Harmonic Distortion Problems in Current Distribution Systems 1 APIC Power & Energy Innovation Forum ATCO experiences by Case Muskens Epcor experiences by Isabella Ciocoiu FortisAlberta experiences by Gordon McKinlay Telus experiences by Dwayne Schultz U of A research findings by Wilsun Xu APIC 2011 Power & Energy Innovation Forum APIC 2011 Harmonic Load Growth in ATCO Electric POD Substations by Case Muskens

Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

Embed Size (px)

Citation preview

Page 1: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

Harmonic Distortion Problems in Current Distribution Systems

1APIC Power & Energy Innovation Forum

ATCO experiences by Case Muskens

Epcor experiences by Isabella Ciocoiu

FortisAlberta experiences by Gordon McKinlay

Telus experiences by Dwayne Schultz

U of A research findings by Wilsun Xu

APIC 2011 Power & Energy Innovation Forum

APIC 2011

Harmonic Load Growth in ATCO Electric POD Substations

by Case Muskens

Page 2: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

APIC 2011

Overview:

PurposeMeasurement IEEE 1459Result SummariesConclusions

APIC 2011

Purpose:

• Establish trending of harmonic load growth in the AE system

• Evaluate different measurement methods discussed in IEEE 1459

• Future implications

Page 3: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

APIC 2011

Project Description:

� 6 substations monitored in 2004� Repeat measurements in 2011 at same substations� Review changes

APIC 2011

Measurement Methodology

The ION meter captures hourly RMS values of load, %THDV, %THDI at the main substation transformer

One second waveform snapshots were recorded during the measurement time and processed per IEEE 1459 power definitions

Page 4: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

APIC 2011

IEEE Std 1459 – 2000 : IEEE Standard Definitions for the Measurement of Electric Power Quantities Under Sinusoidal, Non Sinusoidal, Balanced or Unbalanced Conditions

A brief overview of this standard is now provided

APIC 2011

VIS =

vip =

∫+

=kT

pdtkT

τ

1

Power Definitions Single Phase IEEE 1459

Apparent Power

Instantaneous Power

Active Power

Power FactorS

PPF =

Page 5: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

APIC 2011

21

22 VVVH −=

21

22 IIIH −=

1V

VTHD H

V =

Harmonic Voltage

Harmonic Current

THDV

THDI1I

ITHD H

I =

APIC 2011

The apparent power :

Fundamental effective power:

Non fundamental effective power:

eee IVS ⋅= 3

111 3 eee IVS ⋅=21

22eeeN SSS −=

18

)(3 222222cabcabcba

e

VVVVVVV

+++++=3

2222ncba

e

IIIII

+++=

where

Power definition for 3 phase systems

Page 6: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

APIC 2011

Substations Land Location Load type

Flyingshot 702T Grande Prairie MixedHangingstone 701T Ft. McMurray MixedMichichi 703T Drumheller MixedHigh Level 701T High Level MixedNorcen 701T Red Earth OilfieldBrintnell 901T Wabasca Oilfield

Mixed refers to residential + commercial with some light industrial

APIC 2011

High Level Brintnell Flyingshot 2004 2011 2004 2011 2004 2011

THDi% 7.136 5.462 2.56 4.446 5.43 4.856 THDei% 11.96 9.24 2.76 5.04 8.58 8.32 SeN KVA 466 411 590 679 1484 2004 SeN/Se1 % 11.96 9.7 3.05 5.317 8.67 8.4 THDv% 1.61 0.896 1.226 1.703 1.4 1.4 THDev% 0.88 1.698 1.18

Page 7: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

APIC 2011

Norcen Hangingstone Michichi 2004 2011 2004 2011 2004 2011

THDi% 2.3 1.37 4.73 6.31 3.32 3.758 THDei% 2.38 1.92 8.32 10.95 4.59 5.174 SeN KVA 267 185 1046 1796 711 1113 SeN/Se1 % 2.91 2.136 9 11 4.65 5.5 THDv% 1.673 0.945 3.436 1.763 0.81 1.911 THDev% 0.95 1.38 1.877

APIC 2011

0 2 4 6 8 10 120

2

4

6

8

10

12Substation Distortion Summary: THDI vs. Harmonic Pollution Ratio

THDI%

SeN

/Se1

%

20042011

Norcen

Brintnell

Michichi

Flyingshot

Hangingstone

Highlevel

Page 8: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

APIC 2011

0 2 4 6 8 10 120

2

4

6

8

10

12Substation Distortion Level: Measured vs. IEEE 1459 Effective Value

THDI%

TH

DIe

%

2004

2011

Norcen

Brintnell

Michichi

FlyingshotHangingstone

Highlevel

APIC 2011

1 2 3 4 5 6 7 80

500

1000

1500

2000

2500Substation Distortion Summary: THDI vs. Pod Nonlinear load

THDI%

SeN

KV

A

2004

2011

Norcen

Brintnell

Highlevel

HangingstoneMichichi

Flyingshot

Page 9: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

APIC 2011

Hangingstone has had a 5 Mvar 5th harmonic filter added after 2004 which reduced VTHD but with increased ITHD due to harmonic in feed from 144 kV system.

High Level has had an SVC installed on the 144 kV bus along with an extra line to Sulphur Point substation after 2004, SCR has improved.

Brintnell had a pseudo 12 pulse cancellation scheme (mixed Dy and Yy transformers) with the original pad site loads, but the 5th harmonic has been increasing suggesting reduced effectiveness with new loads

APIC 2011

0 0.5 1 1.5 2 2.5 3 3.5 4 4.5 50

1

2

3

4

5

6

7

8

9

10High Level Substation 701T History Start date Sept 8, 2004/2011 4:00 PM

days

%TH

D o

r M

VA

%THDI phs 2 2004

%THDV phs 2 2004

MVA Loading 2004%THDI phs 2 2011

%THDV phs 2 2011MVA Loading 2011

Page 10: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

APIC 2011

0 1 2 3 4 5 6 7 8 9 10 110

5

10

15

20

25Hangingstone Substation 701T History Start date Sept 1, 2004/2011 6:00 PM

days

%T

HD

or M

VA

%THDI phs 2 2004%THDV phs 2 2004

MVA Loading 2004

%THDI phs 2 2011

%THDV phs 2 2011MVA Loading 2011

APIC 2011

0 0.5 1 1.5 2 2.5 3 3.5 40

5

10

15

20

25

30

Brintnell Substation 901T(2004) and 902T(2011)History Start date Sept 10, 2004/2011 6:00 AM

days

%T

HD

or

MV

A

%THDI phs 2 2004

%THDV phs 2 2004

MVA Loading 2004%THDI phs 2 2011

%THDV phs 2 2011

MVA Loading 2011

Page 11: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

APIC 2011

Conclusions:� Despite a load increase at Flyingshot, the harmonic

pollution ratio (%SeN/Se1) has remained nearly constant� Hangingstone, Brintnell, and Michichi have seen

increases in the harmonic pollution ratio� High Level and Norcen have seen reductions in the

harmonic pollution ratio� Harmonic pollution ratio is nearly equivalent to THDIe%� The THDIe% is a better indicator than THDI% of actual

harmonic load penetration

Telephone Interference Epcor’s cases

by Isabella Ciocoiu

Page 12: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

Contributing Factors:

• 9th (main contributor) and 15th harmonics produced by small, single phase, electronic, residential loads;

• Position of the telephone cable to the power lines (they run in parallel);

• Length of the parallel path (3 or more miles);

• Strength of the magnetic field.

2005-2006Telephone Interference on

Ellerslie Road

Page 13: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

12EEast Industrial

17 St34 St

50 St66 St101 St

23 E25P

Ellerslie Road

17 St34 St

Telus telephone line

-2005 April: I*T=5300-2005 November: I*T=3000-2006 March: I*T=2600-2006 April: I*T=1800-2006 December: I*T=1000

Noise complaints

Telus cabinet

75 St

91 St

53003000

What Epcor did on its circuits:

• 1. Balanced loads on 3 phase circuits. • 2. Fixed several broken neutral connections.• 3. Installed more grounds. • 4. Conducted a trial at the substation

transformers, adjusting the taps to increase the bus voltage (25kV to 25.8 kV): eliminated the suspicion that saturated transformers are the cause of harmonic currents.

• 5. Reduced the load on 23E by transferring about half of the load to another circuit.

Page 14: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

2006-2010Telephone Interference on

41Ave

12E (20MVA)

East Industrial

17 St34 St

50 St66 St101 St

23 E (17.5 MVA)

25P

Ellerslie Road

Telus telephone line

-2006 Dec: I*T=1000-2007 March: I*T=1800-2009 Sept: I*T=2300-2010 July: VAC=105V

Noise complaints

Telus cabinet

75 St

91 St

Dec 2006 -7 Sept 2010

Measured induced voltage

41 AveI*T levels

Page 15: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

12E (1.1 MVA)

East Industrial

Summerside

103 GI

17 St34 St101 St

91 St 66 St 50 St

21SU (3.46 MVA)

11SU (11.67 MVA)

12SU (2.16 MVA)

7 September 2010 - 5 November 2010

104 GI

23E (2.4 MVA)

Telus telephone line

Telus cabinet

Noise complaints

75 St

Ellerslie Road

41 Avenue

-2010 Sept 17: I*T=3600

I*T levels

12E

East Industrial

Summerside 103 GI

17 St34 St101 St

91 St 66 St 50 St

21SU

11SU

12SU

5 November 2010 - 24 November 2010

104 GI

23E

Telus telephone line

Telus cabinet

Noise complaints

75 St

Ellerslie Road

41 Avenue

4546S

-2010 Nov 19: I*T=3500

I*T levels

Page 16: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

12E

East Industrial

Summerside

17 St34 St101 St

91 St 66 St 50 St

21SU

11SU

12SU

After 24 November 2010

104 GI

23E

Telus telephone line

Telus cabinet

Noise complaints

75 St

Ellerslie Road

41 Avenue

4546S

-2010 Nov 29: I*T=5000

93 GII*T levels

What Epcor did:• Approached APIC for technical support in

investigating the telephone interference problem;

• Provided distribution system models and facilitated field measurements.

Page 17: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

Harmonic Issues in FortisAlberta Service Area

by Gordon McKinlay

1. Trends in Harmonic Distortion in FortisAlberta Service

Territory

2. FortisAlberta Pro-Active Harmonic Standards Adopted

3. Telephone Interference

4. Power Line Carrier Automated Meter Reading System

5. IEC Standards for Residential Equipment

Presentation Format

Page 18: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

Tracking Harmonics

�At metering commissioning , harmonic voltage distortion is

sampled

� If VTHD > = 10% at the PCC was designated as a “Worst Harmonic Feeder”.

�Compiled Our Telephone Interference Records

� If a feeder has a history of telephone interference which was mitigated via

insulating telephone lines and not reducing harmonics on lines then it was

added to “Worst Harmonic Feeder” list.

APIC Harmonic Trends

APIC Harmonic Trends

VTHD10%

VTHD & TELUS10%

Normal80%

FortisAlberta Worst Harmonic Feeders

Page 19: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

Passive Approach

�FortisAlberta for many years required customers to meet IEEE 519, but did

not enforce these limits until a problem showed up

Pro-Active Approach

�Requires the customer to meet design compliance before energization.

�We do not actively pursue compliance to pre-pro-active approach customer,

unless they do create a problem.

APIC Standards

Water, Gas and Electric Companies Act

�Requires TELUS approval before jobs can go through, TELUS less likely to

allow jobs to get approval if there might be or is existing telephone issues.

APIC Telephone Interference

Page 20: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

Utility Office

Substation

Service Sites

Wide Area Network (WAN)

Upstream PLC Communication (20

minutes per bit)

Downstream PLC Communication (200

ms per bit or 5 baud)

Fiber Optic Cable

APIC AMR

APIC AMR Spectrum Noise

Page 21: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

APIC Residential Loads

APIC Harmonic Trends

Zero Sequence from Residential

�We are seeing as symptom of the proliferation of harmonics on residential

feeders an increase in zero sequence caused telephone interference.

�The majority of telephone interference problems we currently have are caused

by zero sequence current.

�This has caused us to adopt new standards such as a multi-grounded neutral

on all new construction.

Page 22: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

APIC Residential Standards

FortisAlberta Involvement in Standard Adoptions

�Members of the CSA Technical Committee on Electromagnetic

compatibility (EMC) and are trying to get CSA to adopt low voltage

standards

� IEC 61000-3-2 (≤16 A per phase) and IEC 61000-3-12 (>16 A and ≤ 75 A

per phase )

�These IEC standards ask the manufacturers of electronic equipment

commonly installed in homes, such as TV’s, Lights, Computers, etc. to

meet certain harmonic limits.

Power Induction on Communication Cables

- Telus Experiences

by Dwayne Schultz

Page 23: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

Power Induction on Communication Cables� Very common problem, especially in rural areas where long parallels

between power lines and communication cables exist.

� Power induction results in audible noise (hum or buzz) for telephone users due to harmonics that fall within the voice frequency band (300 Hz to 4000 Hz)

� Induction also affects data transmission, (E.g. data circuits, modems, fax machines)

� Excessive 60 Hz induction levels can cause errors or failure of T1 copper carriers (PCM, HDSL)

� Problems may be steady state or transient in nature.

� Most often problems are related to distribution power lines but occasionally transmission lines can be a source of problem.

� Problems are becoming more prevalent as non-linear power loads increase

Magnetic Field Induction

Page 24: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

Probe Wire Measurement

Power Line Probe Wire I*T Levels

� Probe Wire I*T = Ir X TIF

� I*T is a weighted value of the residual current multiplied by the Telephone Influence Factor

� Ir = residual current is the vector sum of the currents in all phases and neutral conductor at a point on the power system

� I*T can be evaluated directly using 100 foot probe wire measurements taken under power line with specialized test sets (E.g. Triplett – Mitigator)

� Depending on length and separation between systems:� I*T > 500-1000 may cause problems on communication cables � I*T >1000 is likely to cause problems on communication cables

Page 25: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

C Message Weighting Curve

Telephone Interference Factor

0 50003000 400020001000

5000

10000

F re q u e n c y in H e rtz

TIF

(W f)

Telephone Influence FactorCurve

� Telephone Interference Factor (TIF) is a weighting factor that reflects the C message filter and the higher mutual coupling factor which increases at higher frequencies

Page 26: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

Industry Guidelines

� CSA C22.3 No. 3 - Electrical Coordination� Provides Guideline for resolving interference

between power and telecommunication systems (uses I*T levels)

� IEEE 776 – Inductive Coordination� Provides guidelines based on specific levels of

individual harmonics rather than overall I*T levels

� IEEE 519 – Harmonic Control In Power Systems� Provides guidelines for Voltage and Current total

harmonic distortion (THD) and I*T on the power system as well as individual load components

� Power loads may meet the THD requirements of IEEE 519, and still be the prime cause of noise due to high residual I*T level

Effect of the Power Multi-Grounded Neutral

� Current returned in the earth does not provide magnetic cancellation (E.g. Earth return Power systems)

� Since neutral current is 180 degrees out of phase with phase currents it serves to reduce the residual I*T

� Typically the current on the neutral conductor will be 30 to 40% of the total return current on a wye connected power system

� Current on the neutral conductor will be higher near the load and increase as the substation is approached.

Page 27: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

Induction Neutralizing Transformers� Neutralizing transformers can be used to reduce induced

voltage as well as noise on communication cables

� INT's consist of telephone wire pairs wrapped around a laminated iron core and this present a high impedance to longitudinal currents

Induction Neutralizing Transformer

Page 28: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

Placing an INT� INT’s are most effective when all pairs in the cable

are being treated

� Use a Digital INT if there are digital carrier circuits in the cable being treated

� For voltage reduction place INT at a point where induced voltage is half the total

� For noise reduction, the INT must be placed at a point before the circuit noise (Nm) has become too high. E.g. 15 to 17 dBrnC.

� INT’s are most effective for treating harmonics below the 15th Harmonic (900 Hz).

� Depending on location and harmonic content, a reduction of 10 - 25 dBrnC Ng can be expected.

Power Induction Problems 2005-2011

ATCOAlix, Bonneville, Castor, ,Hythe , Stettler, Debolt, Elk Point, Forestburg, Fort McMurray, Galahad, Girouxville, Grande Prairie, Grande Cache, Hardisty, High Prairie, Kitscoty, Oyen,Valleyview

FORTISAcme, Alder Flats, Ardrossan, Bassano, Beaumont, Blue Ridge, Bruderheim, Calmar, Camrose, Chauvin , Chestemere, Cochrane, Czar, Drayton Valley, Edgerton, Entwistle, Fort Assiniboine, Gleichen, Glenwood, Hardisty, Hobbema, Irma, Innisfail Mountain view, Nanton, Olds, Onoway, Pincher Creek, Patricia, Provost, Rimbey, Sedgewick, Stavely, Strathmore, Sundre, Suffield, Sylvan Lake, Taber, Vauxhall, Walsh, Wainwright, Wetaskiwin

Red Deer ElectricHwy 11A

EPCOR41st Ave SW, Ellerslie Road

ENMAXKingsland, Ogden(Capacitor Bank Switching)

Page 29: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

APIC 2011 Power & Energy Innovation Forum

U of A Research Findings

University of Alberta

• What is happening in current distribution systems?

• Key research findings

• What needs to be done to manage the situation?

by Wilsun Xu

1. What is happening?

University of Alberta

10 to 15 years ago

• Industrial customers are the main harmonic producers• Interconnection standards have been established to limit harmonics from them• Such loads inject little harmonics into power system nowadays

Utility system

Harmonics filters

Linear & nonlinear loads

Iharmonics

Utilities have establishedlimits on Iharmonicsflowing intotheir systems at the PCCPCC – point of common coupling

Ih<Ilimit

A standard design practices

Page 30: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

1. What is happening?

University of Alberta

At present

• More and more home appliances are becoming harmonic sources• Although insignificant individually, their collective impact can be big• Blocks of residential loads have become main harmonic sources

-4

-3

-2

-1

0

1

2

3

4

0 100 200 300 400 500 600

Time step

Cu

rre

nt

[A]

PC 1

PC 3

PC 2

-25

-20

-15

-10

-5

0

5

10

15

20

0 100 200 300 400 500 600

Time step

Cu

rre

nt

[A]

MW 1 on

MW 1 off

MW 2 on

MW 2 off

Desktop PC Microwave

- 1

-0 .8

-0 .6

-0 .4

-0 .2

0

0 .2

0 .4

0 .6

0 .8

1

0 1 0 0 2 0 0 3 0 0 4 0 0 5 0 0 6 0 0

CFL

- 8

- 6

- 4

- 2

0

2

4

6

8

0 1 0 0 2 0 0 3 0 0 4 0 0 5 0 0 6 0 0

T i m e S t e p

Cu

rre

nt

[A]

F i llin g W at er

W a sh i n g

R in s in g

R in s in g o ff

S p in n i n g

F a s t S p in n in g

Washer

1. What is happening?

University of Alberta

Typical spectra of a service transformer load SUB

One neighborhood with 100 servicetransformers (70A)

“PCC”

0

2

4

6

8

10

12

3rd 5th 7th 9th 11th 13th 15th Total

Harmonic order

Cu

rre

nt

Dis

tort

ion

(ID

D, %

)

Residential feeder

Total load of the sample neighborhood is about 3MW. For this block of loads

• The harmonic current at the “PCC” would exceed the limits • The telephone interference level would be close to 1000A, >> 500A limit

Additional Challenges: • The presence of 3rd and 9th harmonics (zero sequence)• No single entity is responsible for it• So utilities “own” the problem

Comparison

Page 31: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

2. Key research findings

University of Alberta

• We have done extensive measurements in Edmonton with the help of Epcor• We also conducted field measurements near Beaverlodge (Goodfare sub) with the help of ATCO

IT Index measured at the substation locations

• The design limit for industrial customers is 500!• 4000 is the level where Telus is likely to receive complaints

Telephone interference

University of Alberta

0 2 4 6 8 10 12 140

1000

2000

3000

4000

5000

6000

7000

8000

Power(MW)

IT

12E 2008 23E

M-T1

M-T2

M-T3

P-T1-B1

P-T1-B2

P-T2-B7P-T2-B8

CD-T1-B2

CD-T2-B8

5L4056

21SU

11SU

12SU12E 2011

Simulation: An ideal feeder (loads distributed)Simulation: An ideal feeder (loads concentrated in one location)Simulation: 21SU feederMeasurement results for different feeders

Pow

er I

T L

evel

• The results confirm that the high IT level encountered in today’s distribution system is actually expected and is not caused by some unique feeder conditions.

• All residential feeders with regular load levels are likely to exhibit high IT levels.

Telephone interference2. Key research findings

Page 32: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

University of Alberta

Other concerns

• High harmonic voltage and current levels in both primary & secondary systems

• Overloading of service transformer

• Neutral current in the primary feeder

• Penetration of harmonic currents into the transmission system

• Revenue meter errors (potential concern)

• Resonance caused capacitor/cable failure (potential concern)

0.00%1.00%2.00%3.00%4.00%5.00%6.00%7.00%8.00%9.00%

2011 2012 2013 2014 2015

Year

Annual Growth Rate = 15.30%

Voltage THD

12 am2 am 4 am6 am8 am10 am12 pm2 pm4 pm6 pm8 pm10 pm12 am50

100

150

200

250

300

350

Hours

3rd

Vo

ltag

e C

om

po

nent

(V)

SatSun

3rd Harmonic Voltageat a 138kV Bus

2. Key research findings

University of Alberta

3. What needs to be done?

Residential feeders nowadays consists of multiple blocks of “limit-exceeding” loads

SUB

A neighborhood with 100 servicetransformers (70A)

“PCC”

Neighborhood X

Neighborhood YSUB

A neighborhood with 100 servicetransformers (70A)

“PCC”

Neighborhood X

Neighborhood Y

• Ignoring the situation is not a solution. It is also not fair for other types of customers

• One potential solution is to adopt the IEC device level limits (IEC 61000-3-2)

• Another solution is to install filters in the primary feeders

• Other solutions such as distributed filters may also be possible

Filter Filter

Page 33: Harmonic Distortion Problems in Current Distribution Systemsapic/uploads/Forum/Harmonic distortion... · Harmonic Distortion Problems in Current Distribution Systems APIC Power &

4. Conclusions

University of Alberta

• Clusters of residential homes can inject into distribution systems harmonic currents that exceed the limits established for individual industrial customers of comparable MW sizes.

• High telephone interference levels & high level of harmonic penetrations into transmission systems are becoming a new reality

• There are no easy solutions and quick fixes to the problem due to the distributed nature of the harmonic producers

• Utilities shall work together to impose device level limits like what has been done in Europe

• Feeder level harmonic filtering may become a general distribution system design practice in the future