAY 2
HEAT RELAY 1
OFF
HEAT
COOL
AUTO
AUTO
ON
SYSTEMSWITCH
H1 ANTICIPATOR
C1 ANTICIPATOR
FAN SWITCH
2
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED.
JUMPER RH, RC FOR SINGLE TRANSFORMER.
2
M3203B
L1 (HOT)
L2
1
FAN RELAY
O
CHANGEOVERRELAY (COOL)
CHANGEOVERRELAY (HEAT)
COMPRESSORCONTACTOR 2
COMPRESSORCONTACTOR 1
1
4
6
8
9
10
11
H2
FALL
C2 ANTICIPATOR
RISE
RISE
C1
C2
B
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H2 ANTICIPATOR
L1(HOT)
L2
1
FAN RELAY
SYSTEM SWITCH
OFF
EM. HT.
H1 ANTICIPATORH1
FALL
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED. M3977
AUTO
ON
FAN SWITCH
R
G
CO
C
W1
W2H2
RISE
E
Y1
C1 ANTICIPATOR
C1
RISE
EM. HT.LED (RED)
HEAT
2
3
4
6
8
9
10
CHECKLED (GREEN)
COOL CHANGEOVER VALVEFALL
DR
HBTH
TDR 1
H2 ANTICIPATOR
THERMOSTAT SUBBASE SYSTEM COMPONENTS
AUTO
COOL
TDR 2
X
HPA
COMPRESSORCONTACTOR
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
191 60-2485�8
Fig. 195. Schematic and hookup of T874G with Q674F. Used in heat pump applications.
Fig. 196. Schematic and hookup of T874G with Q674J. Used in heat pump applications.
H1
FALL
O
G
R
E
L
X
W2
FAN RELAY
COOLCHANGEOVERVALVE
EM. HT.
OFF
AUTO
SYSTEMSWITCH
H1 ANTICIPATOR
C1 ANTICIPATOR
AUTO
ON
FAN SWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
M2974
B
EM. HT.RELAY
COMPRESSORCONTACTOR
AUX. HT. RELAY
1
4
6
8
9
10
H2
FALL
RISE
RISE
CO
C1
"B" RELAY
L1 (HOT)L2
1
H2 ANTICIPATOR
2
EM. HT. LED(RED)
Y
AUX.HT. LED(GREEN)
COOL
HEAT
THERMOSTAT SUBBASE SYSTEM COMPONENTS
COMPRESSOR FAULT
H1
FALL
O
G
R
E
L
W2
FAN RELAY
COOLCHANGEOVERVALVE
OFF
ON
SYSTEMSWITCH
H1 ANTICIPATOR
C1 ANTICIPATOR
AUTO
ON
FAN SWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
M2975COMPRESSORCONTACTOR
O.D.T.
1
4
6
8
9
10
H2
FALL
RISE
RISE
CO
C1
L1 (HOT)L2
1
H2 ANTICIPATOR
2
SUPL. HT.LED(RED)
Y
SUPL. HT.
H.C.R.1
H.C.R.1
H.C.R.2
H.C.R.2
H.C.R.3C
THERMOSTAT SUBBASE SYSTEM COMPONENTS
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 192
Fig. 197. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
Fig. 198. Schematic and hookup of T874L with Q674E. Used in standard applications.
H1
FALL
C1
L1 (HOT)L2
1
G
W
U
B
F
R
T
X2
O
Y
FAN RELAY
AUX. HEATERRELAY
COMPRESSORMONITOR
OUTDOORTHERMOSTAT
OUTDOORTHERMISTOR
COOL CHANGEOVERVALVE
COMPRESSORRELAY
AUX. HT.LED (GREEN)
EM. HT.LED (RED)
1
2
3
4
5
6
11
FANSWITCH
AUTO
ON
EM. HT.
HEAT
OFF
COOL
SYSTEMSWITCH
H2
FALL
POWER SUPPLY. PROVIDE DISCONNECT MEANS ANDOVERLOAD PROTECTION AS REQUIRED.
FIELD REMOVABLE JUMPER.
1
2
2
M2970
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1
FALL
W1
Y1
W2
COMPRESSORCONTACTOR
HEAT
AUTO
COOL
SYSTEMSWITCH
H1 ANTICIPATOR AUTO
ON
FANSWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.M2976
R
STAGE 2HEAT RELAY
1
4
6
7
9
10
H2
FALL
C2 ANTICIPATOR
RISEC1
STAGE 1 HEAT RELAY
L1 (HOT)L2
1
H2 ANTICIPATOR
G
FAN RELAY
3
8
OFF
THERMOSTAT SUBBASE SYSTEM COMPONENTS
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
193 60-2485�8
Fig. 199. Schematic and hookup of T874G with Q674F. Used in heat pump applications.
Fig. 200. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
H1
FALL
O
G
R
E
X
FAN RELAY
W3 RELAY
EM. HT.
OFF
AUTO
SYSTEMSWITCH
H1 ANTICIPATOR
C1 ANTICIPATOR
AUTO
ON
FAN SWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED. M2977
B
COMPRESSORCONTACTOR
AUX. HT. RELAY4
5
8
9
10
H2
FALL
RISE
C1
L1 (HOT)L2
1
H2 ANTICIPATOR
2
CHECKLED(RED)
Y
AUX. HT. LED(GREEN)
COOL
HEAT
W3
W2
EM. HT. RELAY
COMPRESSORFAULT
L
HEAT CHANGEOVERVALVE
COOL CHANGEOVERRELAY
3
11
12
CO
RISE
EM. HT. LED (RED)
THERMOSTAT SUBBASE SYSTEM COMPONENTS
T
G
R
Z
X
W1
FAN RELAY
EM. HT.
OFF
SYSTEMSWITCH
AUTO
ON
FAN SWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED. M2978
COMPRESSORCONTACTOR
SERVICE
1
3
6
11
L1 (HOT)L2
1
2
SERVICE LED(YELLOW)
Y
EM. HT.LED (RED)COOL
HEAT
W2
OUTDOORTHERMOSTAT
SEQ 2
K
SEQ 1
HEAT CHANGEOVER VALVE
H2 ANTICIPATORRISE
H2
H1C1
FALL
4
5C1 ANTICIPATOR
12H1 ANTICIPATOR
THERMOSTAT SUBBASE SYSTEM COMPONENTS
OUTDOORTHERMOSTAT
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 194
Fig. 201. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
Fig. 202. Schematic and hookup of T874D with Q674G. Used in standard applications.
T
G
R
Z
X
W1
FAN RELAY
EM. HEAT
OFF
SYSTEMSWITCH
AUTO
ON
FAN SWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED. M2979
COMPRESSORCONTACTOR
SERVICE
1
3
6
11
L1 (HOT)L2
1
2
SERVICE LED(YELLOW)
Y
EM. HT.LED (RED)COOL
HEAT
W2
OUTDOORTHERMOSTAT SEQ 2
K
SEQ 1
HEAT CHANGEOVER VALVE
H2ANTICIPATOR
RISE
H2
H1C1
RISE
4
5C1 ANTICIPATOR
12H1 ANTICIPATOR
RESET
THERMOSTAT SUBBASE SYSTEM COMPONENTS
C815AOUTDOORTHERMISTOR
OUTDOORTHERMOSTAT
H1
FALL
W1
W2
T
RC
RH
O
FAN RELAY B
HEAT RELAY 1
AUTO
OFF
SYSTEMSWITCH
H1 ANTICIPATOR
C1 ANTICIPATOR
NOFANSWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED M2980
THERMOSTAT SUBBASE SYSTEM COMPONENTS
L1 (HOT)L2
1
COMPRESSORCONTACTOR 2
COMPRESSORCONTACTOR 1
1
4
6
7
9
10
12
H2
FALL
C2 ANTICIPATOR
RISE
RISE
C1
C2
Y1
Y2
HEAT RELAY 2
L1 (HOT)L2
1
H2 ANTICIPATOR
A2
"T" RELAY
B
FAN RELAY O
A15
8
11
SERVICELED (RED)
SERVICELED (RED)
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
195 60-2485�8
Fig. 203. Schematic and hookup of T874L with Q674C. Used in heat pump applications.
Fig. 204. Schematic and hookup of T874D with Q674F. Used in standard applications.
CO
FALL
Y
R
W
OFF
SYSTEMSWITCH
C1 ANTICIPATOR
AUTO
ON
FAN SWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
M2981
THERMOSTAT SUBBASE SYSTEM COMPONENTS
4
6
8
9
10
H1
FALL
RISEC1
H1 ANTICIPATOR
2
COMP.FAULT(RED)
AUTO
COMPRESSORCONTACTOR
L1 (HOT)L2
1
G
FAN RELAY
W2
HEAT CHANGEOVERVALVE
A
COMPRESSORFAULT
3
H1
FALL
W1
G
W2
B
HEAT RELAY 1
HEAT
OFF
COOL
SYSTEMSWITCH
H1 ANTICIPATOR
C1 ANTICIPATOR
AUTO
ON
FANSWITCH
1
2
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
LED IS NOT LABELED. JUMPER W2 TO X FOR AUXILIARY HEAT INDICATION. JUMPER E TO X FOREMERGENCY HEAT INDICATION. CONNECT SYSTEM MONITOR TO X TO IDENTIFY WHEN SYSTEMNEEDS TO BE CHECKED.
M2982A
THERMOSTAT SUBBASE SYSTEM COMPONENTS
R
EM. HT. RELAY
COMPRESSORCONTACTOR 2
COMPRESSORCONTACTOR 1
1
4
6
8
9
10
11
H2
FALL
C2 ANTICIPATOR
RISE
RISE
C1
C2
Y1
Y2
HEAT RELAY 2
L1 (HOT)L2
1
2LED(RED)
H2 ANTICIPATOR
AUTO
EM. HT.
X
E
FAN RELAY
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 196
Fig. 205. Schematic and hookup of T874H with Q674C. Used in heat pump applications.
Fig. 206. Schematic and hookup of T874J with Q674J. Used in heat pump applications.
H1
FALL
G
R
X1
L
Y2
OFF
AUTO
SYSTEMSWITCH
H1 ANTICIPATOR
C1 ANTICIPATOR
AUTO
ON
FAN SWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
LEDS ON SOME MODELS.
M2983
THERMOSTAT SUBBASE SYSTEM COMPONENTS
4
6
8
9
10
RISE
RISE
CO
C1
2
LED(RED)
Y1
C
FAN RELAY
COMPRESSORCONTACTOR
L1 (HOT)L2
1
3
X2
LED(RED)
2
2
COOL CHANGEOVERVALVE
H1
FALL Y
G
R
E
L
W2
FAN RELAY
COMPRESSORCONTACTOR
OFF
ON
SYSTEMSWITCH
H1 ANTICIPATOR
C1 ANTICIPATOR
AUTO
ON
FAN SWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
M2984
THERMOSTAT SUBBASE SYSTEM COMPONENTS
COOLCHANGEOVERVALVE
O.D.T.
4
6
8
9
10
H2
FALL
RISECO
L1 (HOT)L2
1
H2 ANTICIPATOR
SUPL. HT.LED (RED)
O
H.C.R.1
H.C.R.1
H.C.R.2
H.C.R.2
H.C.R.3
C
2
3
5
11
12
C1 CO
SUPL. HT.
RISE
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
197 60-2485�8
Fig. 207. Schematic and hookup of T874J with Q674L. Used in heat pump applications.
Fig. 208. Schematic and hookup of T874D with Q674D. Used in standard applications.
H1
FALL Y
G
R
E
L
W2
FAN RELAY
COMPRESSORCONTACTOR
OFF
COOL
SYSTEMSWITCH
H1 ANTICIPATOR
C1 ANTICIPATOR
AUTO
ON
FAN SWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
M2985
THERMOSTAT SUBBASE SYSTEM COMPONENTS
COOL CHANGEOVERVALVE
O.D.T.
4
6
8
9
10
H2
FALL
RISECO
L1 (HOT)L2
1
H2 ANTICIPATOR
SUPL. HT.LED (RED)
O
H.C.R.1
H.C.R.1
H.C.R.2
H.C.R.2
H.C.R.3
C
2
3
5
11
12
C1 CO
SUPL. HT.
RISE
HEAT
H1
FALL
W1
W2
HEAT RELAY 1
H1 ANTICIPATOR
C1 ANTICIPATOR 1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
RC-RH REMOVABLE JUMPER WHEN SPECIFIED.M2986
THERMOSTAT SUBBASE SYSTEM COMPONENTS
COMPRESSORCONTACTOR 2
COMPRESSORCONTACTOR 1
1
5
6
8
9
10
11
H2
FALL
C2 ANTICIPATOR
RISE
RISE
C1
C2
Y1
Y2
HEAT RELAY 2
L1 (HOT)L2
1
H2 ANTICIPATOR
L1 (HOT)
L2
1
RC
RH
2
4
NOFANSWITCH
NOSYSTEMSWITCH
2
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 198
Fig. 209. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
Fig. 210. Schematic and hookup of T874Y with Q674E. Used in heat pump applications.
L
EM. HEAT
OFF
SYSTEMSWITCH
AUTO
ON
FAN SWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
3
6
2
AUX. HT. LED(GREEN)
Y
EM. HT.LED (RED)
COOL
HEAT
H2 ANTICIPATOR
RISE
H2
H1C1
FALL
4
H1/C1ANTICIPATOR
G
W2
B
R
EM. HT. RELAY
COOLCHANGEOVERVALVE
COMPRESSORCONTACTOR
’"B" RELAY
EM. HT.RELAY
L1 (HOT)L2
1
X
E
FAN RELAY
AUX. HT. RELAY
O
M2987
H1
FALLG
B
HEAT
OFF
COOL
SYSTEMSWITCH
H1 ANTICIPATOR
C1 ANTICIPATOR
AUTO
ON
FANSWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.M2988
THERMOSTAT SUBBASE SYSTEM COMPONENTS
R
COMPRESSORCONTACTOR 2
COMPRESSORCONTACTOR 1
1
3
6
8
9
10
11
H2
FALL
C2 ANTICIPATOR
RISE
RISE
C1
C2
Y1
Y2
L1 (HOT)L2
1
FILTERLED(YELLOW)
H2 ANTICIPATOR
AUTO
FAN RELAY
HCO
FALL
CCO
2
4
O
L
F
COOLCHANGEOVERVALVE
HEATCHANGEOVERVALVE
RESETLED(RED)
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
199 60-2485�8
Fig. 211. Schematic and hookup of T874G with Q674F. Used in standard applications.
Fig. 212. Schematic and hookup of T874A with Q674E. Used in standard applications.
H1
FALLG
R
L
X
W2
FAN RELAY
W1 RELAY
EM. HT.
OFF
AUTO
SYSTEMSWITCH
H1 ANTICIPATOR
C1 ANTICIPATOR
AUTO
ON
FAN SWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.M2989
THERMOSTAT SUBBASE SYSTEM COMPONENTS
W1
COMPRESSORFAULT
AUX. HT. RELAY
3
4
6
8
10
H2
FALL
RISEC1
L1 (HOT)L2
1
H2 ANTICIPATOR
2
EM. HT. LED (RED)
Y1
AUX. HT. LED(GREEN)
COOL
HEAT
COMPRESSORCONTACTOR
H1
FALL
W1
W2
HEAT RELAY 1
H1 ANTICIPATOR
C1 ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
RC -RH REMOVABLE JUMPER WHEN SPECIFIED.M2990
THERMOSTAT SUBBASE SYSTEM COMPONENTS
COMPRESSORCONTACTOR 2
COMPRESSORCONTACTOR 1
1
6
8
9
10
11
H2
FALL
C2 ANTICIPATOR
RISE
RISE
C1
C2
Y1
Y2
HEAT RELAY 2
L1 (HOT)L2
1
H2 ANTICIPATOR
L1 (HOT)
L2
1
RC
RH
24
2
G
FAN RELAY
HEAT
AUTO
COOL
SYSTEMSWITCH
AUTO
ON
FANSWITCH
OFF
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 200
Fig. 213. Schematic and hookup of T874L with Q674C. Used in heat pump applications.
H1
FALL
Y
H1
R
LCOMPRESSORCONTACTOR
RELAY 1 N.O. 2
HIGH
ON
SYSTEMSWITCH
H1 ANTICIPATOR
C1 ANTICIPATOR
AUTO
OFF
FAN SWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
M2991
THERMOSTAT SUBBASE SYSTEM COMPONENTS
COOL CHANGEOVERVALVE
4
1
8
9
10
H2
FALL
RISE CO
L1 (HOT)L2
1
H2 ANTICIPATOR
CHECKLED (RED)
C
2
3
5
LO
MED
COMPRESSORCONTACTOR
S1RELAY
S1RELAY N.C.
H2
AUX. HT. RELAY
R1 RELAY N.C. 1
R1 RELAY
K1 RELAY
G1K2 RELAY
G2
R2 RELAY N.O 1
7
O
FIELDREMOVABLEJUMPER
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
201 60-2485�8
Fig. 214. Schematic and hookup of T874A with Q674B. Used in standard applications.
H1
R
L
COMPRESSORCONTACTOR
HIGH
ON
SYSTEMSWITCH
COOL
OFF
FAN SWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
M2992
THERMOSTAT SUBBASE SYSTEM COMPONENTS
COOL CHANGEOVERVALVE4
1
L1 (HOT)L2
1
CHECKLED (RED)
O
2
3
5
LO
MED
AUX. HT. RELAY
R1 RELAY
K1 RELAY
G1K2 RELAY
G2
R2 RELAY N.O. 1
HEAT
C
Y
COMPRESSORCONTACTOR
H1
FALL
H1 ANTICIPATOR
C1 ANTICIPATOR
C1
RISE
S1 RELAY N.C.11
12
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 202
Fig. 215. Schematic and hookup of T874L with Q674B. Used in heat pump applications.
H1
FALL
Y
H1
R
LCOMPRESSORCONTACTOR
RELAY 1 N.O. 2
HIGH
ON
SYSTEMSWITCH
H1 ANTICIPATOR
C1 ANTICIPATOR
COOL
OFF
FAN SWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
M2993
THERMOSTAT SUBBASE SYSTEM COMPONENTS
COOL CHANGEOVERVALVE
4
1
8
9
10
H2
FALL
RISE C1
L1 (HOT)L2
1
H2 ANTICIPATOR
CHECKLED (RED)
C
2
3
5
LO
MED
COMPRESSORCONTACTOR
S1RELAY
S1RELAY N.C.
H2
AUX. HT. RELAY
R1 RELAY N.C. 1
R1 RELAY
K1 RELAY
G1K2 RELAY
G2
R2 RELAY N.O. 1
7
O
FIELDREMOVABLEJUMPER
HEAT
11
12
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
203 60-2485�8
Fig. 216. Schematic and hookup of T874G with Q674J. Used in heat pump applications.
Fig. 217. Schematic and hookup of T874N with Q674C. Used in heat pump applications.
H1
FALL
H2
FALL
CO
RISE
C1RISE
L1 (HOT)
L2
1
2
1
2
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
REMOVE JUMPER FOR INDEPENDENT CONTROL OF W1 AND E TERMINALS.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H1 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
SYSTEMSWITCH
FANSWITCH
AUTO
ON
OFF
EM. HT.
AUTO
EM. HT.RELAY
COOL CHANGEOVERVALVE
COMPRESSORCONTACTOR
M1629
1
2
4
6
8
9
10
Y
C
X
E
W1
R
G
O
AUX. HT.LED (YELLOW)
CHECKLED (RED)
SYSTEMLED(GREEN)
4R
HPS 4R
5R4R
4R
SEQ 1
SEQ 23R
FAN RELAY
M5900
L1 (HOT)
L2
1
Y
L
X
W2
W3
R
ODT
EHR
HEAT CHANGEOVER VALVE
EHR
COMPRESSORCONTACTOR
OPTIONAL COMPRESSOR FAILURE
CHECK LED (GREEN)
FAN SWITCH
ON
AUTO
SYSTEMSWITCH
OFF
AUTO
H2
FALL
H1
FALL
1
4
5
6
H1 ANTICIPATOR
H2ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
C1
RISE
8
9
C1 ANTICIPATOR
W1
D. P.
G
HEAT CONTACTOR #2
FAN RELAY
2
10
CO
HEAT CONTACTOR #3
HEAT CONTACTOR #1
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 204
Fig. 218. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
L1 (HOT)
L2
1
X
L
W2
EM. HT.LED (RED)
AUX. HT.LED (GRN)
AUX. HT.RELAY
FAN RELAY
"B" RELAY
G
COOL CHANGEOVERVALVE
EM. HT. RELAY
COMPRESSOR CONTACTOR
O
Y
E
B
SYSTEMSWITCH
EM. HT.
HEAT
OFF
COOL
H1/C1ANTICIPATOR
C1H1
FALL
H2
W3
AUX. HT.RELAY
H2ANTICIPATOR
1
2
3
2
3
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
TERMINAL LABELED C/X ON SOME MODELS.
W3 TERMINAL AVAILABLE ON SOME MODELS ONLY.
M3683A
AUTO
ON
FANSWITCH
FALL
R
2
3
4
6
THERMOSTAT SUBBASE SYSTEM COMPONENTS
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
205 60-2485�8
Fig. 219. Schematic and hookup of T874C with Q674C. Used in standard applications.
M5901
L1 (HOT)
L2 1
FAN RELAYSERVICELED (RED)
FAN SWITCH
OFF
AUTO
SYSTEMSWITCH
AUTOC1
FALL
H1
FALL 2
4
8
H1 ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
MOMENTARY POSITION. SPRING RETURN TO "ON" UPON SWITCH RELEASE.
H2 OFFSET 12oF FROM H1.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
ON
COMPRESSOR CONTACTOR 1
H2
RISE
10
MONENTARY CIRCUIT
H2ANTICIPATOR
HEAT RELAY 1
HEAT RELAY 2
1
6
2
2
9
CONTROL MODULE
A
W2
W1
O
G
Y1
R
W3
Y25
73
3
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 206
Fig. 220. Schematic and hookup of T874W with Q674C. Used in standard applications.
Fig. 221. Schematic and hookup of T874H with Q674C. Used in heat pump applications.
M5929
H1
FALL
L1 (HOT)
L21
THERMOSTAT SUBBASE SYSTEM COMPONENTS
1
4
6
8
9
10
FANSWITCH
SYSTEMSWITCH
AUTO
OFF
ON
AUTO
SERVICELED (RED)
COMPRESSOR CONTACTOR #2
HEAT RELAY #2
FAN RELAY
COMPRESSOR CONTACTOR #1
HEAT RELAY #3
H1 ANTICIPATOR
H2 ANTICIPATOR
C1
C2RISE
RISE
FALL
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
MOMENTARY POSITION. SPRING RETURN TO "ON" UPON SWITCH RELEASE.
1
CONTROL MODULE
H2
W3
Y1
G
R
W2
Y2
O
2
HEAT RELAY #1
W1
A
MOMENTARY CIRCUIT
7
2
2
5
FALLH3SYSTEM MONITOR
M5902
L1 (HOT)
L2
1
Y2
X
R
COOL CHANGEOVER VALVEFAN SWITCH
ON
AUTO
SYSTEMSWITCH
OFF
AUTO
H1
FALL
2
4
H1 ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
C1 RISE
8
9
C1 ANTICIPATOR
3
10
CO
RISE
O
Y1
G
FAN RELAY
X2
C
X1
FILTER LED (RED)
SERVICELED (YELLOW)
COMPRESSORCONTACTOR
B
24 VAC
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
207 60-2485�8
Fig. 222. Schematic and hookup of T874B with Q674E. Used in standard applications.
Fig. 223. Schematic and hookup of T874S with Q674F. Used in heat pump applications.
M5920
L1 (HOT)
L2
1
C
W
R
FAN RELAY
COMPRESSORCONTACTOR 2
HEAT RELAYMALFUNCTIONLED (RED)
LOW SPEEDLED (GREEN)
FAN SWITCH
ON
AUTO
SYSTEMSWITCH
HEAT
AUTO
COOL
C1
RISE
H1
FALL2
3
4
8
H1 ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
SUBBASE SYSTEM COMPONENTS
Y2
Y1
OFF
COMPRESSORCONTACTOR 1
C2
RISE
9
10
11
C2ANTICIPATOR
C1ANTICIPATOR
L
G
HIGH SPEEDLED (YELLOW)
SYSTEMMONITOR
THERMOSTAT
M5923
L1 (HOT)
L2
1
C
E
R
FAN RELAY
COMPRESSORCONTACTOR 2
EM.HT. RELAYMALFUNCTIONLED (RED)
LOW SPEEDLED (GREEN)
SYSTEMSWITCH
HEAT
AUTO
COOL
C2
RISE
H1 FALL
2
3
4
8
H1 ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
Y2
Y1
OFF
COMPRESSORCONTACTOR 1
CO
RISE
9
10
11
C2ANTICIPATOR
C1ANTICIPATOR
L
G
HIGH SPEEDLED (YELLOW)
5
OCOOL CHANGEOVER VALVE
AUX. HT. RELAY
W2
AUX. HT.LED (RED)
7
RISEC1
EM. HT.
FAN SWITCH
ON
AUTO
H2
FALL
H2 ANTICIPATOR
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 208
Fig. 224. Schematic and hookup of T874A,D with Q674E. Used in standard applications.
M5927
H1
FALL
L1 (HOT)L2
1
L1 (HOT)L2
1
THERMOSTAT SUBBASE SYSTEM COMPONENTS
1
4
6
8
9
10
11
FANSWITCH
SYSTEMSWITCH
AUTO
ON
OFF
HEAT
AUTO
COOL
SERVICELED (RED)
COOL CHANGEOVER VALVE
COMPRESSOR CONTACTOR #2
HEAT RELAY #2
FAN RELAY
COMPRESSOR CONTACTOR #1
HEAT CHANGEOVER VALVE
HEAT RELAY #1
H1 ANTICIPATOR
H2 ANTICIPATOR
C1
C2 RISE
RISE
FALL
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.1
CONTROL MODULE
H2
B
W1
Y1
G
RC
W2
RH
A
Y2
O
SYSTEM MONITOR
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
209 60-2485�8
Fig. 225. Schematic and hookup of T874D with Q674C. Used in standard applications.
M5928
H1
FALL
THERMOSTAT SUBBASE SYSTEM COMPONENTS
1
4
6
8
9
10
11
FANSWITCH
SYSTEMSWITCH
AUTO
ON
OFF
AUTO
SERVICELED (RED)
COOL DAMPER
COMPRESSOR CONTACTOR #2
HEAT RELAY #2
FAN RELAY
COMPRESSOR CONTACTOR #1
HEAT DAMPER
HEAT RELAY #1
H1 ANTICIPATOR
H2 ANTICIPATOR
C1
C2 RISE
RISE
FALL
CONTROL MODULE
H2
B
W1
Y1
G
RC
W2
A
Y2
O
RHL1 (HOT)
L21
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.1
SYSTEM MONTIOR
L1 (HOT)
L21
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 210
Fig. 226. Schematic and hookup of T874G with Q674G. Used in standard applications.
M5930
H1
FALL
L1 (HOT)L2
1
L1 (HOT)
L21
THERMOSTAT SUBBASE SYSTEM COMPONENTS
1
4
6
8
9
10
11
SYSTEMSWITCH
OFF
AUTO
SERVICELED (RED)
FAN RELAY O
COMPRESSOR CONTACTOR #2
HEAT RELAY #2
T RELAY
COMPRESSOR CONTACTOR #1
FAN RELAY B
HEAT RELAY #1
H1 ANTICIPATOR
H2 ANTICIPATOR
C1
C2
RISE
RISE
FALL
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.1
CONTROL MODULE
H2
B
W1
Y1
T
RC
W2
RH
A1
Y2
O
5
7
12
A2SERVICELED (RED)
NO FANSWITCH
SYSTEM MONITOR
SYSTEM MONITOR
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
211 60-2485�8
Fig. 227. Schematic and hookup of T874G with Q674F. Used in heat pump applications.
CO(HEAT)
FALL
H2
FALL
RISE
H1FALL
L1 (HOT)
L21
2
1
2
RISEC1
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
W1 - Y1 JUMPER IS Y TERMINAL; REMOVE JUMPER WHEN W1 RELAY IS USED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
M1230B
1
2
3
4
5
6
8
9
10
11
Y1
W1
B
O
X
X1
E
W2
R
G
W3
X2
W3 RELAY
FAN RELAY
AUX. HT. RELAY
EM. HT.RELAY
COMPRESSORFAULT
CHECKLED (RED)
AUX.HT. LED(GREEN)
EM. HT.LED (RED)
SYSTEMSWITCH
OFF
EM. HT.
HEAT
AUTO
COOLCOOL CHANGEOVERRELAY
HEAT CHANGEOVERRELAYW1 RELAY
COMPRESSORCONTACTOR
C1 ANTICIPATOR
CO(COOL)
H2 ANTICIPATOR
H1 ANTICIPATOR
FANSWITCH
AUTO
ON
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 212
Fig. 228. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
H1 FALLC1
L1 (HOT)
L2
1
1
2
2
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
REMOVABLE JUMPER (INSTALLED).
THERMOSTAT SUBBASE SYSTEM COMPONENTS
H2FALL
H1/C1 ANTICIPATOR
H2 ANTICIPATOR
RESET
EM. HT.
HEAT
OFF
COOL
AUX. HT.LED (GREEN)
EM. HT.LED (YELLOW)
C815A OUTDOOR THERMISTOR
COOL CHANGEOVERVALVE
ELECTRICHEAT RELAY
ELECTRICHEAT RELAY
EM. HT.
O.D.S.
SERVICE
EM. HT. RELAY
FAN RELAY
COMP. RELAY O.L. IN. STAT. HI. PRO.AUTO
ON
M3259
1
2
3
4
5
6
11
12
O
T
C
E
W1
L
G
Y1
R
SENSORLED (RED)
SYSTEMSWITCH
FANSWITCH
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
213 60-2485�8
Fig. 229. Schematic and hookup of T874G with Q674F. Used in heat pump applications.
Fig. 230. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
H1 FALL
H2FALL
CO
RISE
C1
RISE
L1 (HOT)L2
1
2
1
2
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
REMOVABLE JUMPER (INSTALLED).
THERMOSTAT SUBBASE SYSTEM COMPONENTS
O.D.S.
H1 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
SYSTEMSWITCH
FANSWITCH
AUTO
ON
EM. HT.
OFF
HEAT
AUTO
COOL
ELECTRICHT. RELAY
ELECTRICHT. RELAY
M3264
1
2
3
4
5
6
8
9
10
11O
T
C
E
W1
L
G
Y1
R
EM. HT. RELAY
EM. HT.
EM. HT.LED (YELLOW)
RESET
COMP. RELAY O.L. IN. STAT. HI. PRO
FAN RELAY
SERVICE
C815A OUTDOOR THERMISTOR
COOL CHANGEOVERVALVE
AUX. HT.LED (GREEN)
SERVICELED (RED)
H2
FALL
H1
FALLC
L1 (HOT)
L2
1
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
M5068
H1ANTICIPATOR
C ANTICIPATOR
H2ANTICIPATOR
11
6
5
4
3
2
1
FANSWITCH
AUTO
ON
SYSTEMSWITCH
EM .HT.
HEAT
OFF
COOL
AUX. HT.LED(GREEN)
EM. HT.LED (RED)
Y
B
X
E
W2
R
G
L
O
W3
W3 RELAY
COOL CHANGEOVER VALVE
COMPRESSORMONITOR
FAN RELAY
AUX. HT. RELAY
EM. HT. RELAY
HEAT CHANGEOVER VALVE
COMPRESSORRELAY
CHECK LED (RED)
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 214
Fig. 231. Schematic and hookup of T874G with Q674F. Used in heat pump applications.
Fig. 232. Schematic and hookup of T874D with Q674G. Used in standard applications.
C1 RISE
H2 FALL
H1
FALL
H1
RISE
CO
L1 (HOT)
L2
1
2
1
2
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
ONLY TERMINAL B OR O TO BE USED. 0.8A MAX.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
SYSTEMSWITCH
FANSWITCH
AUTO
ON
OFF
EM. HT.
HEAT
AUTO
COOL
FAN RELAY
EM. HT. RELAY
AUX. HT. RELAY
COOL CHANGEOVERVALVE
HEAT CHANGEOVERVALVE
COMPRESSORFAULT
H1ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
M5152
COMPRESSORRELAY
W3 RELAY
AUX. HT.LED (GREEN)
O
L
EM. HT.LED (RED)
G
R
E
X
W2
B
W3
Y12
11
10
9
5
4
3
2
8
L1 (HOT)
L2
1
SYSTEM SWITCH
OFF
H1 ANTICIPATOR
H1
FALL
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED. M3957
RH
C1
Y1
H2
RISE
W1
C1 ANTICIPATOR
C2
RISE
AUTO
1
4
6
8
9
10
COMPRESSORCONTACTOR 2
FALL
HEAT RELAY 1
RC
Y211C2ANTICIPATOR
W2
HEAT RELAY 2
COMPRESSORCONTACTOR 1
L1 (HOT)
L2
1
12
B
5
7
FAN RELAY
O
T
H2ANTICIPATOR
THERMOSTAT SUBBASE SYSTEM COMPONENTS
NO FAN SWITCH
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
215 60-2485�8
Fig. 233. Schematic and hookup of T874W with Q674L. Used in heat pump applications.
Fig. 234. Schematic and hookup of T874G with Q674B. Used in heat pump applications.
FAN
SYSTEM SWITCH
COOL
HEAT
H1 ANTICIPATOR
H1
FALL
M3952
AUTO
ON
FAN SWITCH
R
G
L
Y
X
H3
E
W2
B
EM. HT.LED (YELLOW)
1
2
3
5
4
6
SERVICELED (RED)
COMPRESSORLOW SPEED
FALL
AUX. HT.
O
Y1
COMPRESSORHIGH SPEED
EM. HT.
OFF
EM. HT.
W89HEATPUMPCONTROLPANEL
COOLCHANGEOVER
H2 ANTICIPATOR
H3 ANTICIPATOR
SERVICE LIGHT
EM. HT. LIGHT
T
OUTDOOR RESET
8
9
11
10
12
FALL
C2 ANTICIPATOR
C1ANTICIPATOR
RISE
H2
C1
C2
RESET
THERMOSTAT SUBBASE SYSTEM COMPONENTS
RISE
L2
1
OFF
H1 ANTICIPATOR
H1
FALL
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED. M3961
CO
Y1
H2
RISE
W1
C1 ANTICIPATOR
C1RISE
HEAT
1
4
6
8
9
10
FALL
AUX. HT. RELAY
COMPRESSORCONTACTOR
L1 (HOT)
R
FAN RELAY
O
AUTO
ON
FANSWITCH
AUX. HEATLED (RED)
C
G
H2 ANTICIPATOR
2
COOL CHANGEOVERVALVE
COOL
THERMOSTAT SUBBASE SYSTEM COMPONENTS
SYSTEMSWITCH
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 216
Fig. 235. Schematic and hookup of T874G and Q674F. Used in heat pump applications.
Fig. 236. Schematic and hookup of T874A-D with Q674C. Used in standard applications.
H2FALL
L1 (HOT)
L2 1
R
W2
X
L
G
O
E
Y
RTD1 OTD1
EHR1
ODT2
EHR2
RTD2
RTD3
RTD1
SYSTEMMONITOR
FANRELAY
RD
COOL CHANGEOVER VALVE
EM. HT.RELAY
LACO
COMPRESSORCONTACTOR
CHP
2
3
4
5
8
9
10
H1 FALL
H1 ANTICIPATOR
H2ANTICIPATOR
CHANGEOVER
RISE
C1RISE
C1ANTICIPATOR
OFF
COOL
AUTO
HEAT
EM. HT.
SYSTEMSWITCH
AUTO
ON
FANSWITCH
AUX. HT.LED (GRN)
EM. HT.LED (RED)
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED.
1 M7064
THERMOSTAT SUBBASE SYSTEM COMPONENTS
Y1
RC
1
1
1
M7570
THERMOSTAT SUBBASE SYSTEM COMPONENTS
B
Y2
W2
RH
A
H1 ANTICIPATOR
H2 ANTICIPATOR
C1
RISE
H1FALL
FALL
H2
C2
RISE
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED.
O
1
6
9
10
11
4
8
AUTO
ON
FANSWITCH
SYSTEMSWITCH
OFF
HEAT DAMPER
HEAT RELAY 1
COMPRESSORRELAY 1
HEAT RELAY 2
COMPRESSORRELAY 2
AUTO
SERVICELED (RED)
W1
G
COOL DAMPER
FAN RELAY
CONTROL MODULE
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
217 60-2485�8
Fig. 237. Schematic and hookup of T874C with Q674B. Used in standard applications.
Fig. 238. Schematic and hookup of T874C with Q674F. Used in heat pump applications.
H1
H2
FALL G
B
R
FAN RELAY
OFF
COOL
SYSTEMSWITCH
H2 ANTICIPATOR
H1 ANTICIPATOR
C1 ANTICIPATOR
AUTO
ON
FAN SWITCH
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED. M7716
THERMOSTAT SUBBASE SYSTEM COMPONENTS
3
4
6
8
10
FALL
RISE
C1
L1 (HOT)L2
1
2
1
Y
COMPRESSORCONTACTOR
W1
W2
HEAT 1
HEAT 2
HEAT
5LOW LED (YELLOW)
HI LED (GREEN)
H1
FALL
L1 (HOT)
L2 1
1
2
2
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
FACTORY INSTALLED JUMPER BETWEEN TERMINALS W1 AND Y1.
H1 ANTICIPATOR
FAN SWITCH
AUTO
ON
SYSTEM SWITCH
OFF
COOL
2
4
6
X
O
C
W1
W2
B
R
G
Y1
COOLCHANGEOVERVALVE
FAN RELAY
AUX. HT.RELAY
HEAT PUMPRELAY
M7719
C1 ANTICIPATOR
B RELAY
THERMOSTAT SUBBASE SYSTEM COMPONENTS
COMPRESSORCONTACTOR
AUX. HT.LED (RED)
H2
RISEC1
FALL
H2 ANTICIPATOR
1
8
10
2 STAGE HT.
HT. PUMP
AUX. HT.
CHECKLED (RED)
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 218
Fig. 239. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
Fig. 240. Schematic and hookup of T874A with Q674W. Used in standard applications.
L1 (HOT)
L21
1 2
2
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
FAN SWITCH
AUTO
ON
SYSTEM SWITCH
HEAT
OFF
COOL
2
3
5
11
R
O
X2
T
G
B
W
YM7744
THERMOSTAT SUBBASE SYSTEM COMPONENTS
EM. HT.
H1
H2
FALL
FALL
C1
H1ANTICIPATOR
RESET
U
F
FAN RELAY
AUX. HT.RELAY
OUTDOORTHERMOSTAT
COOLCHANGEOVER VALVE
COMPRESSORCONTACTOR
OUTDOOR SENSOR
COMPRESSORMONITOR
1
4
6
AUX. HT.LED (GREEN)
EM. HT.LED (RED)
FIELD REMOVABLE JUMPER.
L1 (HOT)
L21
1
2
2
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
FAN CONTINUOUS IN ON POSITION.
SYSTEMOFF
ON
FAN
MED
MED
HI
HI
8
10
R
G2
G1
W1
B
Y1
M7745
THERMOSTAT SUBBASE SYSTEM COMPONENTS
LO
LO
H1FALL
C1RISE
C1ANTICIPATOR
H1ANTICIPATOR HEAT
RELAY
K1 RELAY
K2 RELAY
COMPRESSORCONTACTOR
1
4
9
B RELAY L2 L1
K1 K1
K2 K2 K2
3 SPEED FAN SCHEMATIC
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
219 60-2485�8
Fig. 241. Schematic and hookup of T874J with Q674L. Used in heat pump applications.
Fig. 242. Schematic and hookup of T874G with Q674C. Used in standard applications.
RISE
L1 (HOT)
L21
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
FAN SWITCH
AUTO
ON
SYSTEM SWITCH
HEAT
OFF
COOL
2
3
4
5
6
8
9
10
11
12
R
X
E
L
C
G
W2
Y
P
O
FAN RELAY
HEAT CHANGEOVERVALVE NO. 1
HEAT CHANGEOVERVALVE NO. 1
HEAT CHANGEOVERVALVE NO. 2
HEAT CHANGEOVERVALVE NO. 2
HEAT CHANGEOVERVALVE NO. 3
M7742
THERMOSTAT SUBBASE SYSTEM COMPONENTS
COOL CHANGEOVERVALVE
SUPL. HT.
CO
H1
H2
FALL
FALL
CO
C1
RISE
COMPRESSORCONTACTOR
P RELAY
X RELAY
O.D.T.
SUPL. HEATLED (RED)
H1ANTICIPATOR
H2ANTICIPATOR
C1ANTICIPATOR
L1 (HOT)
L2 1H2 ANTICIPATOR
H1 ANTICIPATOR
C1 ANTICIPATOR
FALLH1
R
W2
W1
G
B
1
2
2
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
OVERRIDE IS MOMENTARY POSITION. SPRING RETURN TO (OFF)UPON SWITCH RELEASE.
AUTO
ON
FANSWITCH
SYSTEMSWITCH
AUTO
OVERRIDE
OFF
RISE
C1
C0
FALL
RISE
H2
Y
O
S1
S2
X
A
C
HEAT DAMPER
HEAT RELAY 1
FAN RELAYHEAT RELAY 2
OVERRIDECIRCUIT
OVERRIDECIRCUIT
CHANGEOVER VALVE
COMPRESSORRELAY
SERVICELED (RED)
ON LED (YEL)
M7212
1
4
6
8
9
10
THERMOSTAT SUBBASE SYSTEM COMPONENTS
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 220
Fig. 243. Schematic and hookup of T874G with Q674F. Used in heat pump applications.
Fig. 244. Schematic and hookup of T874J with Q674J. Used in heat pump applications.
H1
FALL
RISE
CO
L1 (HOT)
L2
1
C1
RISE1
2
2
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
TERMINAL LABELED C/X ON SOME MODELS.
C1 ANTICIPATOR
H1 ANTICIPATOR FAN SWITCH
AUTO
ON
SYSTEM SWITCH
AUTO
HEAT
OFF
COOL
1
2
4
6
8
9
10
O
W2
X
E
L
B
R
G
Y
AUX. HEAT RELAY
FAN RELAY
EM. HT. RELAY
B RELAY
M7715
THERMOSTAT SUBBASE SYSTEM COMPONENTS
11
12
COMPRESSORCONTACTOR
EM. HT.
EM. HT.LED (RED)
AUX. HEATLED (GREEN)
COOL CHANGEOVER VALVE
H2
FALL
H2 ANTICIPATOR
RISE
L1 (HOT)
L21
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
FAN SWITCH
AUTO
ON
SYSTEM SWITCH
ON
OFF
2
3
4
5
6
8
9
10
11
12
R
X
E
L
C
G
W2
Y
P
O
FAN RELAY
HEAT CHANGEOVERVALVE NO. 1
HEAT CHANGEOVERVALVE NO. 1
HEAT CHANGEOVERVALVE NO. 2
HEAT CHANGEOVERVALVE NO. 2
HEAT CHANGEOVERVALVE NO. 3
M7743
THERMOSTAT SUBBASE SYSTEM COMPONENTS
COOL CHANGEOVERVALVE
SUPL. HT.CO
H1
H2
FALL
FALL
CO
C1
RISE
COMPRESSORCONTACTOR
P RELAY
X RELAY
O.D.T.
SUPL. HEATLED (RED)
H1ANTICIPATOR
H2ANTICIPATOR
C1ANTICIPATOR
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
221 60-2485�8
Fig. 245. Schematic and hookup of T874R with Q674L. Used in heat pump applications.
Fig. 246. Schematic and hookup of T874C with Q674G. Used in standard applications.
H1
FALL
L1 (HOT)
L2
1
1
2
2
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
TERMINAL LABELED C/X ON SOME MODELS.
H1/C1 ANTICIPATOR
FAN SWITCH
AUTO
ON
SYSTEM SWITCH
HEAT
OFF
COOL
2
3
4
6
O
W2
X
E
L
B
R
G
Y
AUX. HT. RELAY
FAN RELAY
EM. HT. RELAY
B RELAY
M7718
THERMOSTAT SUBBASE SYSTEM COMPONENTS
COMPRESSORCONTACTOR
EM. HT.
EM. HT.LED (RED)
AUX. HT.LED (GREEN)
COOL CHANGEOVER VALVE
H2
C1FALL
H2 ANTICIPATOR
W2
W1
HEAT RELAY 1
OFF
AUTO
SYSTEMSWITCH
1 M7717
THERMOSTAT SUBBASE SYSTEM COMPONENTS
L1 (HOT)
L2
1
Y2
HEAT RELAY 2
RH
RC
Y1
COOL CHANGEOVER VALVE
L1 (HOT)
L2
1
H1 ANTICIPATOR
H2 ANTICIPATOR
C1 RISE
H1FALL
FALLH2
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOADPROTECTION AS REQUIRED.
NO FANSWITCH
1
4
6
8
10
11
9
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
60-2485�8 222
Fig. 247. Schematic and hookup of T874W with Q674L. Used in heat pump applications.
1
T
W3
G
R
E
X1
C
B
O
X2
Y1
Y2
C815A OUTDOOR THERMISTOR
AUX. HT. RELAY
FAN RELAY
EM. HT. RELAY
CHANGEOVERRELAY (HEAT)
CHANGEOVERRELAY (COOL)
COMPRESSORCONTACTOR 1
COMPRESSORCONTACTOR 2
EM.HT.
AUTO
ON
FAN SWITCH
H1 ANTICIPATOR
H2 ANTICIPATOR
H3 ANTICIPATOR
RESET
FALL
FALL
FALL
H1
H3
H2
AUX. HEATLED (GREEN)
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
CONNECT CHANGEOVER RELAY TO 'O' TERMINAL FOR CHANGEOVER IN COOLING OR TO 'B' TERMINAL FOR CHANGEOVER IN HEATING. M6999
C1 ANTICIPATOR
RISE
RISEC2 ANTICIPATOR
C1
C2
EM. HEATLED (RED)
CHECK LED(YELLOW)
HEAT
OFF
COOL
SYSTEMSWITCH
2
2
THERMOSTAT SUBBASE SYSTEM COMPONENTS
1
2
3
4
5
6
8
9
10
11
12
L1 (HOT)L2
1
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
223 60-2485�8
Fig. 248. Schematic and hookup of T874Y with Q674F. Used in heat pump applications.
M5923
L1 (HOT)
L2
1
C
E
R
FAN RELAY
COMPRESSORCONTACTOR 2
EM.HT. RELAYMALFUNCTIONLED (RED)
LOW SPEEDLED (GREEN)
SYSTEMSWITCH
HEAT
AUTO
COOL
C2
RISE
H1 FALL
2
3
4
8
H1 ANTICIPATOR
1 POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
THERMOSTAT SUBBASE SYSTEM COMPONENTS
Y2
Y1
OFF
COMPRESSORCONTACTOR 1
CO
RISE
9
10
11
C2ANTICIPATOR
C1ANTICIPATOR
L
G
HIGH SPEEDLED (YELLOW)
5
OCOOL CHANGEOVER VALVE
AUX. HT. RELAY
W2
AUX. HT.LED (RED)
7
RISEC1
EM. HT.
FAN SWITCH
ON
AUTO
H2
FALL
H2 ANTICIPATOR
60-2485�8 J.H. Rev. 3-01 www.honeywell.com
Home and Building Control Home and Building ControlHoneywell Honeywell Limited-Honeywell Limitée1985 Douglas Drive North 35 Dynamic DriveGolden Valley, MN 55422 Scarborough, Ontario
M1V 4Z9
Printed in U.S.A. on recycled paper containing at least 10% post-consumer paper fibers.
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
Fig. 249. Schematic and hookup of T874C with Q674B. Used in heat pump applications.
C2
RISE
L1 (HOT)L2
1
C1
RISE
H2
FALL
H1
FALL
M18622
H1 ANTICIPATOR
H2 ANTICIPATOR
C1 ANTICIPATOR
C2 ANTICIPATOR
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND OVERLOAD PROTECTION AS REQUIRED.
FIELD WIRE JUMPER TO ALLOW SINGLE SYSTEM TRANSFORMER.
1
2
1
3
4
6
8
9
10
11 Y2
Y1
O
RH
B
W2
RC
G
W1
2
SYSTEMSWITCH
HEAT
OFF
COOL
ON
AUTO
FANSWITCH
HEAT RELAY 1
FAN RELAY
HEAT RELAY 2
HEAT DAMPER
COOL DAMPER
COMPRESSOR CONTACTOR 1
COMPRESSOR CONTACTOR 2
THERMOSTAT SUBBASE SYSTEM COMPONENTS
SERVICELED (RED)
C
X